I'm going to disagree with the following posting:

If the tower is bolted to galvanized pipe that is embedded in concrete
of
which a significant amount is in contact with soil, you have a
"concrete-encased grounding electrode" which is hard to improve upon. It
is
not likely that a ground rod would be worthwhile, since damp concrete
(concrete in intimate contact with soil at grade level) is a fairly good
conductor, and such a footing or foundation has hundreds of times the
surface area of a ground rod.

I have read Ericsson specs for cellular tower installation in that
disagrees with the previous statement.

Standard concrete without conductive enhancing materials can crack, pop
or crumble if subjected to a direct lightning strike if ground rods are
not properly installed.   The water contained within the concrete will
vaporize instantly causing the concrete to fail.
There are types of conductive concrete mixes or additives that can be
used, but the most common practice is to use a ground rod from each leg
with a copper wire bonded to each tower leg.

Our mfg building at work is made from steel I-Beams into concrete.  I
have noticed each I-Beam has its own ground connection.  The strap is
bolted to the beam about 1" above the concrete, then disappears into the
concrete, and suspect there is a ground rod going into the soil beneath
the concrete piling, but that's just a theory, as I dident see it before
the mud was poured.

Ed N3SDO