Good morning, Wrenches. This is an article I'm working on that addresses
this topic...   It's not done yet, as I'm still working on it between the
normal calls and emails we get.   It's centered on our LFP batteries but
can be used more broadly, and it's based on the experiences I've seen with
some of the legacy inverters out there.

Configuring Legacy Inverters with LFP BatteriesOpen-Loop Integration –
Field Experience and Recommendations

My experience with LFP batteries and legacy inverter/charger equipment has
been mixed. Some equipment works reasonably well, while other equipment
presents challenges that require careful configuration and ongoing customer
involvement.

In many cases, these systems can be configured to work with LFP batteries
in an open-loop configuration. However, there are limitations, particularly
with charging algorithms, voltage regulation, battery monitoring, and
maintaining balance between parallel batteries.

The following recommendations are based on my experience working with these
systems in the field.
------------------------------
1. Magnum Configuration Requirements

With Magnum equipment, we haven't encountered many issues connecting LFP
batteries in an open-loop configuration, as long as you take a few
precautions.

   1.

   *Remote Display:* You must have either the Advanced Remote or the
   Advanced Router Remote.
   2.

   *BMK (Battery Monitor Kit):* Do not use the BMK. I've found that it
   barely works reliably with lead-acid batteries, specifically when
   configured with default settings.  With LFP, the errors and warnings it
   generates will cause more headaches than they're worth.
   3.

   *PT-100 Charge Controller:* If you're using a PT-100 with a Magnum
   inverter, you cannot link the inverter charging settings to the charge
   controller settings. Disable this feature in Menu 02E.
   4.

   *Battery Programming:* Program the system using Custom Battery settings.
   I've found this necessary even when a Lithium setting is available. Most
   preprogrammed lithium profiles are designed for 15-cell-series batteries
   rather than 16-cell-series batteries.

2. Charging Configuration

I generally recommend the following charging configurations:

   -

   *Solar Charge Controllers:* Two-stage charging.
   -

   *Inverters/Chargers:* Three-stage charging.

Absorb timer settings are particularly important.

As a general starting point, allow at least 20–30 minutes of absorb time
per parallel battery in the system.

For larger systems with relatively low charging current (less than 8–10% of
the bank's C20 capacity), you may need to increase absorb time to up to one
hour per parallel battery.

*Important: Do not terminate charging based on End Amps or SOC%. Terminate
charging only after the programmed Absorb Done timer completes.*

End Amps and SOC% accuracy are not sufficiently reliable in many of these
systems to use these features for LFP charging. We have found similar
limitations when using them with lead-acid batteries.
3. Battery Temperature Compensation (BTS)

Disconnect the BTS from the inverter and charge controller. Do not allow
battery temperature compensation to operate.

Even with the BTS disconnected, Magnum's output voltage regulation can
introduce overvoltage errors with LFP batteries.

Slightly reducing the absorb voltage target can help minimize these errors.
However, there is a trade-off: lowering the charging voltage can make it
more difficult for the batteries to reach a full charge and balance
properly.

This can increase voltage and SOC differences between batteries,
potentially requiring additional manual balancing of the battery bank.
4. Low Battery Disconnect Settings

Set Low Battery Disconnect at or just above nominal battery voltage.  This
setting depends on the specific battery manufacturer and the number/voltage
of cells in series.

Recommended starting points for Surrette LFP Batteries.
System Voltage Low Battery Disconnect
12V 12.2–12.4V
24V 24.4–24.8V
48V 48.6–49.0V


5. Routine Battery Monitoring and Maintenance

Customers should periodically check the SOC% and individual battery
voltages of all parallel battery stacks.

We recommend performing these checks every 30–60 days, preferably after the
system has completed a full 100% charge.

Pay particular attention to the following:

   -

   SOC% differences between individual batteries.
   -

   Resting voltage differences between individual batteries.

If SOC% is more than 5% out of balance, or resting battery voltages differ
by more than 0.3V, separate the batteries and charge them individually to
100% to rebalance the bank.

The objective is to prevent small differences between batteries from
developing into larger imbalances over time.
------------------------------
6. Other Legacy Inverter and Charger ManufacturersOutBack Power

We have found that the OutBack FM60, FM80, and FM100 charge controllers can
be configured to work with LFP batteries.

*OutBack GT Inverters:* These do not work particularly well with lithium
batteries. Their battery charging algorithm changes based on how quickly
battery voltage rises. This can lead to inconsistent charging and balancing
issues.

*OutBack Radian Inverters:* These can be programmed to work with LFP
batteries.

However, we have also found that pre-2008 Outback inverters, for some
reason, just don't like lithium batteries. Something in the firmware
appears to cause the inverters to bypass absorption, which can lead to
balancing issues.
Schneider Electric

Schneider equipment can also work with LFP batteries.

