The only thing I could find in the whole system that was not up to snuff
was incomplete separation of neutrals and grounds in the sub-panel.  In
other words more than one ground to neutral bond. But the fact remains that
this
system worked flawlessly for 26 years!  I also removed the ground wire from
the transformer but still no difference. What am I missing?

On Thu, Jan 23, 2025 at 10:35 PM John Blittersdorf <
[email protected]> wrote:

> Steve,  I took my scope meter today and checked wave forms at all points.
> All were clean sine waves. I checked the breaker connections and all
> connections back to the inverter and all were tight.
> Voltage drop when pump kicked on was small and only about 1 volt when
> running. Amp were 12 on both legs.
>
> On Thu, Jan 23, 2025 at 9:48 AM Jay via RE-wrenches <
> [email protected]> wrote:
>
>> Are the amps leg the same?
>> Jay
>>
>> On Jan 22, 2025, at 9:29 PM, Steve Higgins via RE-wrenches <
>> [email protected]> wrote:
>>
>> 
>> How do their clocks run?   Is the Xfmer quiet down when the generator
>> runs?
>>
>> If you have an O-scope, check the output waveform off the inverter. My
>> guess is that the output waveform will be deformed, causing extra noise for
>> the Xfmer. You might be able to see this on the frequency as well. It
>> should be solid at 60Hz, but if it's drifting or way off the high side,
>> FETS have probably failed.
>>
>> If you pull the top cover off the inverter the and you look at the FET
>> board, it'll be the fets closest to the Fan on the AC board.
>>
>>
>> <image.png>
>>
>> Steve Higgins
>>
>>
>>
>>
>> On Wed, Jan 22, 2025 at 7:32 PM John Blittersdorf via RE-wrenches <
>> [email protected]> wrote:
>>
>>> Christopher,
>>> Update on the Transformer Humming.  Installed a new PSX-240 from Kirk
>>> and it is LOUDER than the T-240 that I took out.
>>> I have a call into the well driller to see if they have a record of the
>>> pump size or other details. When connected
>>> directly to the grid via transfer switch, still loud noise... same with
>>> battery only.  I did not check the 120VAC 30 amp break
>>> in the backed up loads sub panel. All other wiring was redone as I
>>> switched the pump directly to the grid until I received the
>>> new transformer and back to the inverter again. so all the connections
>>> were redone except the 120 breaker.
>>>
>>> John
>>>
>>>
>>> On Wed, Jan 22, 2025 at 10:30 AM Howie Michaelson via RE-wrenches <
>>> [email protected]> wrote:
>>>
>>>> John,
>>>> If you need a T240 (internal or external), I have a few used ones (and
>>>> maybe a new one) in storage.
>>>> Howie
>>>>
>>>>
>>>> On Wed, Jan 22, 2025, 10:14 AM Christopher Warfel via RE-wrenches <
>>>> [email protected]> wrote:
>>>>
>>>>> I could be a loose electrical or mechanical connection. It's been
>>>>> installed for a while and connections could have loosened up from
>>>>> expansion and contraction.
>>>>>
>>>>> On 1/18/2025 9:06 AM, John Blittersdorf via RE-wrenches wrote:
>>>>> > Hi Wrenches,
>>>>> >   I have a customer with an SW4024 installed in 2003 with the Trace
>>>>> > T220 transformer for
>>>>> > her well pump.  Recently it has started making a lot of noise when
>>>>> the
>>>>> > well pump comes on.
>>>>> > I checked the current on the well pump and it seems to be in the
>>>>> > normal range.  I have never had a transformer failure. Could this be
>>>>> a
>>>>> > failing transformer?
>>>>> >
>>>>> > Also, I have not been able to source a new one (Outback T240).  Are
>>>>> > there other brands
>>>>> > some of you may have used for a step up transformer?
>>>>> >
>>>>> > John Blittersdorf
>>>>> >
>>>>> > _______________________________________________
>>>>> > List sponsored by Redwood Alliance
>>>>> >
>>>>> > Pay optional member dues here: http://re-wrenches.org
>>>>> >
>>>>> > List Address: [email protected]
>>>>> >
>>>>> > Change listserver email address & settings:
>>>>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> >
>>>>> > There are two list archives for searching. When one doesn't work,
>>>>> try the other:
>>>>> > https://www.mail-archive.com/[email protected]/
>>>>> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>> >
>>>>> > List rules & etiquette:
>>>>> > http://www.re-wrenches.org/etiquette.htm
>>>>> >
>>>>> > Check out or update participant bios:
>>>>> > http://www.members.re-wrenches.org
>>>>> >
>>>>> --
>>>>> Christopher Warfel, PE
>>>>> ENTECH Engineering, Inc.
>>>>> PO Box 871, Block Island, RI 02807
>>>>> (401) 447-5773
>>>>>
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>
>>>>> List Address: [email protected]
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> There are two list archives for searching. When one doesn't work, try
>>>>> the other:
>>>>> https://www.mail-archive.com/[email protected]/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org
>>>>>
>>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: [email protected]
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/[email protected]/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other: