Hello Dave,

Please continue working with Sol-Ark support on this issue. While inverter 
calibration is possible with some of our inverters, it requires prior approval 
from management. This step is only taken when we are absolutely certain the 
issue originates from the inverter itself, once this has been determined a 
support member who has been trained and has access to make these changes should 
be able to calibrate the inverter for you. Due to the potential risks involved 
and the confidential nature of the calibration process, we do not share these 
steps externally.

Best Regards,

Jharen Poole
Applications Engineer II
972-575-8875
[cid:39724b23-42e2-4a24-b173-2e150c1db9ac]
________________________________
From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> on behalf of 
Maverick Brown via RE-wrenches <re-wrenches@lists.re-wrenches.org>
Sent: Thursday, May 29, 2025 9:31 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Cc: Maverick Brown <maver...@mavericksolar.com>; RE-wrenches 
<re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Sol-Ark battery calibration

Caution: This email is from an external source.


Dave

I would say this:

Few bible days ago, I worked in Semiconductor Manufacturing Equipment Service. 
We would send our Fluke DVMs, recorders and other measuring tools off to a lab 
to get calibrated so when we measured something, we knew what we were 
measuring. I’m not saying your DVM is out of calibration, it seems like the 
inverter’s DVM is the issue.

Having said that, I assume that if an inverter is measuring something like 
volts or amps (usually via a shunt therefore Volts), it also needs to be 
calibrated.

Now, the question is can a common person like you or me be allowed to edit 
those values on the Sol-Ark.

Outback has their Vbat cal page for charge controllers and trim pots for the 
FNDC and Schneider has their XW Config Tool with calibration procedures.

I think Sol-Ark will send a motherboard to install on the old Master???

I suggest keep calling them and reference your ticket # and see if you can get 
a resolution.

I would also measure along the entire path of both inverter battery cables, 
especially at high load looking for any voltage drops along the way. You might 
find a loose bolt or wonky lug crimp. See if you can both sides of the inverter 
DC breaker.

Good luck!

Thank you,

Maverick

Maverick Brown
Off-Grid Solar Commander since 2006
Maverick Solar Enterprises, Inc.
 • Solar Commander Remote Power
 • SunFlow Systems Cathodic Protection
maver...@mavericksolar.com
512-460-9825



On May 28, 2025, at 2:32 PM, Dave Tedeyan via RE-wrenches 
<re-wrenches@lists.re-wrenches.org> wrote:


Does anyone know whether you can calibrate the battery voltage on Sol-Ark 
inverters? I am on site with two 12k-p inverters. My meter agrees with one of 
them, and the other inverter (the master) is displaying 0.6v lower than both my 
meter and the other inverter.

I have gone through two tech support people who are not being much help.

There are lead acid batteries here.

Thanks!
-Dave


[Logo]<https://www.sungineersolar.com/>
Dave Tedeyan, P.E.
Owner | Sungineer Solar
p: he | him | his
a: 1653 Slaterville Rd. | Ithaca, NY 14850
w: www.sungineersolar.com<http://www.sungineersolar.com/>
c: (607) 270-0370
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to