We generally configure the charging much like the Magnum recommendations:

   -

   Charge controllers operating in two-stage mode.
   -

   Inverter/chargers programmed for three-stage charging.
   -

   User-defined battery settings.
   -

   Carefully configured absorb voltage and timers.

Victron Energy

Victron equipment generally works well with LFP batteries.

I would again recommend using a user-defined battery profile and disabling
adaptive charging.

The Magnum configuration outline above provides a good starting point for
programming and maintaining these systems, although individual equipment
settings and capabilities will vary.
Trace Engineering and Heart Interface

Some older Trace Engineering and Heart Interface inverters can work with
LFP batteries, provided you can control the absorb timer settings.

Inverters such as the older UL, UX, DR, and Heart 458 models do not provide
adequate control over absorb timer settings. This can lead to inconsistent
charging and battery balancing issues.
------------------------------
7. Battery Monitoring Equipment

The battery monitoring equipment I've had the best experience with includes:

   -

   Victron BMV-712.
   -

   Victron BMV-712 Smart.

Traditional battery monitoring equipment from Magnum (BMK), Schneider, and
OutBack (FNDC) is not ideal for LFP applications.

These products were largely designed around lead-acid battery
characteristics. Their SOC calculations and monitoring algorithms are not
necessarily suited to LFP batteries.

I've encountered inaccurate SOC readings, along with numerous errors and
warnings, particularly as battery SOC drops below 50%.

For this reason, I generally prefer monitoring the battery manufacturer's
individual battery data and voltage readings rather than relying
exclusively on the inverter's battery monitor.
------------------------------
8. Summary

If you have a customer willing to work with you, learn the equipment, and
do basic system monitoring and maintenance, you can configure much of this
legacy equipment to work with lithium batteries.

However, if you have a customer who isn't willing to learn the system, or
simply doesn't have the ability or interest to monitor and maintain it, we
strongly recommend a closed-loop system.

Another consideration with much legacy equipment is charging voltage
regulation.

Many of these older inverters and charge controllers simply do not regulate
their charging output particularly well. Their output can be electrically
noisy and can generate high-voltage errors and warnings with LFP batteries.

The pulse-width modulation (PWM) of the charging output can produce voltage
fluctuations that trigger annoying high-voltage errors and warnings in the
battery management system.  This is also often exacerbated by the smaller
capacity of an LFP battery compared with a lead-acid, FLA, AGM, or GEL
battery bank.

Open-loop systems require more attention, more customer education, and a
better understanding of the equipment's limitations. Closed-loop systems
generally provide a much more straightforward installation and support
experience.



*Steve Higgins* *⋅* *Technical Services Manager*
*t* +1.902.597.4020 <(902)%20597-4020>   *m* +1.206.790.5840
<(206)%20790-5840>
*f* +1.902.597.8447 <(902)%20597-8447>   *e* [email protected]
------------------------------
CONFIDENTIALITY: The information transmitted herein is intended only for
the addressee and may contain confidential, proprietary and/or privileged
material. Any unauthorized review, distribution or other use of or the
taking of any action in reliance upon this information is prohibited. If
you receive this email in error, please contact the sender and delete or
destroy this message and all copies.
------------------------------




On Tue, Nov 3, 2026 at 7:06 PM Zeke Yewdall <[email protected]>
wrote:

>  I have used a number of newer magnum inverters with lithium batteries
> pretty successfully with custom absorb/absorb time/float settings (newer
> being 5 to 10 years old or so), on both 24 and 48 volt systems.  I have
> heard that some of the older ones, however, just cannot work with them,
> even with custom settings.  I can't remember what the issue is, but it's
> something that just doing custom settings cannot fix (or maybe it's that
> they can't take custom settings?).   I konw that the standard DIP settings
> on the PT100 don't work, so if you don't have a magnum inverter and ME-ARC
> to do custom settings, the PT100 won't work well with lithium batteries.
>
> I am interested in seeing what the lithium settings on the new Magnum card
> is.  I recently ran into a different inverter (AIMS) which the lithium
> rotary switch setting had an absorb of 57.6 which is okay for some 16 cell
> LFPs, but a bit too high for others -- I've run into a lot that shut off
> the BMS at more like 56.5 or so.  I could not determine what the absorb
> time was, which isn't good. And the float voltage was also 57.6, which is
> really bad.  So, just because an inverter has a lithium setting, doesn't
> necessarily mean it will work with a particular BMS for a particular
> lithium battery.
>
> Zeke
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
>
> https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> https://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
https://lists.re-wrenches.org/mailman/options/re-wrenches_lists.re-wrenches.org/

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
https://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to