Re: [CentOS] [OT] ups advice

2011-04-15 Thread Drew
 - Stick to APC

Five years ago I would have said that. Having worked with Liebert's
GXT2  GXT3units now for the last few years, I'm not so sure I'd want
to go back to APC. For us the biggest bonus of Liebert was we got true
online (double conversion) UPS kit at the same price point as APC's
Line Interactive Smart UPS family.


-- 
Drew

Nothing in life is to be feared. It is only to be understood.
--Marie Curie
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-15 Thread admin lewis
2011/4/14 John R Pierce pie...@hogranch.com:
 On 04/14/11 9:06 AM, admin lewis wrote:
 Hi
 I have a Dell PowerEdge T310 *tower* server.. I have to buy an ups by
 apc... anyone could help me giving an hint ?
 a simple smart ups 1000 could be enough ?



 apc smartups or eaton powerware woudl be my choices.    1000VA should be
 fine.

 avoid consumer UPS's like apc backups, they are junk.


 how long do you need the system to stay powered when the power fails?
 just long enough to shutdown?  or do you need it to stay up for some
 period of time?



Few minutes... 10 minutes should be enough.. and then shutdown the machine ..
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-15 Thread Howard Fleming
Some of the newer HP servers are very picky about power from UPS's, from 
what I have read.

I have used several Best Ferrups UPSs over the years, other than one 
that toasted it's transformer, have never had any trouble out of them 
(just replace the battery every 3 to 4 years).

They are picky about their input power, do not run not connect them to 
an auto regulating transformer (not the proper term?), or on the output 
of other UPSs, it can cause interesting problems

Howard

On 4/14/2011 15:33, Lamar Owen wrote:
 On Thursday, April 14, 2011 02:55:51 PM John R Pierce wrote:
 http://powerquality.eaton.com/Products-services/Backup-Power-UPS/5125.aspx
 or similar for this application.   I'd take one of those up versus the
 same size APC SmartUps any day.

 We have a 5KVA Best Ferrups here that has never worked correctly :-)  But 
 I've seen my share of toasted APC's, too.

 Currently we run older APC SmartUPS (pure sine) for the workstation stuff and 
 Symmetras in the Data Centers.  Looking to put in a Toshiba or similar 500KVA 
 in the secondary Data Center later in the year.

 BTW, another thing the 'good' UPS's do, more important than 'pure
 sinusoidal output' for computer purposes*, is buck/boost voltage regulation.

 Yes.

 * if you're running audio gear off a UPS, you definitely want the
 sinusoidal output, but thats another market entirely.

 Or old 3Com Corebuilder/CellPlex 7000 gear, which shuts down with anything 
 but pure sinewave.
 ___
 CentOS mailing list
 CentOS@centos.org
 http://lists.centos.org/mailman/listinfo/centos
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-15 Thread Howard Fleming


On 4/15/2011 10:48, John R Pierce wrote:
 On 04/15/11 4:38 AM, Howard Fleming wrote:
 I have used several Best Ferrups UPSs over the years, other than one
 that toasted it's transformer, have never had any trouble out of them
 (just replace the battery every 3 to 4 years).

 They are picky about their input power, do not run not connect them to
 an auto regulating transformer (not the proper term?), or on the output
 of other UPSs, it can cause interesting problems...

 I don't think they make any FerrUPS anymore.  Those were based on a
 massive ferroresonant transformer which, yes, is very sensitive to the
 input frequency.  Specifically, they don't like generator power, unless
 it has extremely well regulated frequency output (such as a DC generator
 with a digital sinusoidal converter)

Eaton has the Ferrups line now (still available as far as I know).

I have actually run into the input frequency problem in the past with 
the Ferrups.

I was working at a gas company that for political reasons generated 
their own power inhouse.  Had one Ferrups UPS (of 10?) that was 
complaining about it (kept going online/offline/online  There is a 
parameter in the settings that can be adjusted to allow a greater input 
freq range on the UPS (59.5 - 60.5 hz is the default range, from what I 
remember).  In this case that took care of the problem.

