Re: Surge testing Questions

2009-03-09 Thread emc-p...@ieee.org
In message 
de87437fe365cb458c265ea3d73b6f1d04677...@xbc-mail1.xantrex.com, dated 
Mon, 9 Mar 2009, Ralph McDiarmid ralph.mcdiar...@xantrex.com writes:

Most scopes I've used earth the probe ground-lead through their mains 
power cord, so likely no need to attach the ground clip to anything 
when probing mains voltage.

This can be checked by attaching the ground clip and noting whether 
there is any change in the display. Then leave it attached!
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
Things can always get better. But that's not the only option.
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


AW: dated standards

2009-03-09 Thread emc-p...@ieee.org
Hi,

 

the European EMC ADCO group has decided that in the EC declaration of
conformity the dated references of harmonized standards shall be included. The
European EMC guidelines describes the “presumption of conformity” as
followed (chapter 3.2.2, 3rd paragraph):

 

“The EMC Directive refers to the moment of placing on the market for each
individual apparatus. This means that for apparatus which is continuously

produced over a long period, the applicable standards may change in the course
of time. In this case the provisions explained at 3.2.2.3 concerning

the date of cessation of Presumption of Conformity should be taken into
account. The Date of Cessation ensures that a transition period (usually

three years) is foreseen during which the old and new standards are both
valid. After this time if the manufacturer wishes to continue to benefit from
the Presumption of Conformity a new Declaration of Conformity is required to
the later valid edition of the harmonised standard. This will require an EMC
evaluation to the later version of the published harmonised standard and may
require re-testing. However, it may be that the manufacturer

wishes to continue to meet the essential requirements by continuing use of the
“old” edition (that has ceased to be harmonised) plus other technical

solutions if necessary. As harmonised standards are voluntary this is of
course an acceptable solution but would not give the presumption of

conformity that application of the later edition would confer. In addition, it
will require amendment to the text of the Declaration given that the

method of conformity assessment has now changed. Where new editions become
available and are to be applied it does not necessarily mean that a complete
EMC re-assessment of an existing product is necessary. The evaluation may be
restricted to those modifications directly affecting the apparatus concerned.
For example, the change may only relate to a small range in scope, or one
particular clause or phenomenon.“

 

Therefore our German Market Surveillance Authority (Bundesnetzagentur)
evaluates the “EC-DoCs” in the first step (at the second step “tests”)
in regard to the applied standards.

 

 

Mit freundlichen Grüßen
Yours sincerely

 

Dipl.-Ing. Michael Loerzer
Managing Director
Regulatory Affairs Specialist

 

michael.loer...@globalnorm.de mailto:michael.loer...@globalnorm.de  

Fon: +49 30 3229027-50, Direct Call: -51
Mobile: +49 170 3229027
Fax: +49 30 3229027-59

 

www.Globalnorm.de http://www.globalnorm.de/  


Globalnorm GmbH, Sitz der Gesellschaft: Alt-Moabit 94, 10559 Berlin
Geschaeftsfuehrer/Managing Director: Dipl.-Ing. Michael Loerzer
Amtsgericht Berlin-Charlottenburg HRB 105204 B, USt-ID-Nummer: DE251654448

 

Von: emc-p...@ieee.org [mailto:emc-p...@ieee.org] Im Auftrag von Mark Gandler
Gesendet: Freitag, 6. März 2009 20:09
An: tim.hay...@selexgalileo.com; j...@jmwa.demon.co.uk; emc-p...@ieee.org
Betreff: RE: dated standards

 

Tim and All,
one of our products end up audited in Germany by Bundes... They claim
what our standards were outdated in DoC and they said as long as our product
in on the market we must comply with new versions and it should be mentioned
in DoC. The product is under RTTE. I have prepeared a letter describing what
product did not change and in fact will comply with new versions of the
standards by the virtue what physical requirements of the new standard did not
change as well. 
I am not sure how it is going to end up and the product is already EOL anyway. 
 
Could you please comment and to share if anyone else had similar requests from
auditors?
 
