RE: Constant for Change of Resistance formula.

2002-05-14 Thread Bill Ellingford

Hi Robert, Group
Yes, this is a known factor for mis-measurement.  You must always isolate
the component part / winding etc and measure each resistive element to find
the individual temperature rises.  This is common practice when measuring
motor windings, you would take a sample of windings measuring at the brush
caps (hot brushes quickly removed) at pre-marked segments on the commutator.
This allows you to get a picture of the heat characteristics of a number of
windings and hence heat spread throughout the motor windings.  Yes, accuracy
depends on the resistance being measured but where the formula is applied
(motors, relay coils, transformers, solenoids and other mechelec devices),
the resistance is high enough to get a good result as long as you follow the
guidelines (like those above).

Thanks for raising the measurement factors.

Bill Ellingford

-Original Message-
From: Robert Macy [mailto:m...@california.com]
Sent: 14 May 2002 02:00
To: Bill Ellingford; emc-p...@majordomo.ieee.org
Subject: Re: Constant for Change of Resistance formula.


Bill,

Big oops.

Measuring the resistance to determine the temperature is not productive
*unless* the resistance dominates the resistance measurement.

Picture three equal valued resistances in a row.  The middle one gets very
hot (more than 100C rise) and increases over 40%, the two on the edges are
heat sinked and barely increase in temperature.  The resulting change in
resistance is 13% which implies the temperature in there has only gone up
around 33C.

Measuring the resistance doesn't tell you much.  At least with transformers
the dominant resistance is pretty much the bulk resistance.

- Robert -


-Original Message-
From: Bill Ellingford bill.ellingf...@motion-media.com
To: 'Robert Macy' m...@global.california.com; emc-p...@majordomo.ieee.org
emc-p...@majordomo.ieee.org
List-Post: emc-pstc@listserv.ieee.org
Date: Monday, May 13, 2002 1:56 PM
Subject: RE: Constant for Change of Resistance formula.



Hi Robert / group
OK, Not the best choice of website to demo the answer.  The differing
figures are because the formula has been transposed to give Temp from
change
of R from the original formula which gives R from change of T.  To do this,
another constant (The 234.5 constant) is required.  This is the implied
point of zero resistance for copper on the Celsius scale.  The formula we
use is:

  Rfinal - Rorig
  x (234.5 + Tamb start) -(Tamb finsh - Tamb start)
  Rorig

The Tamb start and finish are the changes (if any) in Room ambient.  If the
room remains at 20c then 234.5 + 20 is the multiplier.

-Original Message-
From: Robert Macy [mailto:m...@california.com]
Sent: 13 May 2002 14:54
To: Bill Ellingford; emc-p...@majordomo.ieee.org
Subject: Re: Constant for Change of Resistance formula.


Bill,

Thanks for the site.

Went there and found the same formula and constant I use.

For copper, Temp Coeff = 3.9 x 10-3

Then I clicked on table of coeff and there was a very long list of
materials, but the temp coeff of copper there was 6.8 x 10-3  ???!!!

Any ideas for this disparity?

- Robert -

   Robert A. Macy, PEm...@california.com
   408 286 3985  fx 408 297 9121
   AJM International Electronics Consultants
   619 North First St,   San Jose, CA  95112


-Original Message-
From: Bill Ellingford bill.ellingf...@motion-media.com
To: 'Colgan, Chris' chris.col...@tagmclaren.com;
emc-p...@majordomo.ieee.org emc-p...@majordomo.ieee.org
Date: Monday, May 13, 2002 5:38 AM
Subject: RE: Constant for Change of Resistance formula.



Hi Folks
Further to the answer given, here is a little more data.
The constant used is for the change of resistance with temperature.  metals
and alloys (conductors) all exhibit a different constant.  This can be used
for calculating temperature rise or resistance change.  i.e. find the temp
rise from a start and finish test measurement on a winding (for example) at
the begining and end of a on load heat run or, find R for a given temp:
using a table or the formula, resistance at various temperatures can be
pre-determined from a measurement made at one particular temperature.

A website with the formulae can be found at
http://hyperphysics.phy-astr.gsu.edu/hbase/electric/restmp.html

Where you have a transition from one metal type to another, you must
measure
each metal part individually.  If you have only two metals in contact, you
may be able to apply a combination of the temp coefficient methods and
transposition of the measurement of change of junction voltage formulae
i.e.
Thermocouple laws.

Hope this adds some value:  Bill Ellingford

-Original Message-
From: Colgan, Chris [mailto:chris.col...@tagmclaren.com]
Sent: 13 May 2002 10:28
To: emc-p...@majordomo.ieee.org
Subject: RE: Constant for Change of Resistance formula.



Ned is referring to the constant used in the temperature rise

RE: Constant for Change of Resistance formula.

2002-05-13 Thread Bill Ellingford

Hi Robert / group
OK, Not the best choice of website to demo the answer.  The differing
figures are because the formula has been transposed to give Temp from change
of R from the original formula which gives R from change of T.  To do this,
another constant (The 234.5 constant) is required.  This is the implied
point of zero resistance for copper on the Celsius scale.  The formula we
use is:

  Rfinal - Rorig  
  x (234.5 + Tamb start) -(Tamb finsh - Tamb start)
  Rorig

The Tamb start and finish are the changes (if any) in Room ambient.  If the
room remains at 20c then 234.5 + 20 is the multiplier.

-Original Message-
From: Robert Macy [mailto:m...@california.com]
Sent: 13 May 2002 14:54
To: Bill Ellingford; emc-p...@majordomo.ieee.org
Subject: Re: Constant for Change of Resistance formula.


Bill,

Thanks for the site.

Went there and found the same formula and constant I use.

For copper, Temp Coeff = 3.9 x 10-3

Then I clicked on table of coeff and there was a very long list of
materials, but the temp coeff of copper there was 6.8 x 10-3  ???!!!

Any ideas for this disparity?

- Robert -

   Robert A. Macy, PEm...@california.com
   408 286 3985  fx 408 297 9121
   AJM International Electronics Consultants
   619 North First St,   San Jose, CA  95112


-Original Message-
From: Bill Ellingford bill.ellingf...@motion-media.com
To: 'Colgan, Chris' chris.col...@tagmclaren.com;
emc-p...@majordomo.ieee.org emc-p...@majordomo.ieee.org
List-Post: emc-pstc@listserv.ieee.org
Date: Monday, May 13, 2002 5:38 AM
Subject: RE: Constant for Change of Resistance formula.



Hi Folks
Further to the answer given, here is a little more data.
The constant used is for the change of resistance with temperature.  metals
and alloys (conductors) all exhibit a different constant.  This can be used
for calculating temperature rise or resistance change.  i.e. find the temp
rise from a start and finish test measurement on a winding (for example) at
the begining and end of a on load heat run or, find R for a given temp:
using a table or the formula, resistance at various temperatures can be
pre-determined from a measurement made at one particular temperature.

A website with the formulae can be found at
http://hyperphysics.phy-astr.gsu.edu/hbase/electric/restmp.html

Where you have a transition from one metal type to another, you must measure
each metal part individually.  If you have only two metals in contact, you
may be able to apply a combination of the temp coefficient methods and
transposition of the measurement of change of junction voltage formulae i.e.
Thermocouple laws.

Hope this adds some value:  Bill Ellingford

-Original Message-
From: Colgan, Chris [mailto:chris.col...@tagmclaren.com]
Sent: 13 May 2002 10:28
To: emc-p...@majordomo.ieee.org
Subject: RE: Constant for Change of Resistance formula.



Ned is referring to the constant used in the temperature rise calculated by
change in resistance formula ie

...

Where dt is the temperature rise, R1 is start resistance, R2 is end
resistance, T1 is start ambient and T2 is end ambient.  234.5 is the formula
constant for copper.

This formula is used extensively when heat testing transformers and coils.

I'm afraid I don't know the constant for brass but I believe the figure may
be related to the inferred absolute zero of a material.  Try asking a
metallurgist?

