Re: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-26 Thread Dinesh Nair



On 04/25/06 05:58 Sangoma Techdesk said the following:
At Sangoma we do quite a lot of back-to back T1 and E1 
connections. T1 is not a very fussy connection, as the baud 
rate is only about 750 kbps.
 
In our experience, for error free communications you can use 
the following rules of thumb:

Up to 50 ft:  Flat patch cable
Up to 500 ft: Ordinary twisted telephone cable Cat 5 may be 
overkill unless you are going hundreds of feet.


we've faced weird intermittent problems and we suspect it's related to 
electrical interference caused by power cables et al in the server rack. 
we've seen this with both sangoma and digium cards when attempting to 
connect asterisk boxes to carrier E1s provided by the local operator. the 
cables used are normal cat5 UTP cables.


--
Regards,   /\_/\   All dogs go to heaven.
[EMAIL PROTECTED](0 0)http://www.alphaque.com/
+==oOO--(_)--OOo==+
| for a in past present future; do|
|   for b in clients employers associates relatives neighbours pets; do   |
|   echo The opinions here in no way reflect the opinions of my $a $b.  |
| done; done  |
+=+
___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
  http://lists.digium.com/mailman/listinfo/asterisk-users


Re: Shielding of T1/E1 cables WAS RE: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-25 Thread Andrew Latham
Also note that the Smart Jack allows the Telco to provide T1
Signalling in places that it couldn't in the past, most smart jacks
that I have used are:

[CO]-Optical-[Hut DMS]--[Hut Smart Jack]-HDSL-[CPE Smart Jack]

For the list, Telco Techs, mostly do as they are told, and are
schooled by the Telco vendors.


On 4/24/06, Rich Adamson [EMAIL PROTECTED] wrote:
 Alexander Lopez wrote:
  I was once told by a lineman that the cables they use didn't have that
  many twists in them because it wasn't needed, and that the extra twists
  would effectively use more cable and thus cost and weigh more than
  triple what they do now.

 Good thing he doesn't work for a cable manufacturer as that's a total
 crock of crap that even an inexperienced person should be able to
 detect. (You can't twist two wires to make them weight three times as
 much, or cost three times as much.)

  He told me that with the number of twists in
  the Cat 5 cable it would cancel out any interference, but he also stated
  that the effective length was calculated using a cable with less twists
  and subsequently 'less dense' and that if using a Cat5e cable you must
  factor that in. so if you use cat5e cable your are fine but you can't go
  as far.

 Essentially true, but the impedance of a T1 cable is different from Cat5
 cables, which is one of the primary factors in limiting distance. Has
 nothing to do with the twists.

 Shielded vs non-shielded has to do with the environment, and how much
 electrical noise there is near the T1 cable. Nothing more, nothing less.

  Regarding the Smart Jack it is mostly used as a location at the CPE
  where the Telco can loop and make sure that the problem is at your end.
  So your assumption is correct that you can plug anything you want into
  it, its one your side of the demark, so if it doesn't work it's YOUR
  problem.


 ___
 --Bandwidth and Colocation provided by Easynews.com --

 Asterisk-Users mailing list
 To UNSUBSCRIBE or update options visit:
http://lists.digium.com/mailman/listinfo/asterisk-users



--
---
Andrew Latham - AKA: LATHAMA (lay-th-ham-eh)
[EMAIL PROTECTED] - [EMAIL PROTECTED] - [EMAIL PROTECTED]
If any of the above are down we have bigger problems than my email!
Hind sight is most always 20/20 or better.
---
___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
   http://lists.digium.com/mailman/listinfo/asterisk-users


Re: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-24 Thread Rich Adamson

Can't anyone stop self-promotion and tell the poor guy what he needs.

A T1/E1 X-over cable using an RJ-45 (8-cond.) is pinned out as follows:

1 - 4
2 - 5
3 - NU
4 - 1
5 - 2
6 - NU
7 - NU
8 - NU

NU = Not Used

I have not in my experience seen any problems with using a Good Quality
Cat5 vs. Cat 3 (telco standard) cable for X-connects.  YMMV, but you
should be fine. As far as the shielding goes, I use UTP cables and
Connectors all the time and some of my X-connects run over 100 feet.


It would probably be helpful for everyone reading this thread to 
understand what the differences are in the two types of cables. 
Primarily impedance matching, twists per foot, shielding, etc.


For short runs, the use of cat5 vs proper T1 cables isn't likely to have 
any impact unless there is a fair amount of induction from electrical 
noise, etc. That can take the form of florescent fixtures, transformers, 
older CRT monitors, etc, etc.