Thanks,
mark
 
 Subject: RE: dated standards
 Date: Fri, 6 Mar 2009 11:24:49 +
 From: tim.hay...@selexgalileo.com
 To: j...@jmwa.demon.co.uk; emc-p...@ieee.org
 
 
 Hi John, All,
 
 Don't forget that under the new EMC Directive you can sign off a DoC on
 the basis that the equipment has been assessed against the essential
 requirements. The fact that you use standard that are out of date is
 immaterial - it is still a valid DoC. People who are getting ready to
 spend money re-certifying because the standards (or indeed the
 Directive) have passed their sell-by date need only satisfy themselves
 that the product has not changed and then write a new DoC against the
 existing evidence and declare under the full EMC assessment route. A bit
 of paperwork instead of a lot of testing.
 
 Still I don't expect the test houses to go broke.
 
 Regards
 Tim
 
 SELEX Sensors and Airborne Systems Limited
 Registered Office: Sigma House, Christopher Martin Road, Basildon, Essex
SS14 3EL
 A company registered in England  Wales. Company no. 02426132
 
 This email and any attachments are confidential to the intended
 recipient and may also be privileged. If you are not the intended
 recipient please delete it from your system and notify the sender.
 You should not copy it or use it for any 

AW: Prototypes and the EMC Directive

2009-03-09 Thread emc-p...@ieee.org
Hello,

in Germany we have a special paragraph in our new EMC act for the design
and testing of equipment:

§ 11 Besondere Regelungen
(1) Während der Entwicklung und Erprobung von Betriebsmitteln hat der
Hersteller
Vorkehrungen zu treffen, um elektromagnetische Störungen von Betriebsmitteln
zu
vermeiden, die von Dritten betrieben werden.


English (inofficial translation):

(1) During the design and test of equipment the manufacturer shall be
arrange precautions to avoid disturbances of equipment which are in
operation of others.

No CE marking and no EC declaration of conformity is required.
 
Mit freundlichen Grüßen
Yours sincerely
 
Dipl.-Ing. Michael Loerzer
Managing Director
Regulatory Affairs Specialist
 
michael.loer...@globalnorm.de 
Fon: +49 30 3229027-50, Direct Call: -51
Mobile: +49 170 3229027
Fax: +49 30 3229027-59
 
www.Globalnorm.de 


Globalnorm GmbH, Sitz der Gesellschaft: Alt-Moabit 94, 10559 Berlin
Geschaeftsfuehrer/Managing Director: Dipl.-Ing. Michael Loerzer
Amtsgericht Berlin-Charlottenburg HRB 105204 B, USt-ID-Nummer: DE251654448


Von: emc-p...@ieee.org [mailto:emc-p...@ieee.org] Im Auftrag von Charles
Blackham
Gesendet: Freitag, 27. Februar 2009 11:46
An: White, Ian
Cc: IEEE Forum
Betreff: Re: Prototypes and the EMC Directive

Ian

compliance whilst still in development and not commercially available is
not required.

the EU Blue Book guide to New Approach Directives states that:

A product must comply with the applicable New Approach directives when it
is placed on the Community market for the first time and put into service.

Placing on the market is the initial action of making a product available
for the first time on the Community market, with a view to distribution or
use in the Community. Making available can be either for payment or free
of charge.

Putting into service takes place at the moment of first use within the
Community by the end user. However, the need to ensure, in the framework
of market surveillance, that products are in compliance with the
provisions of the directives when being put into service is limited.

Specifically the EMC Directive only applies to Equipment, where
Equipment is defined as Apparatus or fixed installation and
apparatus means any finished appliance or combination thereof made
commercially available as a single functional unit, intended for the end
user 

That said, in the unlikely event that your product generates so much EMI
that is causes other people problems, you expect a knock on the door from
someone asking you to fix it sharpish.

You still need to ensure that it is safe to be used by the people who are
working on it.

regards
Charlie



 Could members please advise me on the legal position of fully working
 prototypes of electronics equipment. We need them fully working and in
 Service to test that they meet all design requirements. Do they have to
 comply with all aspects of the EMC Directive before we put them into
 service
 -  when it is still a development item.

  Of course they are not commercially available and operate with in the
 confines of the workplace.

 Thanks

 Ian

 -
 
 This message is from the IEEE Product Safety Engineering Society emc-pstc
 discussion list. To post a message to the list, send your e-mail to
 emc-p...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc
 Graphics (in well-used formats), large files, etc. can be posted to that
 URL.