I have 3 1.4kw units at home, no trouble to date running them off of my 
backup generator (Campbell 5k unit).  They are also 18 years old at this 
point and still going... :o).  Running 3 of my CentOS servers at home in 
fact.
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


[CentOS] [OT] ups advice

2011-04-14 Thread admin lewis
Hi
I have a Dell PowerEdge T310 *tower* server.. I have to buy an ups by
apc... anyone could help me giving an hint ?
a simple smart ups 1000 could be enough ?

thx so much!!

lewis.
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread Bowie Bailey
On 4/14/2011 12:06 PM, admin lewis wrote:
 Hi
 I have a Dell PowerEdge T310 *tower* server.. I have to buy an ups by
 apc... anyone could help me giving an hint ?
 a simple smart ups 1000 could be enough ?

APC's website has a UPS Selector feature that will recommend a UPS
based on your equipment.

-- 
Bowie
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread Kevin Thorpe
On Thu, Apr 14, 2011 at 5:06 PM, admin lewis adminle...@gmail.com wrote:
 Hi
 I have a Dell PowerEdge T310 *tower* server.. I have to buy an ups by
 apc... anyone could help me giving an hint ?
 a simple smart ups 1000 could be enough ?

It depends on how long you want it to run. Your choice is a small UPS
to give your
server just enough time to shut down or a big UPS to allow you to
carry on working
for some time.

In general a fileserver will only need a minimum of 5 to 10 minutes to
shut down as
your workstations are probably already dead. Obviously this has changed now that
people have laptops. If you're running big processes on the server then you need
long enough to let them complete or shut down gracefully.

Of course this assumes reliable power. If you regularly have outages
or bad brownouts
then scale up.
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread Brunner, Brian T.
centos-boun...@centos.org wrote:
 On Thu, Apr 14, 2011 at 5:06 PM, admin lewis
 adminle...@gmail.com wrote:
 Hi
 I have a Dell PowerEdge T310 *tower* server.. I have to buy an ups by
 apc... anyone could help me giving an hint ?
 a simple smart ups 1000 could be enough ?

UPS and Power Supplies are not all the same.  
If the UPS has a stepped voltage output (not smooth sine wave like the
local public grid has) in large enough steps to mess up the power
supply, you wind up with no UPS in effect.

CLEARLY if there are enough steps to the stepped output of the UPS
(which depends on the UPS brand/model), the PC power supply happily will
see it as a sine wave input.  How many is enough depends on the power
supply and the load.


Insert spiffy .sig here:
Life is complex: it has both real and imaginary parts.

//me
***
This email and any files transmitted with it are confidential and
intended solely for the use of the individual or entity to whom
they are addressed. If you have received this email in error please
notify the system manager. This footnote also confirms that this
email message has been swept for the presence of computer viruses.
www.Hubbell.com - Hubbell Incorporated**

___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread admin lewis
2011/4/14 Bowie Bailey bowie_bai...@buc.com:
 On 4/14/2011 12:06 PM, admin lewis wrote:
 Hi
 I have a Dell PowerEdge T310 *tower* server.. I have to buy an ups by
 apc... anyone could help me giving an hint ?
 a simple smart ups 1000 could be enough ?

 APC's website has a UPS Selector feature that will recommend a UPS
 based on your equipment.

 --
 Bowie


I take a APC Smart-UPS 1000VA LCD 230V
It seems good a enough to give 15-20 minutes of power to my server.
very very thanks for your simple but very useful hint.
lewis
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread Les Mikesell
On 4/14/2011 11:36 AM, Kevin Thorpe wrote:

 I have a Dell PowerEdge T310 *tower* server.. I have to buy an ups by
 apc... anyone could help me giving an hint ?
 a simple smart ups 1000 could be enough ?

 It depends on how long you want it to run. Your choice is a small UPS
 to give your
 server just enough time to shut down or a big UPS to allow you to
 carry on working
 for some time.

 In general a fileserver will only need a minimum of 5 to 10 minutes to
 shut down as
 your workstations are probably already dead. Obviously this has changed now 
 that
 people have laptops. If you're running big processes on the server then you 
 need
 long enough to let them complete or shut down gracefully.

 Of course this assumes reliable power. If you regularly have outages
 or bad brownouts
 then scale up.

Don't forget that you need to keep your network equipment powered as 
well if you expect to do more than a graceful shutdown.

