[PSES] Call for Papers - 2016 IEEE 20th Workshop on Signal and Power Integrity (SPI)

2015-10-26 Thread Claudio Siviero
Dear Members,

The 2016 IEEE 20th Workshop on Signal and Power Integrity (SPI) will be
held from May 8 to May 11, 2016 in Turin, Italy.

On behalf of the SPI 2016 Standing Committee, it is my pleasure to invite
you and your colleagues to contribute papers, talks, exhibitions to the
event. Over the past nineteen years, SPI has evolved into a forum of
exchange on the latest research and developments on design,
characterization, modeling, simulation and testing for Signal and Power
Integrity at chip, package, board and system level.

Please check the official website www.spi2016.org for more information
regarding the technical program, venue, traveling and lodging information.
This call for papers is also available at http://www.spi2016.org/cfp.asp.

[Highlights]
- Conference papers published on IEEE Xplore
- Special section of the IEEE Transactions of Components, Packaging and
Manufacturing Technology reserved to best-ranked papers
- "Industry Forum" with both invited and contributed talks from the industry
- Keynote speeches and tutorials on emerging research topics
- Best Student Paper Award
- European IBIS Summit

I am looking forward to seeing you in Turin!

Sincerely,

Prof. Stefano Grivet-Talocia
SPI2016 General Chair
ch...@spi2016.polito.it

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: 


Re: [PSES] EN 62368-1 query

2015-10-26 Thread Richard Nute
 

 

Hi Ron:

 

 

>But, a capacitor charged to such an open-circuit
voltage need to also be rated for that voltage
(probably a DUH moment). Correct?

 

Yes.

 

>Is Table 2 of IEC 61201:1992 equivalent to Table
A.2 of IEC 61201:2007?

 

Yes.

 

>ECMA 287 Table 3.4 ES1 values decrease from 60 V
instead of increasing from 60 V from IEC 62368-1
Table 5 ES1 values.

 

In ECMA 287, Table 3.4 is ordered by capacitance,
while IEC 61201 is ordered by voltage.  The ES1
voltage values in ECMA 287 "are derived from Table
2 of IEC 61201" and are not the values in IEC
61201.   IEC 62368-1 uses the table verbatim.

 

>So, the purpose of 5.2.2.3 is intended to apply
to those capacitors in which their charged
voltages are exposed in ES1 circuits during normal
operating conditions and become exposed in ES2
circuits only after a fault?

 

Yes, although I would use the word "accessible"
as, in the IEC, the word "exposed" has a different
meaning.  

 

(ES1 is not necessarily a circuit, but a voltage
with respect to ground from 0 to 42.4 or a current
to ground from 0 to 0.5 mA.)

Need any more clarification?

 

 

Best regards,

Rich

 

 

 


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: 


Re: [PSES] EN 62368-1 query

2015-10-26 Thread Richard Nute
 

Hi Ron:

 

 

The values in Table 5 are taken, directly, from
IEC 61201, Table A.2 and Figure A.1 (notes 1 and
2).  See Annex A, IEC 61201, for further
information about these values.

 

Upeak is not the correct term; the voltage is the
open-circuit voltage to which the capacitor is
charged.  The correct term would be "prospective
touch voltage" as specified in the note to
5.2.2.1.   

 

For 300 nF and greater, the voltage values are the
d.c. values in Table 4.  As the capacitance gets
smaller, the voltage is larger, but the effect on
the body is, supposedly, the same.  See Clause 11,
IEC 60479.  (We have very little modern
experimental evidence of this theory.)  I
personally doubt that some of the
voltage/capacitance combinations would be benign,
but I'm not going to be the guinea pig that
verifies the table!  Perhaps some of the papers
listed in the IEC 60479 bibliography show that the
values are valid.

 

Recall that ES1 can be accessible.  ES2 is only
accessible in the event of a fault.  ES3 is never
accessible.

 

Back in the old days, plotters used electrostatic
paper hold-down; the platen was charged to a high
voltage, so the capacitance was critical to avoid
an unpleasant electric shock.  The voltage source
used to charge the capacitor would have to be very
wimpy as it, too, would have to be ES1.  I don't
know of a similar construction or equipment today
that employs an accessible stored charge.

 

I hope this provides some answers for you.  If
not, just ask!

