Thank you Eric Lemmon !  Your explanation is the most precise I've read thus 
far.
The last line of your last paragraph said what folks want to hear.  I 
started to respond
to this thread earlier, but after a few minutes of organizing my thoughts, 
my aging pea-brain
said, "Forget this and go get another gin & tonic !  What's another few 
brain cells anyway ?"

de WD7F
John in Tucson

----- Original Message ----- 
From: "Eric Lemmon" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, September 16, 2008 9:59 PM
Subject: RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)


> John,
>
> You are correct that when the power factor is 1.00, the current is in 
> phase
> with the voltage, as it will be in a purely resistive circuit.  In this
> unique case, watts equals volt-amperes.  However, when the load is 
> reactive,
> the current either leads or lags the applied voltage.  A typical case is a
> lightly-loaded induction motor, which may exhibit a power factor around
> 0.65, which is considered to be a "poor" PF.  Some of the current drawn by
> this motor is used to create torque and perform actual work, and this
> current is nearly in phase with the applied voltage.  Some current causes
> heating of the copper windings and the field core, and this current is 
> also
> nearly in phase with the applied voltage.  Both of these currents consume
> true power and are measured in watts.  However, a significant amount of
> current does nothing but magnetize the field windings during part of the 
> AC
> cycle, and that reactive energy is returned to the source as the magnetic
> field collapses just before the field is built up with the opposite 
> polarity
> during the other half of the AC cycle.  There are additional reactive
> losses, such as eddy-current and hysteresis losses, but the magnetizing
> currents are lagging the applied voltage, so they are the cause of 
> "apparent
> power" which is expressed in volt-amperes reactive, also known as VARs.
>
> As was discussed at great length in this forum several months ago, one
> cannot measure true power with separate voltage and current meters.  That 
> is
> because the readings of separate meters are not synchronized in time. 
> Even
> if one uses two "true RMS" DVMs to measure voltage and current, one still
> winds up with nothing more than apparent power based upon volts times
> amperes, or volt-amperes.
>
> To measure true power, one must use an AC power meter that synchronously
> measures current and voltage throughout the entire cycle.  This can be
> performed by a device called a "four-quadrant multiplier" which, as its 
> name
> implies, performs the multiplication of current and voltage through 360
> degrees of phase rotation.  One such instrument is a VIZ Instruments 
> WD-767
> Digital Wattmeter, which sold for about $925.  Another device which has
> become very popular with Hams is the "Kill-A-Watt" meter that costs about
> $20 from several Internet vendors.  Although not as accurate as the 
> WD-767,
> it does perform quite well.
>
> As I stated in an earlier post, the rotating-disk kWH meter on the typical
> residence measures only true power.  It does this magic by combining the
> magnetic fields of two coils: a voltage coil that is connected in parallel
> with the load, and a current coil that is in series with the load.  The
> angular displacement of these coil windings is precisely set so that only
> currents that are exactly in phase with the voltage result in a torque to
> turn the aluminum disk.  A small permanent magnet is placed near the disk 
> so
> that the speed of the disk is proportional to the amount of true power 
> being
> consumed.  Since speed is movement over time, the disk is geared to a
> register that accumulates the number of rotations, which represents power
> over time, which is energy.  Thus, the meter measures kilowatthours.  You
> pay only for the true power that you actually use; you do not pay for
> "apparent power" since volt-amperes is not true power.
>
> 73, Eric Lemmon WB6FLY
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[EMAIL PROTECTED] On Behalf Of John Barrett
> Sent: Tuesday, September 16, 2008 9:13 PM
> To: [email protected]
> Subject: Re: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)
>
> This doesn't mesh up with what I've learned about power factor -- the
> impression that I got was a perfect power factor was 1 (one) (current in
> phase with voltage, equipment using everything the the power company
> charges you for to do useful work). Anything other than PF=1 meant that
> the equipment was using the power less efficiently, and therefore you
> were paying more in KWH than the work actually performed. That
