Zeke and all,

Fortress's manual talks about bypassing the BMS as you mentioned. What
model/manufacturer adjustable DC power supply are you referring to?

Christopher

On Fri, Oct 16, 2026 at 12:14 PM Zeke Yewdall <[email protected]>
wrote:

> It has to be able to charge dead batteries -- many of them will look for
> battery voltage to be in a certain range (like above 45 volts) before it
> starts charging, so that won't work.  And, it has to not hit them with too
> high of voltage when the battery voltage is super low, which can cause the
> BMS to do a high voltage shutdown even though the battery cells are super
> low.  The ones that present 58 volts to a zero volt battery can cause this
> issue, even though they would normally be able to start a 0 volt lead acid
> battery.  If it's 35 volts now, or if you are bypassing the BMS to charge
> it, that might work, but if it's zero voltage because the BMS has turned
> off the discharge fet, the charger can't see the battery to begin charging,
> and the BMS sees way too high of voltage on the terminals, so won't turn on
> the charging fet because it doesn't know why the terminals are so high and
> what the current will be if it turns on.
>
> I've honestly had better luck with a DC power supply that you can adjust
> the max current and max voltage on.  Set it to 52 volts to start, and it
> will current limit while charging it up from 35 volts to a normal range.
>
>
> --
> Zeke Yewdall
> PV Engineer
> NABCEP #031508-89
> [email protected]
> 303-523-3592 <(303)%20523-3592>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
>
> https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> https://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>


-- 

Chris Schaefer’s


*Tel 585-229-2083 or Cell 585-748-1870 *
*5115 S Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
<http://www.solarandwindfx.com> ~ E-mail: [email protected]
<[email protected]>*


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
https://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to