On longer runs, the shielded T1 cables are likely to provide better 
results particularly if there happens to be any electrical noise.


Oh, and if shielded T1 cable is used, the shield at each end of the 
cable must be grounded. (Let's see how many can figure out how to do 
that via an rj45 plug. ;)


___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
  http://lists.digium.com/mailman/listinfo/asterisk-users


Re: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-24 Thread Leo Ann Boon

Rich Adamson wrote:


snip
For short runs, the use of cat5 vs proper T1 cables isn't likely to 
have any impact unless there is a fair amount of induction from 
electrical noise, etc. That can take the form of florescent fixtures, 
transformers, older CRT monitors, etc, etc.


On longer runs, the shielded T1 cables are likely to provide better 
results particularly if there happens to be any electrical noise.


Oh, and if shielded T1 cable is used, the shield at each end of the 
cable must be grounded. (Let's see how many can figure out how to do 
that via an rj45 plug. ;)


Totally agree with you, unshielded cables are only usable if the 
distance is short. Just curious, how should one ground the shield? Do 
you ground it to the ground bar in the server room? Any special 
requirements?


TIA



___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
  http://lists.digium.com/mailman/listinfo/asterisk-users


Re: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-24 Thread Rich Adamson

Leo Ann Boon wrote:

Rich Adamson wrote:


snip
For short runs, the use of cat5 vs proper T1 cables isn't likely to 
have any impact unless there is a fair amount of induction from 
electrical noise, etc. That can take the form of florescent fixtures, 
transformers, older CRT monitors, etc, etc.


On longer runs, the shielded T1 cables are likely to provide better 
results particularly if there happens to be any electrical noise.


Oh, and if shielded T1 cable is used, the shield at each end of the 
cable must be grounded. (Let's see how many can figure out how to do 
that via an rj45 plug. ;)


Totally agree with you, unshielded cables are only usable if the 
distance is short. Just curious, how should one ground the shield? Do 
you ground it to the ground bar in the server room? Any special 
requirements?


That would be one way to do it, at both ends.

Personally, I would not try to install an rj45 on each end of a shielded 
T1 cable, but rather terminate the cable on a patch panel.


___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
  http://lists.digium.com/mailman/listinfo/asterisk-users


RE: Shielding of T1/E1 cables WAS RE: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-24 Thread Alexander Lopez
I was once told by a lineman that the cables they use didn't have that
many twists in them because it wasn't needed, and that the extra twists
would effectively use more cable and thus cost and weigh more than
triple what they do now. He told me that with the number of twists in
the Cat 5 cable it would cancel out any interference, but he also stated
that the effective length was calculated using a cable with less twists
and subsequently 'less dense' and that if using a Cat5e cable you must
factor that in. so if you use cat5e cable your are fine but you can't go
as far.

Regarding the Smart Jack it is mostly used as a location at the CPE
where the Telco can loop and make sure that the problem is at your end.
So your assumption is correct that you can plug anything you want into
it, its one your side of the demark, so if it doesn't work it's YOUR
problem.




  Totally agree with you, unshielded cables are only usable if the
  distance is short. Just curious, how should one ground the shield?
Do
  you ground it to the ground bar in the server room? Any special
  requirements?
 
 That would be one way to do it, at both ends.
 
 Personally, I would not try to install an rj45 on each end of a
shielded
 T1 cable, but rather terminate the cable on a patch panel.
 
 ___
 --Bandwidth and Colocation provided by Easynews.com --
 
 Asterisk-Users mailing list
 To UNSUBSCRIBE or update options visit:
http://lists.digium.com/mailman/listinfo/asterisk-users
___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
   http://lists.digium.com/mailman/listinfo/asterisk-users


RE: Shielding of T1/E1 cables WAS RE: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-24 Thread Colin Anderson
My telco used cat5 as well for the demarc to CPE. It's also with noting that
many channel banks, such as my Atlas, and zapata.conf itself also have
parameters to allow you to tune the gains to compensate for cable signal
loss. I've never had to touch them, and my CPE is about 300 feet from the
PRI demarc (with an ordinary Cat5 cable connecting them) 
___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
   http://lists.digium.com/mailman/listinfo/asterisk-users


Re: Shielding of T1/E1 cables WAS RE: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-24 Thread Rich Adamson

Alexander Lopez wrote:

I was once told by a lineman that the cables they use didn't have that
many twists in them because it wasn't needed, and that the extra twists
would effectively use more cable and thus cost and weigh more than
triple what they do now. 