 

 

Best regards,

Rich

 

 

 


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: 


[PSES] EN 61000-3-3:2013

2015-10-26 Thread Mike Cantwell
EN61000-3-3 is transitioning from the 2008 to 2013 next June. Has anyone gone 
through this and identified any major changes since the 2008 edition?

Is a retest in order for existing equipment? 

Regards, 
Mike

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: 


Re: [PSES] EN 62368-1 query

2015-10-26 Thread Ronald Pickard
Hi Rich,
Thanks for your reply. And, neither would I be in line to be a guinea pig for 
that, but that does remind me of the opening scene in Ghostbusters. :)

But, a capacitor charged to such an open-circuit voltage need to also be rated 
for that voltage (probably a DUH moment). Correct?

I don't as yet have a copy of IEC 61201:2007, but I know that ECMA 287 
(3.2.1.2) Table 3.4 refers to Table 2 of IEC 61201:1992, but the ECMA 287 Table 
3.4 ES1 values decrease from 60 V instead of increasing from 60 V from IEC 
62368-1 Table 5 ES1 values. Is Table 2 of IEC 61201:1992 equivalent to Table 
A.2 of IEC 61201:2007?

So, the purpose of 5.2.2.3 is intended to apply to those capacitors in which 
their charged voltages are exposed in ES1 circuits during normal operating 
conditions and become exposed in ES2 circuits only after a fault? If this is 
correct, then I wish that the authors made it clearer.

Also, a commercially available product with accessible stored charge that comes 
to mind is the Van de Graaff generator and although not technically utilizing a 
stored charge, there is a Jacob's Ladder. Both are primarily intended for 
experimentation and fun.

I look forward to your reply.

Best Regards

Ron Pickard
Regulatory Compliance Engineer
Compound Photonics
D | +1 (602) 883-8039

From: Richard Nute [mailto:ri...@ieee.org]
Sent: Monday, October 26, 2015 12:42 PM
To: Ronald Pickard ; 
EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] EN 62368-1 query


Hi Ron:


The values in Table 5 are taken, directly, from IEC 61201, Table A.2 and Figure 
A.1 (notes 1 and 2).  See Annex A, IEC 61201, for further information about 
these values.

Upeak is not the correct term; the voltage is the open-circuit voltage to which 
the capacitor is charged.  The correct term would be "prospective touch 
voltage" as specified in the note to 5.2.2.1.

For 300 nF and greater, the voltage values are the d.c. values in Table 4.  As 
the capacitance gets smaller, the voltage is larger, but the effect on the body 
is, supposedly, the same.  See Clause 11, IEC 60479.  (We have very little 
modern experimental evidence of this theory.)  I personally doubt that some of 
the voltage/capacitance combinations would be benign, but I'm not going to be 
the guinea pig that verifies the table!  Perhaps some of the papers listed in 
the IEC 60479 bibliography show that the values are valid.

Recall that ES1 can be accessible.  ES2 is only accessible in the event of a 
fault.  ES3 is never accessible.

Back in the old days, plotters used electrostatic paper hold-down; the platen 
was charged to a high voltage, so the capacitance was critical to avoid an 
unpleasant electric shock.  The voltage source used to charge the capacitor 
would have to be very wimpy as it, too, would have to be ES1.  I don't know of 
a similar construction or equipment today that employs an accessible stored 
charge.

I hope this provides some answers for you.  If not, just ask!


Best regards,
Rich




-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: 


Re: [PSES] EN 62368-1 query

2015-10-26 Thread Ronald Pickard
Hi Rich,
Thank you for your patience. Acknowledged on my choice of wording.

No more clarification need on this. Thank you.

Best regards,

Ron Pickard
Regulatory Compliance Engineer
Compound Photonics
D | +1 (602) 883-8039

From: Richard Nute [mailto:ri...@ieee.org]
Sent: Monday, October 26, 2015 3:58 PM
To: Ronald Pickard ; 
EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] EN 62368-1 query



Hi Ron:


>But, a capacitor charged to such an open-circuit voltage need to also be rated 
>for that voltage (probably a DUH moment). Correct?

Yes.

>Is Table 2 of IEC 61201:1992 equivalent to Table A.2 of IEC 61201:2007?

Yes.

