Common point neutral is a good thing.
But distributed earth grounds for the true ground circuit is good too.

The main thing you want to accomplish for safety’s sake is to allow fault 
currents to find the lowest impedance path to ground as possible.  It is OK to 
have some voltage drop on neutral circuits, but if a bad wire causes the 
chassis of a washing machine to become energized, you want that ground wire in 
the cord to find the lowest potential possible.  Otherwise you could be 
touching the washing machine and the faucet at the same time and get zapped.  
If the building ground and plumbing and earth are all at the same potential, 
that would not happen.  

Earth ground circuits are also important to allow circuit breakers to trip as 
soon as a fault happens.  Again, low impedance ground circuits help with that.  
I would drive ground rods.  But I would also make sure that the neutral bars 
are floating and not bonded.  That would prevent ground loops for the normal 
power currents.  

From: Paul McCall 
Sent: Tuesday, May 05, 2015 7:01 PM
To: af@afmug.com 
Subject: [AFMUG] another grounding scenario ??

We are doing a new tower.  Here’s the layout

 

Customer house (Building “A”) has a small building (Building “B” for discussion 
purposes) about 150 feet away from main house.  “B” has a sub-panel and 5 live 
breakers for various things.  There is a 6 gauge ground wire between “B” and 
the Customer house.   “B” connects to another “tack / feeding house”  (Building 
“C”) about 60 feet away with another subpanel running off “B” using a 8 gauge 
ground wire between those two panels.  Neither “B” nor “C” has a ground rod, so 
they are relying on ground that is ultimately, going back to the Customers 
house.

 

Our tower box is going to be 200 feet away from Building “C” and because of 
practicalities, going back to “B” instead is not possible even if we thought 
that was best.   So, I am running 4 gauge wire as our ground from our box to 
“C” but am concerned about making sure the ground is handled from that point 
on.  An electrician on-site said that each building should actually have its 
own “local ground” (his simple answer was “drive a ground rod”) .  

 

The question I have is does that make sense as a complete (best solution)…   
making sure that Panel “C” is well grounded (and “B” too just for good measure) 
??  In the single source ground concept, is his suggestion still make the best 
sense?

 

Paul

 

Paul McCall, Pres.

PDMNet / Florida Broadband 

658 Old Dixie Highway

Vero Beach, FL 32962

772-564-6800 office

772-473-0352 cell

www.pdmnet.com

pa...@pdmnet.net

 


Re: [AFMUG] another grounding scenario ??

2015-05-06 Thread Seth Mattinen

On 5/6/15 7:32 AM, Chuck McCown wrote:

Earth ground circuits are also important to allow circuit breakers to
trip as soon as a fault happens.  Again, low impedance ground circuits
help with that.  I would drive ground rods.  But I would also make sure
that the neutral bars are floating and not bonded.  That would prevent
ground loops for the normal power currents.



With pictures:

https://www.mikeholt.com/instructor2/img/product/pdf/1292432628sample.pdf

~Seth


Re: [AFMUG] another grounding scenario ??

2015-05-06 Thread Paul McCall
Good info.  We did already verify neutrals and grounds are not tied together.  
We will definitely drive ground rods at each panel based on the feedback here.

From: Af [mailto:af-boun...@afmug.com] On Behalf Of Chuck McCown
Sent: Wednesday, May 06, 2015 10:33 AM
To: af@afmug.com
Subject: Re: [AFMUG] another grounding scenario ??

Common point neutral is a good thing.
But distributed earth grounds for the true ground circuit is good too.

The main thing you want to accomplish for safety’s sake is to allow fault 
currents to find the lowest impedance path to ground as possible.  It is OK to 
have some voltage drop on neutral circuits, but if a bad wire causes the 
chassis of a washing machine to become energized, you want that ground wire in 
the cord to find the lowest potential possible.  Otherwise you could be 
touching the washing machine and the faucet at the same time and get zapped.  
If the building ground and plumbing and earth are all at the same potential, 
that would not happen.

Earth ground circuits are also important to allow circuit breakers to trip as 
soon as a fault happens.  Again, low impedance ground circuits help with that.  
I would drive ground rods.  But I would also make sure that the neutral bars 
are floating and not bonded.  That would prevent ground loops for the normal 
power currents.

From: Paul McCallmailto:pa...@pdmnet.net
Sent: Tuesday, May 05, 2015 7:01 PM
To: af@afmug.commailto:af@afmug.com
Subject: [AFMUG] another grounding scenario ??

We are doing a new tower.  Here’s the layout

Customer house (Building “A”) has a small building (Building “B” for discussion 
purposes) about 150 feet away from main house.  “B” has a sub-panel and 5 live 
breakers for various things.  There is a 6 gauge ground wire between “B” and 
the Customer house.   “B” connects to another “tack / feeding house”  (Building 
“C”) about 60 feet away with another subpanel running off “B” using a 8 gauge 
ground wire between those two panels.  Neither “B” nor “C” has a ground rod, so 
they are relying on ground that is ultimately, going back to the Customers 
house.

Our tower box is going to be 200 feet away from Building “C” and because of 
practicalities, going back to “B” instead is not possible even if we thought 
that was best.   So, I am running 4 gauge wire as our ground from our box to 
“C” but am concerned about making sure the ground is handled from that point 
on.  An electrician on-site said that each building should actually have its 
own “local ground” (his simple answer was “drive a ground rod”) .