-- 
   Les Mikesell
lesmikes...@gmail.com
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread m . roth
Kevin Thorpe wrote:
 On Thu, Apr 14, 2011 at 5:06 PM, admin lewis adminle...@gmail.com wrote:
 Hi
 I have a Dell PowerEdge T310 *tower* server.. I have to buy an ups by
apc... anyone could help me giving an hint ?
 a simple smart ups 1000 could be enough ?

 It depends on how long you want it to run. Your choice is a small UPS to
give your server just enough time to shut down or a big UPS to allow you to
 carry on working for some time.

And it depends on what you're trying to deal with: if it's occasional
brown or blackouts, or power flickers (let's not talk about Chicago, for
example), then you need enough power to provide all it will draw for a
couple minutes at most. If you're looking at longer power outages, you'll
need something a lot bigger, though one suitable for the above purpose
would usually allow it to shut down gracefully; it's not like Linux takes
a long, long time to shutdown.
snip
 people have laptops. If you're running big processes on the server then
you need long enough to let them complete or shut down gracefully.

Heh. Depends on your definition of big processes, says the guy whose
users normally are running jobs that run for *days*, if not weeks.

   mark





___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread Bill Campbell
On Thu, Apr 14, 2011, Brunner, Brian T. wrote:
centos-boun...@centos.org wrote:
 On Thu, Apr 14, 2011 at 5:06 PM, admin lewis
 adminle...@gmail.com wrote:
 Hi
 I have a Dell PowerEdge T310 *tower* server.. I have to buy an ups by
 apc... anyone could help me giving an hint ?
 a simple smart ups 1000 could be enough ?

UPS and Power Supplies are not all the same.  
If the UPS has a stepped voltage output (not smooth sine wave like the
local public grid has) in large enough steps to mess up the power
supply, you wind up with no UPS in effect.

We have been using APC UPSs for decades now, and the only major
problem I've seen is batteries swelling in some of the rack-mount
chassis making them difficult to impossible to remove.  By
difficult I mean taking the cover off the UPS to get to the
batteries.  By impossible, taking the cover off reveals that the
construction is such that the batteries won't come out the top.

We lose power fairly frequently here, and need the UPSs to keep
things going long enough to get generator backup started.  I have
found that the APC UPSs really don't like cheap generators.  We
had a week long power outage after the 2001 Clinton Inaugural
windstorm, and I got an inexpensive generator from Sears which
didn't work at all with APC equipment.  We're now using Honda
generators which are very quiet, and have kept things going for
over a week at a time.

Bill
-- 
INTERNET:   b...@celestial.com  Bill Campbell; Celestial Software LLC
URL: http://www.celestial.com/  PO Box 820; 6641 E. Mercer Way
Voice:  (206) 236-1676  Mercer Island, WA 98040-0820
Fax:(206) 232-9186  Skype: jwccsllc (206) 855-5792

Find out just what people will submit to, and you have found out the
exact amount of injustice and wrong which will be imposed upon them; and
these will continue until they are resisted with either words or blows, or
both. The limits of tyrants are prescribed by the endurance of those whom
they oppress. -- Frederick Douglass.
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread Kevin Thorpe
On Thu, Apr 14, 2011 at 6:06 PM, Bill Campbell cen...@celestial.com wrote:

 We lose power fairly frequently here, and need the UPSs to keep
 things going long enough to get generator backup started.  I have
 found that the APC UPSs really don't like cheap generators.  We
 had a week long power outage after the 2001 Clinton Inaugural
 windstorm, and I got an inexpensive generator from Sears which
 didn't work at all with APC equipment.

Cheap generators are just that - cheap. If you look at the output
on a 'scope then you'll never want one anywhere near anything
delicate. Your UPS is probably manfully trying to smooth out the
spikes and if it's really clever trying to correct the frequency of the
AC. All that gets soaked up by the batteries and it knackers them
in no time.

For regular outages it's far better to store DC instead of doing the
full AC - DC - AC - DC cycle. Shame that there isn't a good way of
doing that with standard computer equipment.
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread Devin Reade
Partially echoing what was already said:

- Stick to APC

- Avoid the low end workstation models like the plain BackUPS.
  As a minimum get a BackUPS-Pro. SmartUPS are better.

- Use the sizing app on the APC web site

- Careful of your mains power.  Besides what was mentioned for
  generators, accidentally chaining an APC UPS into AC provided
  by a server room UPS can kill the downstream UPS.

- For controlled shutdowns on battery exhaustion, check out apcupsd.

