Can you swap the strings in each inverter? Then you'll know whether the
issue truly lies in the inverter or the array.

Cheers,
Dave

On Sun, Apr 6, 2025, 1:35 PM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> I should mention that the other inverter also has three strings and is
> experiencing no faults. Neither inverter has an EGC landed in it from the
> array.
>
>
> Jason Szumlanski
>
>
> On Sun, Apr 6, 2025, 11:47 AM david quattro <da...@quattrosolar.com>
> wrote:
>
>> Tech support said if it’s landed in conjunction with the Load Out ground
>> it causes an ‘echo’ on the grounds. Can result in erroneous Arc fault or
>> other error codes.
>>  I think if using a separate wire trough, that trough needs to be
>> physically far from the inverter and close to an electrode.
>>
>>
>>
>> On Sun, Apr 6, 2025 at 8:09 AM Jason Szumlanski <
>> ja...@floridasolardesigngroup.com> wrote:
>>
>>> That's a good point. I didn't install this system, but I know for
>>> certain the PV EGC is not landed in either of the dual Sol-Ark inverters.
>>> It must be landed on a grounding terminal in a wiring trough or load
>>> center. I'll have to track that down. I'm not sure how the GE system is
>>> installed, either.
>>>
>>>
>>> Jason Szumlanski
>>> Principal Solar Designer | Florida Solar Design Group
>>> NABCEP Certified Solar Professional (PVIP)
>>> Florida State Certified Solar Contractor CVC56956
>>> Florida Certified Electrical Contractor EC13013208
>>>
>>>
>>> On Sun, Apr 6, 2025 at 11:03 AM david quattro <da...@quattrosolar.com>
>>> wrote:
>>>
>>>> Hi Jason,
>>>>    SolArk tech support has told us to land the PV equipment ground
>>>> directly to an electrode. ie do not land the PV ground in the
>>>> inverter’s built in ground-bar. This detail wasn’t in their manuals years
>>>> ago. I hope this is helpful 🤙🏼
>>>> David
>>>>
>>>>
>>>>
>>>> On Sun, Apr 6, 2025 at 7:19 AM Jason Szumlanski via RE-wrenches <
>>>> re-wrenches@lists.re-wrenches.org> wrote:
>>>>
>>>>> If anyone is using this tester to do insulation resistance testing, I
>>>>> would appreciate any pointers you have.
>>>>>
>>>>> I have used it successfully to test home run DC strings from
>>>>> rooftop junction boxes to inverters to check for nicks in wires and hard
>>>>> faults to ground or short circuits. However, I am currently facing a
>>>>> Sol-Ark 15K with three strings of PV that all seem to cause an 
>>>>> intermittent
>>>>> DC insulation fault (F24). I have isolated each string by disconnecting 
>>>>> the
>>>>> other strings at the rooftop junction box. With only one string connected
>>>>> to the inverter, regardless of which string it is, I will eventually get
>>>>> the F24 error.
>>>>>
>>>>> Since I have ruled out the home run wiring, It appears the issue must
>>>>> be within the array somewhere. I would like to use the ET600 to help track
>>>>> it down, but I am reading conflicting information on how to properly
>>>>> undertake the test on each string. I know that I can disconnect the
>>>>> conductors between each PV string and the junction box and test each 
>>>>> jumper
>>>>> wire individually while disconnected. But what about the PV module leads
>>>>> within the string of connected modules? I'm suspecting a pinched PV module
>>>>> lead somewhere, but I don't know where to start looking.
>>>>>
>>>>> Jason Szumlanski
>>>>> Florida Solar Design Group
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>
>>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> There are two list archives for searching. When one doesn't work, try
>>>>> the other:
>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org
>>>>>
>>>>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to