Re: [PSES] SCCR Rating Question

2024-05-16 Thread Ralph McDiarmid
We have an answer from UL508A for industrial panels but the question was, “ 
SCCR ratings on industrial machinery”

 

Perhaps it is the question that is the difficulty here.

 

Ralph

 

From: Bill Lawrence  
Sent: Thursday, May 16, 2024 2:50 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] SCCR Rating Question

 

Assume UL 508A

 

Marking is:

 



-Original Message-
From: MIKE SHERMAN mailto:msherma...@comcast.net> >
Sent: May 15, 2024 10:38 PM
To: mailto:EMC-PSTC@LISTSERV.IEEE.ORG> >
Subject: Re: [PSES] SCCR Rating Question

 

Brian —

 

I am equally mystified by qualifying an SCCR with a voltage. Perhaps you could 
network into a friendly UL 408a panel shop and see what they say.  

Mike Sherman 

Sherman PSC LLC

On 05/15/2024 9:05 AM -05 Brian Kunde mailto:bkundew...@gmail.com> > wrote:

 

 

I appreciate the replies, but I am not getting the information I am seeking.  

 

Some machines have just the SCCR Rating, such as 

 

SCCR: 10kA

 

but a few machines we have looked at include a reference to the "Max Voltage", 
such as

 

SCCR: 10kA RMS Symmetrical, 480V Maximum

 

What is the source, code, standard, directive, etc. that calls out the Max 
Voltage as a requirement in the SCCR rating that is printed on the Nameplate 
label?  We cannot find such a source.  

 

In our case, we have a machine that can operate at 230V, 380V, or 480V 
depending on how the motor is wired. So on a machine rated 230V it has a SCCR 
rating that includes the Max Voltage of 480V.  We are getting push-back from 
the field saying that having the voltage on the SCCR rating is confusing. To 
resolve this, we want to remove the reference to the Max Voltage, but before we 
do that, we want to find out if it is mandated in the code or some standard.  

 

I can see where the max voltage might be required on some components. Maybe it 
is an old requirement that is no longer required.  I am just guessing.  

 

Thanks again for your help.

The Other Brian

 

 

On Tue, May 14, 2024 at 3:54 PM Scott Aldous 
<0220f70c299a-dmarc-requ...@listserv.ieee.org 
 > wrote:

Starting on page 7, the white paper that Rich linked to also references UL 
508A, supplement SB, which is a method of determining SCCR for industrial 
control panels without test. The method at a high level involves carrying over 
the SCCR rating of the "weakest link in the chain" from a protective component 
standpoint to the overall panel. I wonder if that method may have been used for 
the machinery in question, with a component level voltage rating (improperly, 
in my opinion) shifted over to the end device. Note that UL 508A includes "at a 
nominal voltage" in its definition of SCCR.

 

On Tue, May 14, 2024 at 12:33 PM Richard Nute mailto:ri...@ieee.org> > wrote:

 

Hi Brian:

 

See the very last line of:

 

https://www.mouser.com/pdfDocs/littelfuse_industrial_whitepaper_increase_sccr.pdf

 

Best regards,

Rich

 

 

 

 

From: Ralph McDiarmid mailto:rmm.priv...@gmail.com> > 
Sent: Tuesday, May 14, 2024 11:41 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG  
Subject: Re: [PSES] SCCR Rating Question

 

Could this number to used to select a suitable circuit breaker and so the 
interrupting voltage is an important parameter?

 

The nameplate rating on the machine should be the information an electrician 
needs during installation and selection of wire size and type.

 

Ralph

 

From: Brian Kunde mailto:bkundew...@gmail.com> > 
Sent: Tuesday, May 14, 2024 11:29 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG  
Subject: [PSES] SCCR Rating Question

 

Greetings to all.  

 

I am new to SCCR ratings on industrial machinery.  The ratings I have seen 
sometimes has a "Maximum Voltage" included, such as;

 

SCCR: 22kA, 600V Maximum

 

Where does the voltage value come from?  In one case, the machine had a line 
voltage rating of "120/208 Vac", but the SCCR rating had a voltage rating of 
"Max 600V".

 

Can this be confusing? Might something think the machine can operate at 600Vac?

 

Thanks for any replies.

