I have a suggestion.

The Atkinson is pretty amazing.  What if you set up each generator with 1 GSCM. 
  
Start signal is sent to generator #1 and the GSCM tries but the generator 
doesn’t start,   I believe it has a fault circuit which maybe you could use to 
trigger generator #2 GSCM AGS start sequence.

Just a thought

jay

 

> On Feb 22, 2025, at 11:50 AM, William Miller via RE-wrenches 
> <[email protected]> wrote:
> 
> Dan:
>  
> The application is an off-grid animal rescue facility with a requirement for 
> high reliability.  We recently acquired a second generator and a Kohler RDT 
> transfer switch.  The RDT will automatically transfer to either of two inputs 
> based on where AC is detected.  However the RDT logic is not capable of 
> transferring the start signal if one generator fails to start.
>  
> I looked at the Atkinson web site but I did not see anything that was quite 
> right.  It may be that they can create something but then I would miss out on 
> that part of the fun.
>  
> It’s easy to overlook how complicated it is starting an internal combustion 
> engine.  You have to crank until the engine starts, you can’t crank too long, 
> you need to try multiple times, etc.  This is why the Trace SW 3-wire start 
> circuitry was so amazing.
>  
> I sketched out an electro-mechanical solution but I soon realized the logic 
> was a bit too complicated.  The inverter will want to attempt the start 
> multiple times before giving up.  I’d like to do the same and then switch to 
> starting the second generator after maybe 3 failed attempts at starting Gen 
> 1.  It seems I need to code some kind of script to execute this logic. This 
> is where the Control by Web solution seems to be the best fit.  I have used 
> their products and they are excellent.
>  
> If others are interested I can post back when I crack this nut.
>  
> Thanks everyone for your collective wisdom and comradery!
>  
> William Miller
>  
> Miller Solar
> 17395 Oak Road, Atascadero, CA 93422
> 805-438-5600
> www.millersolar.com <http://www.millersolar.com/>
> CA Lic. 773985
>  
>  
> From: Dan Fink [mailto:[email protected] <mailto:[email protected]>] 
> Sent: Saturday, February 22, 2025 9:07 AM
> To: [email protected] <mailto:[email protected]>; RE-wrenches
> Subject: Re: [RE-wrenches] Generator failure alarm
>  
> William - have you talked to Atkinson in Utah? Last time I talked to them 
> they could configure just about anything for such applications.
> Dan Fink
> Owner, Buckville Energy Consulting LLC
> IREC Certified Instructor for PV and Small Wind Installation
> NABCEP Certified PV System Inspector
> NABCEP PV Associate
> d <mailto:[email protected]>[email protected] 
> <mailto:[email protected]>
> 970-672-4342
> 
>  
>  
>  
> On Fri, Feb 21, 2025 at 1:54 PM William Miller via RE-wrenches 
> <[email protected] 
> <mailto:[email protected]>> wrote:
>> Colleagues:
>>  
>> Is anyone aware of an off-the-shelf device that will give me a contact 
>> closure if a generator is called and does not produce AC after a set amount 
>> of time?  I am sure I could design and build one but before I do I’d like to 
>> see if there is a ready-made version.
>>  
>> I hope I am not making a pest of myself asking so many questions…
>>  
>> Thanks in advance.
>>  
>> William Miller
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org 
>> <http://www.members.re-wrenches.org/>_______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to