 Website:  http://www.ieee-pses.org/
 Instructions:  http://listserv.ieee.org/request/user-guide.html
 List rules: http://www.ieee-pses.org/listrules.html

 For help, send mail to the list administrators:
 Scott Douglas emcp...@ptcnh.net
 Mike Cantwell mcantw...@ieee.org

 For policy questions, send mail to:
 Jim Bacher:  j.bac...@ieee.org
 David Heald: dhe...@gmail.com


-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that
URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  

RE: Surge testing Questions

2009-03-09 Thread emc-p...@ieee.org
Most scopes I've used earth the probe ground-lead through their mains power
cord, so likely no need to attach the ground clip to anything when probing
mains voltage.


Ralph McDiarmid, AScT 
Compliance Engineering Group 
Xantrex Technology Inc


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of John Woodgate
Sent: Monday, March 09, 2009 2:00 PM
To: emc-p...@ieee.org
Subject: Re: Surge testing Questions

In message 
0ed66cd2c9bd0a459d54fb9119a60567e0b...@mailserver.lecotc.com, dated 
Mon, 9 Mar 2009, Kunde, Brian brian_ku...@lecotc.com writes:

With a grounded Neutral, 0º and 180º is not the zero crossing point 
(zero voltage potential to earth ground) but the 270º angle. Worst case 
would be the 90º angle which would be Peak-Peak plus the Positive Surge 
pulse.

Would you like to re-consider that. The 0 V line on the scope IS 0 V, 
between the hot tip and whatever the ground clip is connected to. If the 
neutral is earthed, it doesn't matter which one the ground clip is 
connected to; 0 V is 0 V.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
Things can always get better. But that's not the only option.
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


RE: EISA 2007

2009-03-09 Thread emc-p...@ieee.org
EISA 2007 amended EPAct 2005, therefore you must read them together to obtain
the scope. See especially 42 USCS 6291, 6293, 6295.  Scope applies to ac-ac
and ac-dc external power supplies and applies to battery chargers except the
standard for battery charges has not been finalized.  A timeline has been
established to review and update standards for external power supplies and
battery chargers.

 

According to DOE, the Act applies specifically to consumer products, and until
Congress changes the statute, the upcoming review of the standards is just
that – clarifying the requirements, not changing the scope.

 

EISA preempted state law for power supplies within its scope (consumer
external power supplies and battery chargers).  California addressed those
power supplies that were not in EISA’s scope; its Code applies to commercial
as well as consumer power supplies.

 

Don Umbdenstock
Manager Compliance Engineering

Tyco Safety Products / Sensormatic
6600 Congress Avenue
Boca Raton, FL 33487 USA
Phone: 561.912.6440
djumbdenst...@tycoint.com mailto:djumbdenst...@tycoint.com  



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Jim Robson
Sent: Tuesday, March 03, 2009 11:27 AM
To: emc-p...@ieee.org
Subject: EISA 2007

 

 

Is anyone familiar with EISA 2007.

 

http://www.govtrack.us/congress/billtext.xpd?bill=h110-6

 

The U.S. Congress has passed a law effective July 1, 2008 called the Energy
Independence and Security Act of 2007. Section 301 of the new law is
dedicated to the efficiency standards for AC or DC output external power
supplies 250 watts and under. The law states that any Class A external power
supply manufactured on or after July 1, 2008, must meet new, higher efficiency
and standby levels based on the output watts. 

TITLE III- ENERGY SAVINGS THROUGH IMPROVED STANDARDS FOR APPLIANCE AND
LIGHTING 

Subtitle A-- Appliance Energy Efficiency

Sec. 301 External power supply efficiency standards.

Sect. 301  requires external power  supplies (up to 250W) must meet certain
efficiency and no load current requirements.   My first interpretation of the
law was the it applied to external power supplies for residential and consumer
appliances.  A fellow colleague disagrees and says if applies to all external
power supplies for all equipment.

Any input on the intended scope would be greatly appreciated.

 

Regards,

Jim Robson

 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org
David Heald dhe...@gmail.com 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org
David Heald dhe...@gmail.com 




Re: Surge testing Questions

2009-03-09 Thread emc-p...@ieee.org
In message 
0ed66cd2c9bd0a459d54fb9119a60567e0b...@mailserver.lecotc.com, dated 
Mon, 9 Mar 2009, Kunde, Brian brian_ku...@lecotc.com writes:

With a grounded Neutral, 0º and 180º is not the zero crossing point 
(zero voltage potential to earth ground) but the 270º angle. Worst case 
would be the 90º angle which would be Peak-Peak plus the Positive Surge 
pulse.