Good thing he doesn't work for a cable manufacturer as that's a total 
crock of crap that even an inexperienced person should be able to 
detect. (You can't twist two wires to make them weight three times as 
much, or cost three times as much.)



He told me that with the number of twists in
the Cat 5 cable it would cancel out any interference, but he also stated
that the effective length was calculated using a cable with less twists
and subsequently 'less dense' and that if using a Cat5e cable you must
factor that in. so if you use cat5e cable your are fine but you can't go
as far.


Essentially true, but the impedance of a T1 cable is different from Cat5 
cables, which is one of the primary factors in limiting distance. Has 
nothing to do with the twists.


Shielded vs non-shielded has to do with the environment, and how much 
electrical noise there is near the T1 cable. Nothing more, nothing less.



Regarding the Smart Jack it is mostly used as a location at the CPE
where the Telco can loop and make sure that the problem is at your end.
So your assumption is correct that you can plug anything you want into
it, its one your side of the demark, so if it doesn't work it's YOUR
problem.



___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
  http://lists.digium.com/mailman/listinfo/asterisk-users


Re: Shielding of T1/E1 cables WAS RE: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-24 Thread Dave Weis


On Mon, 24 Apr 2006, Rich Adamson wrote:

Alexander Lopez wrote:
 I was once told by a lineman that the cables they use didn't have that
 many twists in them because it wasn't needed, and that the extra twists
 would effectively use more cable and thus cost and weigh more than
 triple what they do now. 

Good thing he doesn't work for a cable manufacturer as that's a total 
crock of crap that even an inexperienced person should be able to 
detect. (You can't twist two wires to make them weight three times as 
much, or cost three times as much.)


A foot of cat5 has more than 12 on each of the individual wires inside. 
Not much but there is some difference.


--
Dave Weis I believe there are more instances of the abridgment
[EMAIL PROTECTED]   of the freedom of the people by gradual and silent
  encroachments of those in power than by violent
  and sudden usurpations.- James Madison
___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
  http://lists.digium.com/mailman/listinfo/asterisk-users


Re: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-24 Thread Kevin P. Fleming
Rich Adamson wrote:

 Oh, and if shielded T1 cable is used, the shield at each end of the
 cable must be grounded. (Let's see how many can figure out how to do
 that via an rj45 plug. ;)

You use shielded plugs and jacks, of course :-) That is why the
TE405P/TE410P have shielded jacks (as of about a year ago, IIRC). The
retail packaged cards even ship with four shielded cables included!

Minor point: isn't it safer to only ground the shield on one end?
___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
   http://lists.digium.com/mailman/listinfo/asterisk-users


Re: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-24 Thread Andrew Kohlsmith
On Monday 24 April 2006 12:13, Kevin P. Fleming wrote:
 Minor point: isn't it safer to only ground the shield on one end?

Yes, you *never* shield both ends.  That can cause ground loops and add to the 
long list of what the..? head-scratching problems that telephony has.

As to WHICH end to ground... well that's a subject that holy wars have been 
started over...

-A.
___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
   http://lists.digium.com/mailman/listinfo/asterisk-users


Re: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-24 Thread Rich Adamson

Kevin P. Fleming wrote:

Rich Adamson wrote:


Oh, and if shielded T1 cable is used, the shield at each end of the
cable must be grounded. (Let's see how many can figure out how to do
that via an rj45 plug. ;)


You use shielded plugs and jacks, of course :-) That is why the
TE405P/TE410P have shielded jacks (as of about a year ago, IIRC). The
retail packaged cards even ship with four shielded cables included!


Excellent!


Minor point: isn't it safer to only ground the shield on one end?


Best practices suggests IT/telco equipment racks throughout a building 
share a single grounding system (and not with 24 ga cable). Likewise, 
grounding of both ends of a T1 (eg, shield) is considered best practice. 
Treat a T1 cable as no different then a transmission line with a 1.5mhz 
RF signal.


If rack grounding is totally ignored (which probably happens 
frequently), there is a possibility of a ground loop created through the 
T1 shield. But, the root-cause is the lack of rack grounding, not 
leaving one end of a T1 cable ungrounded.


For safety, also think about the number of devices that are produced 
with poor power supplies, hot chassis, etc. Seen (and felt) several of 
those. ;)


R.

___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
  http://lists.digium.com/mailman/listinfo/asterisk-users


RE: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-24 Thread Sangoma Techdesk

At Sangoma we do quite a lot of back-to back T1 and E1 
connections. T1 is not a very fussy connection, as the baud 
rate is only about 750 kbps.
 
