That's the problem.  Nothing/nobody delivers what it/they're
"rated"/expected to deliver.  I do not consider it acceptable for
shysters to shirk their responsibility by citing "engineering
practice" as an excuse.
Tom


--- In [email protected], "Gerald Pelnar" <[EMAIL PROTECTED]>
wrote:
>
> Eric,
> 
> Nice explanation. Good engineering practice. However, circuits can
be loaded 
> 100% as long as it is not a continuous load (operated for more than 4 
> hours). Vacuum cleaners (not likely to run 4 hours at a time) are more 
> likely limited to 12 amps due to minimum circuit opacity for motor
loads 
> requiring an additional 25% of the load, so as to not overload a 15 amp 
> circuit.
> 
> I apologize to all the non electricians reading this. Due to the
amazingly 
> confusing way the NEC is written, it's hard for electricians to pass
up a 
> good code argument. :)
> 
> Once again, very good engineering practice, Eric, in spite of the code 
> details.
> 
> Gerald Pelnar WD0FYF
> McPherson, Ks
> 
> 
> ----- Original Message ----- 
> From: "Eric Lemmon" <[EMAIL PROTECTED]>
> To: <[email protected]>
> Sent: Thursday, July 17, 2008 10:47 PM
> Subject: RE: RE: [Repeater-Builder] Re: RadioShack Recalls Power
Supplies
> 
> 
> > Ron,
> >
> > That is a good question.  The answer is that one is not supposed to 
> > connect
> > any load greater than 12 amperes to an outlet rated at 15 amperes,
that 
> > is,
> > a NEMA 5-15R receptacle.  The NEC allows two or more 15-ampere-rated 
> > outlets
> > to be installed on a 20-ampere branch circuit (wired with 12 AWG 
> > conductors
> > and a 20A fuse or circuit breaker), but the limit of 12 amperes on
each
> > outlet still applies.
> >
> > Proof of this restriction is evident in the "vacuum cleaner wars" of a
> > decade or so ago.  Hoover came out with a vacuum cleaner with "7
amperes 
> > of
> > cleaning power."  Then Bissel came out with a unit claiming 9
amperes of
> > cleaning power.  Other vacuum cleaner makers entered the fray
until all of
> > the brands had units with "12 amperes of cleaning power."  The
reason that
> > nobody offered a unit with 13 amperes of cleaning power is because
they
> > would then have to equip that unit with a NEMA 5-20P plug and at
least a
> > 14/3 power cord.  Most older homes do not have NEMA 5-20R outlets,
so such 
> > a
> > vacuum cleaner could not be plugged in to the outlets in most homes.
> > Besides, there is no credibility to a laughable rating of
"cleaning power"
> > expressed in amperes!  That is about as silly as claiming that a
mobile
> > radio has "13.8 volts of talk power!"
> >
> > Back to your second question.  By definition, a 15-ampere-rated branch
> > circuit has circuit conductors of #14 AWG or larger, and is
protected by a
> > fuse or circuit breaker rated at 15 amperes.  The fuse or circuit
breaker
> > should hold indefinitely at 15 amperes, but the NEC recognizes that 
> > allowing
> > 100% of rated current is never a good idea, since wiring in attics may
> > already be in a very hot environment.  Therefore, the NEC requires
that no
> > ordinary branch circuit be permitted to be loaded more than 80% of the
> > circuit rating.  That's where the 12 and 16 ampere limits come from.
> >
> > Another issue is voltage drop, which is directly proportional to
circuit
> > loading.  Circuits that are loaded to 100% of rating will probably
have
> > excessive voltage drop, which leads to inefficient operation.  Good
> > electrical design dictates that the wire size be increased for
long runs, 
> > to
> > keep the voltage drop below 3%.  Moreover, an adequate electrical
supply
> > system should never experience more than 80% loading of any
circuit.  Very
> > heavy single loads should have a dedicated branch circuit of suitable
> > capacity, with a single outlet.
> >
> > 73, Eric Lemmon WB6FLY
> >
> >
>