Would you like to re-consider that. The 0 V line on the scope IS 0 V, 
between the hot tip and whatever the ground clip is connected to. If the 
neutral is earthed, it doesn't matter which one the ground clip is 
connected to; 0 V is 0 V.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
Things can always get better. But that's not the only option.
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


RE: Australia C-Tick and safety requirements

2009-03-09 Thread emc-p...@ieee.org
Hi Pat - You had a good question on the IEC equivalent to
UL1449. Do you get any replies? If so - could you forward tem to me?

Thanks!!


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of
pat.law...@slpower.com
Sent: Friday, February 20, 2009 10:50 AM
To: emc-p...@ieee.org
Subject: Re: Australia C-Tick and safety requirements

Hi Dan:

As far as question 2 is concerned (line frequency devices  CISPR 22), 
CISPR 22 does address it.

The Introduction says:
The scope is extended to the whole radio-frequency range from 9 kHz to 
400 GHz, . . . .  50Hz is below the range.
It also says in the Scope:
Procedures are given for the measurement of the levels of spurious 
signals generated by the ITE and limits are specified for the frequency 
range 9 kHz to 400 GHz for both class A and class B equipment. No 
measurements need be performed at frequencies where no limits are 
specified.

Hopefully, a passive surge suppressor is not generating spurious high 
frequency signals during normal operation!


By the way, UL standard 1449 covers testing of 'Surge Protective
Devices'. 
 Is there a similar product standard from the IEC (not basic test 
standards)?

Pat Lawler
EMC Engineer
SL Power Electronics Corp.

Dan Roman dan.ro...@dialogic.com wrote on 02/20/2009 07:23:33 AM:
 I'm passing along two questions for a friend that I cannot answer 
 because they are outside of my product area of expertise.  The 
 product in question is a passive line filter for use with a PC.  It 
 contains overvoltage and line filtering components (some coils, 
 caps, and MOVs).
 
 1.  Does the C-Tick mark for non-telecom equipment require both 
 EMC and safety declarations?  I know that for the telecom equipment 
 my company produces, the ACA requires telecom, safety, and EMC (A-
 tick and C-tick) but I don't know if the safety portion is a telecom
 specific requirement or not.  If the answer is the C-Tick is for EMC
 only, are there other requirements for safety or other marks that 
 would apply to this product in Australia?  I am sure there must be.
 
 2.  Does a passive device like this fall under EMC 
 requirements?  CISPR 22/EN55022 don't specify a lower frequency 
 limit exempting products, so this passive line filter connected to a
 50 Hz supply would appear to need testing.  Everything I deal with 
 has clocks in excess of 1 GHz these days so this question never came
 up where I work!
 
  
 
 It is always interesting getting questions outside of your normal 
 day to day experience.
 -- 
 Dan Roman, N.C.E.
 Product Regulatory Engineer
 Dialogic Research Inc.
 1515 State Rt. 10
 Parsippany, NJ 07054-4538
 *mailto:dan.ro...@dialogic.com
 (Voice: +1 973-967-6485  Fax: +1 973-967-6262
 Intranet: http://compliance.eicon.com/
 Internet: http://www.dialogic.com

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that
URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


RE: Surge testing Questions

2009-03-09 Thread emc-p...@ieee.org
I’ve seen products pass at 0 deg and fail at 180deg.  Perhaps it’s more to
do with current than voltage, or with the sign of the voltage slope.

Ralph McDiarmid, AScT 
Compliance Engineering Group 
Xantrex Technology Inc 

  

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Mike Hopkins
Sent: Monday, March 09, 2009 11:33 AM
To: 'Kunde, Brian'; 'Derek Walton'; 'IEEE EMC Discussion Group'
Subject: RE: Surge testing Questions

 

Well, 61000-4-5 does specify testing at both 0 and 180 degrees. That said, the
only difference I can see between the two conditions is that at zero, the line
voltage is increasing and at 180, it’s decreasing…. 

 

When the document was re-issued, there was considerable discussion about the
length of the test, so words were added to allow testing at rates faster than
one surge/minute. Removing some tests was discussed, but for every test to be
removed, someone had a good reason for keeping it in……

 

Best  Regards,

 

 

Michael Hopkins

Amber Precision Instruments

Office: +1 603 595 6420

Mobile: +1 603 765 3736

m...@amberpi.com

 

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Kunde, Brian
Sent: Monday, March 09, 2009 2:06 PM
To: Mike Hopkins; Derek Walton; IEEE EMC Discussion Group
Subject: RE: Surge testing Questions

 

Our tester won't do Line and Neutral to Ground so we couldn't test that
condition even if we waned to.

