HI Kent,

Thanks for that info.  
Makes sense

jay

> On Jan 19, 2025, at 12:47 PM, Kent via RE-wrenches 
> <[email protected]> wrote:
> 
> Jay,
> 
> If there is a PV ground fault, putting a short across the fuse holder may 
> cause damage by drawing an arc. Use a multimeter to measure voltage across 
> the fuse holder (should be the same as measuring voltage between PV negative 
> and ground); if there is no voltage then there probably isn't a PV ground 
> fault or any ground fault at that time. If there is voltage, then you need to 
> track it down. It isn't necessarily in the PV array - it could be a dc load 
> or even in the battery. If the voltage exceeds the battery voltage, the PV 
> array is the culprit. If you compute the proportion of the negative to ground 
> voltage to open circuit voltage then apply that proportion to the number of 
> modules, it should tell you about where to look. If you have multiple 
> strings, isolate the problem: disconnect all of the PV negative connections 
> and see which one gives you a solid voltage to ground. 
> 
> Kent Osterberg
> Blue Mountain Solar
> 
> 
> On 1/19/2025 6:57 AM, Jay via RE-wrenches wrote:
>> Question about the fuses. 
>> 
>> For testing could you put a short test wire across the ends of the fuse 
>> holder and use a clamp on to test for current? Would it cause any damage?
>> 
>> Instead of potentially going through lots of fuses?  
>> 
>> Jay
>> 
>> 
>> 
>>> On Jan 19, 2025, at 7:48 AM, Mac Lewis via RE-wrenches 
>>> <[email protected]> 
>>> <mailto:[email protected]> wrote:
>>> 
>>> 
>>> Hello Dana,
>>> 
>>> Ground faults are tricky.  Here is how I would tackle this on a sunny day:
>>> 1.  Visual inspection of array, looking for backsheet, wire damage, broken 
>>> glass, critter stuff (nests and bite marks).  Look for water intrusion or 
>>> evidence that water has been somewhere that it shouldn't.
>>> 2.  Visual inspection of all splice boxes, checking for wire insulation 
>>> damage, evidence of water intrusion and critter entry.
>>> 3.  Probe voltage between +, - and Ground (do this at a string level 
>>> initially, and isolate strings and do this at open circuit).  Any evidence 
>>> of bouncing voltage readings, loss of voltage, not rock solid voltage 
>>> suggests you may have a ground fault in that string.  If its in the string 
>>> somewhere, you may see the voltage bounce and read in some fraction of the 
>>> string voltage.  This can tell you where in the string it may be.  FOr 
>>> example, if you have a 5 module string, you may get a 3/5 voltage reading 
>>> if the fault is near the 3rd module.
>>> 4.  Turn off array at combiner and run continuity tests between +, - and 
>>> Ground again (no gfp fuse).  If you have continuity, this may suggest a 
>>> ground fault in conduit run between combiner and FM100.
>>> 
>>> Good Luck, bring extra fuses!
>>> 
>>> On Sun, Jan 19, 2025 at 7:07 AM Dana Orzel via RE-wrenches 
>>> <[email protected] 
>>> <mailto:[email protected]>> wrote:
>>>> Yes I have 2 FM100s
>>>> Dana Orzel
>>>> C: 208.721.7003
>>>> E- [email protected] <mailto:[email protected]>
>>>> 
>>>>> On Jan 18, 2025, at 7:08 PM, Kirpal Khalsa via RE-wrenches 
>>>>> <[email protected] 
>>>>> <mailto:[email protected]>> wrote:
>>>>> 
>>>>> 
>>>>> Dana...
>>>>> Do you have multiple FM 100s? If so only one should have the GFI fuse. 
>>>>> Broken panel with water getting into glass?
>>>>> Turn it off and wait 5 min and turn it on.  Usually clears it especially 
>>>>> if it's a faulty nuisance trip. 
>>>>> Have had numerous FM 100s give faulty afci errors.  Removing the.afci 
>>>>> boards always resolved this issue.  But of course check all you 
>>>>> connections leading to and from the cc.
>>>>> Keep a few extra 1A gfi fuses handy....you may need a couple to test it 
>>>>> all out. 
>>>>> Keep us posted. 
>>>>> Good luck
>>>>> Kirpal
>>>>> 
>>>>> 
>>>>> On Sat, Jan 18, 2025, 2:40 PM Dana Orzel via RE-wrenches 
>>>>> <[email protected] 
>>>>> <mailto:[email protected]>> wrote:
>>>>>> Hey, all you wise ones,
>>>>>> 37 years in the business and I’ve never had a ground fault ever in any 
>>>>>> installation I’ve done or my home systems. I went out to my system here 
>>>>>> an hour ago and one FM 100 is completely turned off claiming ground 
>>>>>> fault on the mate 3S.
>>>>>> I guess my first question is :
>>>>>> 
>>>>>> Is this really a ground fault ?
>>>>>> 
>>>>>> I had removed the ground fault breaker when I upgraded due to space 
>>>>>> considerations
>>>>>> 
>>>>>> In my entire time in this business, I’ve never had to deal with the 
>>>>>> ground fault any suggestions on how I should be tracing this?
>>>>>> 
>>>>>> Has anybody seen this in an FM 100 when it wasn’t a ground fault?
>>>>>> 
>>>>>> I do own a megger&  I’ve never had to use it. I only bought it about 
>>>>>> three months ago cause it seemed like a good idea and I might need to 
>>>>>> use one someday, Maybe I’m psychic ?
>>>>>> now if I could just figure out how to trace this out.
>>>>>> All suggestions welcome thanks all!
>>>>>> 
>>>>>> Dana Orzel
>>>>>> C: 208.721.7003
>>>>>> E- [email protected] <mailto:[email protected]>
>>>>>> _______________________________________________
>>>> 
>>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other: