HI All,

I thought I’d share some details from OB that I got the other day.  

Maybe some or most of you know this but I didn’t.

1. there are 3 blue pots at the bottom of the controller.  The lowest one is 
voltage adjustment.  
Set the calibration to 0, then adjust with that pot.  It leaves the factory 
unadjusted if it’s within 1v, which I presume is at 48v.  

2. If you have a VMP which is close to battery voltage.  It turns out VMP has 
to be 12v above battery volt for the MPPT to work.  
And that voltage isn’t what you measure at the terminals but inside, so it 
could be more or less. 

3. To help with #2 you can adjust the snooze mode amps down from .6 to .2 which 
by chance they found out it helps.  And no they don’t actually know why.