>ECMA 287 Table 3.4 ES1 values decrease from 60 V instead of increasing from 60 
>V from IEC 62368-1 Table 5 ES1 values.

In ECMA 287, Table 3.4 is ordered by capacitance, while IEC 61201 is ordered by 
voltage.  The ES1 voltage values in ECMA 287 "are derived from Table 2 of IEC 
61201" and are not the values in IEC 61201.   IEC 62368-1 uses the table 
verbatim.

>So, the purpose of 5.2.2.3 is intended to apply to those capacitors in which 
>their charged voltages are exposed in ES1 circuits during normal operating 
>conditions and become exposed in ES2 circuits only after a fault?

Yes, although I would use the word "accessible" as, in the IEC, the word 
"exposed" has a different meaning.

(ES1 is not necessarily a circuit, but a voltage with respect to ground from 0 
to 42.4 or a current to ground from 0 to 0.5 mA.)

Need any more clarification?


Best regards,
Rich




-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: 


[PSES] Thank you to Rodney Davis

2015-10-26 Thread McBurney, Ian
Many thanks to Rodney Davis for his help with my Level VI USA Energy efficiency 
enquiry.

Regards;

Ian McBurney
Design & Compliance Engineer.

Allen & Heath Ltd.
Kernick Industrial Estate,
Penryn, Cornwall. TR10 9LU. UK
T: 01326 372070
E: ian.mcbur...@allen-heath.com


Allen & Heath Ltd is a registered business in England and Wales, Company 
number: 4163451. Any views expressed in this email are those of the individual 
and not necessarily those of the company.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: 


[PSES] Stricter limits than legal (CISPR11, IEC, etc.,)

2015-10-26 Thread Itzenheiser, Jerry (GE Healthcare)

Thank you to all for the comments on Stricter limits than legal (CISPR11, IEC, 
etc.,).


Jerry Itzenheiser Jr
EMC Technician - Waukesha
GE Healthcare
Global Engineering Technologies
EMC Laboratory Waukesha

T  + 262-548-2217
M + 262-720-8846
gerald.itzenhei...@med.ge.com
www.ge.com

3000 N. Grandview Blvd.
Mail Code W618
Waukesha, WI  53188

GE imagination at work


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: 


[PSES] EN 62368-1 query

2015-10-26 Thread Ronald Pickard
For all those more familiar than I with this standard, I would appreciate a 
clarification.

I've just purchased EN 62368-1 (assuming IEC 62368-1, too) and have started 
immersing myself in it, but in 5.2.2.3 (Table 5) ES1/ES2 voltage limits from a 
charged capacitor appear to violate the ES1/ES2 voltage limits from 5.2.2.2 
(Table 4). As Table 5 doesn't address Vdc or Vac, I am assuming absolute 
voltages (Upeak not defined) apply here. It appears that up to 25KV (50KV for 
ES2) are allowed depending on capacitor value. And, how would a capacitor be 
charged to 25KV in or then connected to an ES1 circuit without consequence? Am 
I reading this correctly? Are these voltage limits intended for capacitor 
rating limits only? What is the purpose of 5.2.2.3 and Table 5?

The further I get with this, the more questions that pop up for me. I can't 
seem to resolve this in my own feeble grey matter as to why such voltages would 
be allowed. I would like to understand this better and would appreciate if 
someone would clarify this for me and possibly others that may have these or 
similar questions as well.

I look forward to your reply.

Best regards,

Ronald Pickard
Regulatory Compliance Engineer
Compound Photonics
D | +1 (602) 883-8039


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: 


Re: [PSES] 208 split-phase?

2015-10-26 Thread Peter Tarver
Ralph –



I’m less familiar with the CEC, but the NEC does not preclude 208/120 V WYE
to a single-family home (residence).  It all depends on how much one is
willing to pay the utility for the service and proper provisioning and
system design at the use location.





Peter Tarver



*From:* McDiarmid, Ralph [mailto:ralph.mcdiar...@schneider-electric.com]
*Sent:* Thursday, October 22, 2015 15:00
*To:* EMC-PSTC@LISTSERV.IEEE.ORG
*Subject:* Re: [PSES] 208 split-phase?



