Most of us with enough experience (scar tissue) using the PRO series schneider 
products know the firmware is problematic and Schneider managed to build in a 
laundry list of issues that the plus series never had. That being said, 
although Shneider PRO product firmware is an easy target. I would definitely 
check the wiring first. Particularly with DIY installations improper Ground and 
neutral connections are a common cause for the failures you are describing.
Personally, I have had my share of problems with the PRO series Scheider 
products, but have never seen any equipment damage. I have however seen 
numerous instances of installer error particularly with the previously 
mentioned Neutral and ground circuits. Common mistakes are multiple Neutral to 
ground bonding points rather than just one and only one. Improperly or 
undersized, or even missing Neutral conductors. I have even seen a "hot" wire 
used as a neutral, and shockingly the 120 Volt devices that were being supplied 
with 240 Volts managed to survive for a few weeks. For sure check all the 
onsite wiring before diving into inverter firmware issues.
Pieter Huebner
Project Manager
Off Grid Enterprises
________________________________
From: RE-wrenches <[email protected]> on behalf of Luke 
Christy via RE-wrenches <[email protected]>
Sent: Thursday, December 4, 2025 11:18 AM
To: RE-wrenches <[email protected]>
Cc: Luke Christy <[email protected]>
Subject: Re: [RE-wrenches] Off-grid Firmware XW Pro

Kevin,
 Can you elaborate on some of the issues you’ve sen with XW Pro off grid and 
with the >V2.04 firmware versions? I have a few XW Pro units out there fully 
off-grid running newer firmware and I haven’t had any trouble— yet.

Thanks,
-Luke

Luke Christy
Renewable energy consultant

NABCEP Certified PV Installation Professional™:

Solar Gain Services, LLC
PO Box 531
Monte Vista, CO 81144
719.588.3044
[email protected]

On Dec 4, 2025, at 9:52 AM, Kevin Pegg via RE-wrenches 
<[email protected]> wrote:

I’d zero in on the firmware first. Bad wiring can cause issues, but if it’s 
actually letting the smoke out of electronics, pretty high chance it’s the bad 
firmware that Schneider knows all about but refused to address.

If it’s got 2.04 firmware get rid of it. Downgrade to 1.11. It’s the only 
stable software for that system IMO.

https://www.se.com/us/en/product-range/66297-xw-pro/#software-and-firmware

My only other comment is I am seeing best client satisfaction by un-installing 
anything Scheider made post 2019 and replacing it with a better brand that just 
works reliably and consistently.

Kevin

From: RE-wrenches <[email protected]> On Behalf Of Mac 
Lewis via RE-wrenches
Sent: Thursday, December 4, 2025 5:56 AM
To: RE-wrenches <[email protected]>
Cc: Mac Lewis <[email protected]>
Subject: [RE-wrenches] Off-grid Firmware XW Pro

Hello Wrenches,

I am visiting a site with an XW Pro and it sounds like it's burning up 
appliances.  This system was installed by neighbors so it may be a wiring 
problem but I also wonder if it may have the bad firmware that was doing this 
(generator interaction was the problem I think).

Can anyone remind me of the proper firmware that we should run for an off-grid 
system with the XW Pro?  How to get it?  And any other nuances that I should be 
aware of?

Thanks in advance!

--




Mac Lewis

"Yo solo sé que no sé nada." -Sócrates

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to