Re: [Elecraft] Power Factor

2020-03-05 Thread Walter Underwood
In the late 1980s, HP Labs was having wiring failures and fires in the cubicle 
wiring. Someone visited from MIT Project Athena and made a side comment about 
their wiring problems with computers at every desk. For a while, HP Labs had 
extension cords strung everywhere to reduce the demand on the wiring. Those 
went away when Steelcase replaced all the cubicle wiring with stuff that could 
handle the triplen current.

wunder
K6WRU
Walter Underwood
CM87wj
http://observer.wunderwood.org/ (my blog)

> On Mar 4, 2020, at 10:44 PM, Jim Brown  wrote:
> 
> On 3/4/2020 10:15 PM, Jim Brown wrote:
>> Power factor is a quantity associated with mains power (and similar power 
>> distribution systems). In the old days (when I went through EE), it was, 
>> indeed, related to the phase angle.
> 
> I meant to add that power factor now includes the triplen harmonics resulting 
> from non-sinusoidal current with power systems that are mostly electronic 
> loads. Current flows mostly in short peaks at the positive and negative peaks 
> of the mains waveform to charge the filter capacitors in the power supply; as 
> a result, the voltage waveform is rounded off and the current is rich in 
> harmonics of the mains frequency, 50 or 60 Hz.
> 
> Nearly all power distribution uses 3-phase wiring, and "triplen" harmonics 
> (those whose number is divisible by 3) add in the neutral, no matter how well 
> balanced the load between phases. This turned into a major problem roughly 50 
> years ago, when a very high fraction of current in these systems was 
> delivered to electronic loads, everything from fluorescent lights to 
> computers to anything with an AC to DC power supply. The most dangerous side 
> effect is that triplen currents in the neutral of 3-phase systems can be 
> almost twice the current in the phases, which can cause destructive failures 
> in older systems, where the neutral used conductors and hardware rated for 
> half the current in the phases! The movie "The Flaming Inferno" is based on 
> the true story of a massive fire in a high rise that was started by that 
> neutral current, spread through the building in vertical "riser" spaces, and 
> that was fueled by the insulation on the cables themselves! Sometime in the 
> last century, a
  major TV station almost went off the air because excessive heating of their 
power distribution was close to catching on fire! I attended an SBE (Society of 
Broadcast Engineers) meeting led by the consultant who worked with the station 
engineers on the problem.
> 
> MAJOR changes were made to standards for mains wiring after this event, 
> including the rating of transformers and neutral hardware to handle the peak 
> currents and the harmonic content, conduit requirements for the wiring, and 
> requirements for insulation on the wiring that does not contribute to flame 
> spread and that does not produce toxic fumes.
> 
> BTW -- the triplen harmonics also appear on equipment ground, and are the 
> reason why we mostly hear power line noise in the audio as "buzz" (triplen 
> harmonics of 50/60 Hz) rather than "hum" (pure 50/60 Hz).
> 
> There's a not-too-technical discussion of all of this written for hams in 
> http://k9yc.com/GroundingAndAudio.pdf
> and a more detailed one written for sound and video professionals in
> http://k9yc.com/SurgeXPowerGround.pdf
> 
> 73, Jim K9YC
> __
> Elecraft mailing list
> Home: http://mailman.qth.net/mailman/listinfo/elecraft
> Help: http://mailman.qth.net/mmfaq.htm
> Post: mailto:Elecraft@mailman.qth.net
> 
> This list hosted by: http://www.qsl.net
> Please help support this email list: http://www.qsl.net/donate.html
> Message delivered to wun...@wunderwood.org 

__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com 


Re: [Elecraft] Power Factor

2020-03-05 Thread Adrian
Jim, Ok on that, I am a retired tradesman in the electrical industry, and
looking at why an antenna radiates best when reactance is zero leaving only
a resistance load (not taking radiation angle into account),
would seem to be because the voltage and current across the radiated load
are in phase providing maximum power dissipation, whereas any added
reactance with phase shift would diminish that ,
 as well as change the impedance.

I understand there are other factors in efficient power transfer, but I am
confident above is part of the picture. As you know it's the reason
capacitors were used in fluorescent light fittings with inductive ballasts
 for power factor correction . On my Delta loop it is great on 80m, but on
40m and up I switch in a 100pF capacitor  to null the inductive reactance I
see on the antenna there, reducing swr from 5.1:1 to 1.7:1
at the feedpoint.

It should be better, not needing that, but not all antennas follow a
resonant trend through the bands. Due to compromises etc working around
buildings and structures to do the best with what you have.

Adrian ... vk4tux

-Original Message-
From: elecraft-boun...@mailman.qth.net
[mailto:elecraft-boun...@mailman.qth.net] On Behalf Of Jim Brown
Sent: Thursday, 5 March 2020 4:45 PM
To: elecraft@mailman.qth.net
Subject: [Elecraft] Power Factor

On 3/4/2020 10:15 PM, Jim Brown wrote:
> Power factor is a quantity associated with mains power (and similar 
> power distribution systems). In the old days (when I went through EE), 
> it was, indeed, related to the phase angle.