The Other Brian

 

 


  _  


This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG   

All emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/ 
  

Website: https://ewh.ieee.org/soc/pses/   
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)  
List rules: https://ewh.ieee.org/soc/pses/listrules.html 

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net  
Rick Linford at: 

Re: [PSES] SCCR Rating Question

2024-05-16 Thread Bill Lawrence
Assume UL 508A

Marking is:


-Original Message-
From: MIKE SHERMAN 
Sent: May 15, 2024 10:38 PM
To: 
Subject: Re: [PSES] SCCR Rating Question

Brian 
 
I am equally mystified by qualifying an SCCR with a voltage. Perhaps you could 
network into a friendly UL 408a panel shop and see what they say.  


Mike Sherman 
Sherman PSC LLC
On 05/15/2024 9:05 AM -05 Brian Kunde  wrote:
 
 
I appreciate the replies, but I am not getting the information I am seeking.  
Some machines have just the SCCR Rating, such as 
 
SCCR: 10kA
 
but a few machines we have looked at include a reference to the "Max Voltage", 
such as
 
SCCR: 10kA RMS Symmetrical, 480V Maximum
 
What is the source, code, standard, directive, etc. that calls out the Max 
Voltage as a requirement in the SCCR rating that is printed on the Nameplate 
label?  We cannot find such a source.  
 
In our case, we have a machine that can operate at 230V, 380V, or 480V 
depending on how the motor is wired. So on a machine rated 230V it has a SCCR 
rating that includes the Max Voltage of 480V.  We are getting push-back from 
the field saying that having the voltage on the SCCR rating is confusing. To 
resolve this, we want to remove the reference to the Max Voltage, but before we 
do that, we want to find out if it is mandated in the code or some standard.  
 
I can see where the max voltage might be required on some components. Maybe it 
is an old requirement that is no longer required.  I am just guessing.  
 
Thanks again for your help.
The Other Brian
 


On Tue, May 14, 2024 at 3:54 PM Scott Aldous 
<0220f70c299a-dmarc-requ...@listserv.ieee.org 
(mailto:0220f70c299a-dmarc-requ...@listserv.ieee.org)> wrote:
Starting on page 7, the white paper that Rich linked to also references UL 
508A, supplement SB, which is a method of determining SCCR for industrial 
control panels without test. The method at a high level involves carrying over 
the SCCR rating of the "weakest link in the chain" from a protective component 
standpoint to the overall panel. I wonder if that method may have been used for 
the machinery in question, with a component level voltage rating (improperly, 
in my opinion) shifted over to the end device. Note that UL 508A includes "at a 
nominal voltage" in its definition of SCCR.

On Tue, May 14, 2024 at 12:33 PM Richard Nute mailto:ri...@ieee.org)> wrote:
 
Hi Brian:
 
See the very last line of:
 
https://www.mouser.com/pdfDocs/littelfuse_industrial_whitepaper_increase_sccr.pdf
 
Best regards,
Rich
 
 
 
 
From: Ralph McDiarmid mailto:rmm.priv...@gmail.com)> 
Sent: Tuesday, May 14, 2024 11:41 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG (mailto:EMC-PSTC@LISTSERV.IEEE.ORG)
Subject: Re: [PSES] SCCR Rating Question


 
Could this number to used to select a suitable circuit breaker and so the 
interrupting voltage is an important parameter?
 
The nameplate rating on the machine should be the information an electrician 
needs during installation and selection of wire size and type.
 
Ralph
 
From: Brian Kunde mailto:bkundew...@gmail.com)> 
Sent: Tuesday, May 14, 2024 11:29 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG (mailto:EMC-PSTC@LISTSERV.IEEE.ORG)
Subject: [PSES] SCCR Rating Question

 
Greetings to all.  
 

I am new to SCCR ratings on industrial machinery.  The ratings I have seen 
sometimes has a "Maximum Voltage" included, such as;

 

SCCR: 22kA, 600V Maximum

 

Where does the voltage value come from?  In one case, the machine had a line 
voltage rating of "120/208 Vac", but the SCCR rating had a voltage rating of 
"Max 600V".

 

Can this be confusing? Might something think the machine can operate at 600Vac?

 

Thanks for any replies.

The Other Brian

 

 



This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG (mailto:EMC-PSTC@LISTSERV.IEEE.ORG) 
All emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/ 
Website: https://ewh.ieee.org/soc/pses/ 
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html 
For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net (mailto:msherma...@comcast.net)
Rick Linford at: linf...@ieee.org (mailto:linf...@ieee.org) 
For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org (mailto:j.bac...@ieee.org) 

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTCA=1 

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
EMC-PSTC@LISTSERV.IEEE.ORG (mailto:EMC-PSTC@LISTSERV.IEEE.ORG) 
All emc-pstc postings are archived and searchable on the web at: 
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/ 
Website: https://ewh.ieee.org/soc/pses/ 
Instructions: