Key points of using the Classic for charging lithium are to unplug the BTS and 
turn off temp comp, set equalize to 1/10v higher than absorb(in case someone 
button pushes) and disable equalize. We have thousands in the field 
successfully charging lithium batteries. A WBJR and shunt can be added to 
provide accurate SOC.

Sue Stankevitz
MidNite Solar, Inc.<https://www.midnitesolar.com/index.php>
(360) 403-7207 (XT122)
[cid:[email protected]]

From: RE-wrenches <[email protected]> On Behalf Of Jim 
Gowdy via RE-wrenches
Sent: Wednesday, November 26, 2025 12:51 AM
To: [email protected]; RE-wrenches <[email protected]>
Cc: Jim Gowdy <[email protected]>
Subject: Re: [RE-wrenches] New Lithium Batteries on Sunny Island System

Thanks for the information.  I emailed both SMA and Midnight and we'll see what 
they say.

On Tue, Nov 25, 2025 at 7:08 PM William Miller via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
I just left the temp sensor dangling in mid air. This way the Sunny Island at 
least could react to ambient temperature.


William Miller
Miller Solar.com
805-438-5600
www.millersolar.com<http://www.millersolar.com>


On Tue, Nov 25, 2025 at 6:10 PM Jerry Shafer 
<[email protected]<mailto:[email protected]>> wrote:
William, Wrenches,
I have done several over the past couple years, the only issue I had, I needed 
to build a resister that mimiced the BTSas 75 degrees, because the SI.s will 
brop and raise max voltage according to the temp, this must be changed to 
prevent this as the battery BMS will or at least should do that anyway. Now I 
dont know about your batteries and I would suggest that you look at the battery 
cables sizes, I looked at a system that had these so called hight output 
batteries with # 8 plug in cables, worked very poorly just a FYI
Fun times

On Tue, Nov 25, 2025 at 9:42 AM William Miller via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
Jim:

I haven’t tried lithium batteries with a traditional charge controller yet.  
All of the equipment you list was designed for lead acid.  The narrower voltage 
range of the lithium may confuse the charge controller. Same with the AGS 
triggering.

I know if you call SMA for tech support they may hang up on you when you tell 
them there are lithium batteries.

It may work right away or you may spend a lot of time making it kind of work. I 
hope you can make the client understand this is an experiment. Tech support 
from the battery manufacturer may not be great being a Chinese company.

These days I pair lithium only with inverters designed for them.

Good luck.

William Miller
Miller Solar.com
805-438-5600
www.millersolar.com<http://www.millersolar.com>


On Tue, Nov 25, 2025 at 7:33 AM Jim Gowdy via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
Hello All,
     I have a client that just got some lithium batteries and they have a sunny 
island inverter with a Midnight Charge controller.  I've heard and experienced 
integrating Lithium batteries into a Sunny Island inverter is challenging and 
could create problems.  Has anyone had experience with these batteries or 
installing lithium batteries with these components?  Below are some details 
about the system so far.....

System:
48v

NEW BATTERY:
China Aviation Lithium Battery CO.
model: CA180F
nominal voltage: 3.2v
rated capacity: 180Ah
rated energy: 576Wh

Inverter:
Sunny Island
model: SI 4548-US-10

CHARGE CONTROLLER:
Midnight Solar Classic 150

SOLAR ARRAY:
N/A....it was dark when I was at the site so I couldn't take any notes



--
Jim with Gowdy Electric
Cambria, Ca 93428
business  805 927 2630
cell  805 975 5279
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


--
Jim with Gowdy Electric
Cambria, Ca 93428
business  805 927 2630
cell  805 975 5279
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to