So Sue, where does the MN PowerFlo 16 product stand in regards to class I,
div II rating?

Christopher

On Wed, Sep 10, 2025 at 6:58 AM Sue Stankevitz via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> They may be looking for the Class 1 Div 2 rating with means that it has
> been designed to safely operate in environments where flammable vapors or
> gases exist and have the potential to rise to ignitable concentrations.
> Midnite had to get a charge controller certified to that standard several
> years ago.
>
>
>
> Sue Stankevitz
> MidNite Solar, Inc. <https://www.midnitesolar.com/index.php>
> (360) 403-7207 (XT122)
>
>
>
> *From:* RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> *On
> Behalf Of *Jay via RE-wrenches
> *Sent:* Tuesday, September 9, 2025 6:27 PM
> *To:* RE-wrenches <re-wrenches@lists.re-wrenches.org>
> *Cc:* Jay <jay.pe...@gmail.com>
> *Subject:* Re: [RE-wrenches] Flammable Vapor Ignition Resistant
>
>
>
> What would be the rating for that?
>
>
>
> Is it a NEMA or?
>
>
>
> Jay
>
>
>
> On Sep 9, 2025, at 3:08 PM, Glenn via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> 
>
> Unfortunately  codes and standards are constantly changing and inspectors
> are trying to catchup and interpret them as quickly as possible to ensure
> compliance for safety sake.
>
> Erring on the side of safety is their job until educated otherwise
>
>
>
> -Glenn
>
>
>
> On Sep 9, 2025 17:00, Jason Szumlanski via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>
> That's a first for me. The Enphase battery is sealed, but I don't know if
> that qualifies as sealed against vapor.
>
>
>
> I'd reach out to Enphase to get some guidance on that. It's always
> something with these AHJs.
>
>
> Jason Szumlanski
>
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
>
> Florida Certified Electrical Contractor EC13013208
>
>
>
>
>
> On Tue, Sep 9, 2025 at 4:13 PM Zeke Yewdall via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> My interpretation of this is that he wants to make sure that the battery
> cannot ignite a flammable vapor cloud from gasoline being spilled in
> the garage.  If he's saying that no electrical equipment that might create
> a spark (such as with a relay or switch or circuit breaker) can be below
> 18", that may be the case.   I might be completely off base here, but I
> don't think it has anything to do with it being a battery really, but just
> a piece of electrical equipment that might have relays or sparking things
> inside?  Maybe?  In which case... does the 5p have any relays or
> contactors, or is it's BMS all solid state?  And second question would be
> can you document that.
>
>
>
> Zeke
>
>
>
> ---------------------------------
>
> Seeking your suggestions and direction. My AHJ - after acknowledging that
> the Enphase 5p battery has a floor mount option - now insists that it must
> be 18-inches above the garage floor unless I can produce something that
> says it is "Flammable Vapor Ignition Resistant."
>
> We all know there is no open flame from an ESS and I know the 9540A
> depicts a battery at 6-inches.
>
> Anybody run into this and have suggestions on what I might show back to
> the AHJ?
>
> Howard "Scot" Arey
> Owner, Solar CenTex
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

Chris Schaefer’s


*Tel 585-229-2083 or Cell 585-748-1870 *
*5115 S Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
<http://www.solarandwindfx.com> ~ E-mail: ch...@solarandwindfx.com
<ch...@solarandwindfx.com>*


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to