Ours all have fuses on the high side. 34.5 KV. GOAB's on the low side.

Chuck



Chuck Kraly wrote:

>Actually guys, it is not a fuse per say, it is fed from a circuit breaker.
>Not the kind found in the home either.
>Most likely there was a stuck breaker which DOES happen. And from the video
>I would venture to say it was a 69Kv primary at least. My employer (The
>Board of Public Utilities in Kansas City Kansas), Had a lightning strike hit
>one of our 161kv/69kv transformers and it took them about 9 hours to put the
>fire out. The insulating oil has a high flashpoint, but when it does catch
>fire....look out
>Chuck K0XM
>Lead Substation Technician (25 Yrs)
>
> 
>
>-----Original Message-----
>  
>
>
> ------------------------------------------------------------------------
>
> Subject:
> Re: [Repeater-Builder] had a little power supply trouble the
> From:
> [email protected]
> To:
> [email protected]
>
> To:
> [email protected]
>
>
>More than likely the fusing was proper. Typically substation transformer 
>size along with fusing is coordinated and engineered rather extensively. 
>My suspicion is that a component failure may have contributed to the 
>total failure of the transformer. It is possible the a fuse did open, 
>but that the fuse holder assembly could have failed in such a way that 
>an arc continued the current flow regardless of the open fuse.
>
>It would be interesting to know exactly what did happen.
>
>Chuck
>WB2EDV
>
>
>
>
>
>
>
>
> 
>Yahoo! Groups Links
>
>
>
> 
>
>  
>





 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/Repeater-Builder/

<*> To unsubscribe from this group, send an email to:
    [EMAIL PROTECTED]

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/
 


Reply via email to