I meant to add that power factor now includes the triplen harmonics
resulting from non-sinusoidal current with power systems that are mostly
electronic loads. Current flows mostly in short peaks at the positive and
negative peaks of the mains waveform to charge the filter capacitors in the
power supply; as a result, the voltage waveform is rounded off and the
current is rich in harmonics of the mains frequency, 50 or 60 Hz.

Nearly all power distribution uses 3-phase wiring, and "triplen" 
harmonics (those whose number is divisible by 3) add in the neutral, no
matter how well balanced the load between phases. This turned into a major
problem roughly 50 years ago, when a very high fraction of current in these
systems was delivered to electronic loads, everything from fluorescent
lights to computers to anything with an AC to DC power supply. The most
dangerous side effect is that triplen currents in the neutral of 3-phase
systems can be almost twice the current in the phases, which can cause
destructive failures in older systems, where the neutral used conductors and
hardware rated for half the current in the phases! The movie "The Flaming
Inferno" is based on the true story of a massive fire in a high rise that
was started by that neutral current, spread through the building in vertical
"riser" spaces, and that was fueled by the insulation on the cables
themselves! Sometime in the last century, a major TV station almost went off
the air because excessive heating of their power distribution was close to
catching on fire! I attended an SBE (Society of Broadcast Engineers) meeting
led by the consultant who worked with the station engineers on the problem.

MAJOR changes were made to standards for mains wiring after this event,
including the rating of transformers and neutral hardware to handle the peak
currents and the harmonic content, conduit requirements for the wiring, and
requirements for insulation on the wiring that does not contribute to flame
spread and that does not produce toxic fumes.

BTW -- the triplen harmonics also appear on equipment ground, and are the
reason why we mostly hear power line noise in the audio as "buzz" 
(triplen harmonics of 50/60 Hz) rather than "hum" (pure 50/60 Hz).

There's a not-too-technical discussion of all of this written for hams in
http://k9yc.com/GroundingAndAudio.pdf
and a more detailed one written for sound and video professionals in
http://k9yc.com/SurgeXPowerGround.pdf

73, Jim K9YC
__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html Message
delivered to vk4...@gmail.com 

__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com 


[Elecraft] Power Factor

2020-03-04 Thread Jim Brown

On 3/4/2020 10:15 PM, Jim Brown wrote:
Power factor is a quantity associated with mains power (and similar 
power distribution systems). In the old days (when I went through EE), 
it was, indeed, related to the phase angle.


I meant to add that power factor now includes the triplen harmonics 
resulting from non-sinusoidal current with power systems that are mostly 
electronic loads. Current flows mostly in short peaks at the positive 
and negative peaks of the mains waveform to charge the filter capacitors 
in the power supply; as a result, the voltage waveform is rounded off 
and the current is rich in harmonics of the mains frequency, 50 or 60 Hz.


Nearly all power distribution uses 3-phase wiring, and "triplen" 
harmonics (those whose number is divisible by 3) add in the neutral, no 
matter how well balanced the load between phases. This turned into a 
major problem roughly 50 years ago, when a very high fraction of current 
in these systems was delivered to electronic loads, everything from 
fluorescent lights to computers to anything with an AC to DC power 
supply. The most dangerous side effect is that triplen currents in the 
neutral of 3-phase systems can be almost twice the current in the 
phases, which can cause destructive failures in older systems, where the 
neutral used conductors and hardware rated for half the current in the 
phases! The movie "The Flaming Inferno" is based on the true story of a 
massive fire in a high rise that was started by that neutral current, 
spread through the building in vertical "riser" spaces, and that was 
fueled by the insulation on the cables themselves! Sometime in the last 
century, a major TV station almost went off the air because excessive 
heating of their power distribution was close to catching on fire! I 
attended an SBE (Society of Broadcast Engineers) meeting led by the 
consultant who worked with the station engineers on the problem.


MAJOR changes were made to standards for mains wiring after this event, 
including the rating of transformers and neutral hardware to handle the 
peak currents and the harmonic content, conduit requirements for the 
wiring, and requirements for insulation on the wiring that does not 
contribute to flame spread and that does not produce toxic fumes.


BTW -- the triplen harmonics also appear on equipment ground, and are 
the reason why we mostly hear power line noise in the audio as "buzz" 
(triplen harmonics of 50/60 Hz) rather than "hum" (pure 50/60 Hz).


There's a not-too-technical discussion of all of this written for hams 
in http://k9yc.com/GroundingAndAudio.pdf

and a more detailed one written for sound and video professionals in
http://k9yc.com/SurgeXPowerGround.pdf

73, Jim K9YC
__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com