Based on the APC web site, if you installed a network
management card in the smart slot then it will give you the SNMP
connectivity.
You can use any one of these (from APC
website):
-----------------------
Network Management Card
Products Part Number
UPS Network Management Card AP9617
UPS Network Management Card w/ Environmental Monitoring & Out of Band Management AP9618
UPS Network Management Card w/ Environmental Monitoring AP9619
Products Part Number
UPS Network Management Card AP9617
UPS Network Management Card w/ Environmental Monitoring & Out of Band Management AP9618
UPS Network Management Card w/ Environmental Monitoring AP9619
------------------------
After
you've done this then the MIB is on the CD that came with the Management card,
and using GETIF (Clusty search for the free software - it's a MIB walker) you
can find the OIDs you need to monitor. Then it's a simple matter to have SA
check it.
Personally my fav is the 9619 so I can monitor temp and humidity in the
data closet as well.
As for
the OIDs I've used, here's a basic few. NOTE: depending on the card you
install not all of these will be available:
------------------------
.1.3.6.1.4.1.318.1.1.1.2.2.1.0
APC UPS Advanced Battery
Capacity
.1.3.6.1.4.1.318.1.1.1.2.2.2.0 APC UPS Advanced Battery Temperature
.1.3.6.1.4.1.318.1.1.1.2.2.3.0 APC UPS Advanced Battery Run Time Remaining
.1.3.6.1.4.1.318.1.1.1.2.2.4.0 APC UPS Advanced Battery Replace Indicator
.1.3.6.1.4.1.318.1.1.1.2.2.6.0 APC UPS Advanced Battery Number of Bad Battery Packs
.1.3.6.1.4.1.318.1.1.1.3.2.5.0 APC UPS Advanced Input Line Fail Cause
.1.3.6.1.4.1.318.1.1.1.4.1.1.0 APC UPS Basic Output Status
.1.3.6.1.4.1.318.1.1.1.4.2.3.0 APC UPS Advanced Output Load
.1.3.6.1.4.1.318.1.1.1.7.2.3.0 APC UPS Advanced Test Diagnostic Results
.1.3.6.1.4.1.318.1.1.1.7.2.4.0 APC UPS Advanced Test Last Diagnostics Date
.1.3.6.1.4.1.318.1.1.2.1.1.0 APC UPS Environment Ambient Temperature
.1.3.6.1.4.1.318.1.1.2.1.2.0 APC UPS Environment Relative Humidity
.1.3.6.1.4.1.318.1.1.2.1.3.0 APC UPS Environment Ambient Temperature 2
.1.3.6.1.4.1.318.1.1.2.1.4.0 APC UPS Environment Relative Humidity 2
.1.3.6.1.4.1.318.1.1.2.2.2.1.5.1 APC UPS Contact Entry 1
.1.3.6.1.4.1.318.1.1.2.2.2.1.5.2 APC UPS Contact Entry 2
.1.3.6.1.4.1.318.1.1.2.2.2.1.5.3 APC UPS Contact Entry 3
.1.3.6.1.4.1.318.1.1.2.2.2.1.5.4 APC UPS Contact Entry 4
.1.3.6.1.4.1.318.1.1.1.2.2.2.0 APC UPS Advanced Battery Temperature
.1.3.6.1.4.1.318.1.1.1.2.2.3.0 APC UPS Advanced Battery Run Time Remaining
.1.3.6.1.4.1.318.1.1.1.2.2.4.0 APC UPS Advanced Battery Replace Indicator
.1.3.6.1.4.1.318.1.1.1.2.2.6.0 APC UPS Advanced Battery Number of Bad Battery Packs
.1.3.6.1.4.1.318.1.1.1.3.2.5.0 APC UPS Advanced Input Line Fail Cause
.1.3.6.1.4.1.318.1.1.1.4.1.1.0 APC UPS Basic Output Status
.1.3.6.1.4.1.318.1.1.1.4.2.3.0 APC UPS Advanced Output Load
.1.3.6.1.4.1.318.1.1.1.7.2.3.0 APC UPS Advanced Test Diagnostic Results
.1.3.6.1.4.1.318.1.1.1.7.2.4.0 APC UPS Advanced Test Last Diagnostics Date
.1.3.6.1.4.1.318.1.1.2.1.1.0 APC UPS Environment Ambient Temperature
.1.3.6.1.4.1.318.1.1.2.1.2.0 APC UPS Environment Relative Humidity
.1.3.6.1.4.1.318.1.1.2.1.3.0 APC UPS Environment Ambient Temperature 2
.1.3.6.1.4.1.318.1.1.2.1.4.0 APC UPS Environment Relative Humidity 2
.1.3.6.1.4.1.318.1.1.2.2.2.1.5.1 APC UPS Contact Entry 1
.1.3.6.1.4.1.318.1.1.2.2.2.1.5.2 APC UPS Contact Entry 2
.1.3.6.1.4.1.318.1.1.2.2.2.1.5.3 APC UPS Contact Entry 3
.1.3.6.1.4.1.318.1.1.2.2.2.1.5.4 APC UPS Contact Entry 4
--------------------------------
Also,
Note, if you are monitoring a large number of APC UPSs (like in a campus
environment) then I recommend purchasing APCs ISX Manager. It will do all
monitoring of devices for you and even keep their firmware up to
date!!!
Hope
this helps!!!!!
Michael D. Shook
Technical Analyst
[EMAIL PROTECTED]
863 668 4477
(work)
863 860 4070 (cell)
863 665 1261 (fax)
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ahmed Hassan
Sent: Monday, January 09, 2006 3:39 AM
To: Salive
Subject: [SA-list] Mibs for Smart-UPS RT 10000XLIJust checking whether anyone is using SAlive to monitor a Smart-UPS RT 10000XLI? If so what/how are they using SAlive to perform the checks and any MIBS etc available to share.
Thanks
Play Santa's Celebrity Xmas Party, an exclusive game from Yahoo!