 

In Europe, it is common to have 230VAC with a grounded neutral, so to properly
perform the Surge Test you have to test both Line to Ground and Neutral to
Ground.  Some labs even test worst case and perform the Surge test at 264VAC. 

 

With a grounded Neutral, 0º and 180º is not the zero crossing point (zero
voltage potential to earth ground) but the 270º angle. Worst case would be
the 90º angle which would be Peak-Peak plus the Positive Surge pulse. 

 

If you are not using a grounded Neutral or center-tap power system,  the true
zero crossing can float around so you have to test both line to ground and
neutral to ground to make sure you are testing the worst case voltage
potential.

 

I would think that the 0º angle point and the 180º angle point would be
exactly the same so I do not think you have to do both.  If someone disagrees,
please let me know and why.

 

Testing both the 0º and 180º angles during a 2KV test will turn a 4 hour
test into a 5 ½ hour test which is more money for the test lab to “follow
the standard”.  

 

The Other Brian

 

 

 


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Mike Hopkins
Sent: Friday, March 06, 2009 5:51 PM
To: 'Derek Walton'; 'IEEE EMC Discussion Group'
Subject: RE: Surge testing Questions

 

I believe the intention has always been to test line-to-ground (normal mode)

and then neutral-ground (common mode). It's been a few years since I was

convenor of that group and don't recall all the discussions. I believe

coupling multiple lines may have been discussed, but there are real problems

producing the proper waveforms for all conditions == especially for 3-phase

systems where multiple lines can be involved in a common mode test. Of

course, a product standard could require the line + neutral to ground tests,

but I'm not aware of any that do. If they did, I wouldn't guarantee the

waveforms to be correct from all generators under this condition. I believe

that the single line to ground common mode test has been around since the

old 801-5. 

 

In the US, ANSI/IEEE and many companies take the position that the transient

can come in any way it wants to, so line + neutral to ground is commonly

(excuse the PUN) done.

 

In section 8 of Edition 2 it's stated that for a.c. power ports five

positive and five negative pulses each at 0º, 90º, 180º and at 270º shall
be

done  So I'd say 180 IS a test as is 0 degrees...

 

 

Note 2 of that section also states that, Product committees may select

different phase angles and either increase or reduce the number of surges

per phase...

 

 

Hope this is helpful

 

 

Michael Hopkins

Amber Precision Instruments

Office: +1 603 595 6420

Mobile: +1 603 765 3736

m...@amberpi.com

 



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Derek Walton

Sent: Friday, March 06, 2009 11:22 AM

To: IEEE EMC Discussion Group

Subject: Surge testing Questions

 

Good day folks,

 

I have a question or two concerning the latest surge test document 

EN61000-4-5:

 

1) when the pulse is applied on a power lead between line and ground, is 

it done Line to ground, then Neutral to Ground OR, is it Line and 

Neutral to Ground.

 

One would think if this were a common mode test ( since it's referenced 

to Ground ) that the pulse be applied Line and Neutral to ground 

simultaneously. However, the wording in -5 clause 8.2 states 

*successively *implying Line to ground then Neutral to ground. This 

implies separate tests.

 

2) On an AC waveform, is the 180 degree position a test condition? I 

RE: Surge testing Questions

2009-03-09 Thread emc-p...@ieee.org
Well, 61000-4-5 does specify testing at both 0 and 180 degrees. That said, the
only difference I can see between the two conditions is that at zero, the line
voltage is increasing and at 180, it’s decreasing…. 

 

When the document was re-issued, there was considerable discussion about the
length of the test, so words were added to allow testing at rates faster than
one surge/minute. Removing some tests was discussed, but for every test to be
removed, someone had a good reason for keeping it in……

 

Best  Regards,

 

 

Michael Hopkins

Amber Precision Instruments

Office: +1 603 595 6420

Mobile: +1 603 765 3736

m...@amberpi.com

 

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Kunde, Brian
Sent: Monday, March 09, 2009 2:06 PM
To: Mike Hopkins; Derek Walton; IEEE EMC Discussion Group
Subject: RE: Surge testing Questions

 

Our tester won't do Line and Neutral to Ground so we couldn't test that
condition even if we waned to.

