David,
The SW4024 inverter has a SELL mode that allows power to flow back to
the grid from the AC1 terminals. Make sure that the SELL mode is not
selected; that may take of the problem. If not, connect the utility
power to the AC2 terminals, it shouldn't be possible for the SW inverter
to backfeed power to the the AC2 terminals.
Kent Osterberg
Blue Mountain Solar
On 1/10/2026 1:12 PM, David Palumbo via RE-wrenches wrote:
Wrench,
An off-grid installation of mine from many years ago has is now using
grid power instead of a generator. The utility is telling the
homeowner that they are going to disconnect him because his house is
back feeding 1 amp into their grid power.
I've been retired for many years now and did not do any of the work to
connect the utility power to his Trace SW4024 inverter/charger. The
utility power became available when his son brought in utility power
for his maple sugaring operation in the neighborhood, and the father
connected power to his house to replace his fossil fueled generator
for additional charging into his battery bank. They do not have a grid
interconnect sellback agreement with the utility.
I have no experience with this, but I'm assuming that the utility grid
is seeing power from its input connection to his Trace SW4024. Does
that sound right? If so, is there a simple solution to fix this
problem while continuing to use the grid power through his SW inverter?
Thanks for any advice that may help.
David Palumbo
Hyde Park, VT
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here:http://re-wrenches.org
List Address:[email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org