NEC art 210.4 and 210.5 seem to allow it and the CEC here in Canada
certainly allows it. For large residential highrises, it's probably simpler
and cost effective to distribute 120/208 throughout the building (1/3 of
the suites on one 208 leg, and so on)  Phase balancing would be part of the
building electrical plan.  Sending a single-phase MV feeder to 1MVA,
120/240V transformer is likely a comprehmise

It's different for low density residential where stringing a mile or two of
single-phase MV to feed 120/240 pole transformers throughout the
neighborhood makes more sense.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas 
Mike Cantwell 

For policy questions, send mail to:
Jim Bacher:  
David Heald: 


Re: [PSES] EN 62368-1 query

2015-10-26 Thread Scott Aldous
Hi Ronald,

It may be helpful for you to purchase a copy of 62368-2, which has the
rationale for the requirements in 62368-1.

Others can provide more detail and probably explain better than I, but in
general Table 4 has voltage *or* current limits, and Table 5 has
capacitance *and* voltage limits. Table 4 is based on current (concerned
with electrical shock), while Table 5 is based on energy (concerned with
energy hazard), so you aren't comparing apples to apples by just looking at
the voltage values in each table.

*Table 4 (Electric Shock)*

See Figure 21, and the explanation at the end of 5.2.2.1. "For any voltage
up to the voltage limit, there is no limit for the current. Likewise for
any current up to the current limit, there is no limit for the voltage..."

   - For low voltage circuits, the current is limited by the impedance
   through the human body. The currents assumed to flow through the human body
   at the ES1 voltage limits are lower than that which causes undesirable
   physiological effects.
   - There could be an ES1 circuit up to 25kV, or even higher in theory
   (with currents in normal, abnormal and single fault conditions limited to
   comply with the applicable limit). As long as the current is limited to
   values below that which causes undesirable physiological effects, the
   voltage doesn't matter. This is similar to the Limited Current Circuit from
   60950-1, clause 2.4.

*Table 5 (Capacitor Energy)*

For the energy from a capacitor, the table takes into account capacitance
and voltage, so both need to be taken into account since the equation for
available energy from a capacitor includes both variables. This is similar
to 2.1.1.5c)2) from 60950-1.

A bit more info here

(see
section III).



On Mon, Oct 26, 2015 at 10:31 AM, Ronald Pickard <
ronald.pick...@compoundphotonics.com> wrote:

> For all those more familiar than I with this standard, I would appreciate
> a clarification.
>
>
>
> I’ve just purchased EN 62368-1 (assuming IEC 62368-1, too) and have
> started immersing myself in it, but in 5.2.2.3 (Table 5) ES1/ES2 voltage
> limits from a charged capacitor appear to violate the ES1/ES2 voltage
> limits from 5.2.2.2 (Table 4). As Table 5 doesn’t address Vdc or Vac, I am
> assuming absolute voltages (Upeak not defined) apply here. It appears that
> up to 25KV (50KV for ES2) are allowed depending on capacitor value. And,
> how would a capacitor be charged to 25KV in or then connected to an ES1
> circuit without consequence? Am I reading this correctly? Are these voltage
> limits intended for capacitor rating limits only? What is the purpose of
> 5.2.2.3 and Table 5?
>
>
>
> The further I get with this, the more questions that pop up for me. I
> can’t seem to resolve this in my own feeble grey matter as to why such
> voltages would be allowed. I would like to understand this better and would
> appreciate if someone would clarify this for me and possibly others that
> may have these or similar questions as well.
>
>
>
> I look forward to your reply.
>
>
>
> Best regards,
>
>
>
> *Ronald Pickard*
> Regulatory Compliance Engineer
> *Compound Photonics*
> D | +1 (602) 883-8039
>
> -
> 
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to 
> emc-p...@ieee.org
>
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
>
> Attachments are not permitted but the IEEE PSES Online Communities site at
> http://product-compliance.oc.ieee.org/ can be used for graphics (in
> well-used formats), large files, etc.
>
> Website: http://www.ieee-pses.org/
> Instructions: http://www.ieee-pses.org/list.html (including how to
> unsubscribe) 
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
> Scott Douglas sdoug...@ieee.org
> Mike Cantwell mcantw...@ieee.org
>
> For policy questions, send mail to:
> Jim Bacher j.bac...@ieee.org
> David Heald dhe...@gmail.com
>



-- 
Scott Aldous
Compliance Engineer
Google
650-253-1994
scottald...@google.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List