- Decide whether your UPS will power one server or a few.  If you're
  powering a few, decide whether the control is master-slave (which
  you can do with a serial/USB cable to the master, then network
  to the slaves), or if you need the more expensive setup where the
  UPS talks directly to multiple servers.  I think the former is fine
  (as long as your network switches are on the UPS), but ymmv.

Devin

___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread John R Pierce
On 04/14/11 9:06 AM, admin lewis wrote:
 Hi
 I have a Dell PowerEdge T310 *tower* server.. I have to buy an ups by
 apc... anyone could help me giving an hint ?
 a simple smart ups 1000 could be enough ?



apc smartups or eaton powerware woudl be my choices.1000VA should be 
fine.

avoid consumer UPS's like apc backups, they are junk.


how long do you need the system to stay powered when the power fails?  
just long enough to shutdown?  or do you need it to stay up for some 
period of time?


___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread John R Pierce
On 04/14/11 9:49 AM, Brunner, Brian T. wrote:
 UPS and Power Supplies are not all the same.
 If the UPS has a stepped voltage output (not smooth sine wave like the
 local public grid has) in large enough steps to mess up the power
 supply, you wind up with no UPS in effect.

 CLEARLY if there are enough steps to the stepped output of the UPS
 (which depends on the UPS brand/model), the PC power supply happily will
 see it as a sine wave input.  How many is enough depends on the power
 supply and the load.


switched PC/Server PSU's *so* don't give a bleep about sinusoidal power, 
its not funny.   first thing they do is full wave rectify the power to 
DC, then they run that DC through a high frequency (several 100Khz 
usually) oscillator and into a toroidal transformer.  they would be 
perfectly happy running off a full squarewave




___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread John R Pierce
On 04/14/11 10:54 AM, Devin Reade wrote:
 Partially echoing what was already said:

 - Stick to APC

I'd take Eaton Powerware (fka Best Power) over APC any day.

http://powerquality.eaton.com/Products-services/Backup-Power-UPS/5125.aspx  
or similar for this application.   I'd take one of those up versus the 
same size APC SmartUps any day.

BTW, another thing the 'good' UPS's do, more important than 'pure 
sinusoidal output' for computer purposes*, is buck/boost voltage regulation.




* if you're running audio gear off a UPS, you definitely want the 
sinusoidal output, but thats another market entirely.


___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread Brent L. Bates
 apcupsd doesn't work with new APC UPS's.  APC has changed to some
proprietary protocol, microlink?, for talking to their UPS's, so apcupsd
doesn't work any more or at least not fully.  There has been some discussion
about this issue on the apcupsd users email list.
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread Les Mikesell
On 4/14/2011 1:55 PM, John R Pierce wrote:
 On 04/14/11 10:54 AM, Devin Reade wrote:
 Partially echoing what was already said:

 - Stick to APC

 I'd take Eaton Powerware (fka Best Power) over APC any day.

 http://powerquality.eaton.com/Products-services/Backup-Power-UPS/5125.aspx
 or similar for this application.   I'd take one of those up versus the
 same size APC SmartUps any day.

Keep in mind that pretty much all of them that don't have multiple 
battery/control modules and auto-switching (like the big APC Symmetra's) 
  will have their own failure modes 3 or 4 years out if you just plug 
them in and forget them.  That is, they will cause downtime even if you 
don't have a power failure.

-- 
   Les Mikesell
lesmikes...@gmail.com
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread m . roth
Les Mikesell wrote:
 On 4/14/2011 1:55 PM, John R Pierce wrote:
 On 04/14/11 10:54 AM, Devin Reade wrote:
 Partially echoing what was already said:

 - Stick to APC

 I'd take Eaton Powerware (fka Best Power) over APC any day.

 http://powerquality.eaton.com/Products-services/Backup-Power-UPS/5125.aspx
 or similar for this application.   I'd take one of those up versus the
 same size APC SmartUps any day.

 Keep in mind that pretty much all of them that don't have multiple
 battery/control modules and auto-switching (like the big APC Symmetra's)
   will have their own failure modes 3 or 4 years out if you just plug
 them in and forget them.  That is, they will cause downtime even if you
 don't have a power failure.

