Hey everyone,

I’m looking for some clarification on conductor ampacity ratings as they
relate to battery cables. My understanding is that the term ‘free air’
wasn’t actually defined in the NEC until 2020 and that conductors installed
in a nipple, wire trough, conduit body, or enclosure don’t qualify as ‘free
air.’ That said, I’ve noticed some battery manufacturers and installers
seem to be applying Table 310.17 (free air) rather than 310.16 (raceway)
when specifying conductor sizes—particularly for battery-to-inverter
connections.

For example, a battery manufacturer offers a 48Vdc LFP battery with 10kW
continuous output, which would suggest needing a conductor rated for ~245A
(safety factor included). However, they provide a wire trough for the
battery to inverter connection and provide a 1/0 Cu battery cable. This
seems undersized if 310.16 applies. Am I overthinking this, or are these
configurations typically tested and listed accordingly?

I see similar situations across multiple manufacturers, and while I don’t
put too much trust in marketing images, I noticed SimpliPHI using a single
1-1/4” conduit from a stack of 6.6 batteries to a 15kW inverter, which also
raises questions. Is there a code-compliant rationale I’m missing, or are
manufacturers and installers misapplying Table 310.17? I spoke with one
applications engineer that referenced table 310.17 as the “battery cable
table”. I get the value of running free aired battery cables with regard to
ampacity allowance, but I also see the value in protecting energized
conductors in a raceway. Would love to hear your insights!
Best,

Chris Sparadeo


C_802-369-4458
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to