I had a thought. What about just backing up one of the two 200A panels with
an off-the-shelf residential MID, and install an automatic transfer switch
on the other 200A panel with the primary source being the grid, and
auxiliary source being the inverter output, possibly through a feeder from
the first 200A panel.

This would allow backup of all loads on a single 200A MID. I would comply
with 710.15(A) (NEC 2020) without any required load management.

Better yet, make the auxiliary source for the second 200A panel a feeder
from a smart load breaker in the MID for load management purposes. The EG4
GridBOSS can send a 125A feeder to the other panel. That would be more than
sufficient for practical purposes in a grid outage.


Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208

On Thu, Feb 5, 2026, 8:48 AM Jay <[email protected]> wrote:

> I reread your question.
>
> I think the only way to be sure the internal transfer switches in the
> inverters all switch at the same time on a big high load ( exceeding
> potentially the max current rating of a single relay) multi stack inverter
> system is to use external transfer switch’s.
>
> The system I installed is never going to exceed 200 amps, probably never
> exceed 80 amps. 2 inverters can more than handle the load. The 3rd was
> installed as built in redundancy to make it easier in case one fails. As
> the system won’t run on 1.  So I didn’t have to worry about exceeding relay
> capacity.
>
> I think this is one of the potential problems with paralleled systems vs
> larger single 120/240 inverter’s which we don’t really have here in the US.
>
>
>
> On Feb 4, 2026, at 7:05 PM, Jay <[email protected]> wrote:
>
> 
> I have a 3 stack eg4 18k and while watching the inverters online they are
> totally balanced.
>
> Jay
>
> On Feb 4, 2026, at 4:29 PM, Jason Szumlanski via RE-wrenches <
> [email protected]> wrote:
>
> 
> Hi all,
>
> When backing up a 400A service with multiple paralleled all-in-one
> inverters by combining the AC inputs and outputs, the individual inverter
> transfer switches must operate in a synchronized manner. Come to think of
> it, the same thing applies to backing up 200A service with paralleled
> inverters. Are these tested for this function? – I assume so.
>
> I'm really asking because Sol-Ark seems to be the only brand that
> specifically addresses 400A service in documentation, although not very
> clearly in the manual itself. Their training and literature support passing
> through additive grid pass-through with multiple inverters, which implies
> that they are additive in their ability to transfer power. See attached
> examples.
>
> I have not found anything from EG4 (for the 18kPV) or the Midnite AIO that
> specifically addresses this.
>
> In other words, how can we assume that paralleled inverters will be
> additive in terms of their ability to transfer high levels of current that
> exceed the rating of a single unit? Is that even addressed in listings? The
> documentation is quite poor from all manufacturers (no surprise there!)
>
> I do have a couple of grid-interactive Midnite AIO systems with four
> paralleled AIOs backing up 400A services, and so far, so good. My engineer
> signed off on that.
>
>
> Jason Szumlanski
>
>
> * <http://www.floridasolardesigngroup.com/>*
> <Image 1171.jpg>
> <Image 1172.jpg>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to