Friends: When I design a lead-acid battery system I decide if I need over-current protection right at the battery or not. My logic is: if the leads are short, don’t go through a wall and are well protected, I can rely on OCPD in the BOS cabinets. If any of these criteria is a no I put appropriately rated class T fuses right at the battery.
I’m thinking that since BMS devices have over-current protection baked-in, fusing at the battery would not be necessary for BMS equipped batteries in any case. Do you agree with that premise? William Miller Miller Solar.com 805-438-5600 www.millersolar.com
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org