*shrug* You run the self-test every so often, or have apcupsd do it. In
any case, when the replace battery light *first* goes on, order new
ones, and replace 'em when they come in.

mark

___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread Lamar Owen
On Thursday, April 14, 2011 02:51:02 PM John R Pierce wrote:
 switched PC/Server PSU's *so* don't give a bleep about sinusoidal power, 
 its not funny.   first thing they do is full wave rectify the power to 
 DC, then they run that DC through a high frequency (several 100Khz 
 usually) oscillator and into a toroidal transformer.  they would be 
 perfectly happy running off a full squarewave

Actually, a squarewave with the same RMS as a sine wave will full-wave rectify 
and filter to a lower DC voltage than the sinewave.  The supply may or may not 
be able to deal with that.  

To work the math, 120Vac RMS yields a peak voltage for a sinewave of about 170V 
(Vpeak=Vrms*square-root-of-two); full-wave rectified and filtered that gives 
170V DC (with some ripple, depending upon the size of the filter capacitor 
relative to the current drawn); a squarewave at 120Vac RMS yields a peak 
voltage of 120V, and a filtered DC of 120V, equal to the filtered DC for an 
input RMS AC voltage of 84Vac RMS (for a sinewave, 
Vrms=Vpeak/square-root-of-two); if your power supply can deal with that.

Also, the odd-order harmonics may create their own havoc in the filtering.  So, 
no, there's more to it than meets the eye.

I are a EE; degree and all. :-)

But if you don't believe me, please look at:
http://www.opamp-electronics.com/tutorials/measurements_of_ac_magnitude_2_01_03.htm
 
and come back later
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread Lamar Owen
On Thursday, April 14, 2011 02:55:51 PM John R Pierce wrote:
 http://powerquality.eaton.com/Products-services/Backup-Power-UPS/5125.aspx  
 or similar for this application.   I'd take one of those up versus the 
 same size APC SmartUps any day.

We have a 5KVA Best Ferrups here that has never worked correctly :-)  But 
I've seen my share of toasted APC's, too.

Currently we run older APC SmartUPS (pure sine) for the workstation stuff and 
Symmetras in the Data Centers.  Looking to put in a Toshiba or similar 500KVA 
in the secondary Data Center later in the year.

 BTW, another thing the 'good' UPS's do, more important than 'pure 
 sinusoidal output' for computer purposes*, is buck/boost voltage regulation.

Yes.

 * if you're running audio gear off a UPS, you definitely want the 
 sinusoidal output, but thats another market entirely.

Or old 3Com Corebuilder/CellPlex 7000 gear, which shuts down with anything but 
pure sinewave.
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread Les Mikesell
On 4/14/2011 2:13 PM, m.r...@5-cent.us wrote:

 Keep in mind that pretty much all of them that don't have multiple
 battery/control modules and auto-switching (like the big APC Symmetra's)
will have their own failure modes 3 or 4 years out if you just plug
 them in and forget them.  That is, they will cause downtime even if you
 don't have a power failure.

 *shrug* You run the self-test every so often, or have apcupsd do it. In
 any case, when the replace battery light *first* goes on, order new
 ones, and replace 'em when they come in.

I think we've had many where the replace battery light never came on 
until after they had dropped power.

-- 
   Les Mikesell
lesmikes...@gmail.com
___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos


Re: [CentOS] [OT] ups advice

2011-04-14 Thread m . roth
Les Mikesell wrote:
 On 4/14/2011 2:13 PM, m.r...@5-cent.us wrote:

 Keep in mind that pretty much all of them that don't have multiple
 battery/control modules and auto-switching (like the big APC
 Symmetra's)
will have their own failure modes 3 or 4 years out if you just plug
 them in and forget them.  That is, they will cause downtime even if you
 don't have a power failure.

 *shrug* You run the self-test every so often, or have apcupsd do it. In
 any case, when the replace battery light *first* goes on, order new
 ones, and replace 'em when they come in.

 I think we've had many where the replace battery light never came on
 until after they had dropped power.

Ok. We have mostly APC SmartUps 3000 rackmounts. They seem to work well.
Btw, if you order *other* than OEM batteries, regardless of what the
websites say, be *sure* that it's HR (high rate) batteries. About a year,
year and a half ago, I had all kinds of grief over that.

mark

___
CentOS mailing list
CentOS@centos.org
http://lists.centos.org/mailman/listinfo/centos