Hi Jay,
I agree with Brad that Evacuated tubes are not a good (or even a reasonably 
possible) candidate for a drainback retrofit. If they are pass-through tubes, 
then they cannot fully drain as piping connections typically come through 
header connections at the tops of the tubes. If they are sealed heat-pipe 
tubes, then not only is the header unlikely to drain properly, but the tubes 
themselves will stagnate at a very high temperature without heat transfer fluid 
flow. 

I recommend a diversion heat- dump arrangement such as Todd suggests.Use 
paralleled runs of conventional hot water baseboard fin tube for the heat 
dissipator. This stuff is readily available at almost every plumbing supply 
house and it works well.  

Diversion can be activated by either an electric 3-way valve and a set point 
controller, or the passive wax-thermostat 3-way valve that you mention. I have 
used both methods extensively with good results. The wax thermostat will 
probably be significantly harder to find. Some years ago I ordered them through 
Low Energy Systems in Denver. Reach out to me off list and and I can supply 
some contact information. 

-Luke
 
Luke Christy
Renewable energy consultant

NABCEP Certified PV Installation Professional™: 

Solar Gain Services, LLC
PO Box 531
Monte Vista, CO 81144
719.588.3044
sgsrenewab...@gmail.com



> On Jun 17, 2025, at 3:46 PM, jay via RE-wrenches 
> <re-wrenches@lists.re-wrenches.org> wrote:
> 
> In doing research today I found the following, not sure where I can buy them 
> at this point.
> 
> 1. solar dissipation tubes.  that will do about 12,000 btu or at least this 
> one does. 
> 
> 2. 3 way thermostatic valve which uses a type of wax that opens and closes it 
> at a specific temp and routes the heat through the dissipation tube vs the 
> heat exchanger down below.
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to