In NM if you have batteries and an inverter which is rated above 10kw it lowers the total amount you can supply to the grid to stay under the 10kw ac for net metering
I can’t remember the exact details.
On Nov 26, 2025, at 11:43 AM, August Goers via RE-wrenches <[email protected]> wrote:
It looks like Oncor is using the total generation facility nameplate of PV + ESS inverter ratings, or something along those lines. That's the same as we see in PG&E territory here in California. You might be able to use a PCS setting to limit grid battery charging and then maybe use Aggregate power export limit (see 5.4):
There are many solutions that PCS will provide if the utility recognizes PCS as a bonafide solution.
-August
On Wed, Nov 26, 2025 at 6:57 AM scot.arey--- via RE-wrenches < [email protected]> wrote:
In my 13 years installing solar in Texas, I've never had a utility come back and say "you must set a PCS limit of 2KW through this 25KW transformer or you can pay to upgrade the transformer."
System is 12KW of solar (9KW AC equiv.) and 6x Enphase 5P batteries (23KW AC) so total of 32KW of potential power export if the batteries were grid-exporting at same time of peak solar production. I can see the batteries charging at 23KW if charging from grid
but of course solar can never be a load. And exporting battery power simply not a financially smart option.
So the only answer I can come up with is this transformer is serving more than this home and seems undersized by utility if it's serving multiple homes with 200-amp services. Few words from Oncor is that this is the issue.
I alerted Oncor to the Power Control System capabilities to limit power export and they are insistent that 2KW is all they can take (they never said if this a import or export limit). I asked if this was a grid-tied system only with no ESS, would it have come
back with the same 9KW (AC) limit? I think they are tripping over the combined connected capacity of solar + ESS.
Anybody else in Texas running into this recently? I told Oncor I'd be perfectly fine with 9KW export capability (the solar) and limit grid-charging to this power, too.
This isn't Hawaii...so I'm super surprised and about to lose a lot of money.
Howard "Scot" Arey
Owner, Solar CenTex
NABCEP PV Installation Professional
TECL 29755
254-300-1228
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: [email protected]Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/[email protected]/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org
|
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org