In our experience, for error free communications you can use 
the following rules of thumb:
Up to 50 ft:  Flat patch cable
Up to 500 ft: Ordinary twisted telephone cable Cat 5 may be 
overkill unless you are going hundreds of feet.


David Yat Sin
Sangoma Technologies
(905) 474 1990 x119
(800) 388 2475 x199
MSN: [EMAIL PROTECTED]
Email: [EMAIL PROTECTED]
Wiki: http://sangoma.editme.com
 



 
 Date: Mon, 24 Apr 2006 20:19:02 +0800
 From: Leo Ann Boon [EMAIL PROTECTED]
 Subject: Re: Pinouts for T1/E1 crossover cable WAS RE:
   [Asterisk-Users] what   cable to connect a legacy PBX 
 to a TE410P ?
 To: [EMAIL PROTECTED],Asterisk Users Mailing List -
   Non-Commercial Discussion   
 asterisk-users@lists.digium.com
 Message-ID: [EMAIL PROTECTED]
 Content-Type: text/plain; charset=ISO-8859-1; format=flowed
 
 Rich Adamson wrote:
 
  snip
  For short runs, the use of cat5 vs proper T1 cables isn't likely to 
  have any impact unless there is a fair amount of induction from 
  electrical noise, etc. That can take the form of florescent 
 fixtures, 
  transformers, older CRT monitors, etc, etc.
 
  On longer runs, the shielded T1 cables are likely to provide better 
  results particularly if there happens to be any electrical noise.
 
  Oh, and if shielded T1 cable is used, the shield at each end of the 
  cable must be grounded. (Let's see how many can figure out 
 how to do 
  that via an rj45 plug. ;)
 
 Totally agree with you, unshielded cables are only usable if 
 the distance is short. Just curious, how should one ground 
 the shield? Do you ground it to the ground bar in the server 
 room? Any special requirements?
 
 TIA
 
 
 
 
 


___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
   http://lists.digium.com/mailman/listinfo/asterisk-users


Re: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-23 Thread Salah Eddine ELMRABET
Hello,

The pinout is like 1,2,4,5 you need to use LED and check the signal, connect the telco send with your receive, your receive wth the telco send.

you need to be sure about some parametres, the line code (HDB3 or other, the CRC4 is on or off, the impedance 75 or 120 if you are using CAT5 you need to configure 120 ohm.

the best way is to test all parametres if you don't now your telco's parametres.

Best Regards,
On 4/22/06, Steve Totaro [EMAIL PROTECTED] wrote:
LOL-Original Message-From: Paul Mahler [mailto:
[EMAIL PROTECTED]]Sent: Sat 4/22/2006 11:09 AMTo: asterisk-users@lists.digium.comCc:Subject:Re: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?
A T carrier cable is not the same as an ethernet cable. A T carriercable uses a real metal shielded RJ-45 and loosely twisted pair wire.With most modern T carrier equipment, you can use a CAT-5 ethernet cableinstead of a real T carrier cable. A T-carrier crossover cable does nothave the same wiring pattern as a crossover ethernet cable. With anolder piece of equipment like the Matra, I would be tempted to purchasea real T carrier crossover cable. This is covered in my book, by the way.
Louis-David Mitterrand wrote:Hello,I am about to put an asterisk server between the telco E1 and our oldMatra PBX.Should I use an ethernet cross cable? Something else?
Paul [EMAIL PROTECTED]www.signate.com___--Bandwidth and Colocation provided by 
Easynews.com --Asterisk-Users mailing listTo UNSUBSCRIBE or update options visit:http://lists.digium.com/mailman/listinfo/asterisk-users
___--Bandwidth and Colocation provided by Easynews.com --Asterisk-Users mailing listTo UNSUBSCRIBE or update options visit:
http://lists.digium.com/mailman/listinfo/asterisk-users
___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
   http://lists.digium.com/mailman/listinfo/asterisk-users


Re: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-22 Thread Paul Mahler
A T carrier cable is not the same as an ethernet cable. A T carrier  cable uses 
a real metal shielded RJ-45 and loosely twisted pair wire.  With most modern T 
carrier equipment, you can use a CAT-5 ethernet cable  instead of a real T 
carrier cable. A T-carrier crossover cable does not  have the same wiring 
pattern as a crossover ethernet cable. With an  older piece of equipment like 
the Matra, I would be tempted to purchase  a real T carrier crossover cable. 
This is covered in my book, by the way. 
 
Louis-David Mitterrand wrote: 

Hello, 
 
I am about to put an asterisk server between the telco E1 and our old  Matra 
PBX.   
Should I use an ethernet cross cable? Something else?

