Hi,

Sealed Lead Acid Gel batteries do not vent under normal conditions.
Referring to 12 V batteries: Just make sure the maximum charging voltage is
as per the batteries spec. (usually about 12.65V at 25deg C) My experience
is that even when they have been left erroneously charging continuously in
equalization mode at 14.4V they bulge, dry out &  loose capacity pretty
quickly but they don't gas and they don't leak.  Sealed Gel cells generally
should not be equalized at a higher charging voltage. So if you have an
equalization setting disable it.  Some chargers may have a temp sensor which
should be placed on the batteries casing, this helps to adjust the chargers
batteries charging voltage to match changes in temperature.

As such they are safe to have in the same room as your equipment.

I have not yet used AGM type sealed batteries, but they are supposed to be
much more durable under repeated deep discharge cycles, a batteries worst
enemy in reducing their lifetime.  For this reason they are highly
recommended for Solar systems.

Peter

On Sat, Aug 7, 2010 at 5:05 PM, tahrens301 <[email protected]> wrote:

>
>
> Hi Folks,
>
> I got a couple of the large AGM batteries for
> a solar installation, and was wondering if
> there is any condition that will lead them
> to vent inside the enclosure? They are sealed,
> but probably have one-way valves.
>
> Can I put the solar controller in the same
> enclosure?
>
> Figured some of you folks have done solar stuff
> before.
>
> Thanks,
>
> Tim
>
>  
>

Reply via email to