 

In Europe, it is common to have 230VAC with a grounded neutral, so to properly
perform the Surge Test you have to test both Line to Ground and Neutral to
Ground.  Some labs even test worst case and perform the Surge test at 264VAC. 

 

With a grounded Neutral, 0º and 180º is not the zero crossing point (zero
voltage potential to earth ground) but the 270º angle. Worst case would be
the 90º angle which would be Peak-Peak plus the Positive Surge pulse. 

 

If you are not using a grounded Neutral or center-tap power system,  the true
zero crossing can float around so you have to test both line to ground and
neutral to ground to make sure you are testing the worst case voltage
potential.

 

I would think that the 0º angle point and the 180º angle point would be
exactly the same so I do not think you have to do both.  If someone disagrees,
please let me know and why.

 

Testing both the 0º and 180º angles during a 2KV test will turn a 4 hour
test into a 5 ½ hour test which is more money for the test lab to “follow
the standard”.  

 

The Other Brian

 

 

 


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Mike Hopkins
Sent: Friday, March 06, 2009 5:51 PM
To: 'Derek Walton'; 'IEEE EMC Discussion Group'
Subject: RE: Surge testing Questions

 

I believe the intention has always been to test line-to-ground (normal mode)

and then neutral-ground (common mode). It's been a few years since I was

convenor of that group and don't recall all the discussions. I believe

coupling multiple lines may have been discussed, but there are real problems

producing the proper waveforms for all conditions == especially for 3-phase

systems where multiple lines can be involved in a common mode test. Of

course, a product standard could require the line + neutral to ground tests,

but I'm not aware of any that do. If they did, I wouldn't guarantee the

waveforms to be correct from all generators under this condition. I believe

that the single line to ground common mode test has been around since the

old 801-5. 

 

In the US, ANSI/IEEE and many companies take the position that the transient

can come in any way it wants to, so line + neutral to ground is commonly

(excuse the PUN) done.

 

In section 8 of Edition 2 it's stated that for a.c. power ports five

positive and five negative pulses each at 0º, 90º, 180º and at 270º shall
be

done  So I'd say 180 IS a test as is 0 degrees...

 

 

Note 2 of that section also states that, Product committees may select

different phase angles and either increase or reduce the number of surges

per phase...

 

 

Hope this is helpful

 

 

Michael Hopkins

Amber Precision Instruments

Office: +1 603 595 6420

Mobile: +1 603 765 3736

m...@amberpi.com

 



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Derek Walton

Sent: Friday, March 06, 2009 11:22 AM

To: IEEE EMC Discussion Group

Subject: Surge testing Questions

 

Good day folks,

 

I have a question or two concerning the latest surge test document 

EN61000-4-5:

 

1) when the pulse is applied on a power lead between line and ground, is 

it done Line to ground, then Neutral to Ground OR, is it Line and 

Neutral to Ground.

 

One would think if this were a common mode test ( since it's referenced 

to Ground ) that the pulse be applied Line and Neutral to ground 

simultaneously. However, the wording in -5 clause 8.2 states 

*successively *implying Line to ground then Neutral to ground. This 

implies separate tests.

 

2) On an AC waveform, is the 180 degree position a test condition? I ask 

because it states Zero crossing point. If this is NOT where is the 

exemption?

 

Many thanks in advance.

 

Derek Walton

L F Research

 

-



This message is from the IEEE Product Safety Engineering Society emc-pstc

discussion list. To post a message to the list, send your e-mail to

emc-p...@ieee.org

 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

Graphics (in 

RE: Surge testing Questions

2009-03-09 Thread emc-p...@ieee.org
Our tester won't do Line and Neutral to Ground so we couldn't test that
condition even if we waned to.

 

In Europe, it is common to have 230VAC with a grounded neutral, so to properly
perform the Surge Test you have to test both Line to Ground and Neutral to
Ground.  Some labs even test worst case and perform the Surge test at 264VAC. 

 

With a grounded Neutral, 0º and 180º is not the zero crossing point (zero
voltage potential to earth ground) but the 270º angle. Worst case would be
the 90º angle which would be Peak-Peak plus the Positive Surge pulse. 

 

If you are not using a grounded Neutral or center-tap power system,  the true
zero crossing can float around so you have to test both line to ground and
neutral to ground to make sure you are testing the worst case voltage
potential.

 

I would think that the 0º angle point and the 180º angle point would be
exactly the same so I do not think you have to do both.  If someone disagrees,
please let me know and why.

 

Testing both the 0º and 180º angles during a 2KV test will turn a 4 hour
test into a 5 ½ hour test which is more money for the test lab to “follow
the standard”.  

 

The Other Brian

 

 

 


From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Mike Hopkins
Sent: Friday, March 06, 2009 5:51 PM
To: 'Derek Walton'; 'IEEE EMC Discussion Group'
Subject: RE: Surge testing Questions

 

I believe the intention has always been to test line-to-ground (normal mode)

and then neutral-ground (common mode). It's been a few years since I was

convenor of that group and don't recall all the discussions. I believe

coupling multiple lines may have been discussed, but there are real problems

producing the proper waveforms for all conditions == especially for 3-phase

systems where multiple lines can be involved in a common mode test. Of

course, a product standard could require the line + neutral to ground tests,

but I'm not aware of any that do. If they did, I wouldn't guarantee the

waveforms to be correct from all generators under this condition. I believe

that the single line to ground common mode test has been around since the

old 801-5. 

 

In the US, ANSI/IEEE and many companies take the position that the transient

can come in any way it wants to, so line + neutral to ground is commonly

(excuse the PUN) done.

 

In section 8 of Edition 2 it's stated that for a.c. power ports five

positive and five negative pulses each at 0º, 90º, 180º and at 270º shall
be

done  So I'd say 180 IS a test as is 0 degrees...

 

 

Note 2 of that section also states that, Product committees may select

different phase angles and either increase or reduce the number of surges

per phase...

 

 

Hope this is helpful

 

 

Michael Hopkins

Amber Precision Instruments

Office: +1 603 595 6420

Mobile: +1 603 765 3736

m...@amberpi.com

 



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Derek Walton

Sent: Friday, March 06, 2009 11:22 AM

To: IEEE EMC Discussion Group

Subject: Surge testing Questions

 

Good day folks,

 

I have a question or two concerning the latest surge test document 

EN61000-4-5:

 

1) when the pulse is applied on a power lead between line and ground, is 

it done Line to ground, then Neutral to Ground OR, is it Line and 

Neutral to Ground.

 

One would think if this were a common mode test ( since it's referenced 

to Ground ) that the pulse be applied Line and Neutral to ground 

simultaneously. However, the wording in -5 clause 8.2 states 

*successively *implying Line to ground then Neutral to ground. This 

implies separate tests.

 

2) On an AC waveform, is the 180 degree position a test condition? I ask 

because it states Zero crossing point. If this is NOT where is the 

exemption?

 

Many thanks in advance.

 

Derek Walton

L F Research

 

-



This message is from the IEEE Product Safety Engineering Society emc-pstc

discussion list. To post a message to the list, send your e-mail to

emc-p...@ieee.org

 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

Graphics (in well-used formats), large files, etc. can be posted to that

URL.

 

Website:  http://www.ieee-pses.org/

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net

Mike Cantwell mcantw...@ieee.org

 

For policy questions, send mail to:

Jim Bacher:  j.bac...@ieee.org

David Heald: dhe...@gmail.com

 

-



This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

Graphics (in well-used formats), large files, etc. can be posted to that URL.

 

Website:  http://www.ieee-pses.org/

Instructions:  

RE: De-Rating internal Connectors for Temperature

2009-03-09 Thread emc-p...@ieee.org
I appreciate the replies and the debating was very interesting.  To re-cap, we
are trying to see if we can come up with a simple way to calculate the
temperature rise in a connector at different current levels if we already know
that the temperature rise is 30ºC at the rated current (which is how most
connectors are rated). 

We know the calculated results would be just an estimate and we are making the
assumption that the power dissipation and thermal resistance would stay fairly
constant in the temperature range that we want to calculate.

I took John's advice and decided to do some measurements just to see if the
results would track our I^2 presumption.

I took a standard Molex connector (single) pin and socket rated 19 amps (this
is NOT the 50 amp connector from my original email) and soldered them onto 16
AWG wire and mounted them in free space and connected the wires to my Ground
Bond Tester (constant current source).  I stuck a thermocouple with thermal
paste into the connector pin as close to the junction as possible.

