It is the inverter that trips off not the breaker and nothing needs to
be done to restore power except to reset the inverter. It isn't unusual
for an inverter to trip off due to overload faster than a breaker
responds. But I wouldn't expect the inverter to trip off due to an arc
fault.
The electrician has been out there twice looking for a problem with the
wiring and found nothing.
Kent Osterberg
Blue Mountain Solar
On 11/21/2025 3:35 PM, Tom McCalmont wrote:
Maybe it’s a real arc-fault in the system somewhere, and the breaker
is trying to tell you that.
*Tom McCalmont
*CEO, Paired Power
pairedpower.com <http://pairedpower.com> | LinkedIn
<https://www.linkedin.com/company/paired-power/>
Direct: (669) 877-2931
On Nov 21, 2025, at 3:32 PM, Kent via RE-wrenches
<[email protected]> wrote:
Fellow Wrenches,
I have a system that we installed a few weeks ago that is driving us
crazy with overload faults. It is a remote cabin with maybe a half
dozen circuits being fed by a Little Rosie inverter. Every couple
weeks the power system shuts down with the Little Rosie showing an
overload for no apparent reason. Client resets the inverter and
everything runs fine for a couple weeks or so. The system seems to
have no trouble when the Arc Fault (a Siemens arc fault breaker in a
100-A Siemens panel) breaker is turned off. Any of you have similar
issues with these breakers? It is weird that the breaker could
actually be causing the inverter to trip off.
Kent Osterberg
Blue Mountain Solar
_______________________________________________
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org