That version of sol ark is known for out of balance loads shutting the inverter off. 

To the best of my knowledge there is no fix. 
The work around was stated earlier in using an auto former. 
Or replacing the inverter with the 15kw which doesn’t have those issues 

Jay





On Oct 7, 2025, at 10:04 AM, Amanda Potter via RE-wrenches <[email protected]> wrote:

No AC-Coupling.

This 3 yr. old 12k will not run an older worm-drive Skilsaw, nor a Dewalt Chop saw.
One at a time, either one will shut the whole house down when you hit the trigger.
Sol-Ark says you need to run a load on the opposite leg to make it work.
(The customer was Not happy with that answer.)
It’s only a 20a, 120vac circuit & the 12k has less than 100w loads.
It does not open the circuit breaker at all.

Amanda Potter
Energy Storage Systems
NABCEP PVIP 
Adirondack Battery & Solar, LLC
(315) 212-2114

On Oct 6, 2025, at 2:35 PM, Tyrone Houck via RE-wrenches <[email protected]> wrote:


Im confused as to your question. Are you finding that the sol ark is not able to operate at 9k continuous on the output? Or that it won't pass 12k on the input with AC coupling?


   

On Mon, Oct 6, 2025, 8:57 AM Amanda Potter via RE-wrenches <[email protected]> wrote:
Hello Wrenches,
I’ve been trying to research the threads here for what relief, if any, Installers have gotten from Sol-Ark for there false claims of the AC Load Output of the 12K.

(I know, I know… As one of our awesome Installers from Maine told me, “Don’t drink the koolaid!)

Thanks ahead of time.

Amanda Potter
Energy Storage Systems
NABCEP PVIP
Adirondack Battery & Solar, LLC
(315) 212-2114
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to