I have a situation with a utility company that requires us to have a single visible load break disconnect switch that isolates only the "renewable sources" without disconnecting the house loads. To do this, the only way possible seems to be combining the inverters in a load center and then using the main lugs in the load center to go to a fusible disconnect switch, and then the backup load lugs in the Gateway 3.
The problem with that is I have not been able to find a 125 amp load center that accepts multiple backfed breaker fasteners. Square D has a 100 amp load center that accepts two breaker hold down kits, but for two Powerwalls we need 125A. Other than going to a panel board with bolt on breakers, can you think of any other way to comply? Jason Szumlanski Florida Solar Design Group We
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org