The question I have is does that make sense as a complete (best solution)…   
making sure that Panel “C” is well grounded (and “B” too just for good measure) 
??  In the single source ground concept, is his suggestion still make the best 
sense?

Paul

Paul McCall, Pres.
PDMNet / Florida Broadband
658 Old Dixie Highway
Vero Beach, FL 32962
772-564-6800 office
772-473-0352 cell
www.pdmnet.comhttp://www.pdmnet.com/
pa...@pdmnet.netmailto:pa...@pdmnet.net



[AFMUG] another grounding scenario ??

2015-05-05 Thread Paul McCall
We are doing a new tower.  Here's the layout

Customer house (Building A) has a small building (Building B for discussion 
purposes) about 150 feet away from main house.  B has a sub-panel and 5 live 
breakers for various things.  There is a 6 gauge ground wire between B and 
the Customer house.   B connects to another tack / feeding house  (Building 
C) about 60 feet away with another subpanel running off B using a 8 gauge 
ground wire between those two panels.  Neither B nor C has a ground rod, so 
they are relying on ground that is ultimately, going back to the Customers 
house.

Our tower box is going to be 200 feet away from Building C and because of 
practicalities, going back to B instead is not possible even if we thought 
that was best.   So, I am running 4 gauge wire as our ground from our box to 
C but am concerned about making sure the ground is handled from that point 
on.  An electrician on-site said that each building should actually have its 
own local ground (his simple answer was drive a ground rod) .

The question I have is does that make sense as a complete (best solution)...   
making sure that Panel C is well grounded (and B too just for good measure) 
??  In the single source ground concept, is his suggestion still make the best 
sense?

Paul

Paul McCall, Pres.
PDMNet / Florida Broadband
658 Old Dixie Highway
Vero Beach, FL 32962
772-564-6800 office
772-473-0352 cell
www.pdmnet.comhttp://www.pdmnet.com/
pa...@pdmnet.netmailto:pa...@pdmnet.net



Re: [AFMUG] another grounding scenario ??

2015-05-05 Thread Jeremy
The electricians that I have spoken with say bond to existing power ground
and then pound another rod right at your connection.  That is what we've
always done.

On Tue, May 5, 2015 at 7:01 PM, Paul McCall pa...@pdmnet.net wrote:

  We are doing a new tower.  Here’s the layout



 Customer house (Building “A”) has a small building (Building “B” for
 discussion purposes) about 150 feet away from main house.  “B” has a
 sub-panel and 5 live breakers for various things.  There is a 6 gauge
 ground wire between “B” and the Customer house.   “B” connects to another
 “tack / feeding house”  (Building “C”) about 60 feet away with another
 subpanel running off “B” using a 8 gauge ground wire between those two
 panels.  Neither “B” nor “C” has a ground rod, so they are relying on
 ground that is ultimately, going back to the Customers house.



 Our tower box is going to be 200 feet away from Building “C” and because
 of practicalities, going back to “B” instead is not possible even if we
 thought that was best.   So, I am running 4 gauge wire as our ground from
 our box to “C” but am concerned about making sure the ground is handled
 from that point on.  An electrician on-site said that each building should
 actually have its own “local ground” (his simple answer was “drive a ground
 rod”) .



 The question I have is does that make sense as a complete (best
 solution)…   making sure that Panel “C” is well grounded (and “B” too just
 for good measure) ??  In the single source ground concept, is his
 suggestion still make the best sense?



 Paul



 Paul McCall, Pres.

 PDMNet / Florida Broadband

 658 Old Dixie Highway

 Vero Beach, FL 32962

 772-564-6800 office

 772-473-0352 cell

 www.pdmnet.com

 pa...@pdmnet.net





Re: [AFMUG] another grounding scenario ??

2015-05-05 Thread Bill Prince
The general rule is one grounding point. However, if the sub panels are 
far enough apart and/or the interconnecting ground wire is too small, 
you might consider adding another ground rod. I'm guessing that the 
distance to your tower is far enough away from the original ground and 
the interconnect is small enough that you might want to drive another 
ground rod.


OTOH, I am not an electrician...

bp
part15sbs{at}gmail{dot}com

On 5/5/2015 6:01 PM, Paul McCall wrote:


We are doing a new tower.  Here�s the layout

Customer house (Building �A�) has a small building (Building �B� for 
discussion purposes) about 150 feet away from main house.  �B� has a 
sub-panel and 5 live breakers for various things.  There is a 6 gauge 
ground wire between �B� and the Customer house.   �B� connects to 
another �tack / feeding house�  (Building �C�) about 60 feet away with 
another subpanel running off �B� using a 8 gauge ground wire between 
those two panels.  Neither �B� nor �C� has a ground rod, so they are 
relying on ground that is ultimately, going back to the Customers house.


Our tower box is going to be 200 feet away from Building �C� and 
because of practicalities, going back to �B� instead is not possible 
even if we thought that was best.   So, I am running 4 gauge wire as 
our ground from our box to �C� but am concerned about making sure the 
ground is handled from that point on.  An electrician on-site said 
that each building should actually have its own �local ground� (his 
simple answer was �drive a ground rod�) .


The question I have is does that make sense as a complete (best 
solution)�   making sure that Panel �C� is well grounded (and �B� too 
just for good measure) ??  In the single source ground concept, is his 
suggestion still make the best sense?