If worse came to worse I have a dual 5548 powerpanel I could pull one of
the inverters off. Feel free to contact me off list.

Daryl DeJoy
NABCEP Certified PVIP since 2006
Island Energy Storage
(207)479-2252

On Thu, Sep 24, 2026, 2:47 PM Jay <[email protected]> wrote:

>
>
> > On Sep 24, 2026, at 5:59 AM, Jay <[email protected]> wrote:
> >
> > I have to say I’ve never seen that behavior before with it changing
> parameters.
> >
> > I’ve seen many false ags start situations but it’s never shut the
> inverter down.
> >
> > I would try to replace the chip set if you could find one. As I don’t
> think it’s the display/buttons that are causing the problem
> >
> > Jay
> >
> >
> >
> >
> >
> >> On Sep 23, 2026, at 11:40 PM, David Coale <[email protected]>
> wrote:
> >>
> >> 
> >> Hi All,
> >>
> >> I have a system with two SW5548 inverters paralleled together.  One of
> the inverters randomly changes the input parameters and ends up trying to
> turn on the generator, and since there is no generator, the system gets a
> fault.  I have also seen it set the gen to an EQ charge.  I can redo all
> the settings, but this does not last long before the shenanigans begin
> again.
> >>
> >> I took apart the buttons and cleaned them all, but this did not change
> anything.  I then took the cover off and cleaned the control board as best
> I could and re-seated the ribbon cables.  Still no luck.
> >>
> >> Any ideas/experieance with this? Replacing the inverters with a more
> modern version would be very expensive and time-consuming, as the panels
> would also have to be rewired.
> >>
> >> Thanks,
> >>
> >> David
> >> _______________________________________________
> >> List sponsored by Redwood Alliance
> >>
> >> Pay optional member dues here: http://re-wrenches.org
> >>
> >> List Address: [email protected]
> >>
> >> Change listserver email address & settings:
> >>
> https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/
> >>
> >> There are two list archives for searching. When one doesn't work, try
> the other:
> >> https://www.mail-archive.com/[email protected]/
> >>
> https://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/
> >>
> >> List rules & etiquette:
> >> http://www.re-wrenches.org/etiquette.htm
> >>
> >> Check out or update participant bios:
> >> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
>
> https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> https://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/

There are two list archives for searching. When one doesn't work, try the other: