Martin,

Sure!  The National Electrical Code (NEC) requires that the equipment
grounding conductor (green or bare wire) must always follow the same route
and wireway used by the supply and return conductors.  There must never be
any deviation from this basic requirement.  The three wires (hot, neutral,
and ground) feeding every receptacle must always run together, but the R56
manual proposes that the grounding conductors of some "technical"
receptacles shall follow a path separate from the hot and neutral
conductors.  That is not allowed by the NEC, since that would greatly
increase the impedance of the grounding system and thereby reduce the
protection of the circuit against faults.  Also, the NEC requires that the
system grounding conductors, equipment grounding conductors, and lightning
protection grounding conductors must ultimately be bonded together to create
ONE grounding system.  The R56 manual proposes a scheme that creates
separate grounding circuits that can create dangerous voltages on some
circuits if a fault occurs on another circuit.  Despite some really creative
schemes to create separate grounding paths, such schemes are not allowed by
the NEC or by state electrical codes based upon the NEC.

Readers following this thread should be aware that the NEC is updated every
three years, and becomes law as each state or commonwealth ratifies it
through legislative action.  The current edition of the National Electrical
Code, NFPA 70, is the 2008 edition.

73, Eric Lemmon WB6FLY


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of rahwayflynn
Sent: Wednesday, April 08, 2009 6:39 PM
To: [email protected]
Subject: [Repeater-Builder] Re: Motorola R56 grounding



--- In [email protected]
<mailto:Repeater-Builder%40yahoogroups.com> , "Eric Lemmon" <wb6...@...>
wrote:
> However, there are a few recommendations for equipment 
> grounding that violate the National Electrical Code, and would be
> nixed by a competent electrical inspector. 

Eric,
I have NFPA 70 and the R56 document: Do you have examples of the the above?
I would like to do an "eyeball compare". 

With that in mind, a precedence statement needs to go into the tower lease
agreement I have in the library.

Martin