Jeff,

Right you are!  The Square D circuit breakers found in home improvement
stores are the common "QO" or "Homeline" variety, which have a fast magnetic
trip action.  Commercial electrical supply houses either stock or can get on
short notice the QO-HM (plug-in) or QOB-HM (bolt-on) circuit breakers with
the high magnetic action.  Large-frame breakers in the 100 to 1600 ampere
class usually have adjustable delay and trip points.  Here's the blurb from
the Square D catalog:

"QO-HM and QOB-HM high-magnetic circuit breakers are recommended for area
lighting (athletic fields, parking lots, outdoor signs, etc.) when using
lamps of inherent high inrush current, individual dimmer applications, or
other applications where high inrush current exceeds standard tripping
conditions.  These circuit breakers are available in one-pole 15 and 20
amperes only.  QO-HM and QOB-HM circuit breakers are physically
interchangeable with standard QO and QOB circuit breakers and accommodate
the complete range of QO accessories."

I am amazed that commercial and cellular site owners and operators are too
often unaware of the high inrush currents drawn by large power supplies at
startup.  Depending upon where in the AC cycle the switch is closed, a
typical transformer-input power supply can draw well over 100 amperes for an
instant.  A lot of electricians who should know better are not aware of
"special application" circuit breakers, and routinely install the standard
breakers on every job.

73, Eric Lemmon WB6FLY
 

-----Original Message-----
From: [email protected]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff DePolo
Sent: Wednesday, January 17, 2007 6:52 PM
To: [email protected]
Subject: RE: [Repeater-Builder] Re: Power Supplies going up in smoke (non
filtered)

> Even the common plug-in circuit breakers made by Square D,
> Cutler-Hammer, and others are available in high-inrush 
> versions- but you
> won't find them at Home Depot.

Yeah, I know. I've always heard them called "hi-mags", meaning higher
magnetic (current) trip point as compared to standard breakers, yet still
have the same thermal trip point for longer-term protection. I seem to
recall larger industrial breakers having a built-in delay for inrush current
trip protection. You're the power guy, you tell me :-)