Jason,

I think it is valuable to have SOC information available if you also have an 
InsightHome device that can show the SOC data for reference etc. For legacy 
inverters, voltage still makes the decisions.

I don’t know of any battery that communicates together to balance between 
individual battery entities. That still leaves the necessity to charge via 
voltage high enough to get all batteries to high and similar SOC.

The E-BOX says via Pylontech protocol that its battery voltage range is 46.5V 
to 56.8V, so I think 48V LBCO is fine and certainly 44 is too low.

There is a “.8” version of battery firmware and a “.16” version. I can send you 
the .16 version that I have (SPBMS16SRP2205V1.5.18.C16). I use HyperTerminal to 
install the software and it is the absolute easiest battery to view the details 
using the Pytes USB to Serial cable (other cable brands could also work). 
HyperTerminal was provided free by Pytes. I can send you that as well. A lot of 
this might still be on their  website.  

I lieu of having a Pytes Hub to stack the existing bank as multiple groups of 
10 batteries, you could upgrade each battery to .16 firmware and make two 
communicating stacks of 10 that don’t communicate together. If you have 
InsightHome, you can wire the CAN port of the left 10 to Insight and the RS485 
port of the right stack to Inight and make “two battery banks” show up in 
Insight. On the Pytes, the CAN RJ45 Blue pair is CAN and the Orange Pair is 
RS485 (from the RS485 port). If you have InsightFacity you can use both CAN 
ports. CAN devices show up automatically and RS485 device need to be setup via 
InsightLocal / Setup / Device Detection / Detect Device / RS-485: 1 to 10. 

On the Charge Controllers, I would set Absorb to 55.2 for 3 hours. 

I even started using EQ at 56.0 on some systems. 

Good luck today!


Maverick Brown
Off-Grid Solar Commander since 2006
Maverick Solar Enterprises, Inc.
 • Solar Commander Remote Power
 • SunFlow Systems Cathodic Protection 
maver...@mavericksolar.com
512-460-9825

> On May 16, 2025, at 6:22 PM, Jason Szumlanski via RE-wrenches 
> <re-wrenches@lists.re-wrenches.org> wrote:
> 
> The advantages of closed loop communication between LFP batteries and 
> inverter systems are pretty obvious. But when you are operating in an open 
> loop because you are working with a legacy inverter that does not support 
> battery communication, how important is it for batteries to be wired 
> together? 
> 
> I started contemplating this today when I ran into a Pytes stack of 20 E-Box 
> 48100R (5kWh) batteries. Whoever installed them wired all 20 in a single 
> communication daisy chain. Come to find out, this version of the battery only 
> supports 8 or 16 in a communications network. The bank is connected to a 
> couple of XW+ inverters, so it is operating based on voltage. The owner must 
> have had to use an unconventional method to turn the batteries on, because 
> typically you would only press the switch on the master battery. In this 
> case, that doesn't work because the communication chain is broken at some 
> point. 
> 
> The reason for my visit was the battery is sitting at 43 volts because the 
> generator didn't start and the low battery disconnect was set to 44 volts, 
> well below the 49 volts recommended by Pytes. Side note:  I could not set the 
> low battery cut out higher than 48V with these inverters. 
> 
> I was there to get these jump started with a Chargeverter. I rigged it up and 
> got things going, but various batteries were alarming out. Ultimately I just 
> disconnected the communication cables on all the batteries and they all 
> started charging from the Chargeverter which was connected to the common bus. 
> Awesome!
> 
> So back to the original question... Are the batteries really doing anything 
> in terms of balancing when they are connected in a communications daisy chain 
> when they are not enclosed loop communications with an inverter? How 
> important is the communication anyway? And in this case, assuming that the 
> maximum batteries in a communication chain is eight, I would probably be 
> better off setting up four separate communications with four master batteries 
> in groups of five. Again, I'm not sure how important that is in terms of 
> balancing. What if I had different quantities per communication group? 
> They're not talking to each other anyway!
> 
> Not to muddy up this thread, but I will say that the Chargeverter saved the 
> day. Within 20 minutes, I was able to get the inverters turned on and the SCP 
> to help me identify what went wrong. Then I turned on the inverters and got 
> them charging the batteries simultaneously with the Chargeverter and solar. 
> It really just needed a jump start! I had rigged it up in a way that I could 
> easily do this and then safely disconnect the Chargeverter while the rest of 
> the system continued to charge the batteries. It was my first experience with 
> this little gem, and I'm happy to have it in my toolbox now.
> 
> Tomorrow I am going back to restart the charging process and hopefully get 
> the batteries up to 100%. I also plan to check the firmware, which I am 
> almost positive is mismatched in this stack of batteries. All of my off-grid 
> systems are a boat ride away, so I'm going to pretend it's a weekend and I'm 
> not working. Haha.
> 
> 
> Jason Szumlanski 
> Florida Solar Design Group 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to