Jeff,

The primary purpose of the equipment grounding conductor (green wire) is to
provide a low-impedance path for fault current on a branch circuit.  The
lowest-possible impedance is realized only when the EGC is routed alongside
the phase conductor.  Article 250.24(C)(1) states:  "This conductor shall be
routed with the phase conductor..."  I didn't quote the entire sentence,
because it is very long.

The reason for keeping the equipment grounding conductors separate is very
simple;  we are talking about a hospital, not some ordinary radio shack.
The critical (red) buss likely feeds catheter labs, dialysis machines,
mechanical respirators, and similar equipment that is connected to human
bodies.  Even a few milliamperes of stray current flowing through a
grounding conductor may take a side trip through a patient's heart and kill
them.  It the cath lab, there are usually grounding monitors that will cause
an alarm if any stray current is detected.  The notion that someone is
jury-rigging an electrical connection that will make common connections
between a white and a red system is frightening.  Although such a connection
will likely be passive most of the time, if a fault occurs in the equipment,
that fault may perturb critical medical equipment- with tragic results.

In the hospital where I have a repeater on the red circuit, that circuit is
separately-derived by definition, since it has a separate transformer
upstream of the automatic transfer switch.  Even though I am a certified
electrical inspector, I asked for an independent inspection and a signed
certificate of compliance before I plugged anything in.

One of the previous posters suggested putting the computer on the white
buss, with the repeater on the red buss.  That's a good idea, but be careful
to use a fiber-optic link to pass data between them, else the two devices
will have a common ground connection through the data cable's shield.

73, Eric Lemmon WB6FLY


 

-----Original Message-----
From: [email protected]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff DePolo
Sent: Monday, July 14, 2008 8:20 AM
To: [email protected]
Subject: RE: [Repeater-Builder] Switching a Repeater Betwen AC Sources

> It is important to switch all three power leads, not just the 
> hot lead,
> because neutrals from separate sources cannot be made common- 
> especially
> when a separately-derived power source is involved- and the equipment
> grounds must guide any fault current back to the source via 
> the most direct
> route, which is alongside the respective hot conductor.

Eric, you probably have more experience with industrial electrical than I
do, but I can't recall anywhere in NEC where switching EGC is permitted,
even with separately-derived systems. My copy of NEC is back at the shop,
maybe you have yours handy and can provide a reference for my own
edjumication. 

I would tend to think that in a large industrial complex like a hospital or
high-rise building that the distributed, and unavoidable, ground paths,
(i.e. the entire building including conduits, building steel, concrete,
water pipes, etc.) is almost guaranteed to pose a much lower impedance fault
current path than can a single equipment grounding conductor run alongside
the hot.

As a sidebar, many, if not most, emergency generator installations at
communication sites are not seperately-derived systems because the neutrals
*are* tied together at the transfer switch. However, in the instant case,
where it is unknown whether or not the "red" and "white" are on separate
systems, I agree that switching the neutral and hot is the only safe way to
go.

--- Jeff WN3A



 