  
Paul [EMAIL PROTECTED]
www.signate.com



___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
   http://lists.digium.com/mailman/listinfo/asterisk-users


RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-22 Thread Steve Totaro
LOL


-Original Message-
From:   Paul Mahler [mailto:[EMAIL PROTECTED]
Sent:   Sat 4/22/2006 11:09 AM
To: asterisk-users@lists.digium.com
Cc: 
Subject:Re: [Asterisk-Users] what cable to connect a legacy PBX to a 
TE410P ?

A T carrier cable is not the same as an ethernet cable. A T carrier  cable uses 
a real metal shielded RJ-45 and loosely twisted pair wire.  With most modern T 
carrier equipment, you can use a CAT-5 ethernet cable  instead of a real T 
carrier cable. A T-carrier crossover cable does not  have the same wiring 
pattern as a crossover ethernet cable. With an  older piece of equipment like 
the Matra, I would be tempted to purchase  a real T carrier crossover cable. 
This is covered in my book, by the way. 
 
Louis-David Mitterrand wrote: 

Hello, 
 
I am about to put an asterisk server between the telco E1 and our old  Matra 
PBX.   
Should I use an ethernet cross cable? Something else?

  
Paul [EMAIL PROTECTED]
www.signate.com



___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
   http://lists.digium.com/mailman/listinfo/asterisk-users



winmail.dat___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
   http://lists.digium.com/mailman/listinfo/asterisk-users


Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-22 Thread Alexander Lopez
Can't anyone stop self-promotion and tell the poor guy what he needs.

A T1/E1 X-over cable using an RJ-45 (8-cond.) is pinned out as follows:

1 - 4
2 - 5
3 - NU
4 - 1
5 - 2
6 - NU
7 - NU
8 - NU

NU = Not Used

I have not in my experience seen any problems with using a Good Quality
Cat5 vs. Cat 3 (telco standard) cable for X-connects.  YMMV, but you
should be fine. As far as the shielding goes, I use UTP cables and
Connectors all the time and some of my X-connects run over 100 feet.



-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Totaro
Sent: Saturday, April 22, 2006 11:49 AM
To: Paul Mahler; Asterisk Users Mailing List - Non-Commercial Discussion
Subject: RE: [Asterisk-Users] what cable to connect a legacy PBX to a
TE410P ?

LOL


-Original Message-
From:   Paul Mahler [mailto:[EMAIL PROTECTED]
Sent:   Sat 4/22/2006 11:09 AM
To: asterisk-users@lists.digium.com
Cc: 
Subject:Re: [Asterisk-Users] what cable to connect a legacy PBX
to a TE410P ?

A T carrier cable is not the same as an ethernet cable. A T carrier
cable uses a real metal shielded RJ-45 and loosely twisted pair wire.
With most modern T carrier equipment, you can use a CAT-5 ethernet cable
instead of a real T carrier cable. A T-carrier crossover cable does not
have the same wiring pattern as a crossover ethernet cable. With an
older piece of equipment like the Matra, I would be tempted to purchase
a real T carrier crossover cable. This is covered in my book, by the
way. 
 
Louis-David Mitterrand wrote: 

Hello, 
 
I am about to put an asterisk server between the telco E1 and our old
Matra PBX.   
Should I use an ethernet cross cable? Something else?

  
Paul [EMAIL PROTECTED]
www.signate.com



___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
   http://lists.digium.com/mailman/listinfo/asterisk-users


___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
   http://lists.digium.com/mailman/listinfo/asterisk-users


Re: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-22 Thread John Novack



Alexander Lopez wrote:


Can't anyone stop self-promotion and tell the poor guy what he needs.

Seems to me that SOME self promotion belongs on the biz list, and for 
those considered in the inner circle it is OK here!


Everyone is equal. Some are more equal than others

JMO

John Novack

___
--Bandwidth and Colocation provided by Easynews.com --

Asterisk-Users mailing list
To UNSUBSCRIBE or update options visit:
  http://lists.digium.com/mailman/listinfo/asterisk-users


Re: Pinouts for T1/E1 crossover cable WAS RE: [Asterisk-Users] what cable to connect a legacy PBX to a TE410P ?

2006-04-22 Thread Andrew

Alexander Lopez wrote:


I have not in my experience seen any problems with using a Good Quality
Cat5 vs. Cat 3 (telco standard) cable for X-connects.  YMMV, but you
should be fine. As far as the shielding goes, I use UTP cables and
Connectors all the time and some of my X-connects run over 100 feet
 



I have used cat-5 for everything communications. serial printers, dumb 
terminals, DS1  and even 10/100 ethernet. :-) It's easier to have it 