> description excludes the possibly that the equipment could use more
> power than the power company records as being delivered (heck,
> conservation of energy says that in any case). any load reactance
> (inductive or capacitive) and the very low PF numbers stated sound more
> like what I get off my linear power supplies with big capacitance and no
> power factor correction. In any case, anything other than PF=1 should
> mean that you are paying for more power than you are actually using.
>
> Tell me where I goofed this up ??
>
> Bob M. wrote:
>>
>> Thank you Eric. This was the explanation I was looking for. The UPS is
>> saving me money when drawing 181 Volt-Amps, yet the electric meter is
>> only recording and charging me for 31 Watts. I wonder if APC did this
>> on purpose. I don't know how much current is actually being fed to the
>> batteries; they've been in there for a couple of months and should be
>> fully charged by now, so it should just be trickling them (eight 12V
>> 7A SLA cells in series/parallel for 48V).
>>
>> Bob M.
>> ======
>> --- On Tue, 9/16/08, Eric Lemmon <[EMAIL PROTECTED]
> <mailto:wb6fly%40verizon.net>
>> <mailto:wb6fly%40verizon.net>> wrote:
>>
>> > From: Eric Lemmon <[EMAIL PROTECTED] <mailto:wb6fly%40verizon.net>
> <mailto:wb6fly%40verizon.net>>
>> > Subject: RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)
>> > To: [email protected]
> <mailto:Repeater-Builder%40yahoogroups.com>
>> <mailto:Repeater-Builder%40yahoogroups.com>
>> > Date: Tuesday, September 16, 2008, 9:21 PM
>> > Albert,
>> >
>> > You are forgiven, because you pose an important question!
>> >
>> > The spinning aluminum disk in the kilowatthour meter found
>> > on most
>> > residential service-entrance panels measures true power in
>> > kilowatts versus
>> > time, which equals energy. Thus, your electric utility
>> > charges you for the
>> > true power you use, not for volts times amperes- known as
>> > reactive power.
>> > Although the utility must provide the capability to supply
>> > all of the
>> > amperes you need, some of those amperes are "given
>> > back" to the utility due
>> > to a lower than unity power factor. That is why many
>> > utility companies
>> > charge a "kVAR Penalty" to certain industrial
>> > power users whose volt-ampere
>> > demands far exceed their watt demands, meaning that the
>> > power factor is low.
>> > Industrial power users strive to keep their power factors
>> > at 0.95 or above,
>> > to avoid some really painful penalties! The power factor,
>> > or PF, is simply
>> > watts divided by volts time amperes.
>> >
>> > The issue of power factor is why large Diesel generator
>> > sets have ratings
>> > such as 1000 kW/1250 kVAR. In simple terms, any AC
>> > generator requires
>> > torque (engine horsepower) to meet true power demands, and
>> > excitation (field
>> > flux intensity) to meet reactive power demands. When the
>> > generator load is
>> > reactive, that is, it has a power factor less than unity,
>> > the generator must
>> > not only have the horsepower to supply the energy in watts,
>> > but it must have
>> > excess capacity to handle the additional current required
>> > by motors and
>> > other low-power-factor loads. In a nutshell, that is why a
>> > 1000 watt
>> > generator may be unable to keep running a refrigerator that
>> > uses only 900
>> > watts; the fridge may require 1200 VA to operate because it
>> > has a low power
>> > factor, and the small generator has no ability to handle
>> > such loads.
>> > Because of its relatively small amount of spinning mass,
>> > such a small
>> > generator probably could not even handle the
>> > refrigerator's starting
>> > current- which is about 5 to 6 times its running current.
>> >
>> > 73, Eric Lemmon WB6FLY
>> >
>> >
>> >
>> > -----Original Message-----
>> > From: [email protected]
> <mailto:Repeater-Builder%40yahoogroups.com>
>> <mailto:Repeater-Builder%40yahoogroups.com>
>> > [mailto:[email protected]
> <mailto:Repeater-Builder%40yahoogroups.com>
>> <mailto:Repeater-Builder%40yahoogroups.com>] On Behalf Of
>> > Albert
>> > Sent: Tuesday, September 16, 2008 2:13 PM
>> > To: [email protected]
> <mailto:Repeater-Builder%40yahoogroups.com>
>> <mailto:Repeater-Builder%40yahoogroups.com>
>> > Subject: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging
>> > Power)
>> >
>> > Hopefully, you will forgive me for hijacking the post, but
>> > this brings up a
>> > question I have had for a long time. What on earth is a
>> > "volt-amp"?
>> > My logic would state that is is the same as a watt, which
>> > is volts x amps,
>> > as you probably well know. So what on earth is it?
>> >
>> > Confused.....
>> >
>> > Albert
>>
>>
>
>
>

Reply via email to