Passing current through the connector pins gave me the following results:

5A = 2.5ºC rise over ambient
10A = 11ºC rise
15A = 22ºC rise
20A = 44ºC rise 

So it would seem that in this case our assumption was pretty close if not
right on. Doubling the current gave us approximately a 4X change in our
temperature rise.

We'll have to do more real world measurements to see if the results are
similar with other connectors.  

Thanks for everyone's help.
The Other Brian



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of John Woodgate
Sent: Sunday, March 08, 2009 5:21 PM
To: john...@itesafety.com
Cc: emc-p...@ieee.org
Subject: Re: De-Rating internal Connectors for Temperature

In message 49b42f6e.3030...@itesafety.com, dated Sun, 8 Mar 2009, 
Robert Johnson john...@itesafety.com writes:

Temperature is not proportional to current or current squared or 
power..
Temperature rise is not proportional to current or current squared or 
power.
These formulas were all pure guesses.

Not in my case: I explained its approximate nature.

Temperature is proportional to kinetic energy (more or less).

Power is energy per unit time. If power is constant, whatever is 
proportional to energy is proportional to power.

You need to go back to the physics and figure out where the energy is 
going and how the energy relates to the temperature of a substance. It 
turns out to be a very complicated subject (eg).

You can make anything complicated. The genius is in making it simple.

A second major flaw here is a misunderstanding about temperature 
manipulation.
You can double the temperature of a product from 1°C to 2°C. You can 
also double the temperature of a product from 50°C to 100°C. You can 
increase the temperature of a product a million fold to 1°C (from 
.01°C). You have to be really careful if you are manipulating 
temperatures without using an absolute scale. If you are trying to 
relate something to a fraction of the temperature scale (like Celsius 
or Fahrenheit) you can quickly get into trouble.

I made it clear that the connector problem is a matter of temperature 
RISE, not temperature on a scale. Others may have considered 
temperatures on a scale; that is indeed very liable to cause errors.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
Things can always get better. But that's not the only option.
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

LECO Corporation Notice:  This communication may contain confidential
information intended for the named recipient(s) only. If you received this by
mistake, please destroy it and notify us of the error.  Thank  you.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net

Re: China WEEE

2009-03-09 Thread emc-p...@ieee.org
The regulation takes effect January 1, 2011.
 
China will establich a WEEE processing fund.  Manufacturers, importers, or
agents have obligation to pay into the fund.  (Article 7)

 
On 3/9/09, James, Chris c...@dolby.co.uk wrote: 

If anyone is looking at this then here are some possibly useful links:

Info
http://www.chinaenvironmentallaw.com/2009/03/06/china-weee-finally-did-
it/


Regulation (Chinese only)
http://www.gov.cn/zwgk/2009-03/04/content_1250419.htm


Google page translation
http://translate.google.com/translate?prev=hphl=enu=http%3A%2F%2Fwww.
gov.cn%2Fzwgk%2F2009-03%2F04%2Fcontent_1250419.htmsl=zh-CNtl=en

-
This message (including any attachments) may contain confidential
information intended for a specific individual and purpose.  If you
are not the intended recipient, delete this message.  If you are
not the intended recipient, disclosing, copying, distributing, or
taking any action based on this message is strictly prohibited.

-

This message is from the IEEE Product Safety Engineering Society 
emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to 
that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com



-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org
David Heald dhe...@gmail.com 




China WEEE

2009-03-09 Thread emc-p...@ieee.org
If anyone is looking at this then here are some possibly useful links:

Info
http://www.chinaenvironmentallaw.com/2009/03/06/china-weee-finally-did-
it/


Regulation (Chinese only)
http://www.gov.cn/zwgk/2009-03/04/content_1250419.htm


Google page translation
http://translate.google.com/translate?prev=hphl=enu=http%3A%2F%2Fwww.
gov.cn%2Fzwgk%2F2009-03%2F04%2Fcontent_1250419.htmsl=zh-CNtl=en


This message (including any attachments) may contain confidential
information intended for a specific individual and purpose.  If you
are not the intended recipient, delete this message.  If you are
not the intended recipient, disclosing, copying, distributing, or
taking any action based on this message is strictly prohibited.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Preamplifier

2009-03-09 Thread emc-p...@ieee.org
Dear Members,
 
Could you please recommend a preamplifier to cover frequency range 26.5GHz -
40GHz?  It would be of great help if you know the price.  You may wish to
reply offline.
 
Thank you.
 
Best regards,
Grace
-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org
David Heald dhe...@gmail.com