Hi william This is exactly the same type of ags the radian has It’s supposed to work with a generator that has the auto start function in it. So the inverter just sends a start signal to it. The radian had a default of around 15 minutes if memory serves. IE if the genny doesn’t start in that amount of time the inverter ags would fault Most generators have some number of start attempts afterwards it will usually fault. Requiring a human to clear the generator fault. The inverter start signal isn’t connected to the starter so the generator won’t continue to crank. I don’t think the envy inverter goes into a fault mode. I think the printed responses from fortress are clueless There is another part that is problematic. If you have the ags start say 20% -80%. And you want to turn the generator on to charge batteries at 40% it won’t charge. It will pass through to the loads. I have talked to them that remote manual start generator should just charge up to the upper limit thats set. Yeah didn’t get anywhere. So you have to set the ags start % to where it is and then start the generator. That all said. I have a 3 stack that has been without any issues at all. Fully off grid, ags. Works Jay On Sep 8, 2025, at 5:16 PM, William Miller via RE-wrenches <[email protected]> wrote:
|
_______________________________________________ List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org