Regards

Chris Colgan
Compliance Engineer
TAG McLaren Audio Ltd
The Summit, Latham Road
Huntingdon, Cambs, PE29 6ZU
*Tel: +44 (0)1480 415 627
*Fax: +44 (0)1480 52159
* Mailto:chris.col...@tagmclaren.com
* http://www.tagmclaren.com




 -Original Message-
 From: Robert Wilson [SMTP:robert_wil...@tirsys.com]
 Sent: Friday, May 10, 2002 7:00 PM
 To: emc-p...@majordomo.ieee.org; Ned Devine
 Subject: RE: Constant for Change of Resistance formula.

 What are the units? 234.5 ...what?? Looking at what the units are, will
 basically tell you exactly what the property is related to.



 Nonetheless, you cannot possibly directly determine what the temperature
 change of something as physically and geometrically complex as a
 connector, merely by factoring in what its resistance change is. Among
 other things, the solution is extremely non-linear and iterative. Changing
 resistance will generate more heat, which will increase temperature, which
 will generate even more heat and on and on! Add this to the fact the
 resistance coefficient with temperature is itself non-linear, and you can
 see how this complicates things further. The final temperature that the
 system stabilizes at, is reached when the logarithmically increasing
 (i.e. also very non-linear) heat transfer to the environment caused by
 increasing temperature, balances increased heat being generated.



 To reach a solution, you need to iterate your calculations, where the
 results of one calculation are plugged as variables

RE: Constant for Change of Resistance formula.

2002-05-13 Thread Bill Ellingford

Hi Folks
Further to the answer given, here is a little more data.
The constant used is for the change of resistance with temperature.  metals
and alloys (conductors) all exhibit a different constant.  This can be used
for calculating temperature rise or resistance change.  i.e. find the temp
rise from a start and finish test measurement on a winding (for example) at
the begining and end of a on load heat run or, find R for a given temp:
using a table or the formula, resistance at various temperatures can be
pre-determined from a measurement made at one particular temperature.

A website with the formulae can be found at
http://hyperphysics.phy-astr.gsu.edu/hbase/electric/restmp.html

Where you have a transition from one metal type to another, you must measure
each metal part individually.  If you have only two metals in contact, you
may be able to apply a combination of the temp coefficient methods and
transposition of the measurement of change of junction voltage formulae i.e.
Thermocouple laws.

Hope this adds some value:  Bill Ellingford

-Original Message-
From: Colgan, Chris [mailto:chris.col...@tagmclaren.com]
Sent: 13 May 2002 10:28
To: emc-p...@majordomo.ieee.org
Subject: RE: Constant for Change of Resistance formula.



Ned is referring to the constant used in the temperature rise calculated by
change in resistance formula ie

 ... 

Where dt is the temperature rise, R1 is start resistance, R2 is end
resistance, T1 is start ambient and T2 is end ambient.  234.5 is the formula
constant for copper.

This formula is used extensively when heat testing transformers and coils.

I'm afraid I don't know the constant for brass but I believe the figure may
be related to the inferred absolute zero of a material.  Try asking a
metallurgist?

Regards

Chris Colgan
Compliance Engineer
TAG McLaren Audio Ltd
The Summit, Latham Road
Huntingdon, Cambs, PE29 6ZU
*Tel: +44 (0)1480 415 627
*Fax: +44 (0)1480 52159
* Mailto:chris.col...@tagmclaren.com
* http://www.tagmclaren.com




 -Original Message-
 From: Robert Wilson [SMTP:robert_wil...@tirsys.com]
 Sent: Friday, May 10, 2002 7:00 PM
 To:   emc-p...@majordomo.ieee.org; Ned Devine
 Subject:  RE: Constant for Change of Resistance formula.
 
 What are the units? 234.5 ...what?? Looking at what the units are, will
 basically tell you exactly what the property is related to.
 
  
 
 Nonetheless, you cannot possibly directly determine what the temperature
 change of something as physically and geometrically complex as a
 connector, merely by factoring in what its resistance change is. Among
 other things, the solution is extremely non-linear and iterative. Changing
 resistance will generate more heat, which will increase temperature, which
 will generate even more heat and on and on! Add this to the fact the
 resistance coefficient with temperature is itself non-linear, and you can
 see how this complicates things further. The final temperature that the
 system stabilizes at, is reached when the logarithmically increasing
 (i.e. also very non-linear) heat transfer to the environment caused by
 increasing temperature, balances increased heat being generated. 
 
  
 
 To reach a solution, you need to iterate your calculations, where the
 results of one calculation are plugged as variables into the next
 iteration. Typically a thermal analysis program will require several
 hundred iteration before a converged solution results.
 
  
 
 Bob Wilson 
 TIR Systems Ltd. 
 Vancouver. 
 
 -Original Message-
 From: Ned Devine [mailto:ndev...@entela.com] 
 Sent: May 10, 2002 8:29 AM
 To: emc-p...@majordomo.ieee.org
 Subject: Constant for Change of Resistance formula.
 
  
 
 Hi,
 
  
 
 Does any one know how the constant for CoR formula was determined?  I know
 the K is 234.5 for copper and 226 for aluminum, but what property is this
 related to?  
 
  
 
 I am trying to determine the change in temperature of a connector, based
 on the change of resistance.  The connector contacts are made of brass.  
 
  
 
 Thanks
 
  
 
 Ned
 
  
 
  
 
 Ned Devine 
 Program Manager 
 Entela, Inc. 
 3033 Madison Ave. SE 
 Grand Rapids, MI  49548 
 1 616 248 9671 Phone 
 1 616 574 9752 Fax 
 ndev...@entela.com e-mail 
 
 Entela, Inc. A Certified Woman Owned Business 
 www.entela.com 
 
  
 
  
 
  
 
  
 
  
 
  
 


**  
   Please visit us at www.tagmclaren.com
**

The contents of this E-mail are confidential and for the exclusive
use of the intended recipient. If you receive this E-mail in error,
please delete it from your system immediately and notify us either
by E-mail, telephone or fax. You  should not  copy, forward or 
otherwise disclose the content of the E-mail.

TAG McLaren Audio Ltd
The Summit, 11 Latham Road
Huntingdon, Cambs, PE29 6ZU
Telephone : 01480 415600 (+44 1480 415600)
Facsimile : 01480 52159 (+44 1480 52159

RE: RTTE Directive

2002-05-09 Thread Bill Ellingford
Hi Group, John etc.
The RTTE has provision Network Access essential requirements (for wired
products) to be added if the commission find a need.  Currently, there are
no requirements except for those added to cover France Telecom.  Parts of
the French POTs network use old technology where certain transformers
(possibly A type relays) become saturated and thus will not pass any audio
if the line current drawn exceeds 60mA.
 
For an interim period, the commission have included the Line feeding tests
(60mA current limit) from TBR21 as an applicable, essential requirement for
France.  There is a withdrawal date for this requirement so it to will soon
vanish.
 
I agree with John, many sales chains are unhappy taking product with no
network access test results, we therefore choose to voluntarily apply the
TBR standards as a means of demonstrating compliance with the former,
applied essential requirements to show to any interested parties.  This
testing can of course be of further benefit, as many reports can be used in
other countries to support an overseas approval application.  This is
particulalry true of more modern technologies like ISDN BRI and PRI, ONP
etc.  A good example of this is TBR3 which is widely accepted as the Euro /
CEPT ISDN test standard.  Investigate the standards you apply as part of any
One stop multi-country approvals strategy.
 
I also agree that other, design standards may be applied.  The directive
calls for all PTOs to provide a list of interface specifications for the
ports available on their networks.  Many PTOs are quoting earlier national
specification for this purpose (I see some BS specs on the BT site) and many
refer to the NETs and TBRs from previous years.
 
Do not forget that Wireless interfaces do still have connection requirements
under the directive, where possible these are harmonised (ETSI) but due to
deviation in frequency allocations and terrain, many remain based on
National standards.
 
This is only a brief answer, obviously there is a lot more content in the
actual body of the directive.  This should be essential (but not bed time)
reading for this subject!
the 99/5/EC directive can be downloaded from our favourite EUROPA server.
 
Hope this helps.  Best regards
 
Bill Ellingford 
 
Approvals  Conformance manager
Motion Media Technology Ltd

-Original Message-
From: j...@aol.com [mailto:j...@aol.com]
Sent: 08 May 2002 17:06
To: jjuh...@fiberoptions.com
Cc: emc-p...@majordomo.ieee.org
Subject: Re: RTTE Directive


In a message dated 5/8/2002, John Juhasz writes:




it appears that it is not required to test the interface itself to
'telecom specs' such as those in the CTR21. 





Hi John:

Your interpretation is correct.  For wireline POTS products/interfaces, the
only requirements that apply under the RTTE directive are safety and EMC.
There are no regulatory requirements whatsoever for the type of
specifications called out in CTR 21.  CTR 21 ceased to be a regulatory
requirement when the RTTE directive came into force on April 8, 2000.

That being said, many manufacturers are uncomfortable with having no
regulatory requirements for telecom.  One option is to continue voluntary
testing to CTR 21.  Another option is to obtain the individual reference
standards that the RTTE directive requires each operator of a public network
to publish.  Most of the major operators have posted these on their web
sites.  

A third option is to review CTR 21 and the relevant reference
specifications, then use engineering judgment to design and test your
interface.  This is the preferred approach if you are seeking minimum cost
and/or maximum compatibility with the various national networks.

The bottom line is that the telecom aspects of your product performance are
now a matter between you and your customer, rather than between you and the
regulators.


Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848
http://www.randolph-telecom.com 



*


Employment

2002-05-08 Thread Bill Ellingford

Hi Guys
I have been a member of these interest groups for some time and a once
regular contributor to Treg.  Please allow me to question job opportunities
in the Bristol / S Wales area UK.  I attach a brief resume.  

Please skip this message if this is outside your scope.  Many thanks to
anyone who can offer any leads, info, help etc.




I am seeking employment opportunities in the ITT industry, preferably
around the Bristol, South Wales borders region UK.  I am currently working
as Approvals and Conformance Manager with specialised knowledge in the
Telecom domain.  My work covers Safety, EMC and Network access as well as
monitoring global change and EU directives.  My role also touches on HS.

I support the company and its distributors on approvals and certification
exercises in most global regions but most often USA, Canada, EU, S Africa
and Australasia.  I project manage multiple submissions for a range of
products and enhancements and advise at design stage on product
construction.  I also manage a database of Compliance Affecting Parts to
assist submissions with UL.

In addition to the compliance side, I also currently manage the company
conformance test schedules, checking manufactured devices meet operational
and functional specs.

I also provide advice and test methodology for POT's, ISDN (BRI and PRI),
X.21, X.25 E1, E2, E3 (and T1).  In the past I have worked in the standards
industry including participation in standards development, I have also
worked as a consultant in standards and compliance engineering for many
years before moving for a more settled role within industry.  I have a young
family, hence my preference to stay in the Glos / Bristol / Newport region.

I would be very pleased to hear from anyone within the group with news on
any possible openings / positions in this area.

Bill Ellingford
Approvals / Conformance Manager, 
Motion Media Technology Ltd

company E-mail address valid until 17 May 02


*

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: A very nice game

2002-04-24 Thread Bill Ellingford

URGENT
Please be aware that the above E-mail to the EMC group contained a virus.
Fortunately our system removed it from the message.
Bill Ellingford

-Original Message-
From: jmw [mailto:j...@jmwa.demon.co.uk]
Sent: 24 April 2002 22:59
To: emc-p...@ieee.org
Subject: A very nice game



--  Virus Warning Message (on gemini2)

setup.exe is removed from here because it contains a virus.

-


*

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: product modifications by the end user

2002-03-19 Thread Bill Ellingford

Hi Folks
Safety compliance for an add-in card is not an impossibiity!
You can follow EN 60950 and come up with a compliant product design which
allows user access to internal SELV status parts.  This is often the case
with PC's.  You may then design a card for installation within such a
product which, together with the installation instructions, is deemed a
compliant product.  The same is true of certain games machines having SELV
cartridge ports where a cover is removed allowing expansion memory etc. to
be fitted.

PCs designed in this way often require no tools to remove the access cover,
some have knurled nuts or twist locks.

I even beleive there is a UL scheme (although I haven't checked for a few
months) to cover PCs designed in this way and also a scheme to cover a UL
Listed Accessory card for use in these.  This scheme includes the
documentation in the listing.

There may still be some EMC issues to address but safety compliance is not
impossible!

Bill Ellingford

-Original Message-
From: geor...@lexmark.com [mailto:geor...@lexmark.com]
Sent: 19 March 2002 14:26
To: Colgan, Chris
Cc: 'Emc-Pstc' (E-mail)
Subject: Re: product modifications by the end user





Chris,

Every set of existing rules has an intent, to be achieved by
following the letter of the rules.  Personally, I always consider
meeting the intent far superior to meeting the letter of rules.
Example, the letter of the law says we must stop at stop signs before
proceeding.  The intent is to avoid accidents.  We all know that
sometimes we must exceed the rules, i.e. defensive driving, because
the situation demands it.  We also know that if the stop sign is in
the middle of a desert, and we can see 5 miles in all directions,
one would be meeting the intent of the law if no other cars could be
seen, an we did not stop at the sign.

The intent of IEC 60950 and like standards is to avoid personal injury
and property damage.  End users are generally considered operators
under the standard.  As such, they are to be reasonably prevented
from access to hazards in the equipment.  This does not mean that
the equipment must be in a welded steel box, but that tools are
required to enter hazardous areas, and the operator manual does not
direct the operator to access such areas.

The General Principles of 60950 (page 19) clearly states under
Electric Shock : Prevent operator access to parts at hazardous voltage
by fixed or locked covers, interlocks, etc.  Page 17 indicates that
operators are assumed to be oblivious to electrical hazards.

When all else fails in such situations as yours, I get something in
writing indicating that my team has explained the hazards and risks,
and the the Product Manager (or other responsible party) understands
and accepts these risks.  This usually closes the issue.

George





Colgan, Chris chris.colgan%tagmclaren@interlock.lexmark.com on
03/19/2002 07:36:09 AM

Please respond to Colgan, Chris
  chris.colgan%tagmclaren@interlock.lexmark.com

To:   'Emc-Pstc' (E-mail)
emc-pstc%majordomo.ieee@interlock.lexmark.com
cc:(bcc: George Alspaugh/Lex/Lexmark)
Subject:  product modifications by the end user




Hello good people

Just say someone in your marketing department came up with the bright idea
of selling upgrade kits to an unqualified, untrained end user that involved
removing the top cover of a product.  In the process not only would the
victim be exposed to hazardous voltages (if the product was still connected
to the mains) but he/she would also have to wire up mains connections.
There would also be a possibility that critical insulation would be
disturbed.

Apart from telling them that they were mad and suggesting that someone could
be killed or seriously injured, would there be any black and white
legislation that you could use to help bin this idea?  I can't find anything
specific in EN60065 or the LVD.

Thanks for any input

Chris Colgan
Compliance Engineer
TAG McLaren Audio Ltd
The Summit, Latham Road
Huntingdon, Cambs, PE29 6ZU
*Tel: +44 (0)1480 415 627
*Fax: +44 (0)1480 52159
* Mailto:chris.col...@tagmclaren.com
* http://www.tagmclaren.com








---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


*

---
This message is from the IEEE EMC

RE: CE Mark on Product Packaging

2002-03-15 Thread Bill Ellingford

Hi Guys
My wording may have been put together in haste however, I think the
important part of the directive is the word OR.  The manufacturer OR his
authorised representative, established within the community.  I had always
beleived this was interpreted as one or the other must be within the EEC
(now EU).  

This does differ from the RTTE requirement and is the basis for the
differing needs to CE mark packaging.  I am of course interested in other
views on this interpretation. 
Bill Ellingford

-Original Message-
From: Scott Lemon [mailto:sle...@caspiannetworks.com]
Sent: 15 March 2002 14:43
To: emc-pstc
Cc: Bill Ellingford; 'Russell'
Subject: Re: CE Mark on Product Packaging



Correct me if I am wrong, but I do not believe the statement below is
entirely
correct.  It is my understanding (per EMC directive and published
guidelines)
that the Manufacturer or Authorized Representative is responsible for
affixing
the CE marking and drawing up the DoC and that only the Authorized Rep (if
applicable) must be established within the community.  In other words, the
Manufacturer (who draws up the DoC and tech docs) does not have to be
established in the community, but if an Authorized Rep is used, they must
be.
It is clear that when neither the Manufacturer or the Auth Rep are
established
within the community, the obligation to keep the DoC available is the
responsibility of the party placing the product on the market (importer).

Scott Lemon
Caspian Networks

Bill Ellingford wrote:

 Under the EMC directive, the person making a DOC and
 placing the goods on the market would be an EU resident.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


*

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Voltage Spikes on Power Lines etc

2002-03-15 Thread Bill Ellingford

One clear piece of evidence is that safety standards committees always
specify much larger creepage and clearance distances for externaly supplied
hazardous voltages than for those generated within a product.  A good
example are the two sets of tables in IEC or EN 60 950.  This is to
accomodate high voltage spikes and lightning induced voltages etc.
Bill Ellingford

-Original Message-
From: George Stults [mailto:george.stu...@watchguard.com]
Sent: 14 March 2002 17:17
To: emc-p...@majordomo.ieee.org
Subject: Voltage Spikes on Power Lines etc




Hi Folks,

I am trying right now to convince some folks that power line voltage spike
problems can be and usually are severe enough to degrade or kill ITE
products that don't have adequate over-voltage protection.   I found a link
using Google that describes the problems [
http://www.kalglo.com/powrline.htm ] but I'm looking for additional links to
specifics or summaries if any one knows of such.

Thanks in advance.

George S. 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


*

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: CE Mark on Product Packaging

2002-03-15 Thread Bill Ellingford

I beleive the change in stance is due to the change in requirement regarding
a European presence.  Under the EMC directive, the person making a DOC and
placing the goods on the market would be an EU resident.  The RTTE allows
parties outside of the EU to make the DOC and hold the Technical file, it is
the person placing product on the market who carries legal liability.  This
means that goods can be imported into the EU with the CE declaration so
marking the packaging resolves customs issues in these circumstances.

Bill Ellingford

-Original Message-
From: Russell [mailto:r@totalise.co.uk]
Sent: 14 March 2002 15:39
To: emc-pstc
Subject: CE Mark on Product Packaging



Does anybody know why the placing of the CE mark on product packaging is 
compulsory under the RTTE Directive, yet optional under the EMC and LVD 
Directives?

Or am I wrong?

Only curious,

Russell.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


*

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: RTTE and video out

2002-03-13 Thread Bill Ellingford
Difficult one to call but this device may be subject to RTTE as, depends on
how it is connected and used.  It will probably have a 75 Ohm output which
will match a TV antenna impedance and thus be capable of transmitting
(albeit a short distance).  Can you get around this with warnings in the
User Guide?

Bill Ellingford

-Original Message-
From: Kim Boll Jensen [mailto:kimb...@post7.tele.dk]
Sent: 13 March 2002 10:49
To: EMC-PSTC; treg
Subject: RTTE and video out


Hi all

I have an equipment which can convert audio and video (phono connector)
signal from a PC to a normal HF antenna signal which can be transmitted
though a normal antenna cable in the house to your radio and TV sets.

The voltage of the HF signal is the same as normal received from an
antenna.

Does this product fall under the RTTE directive ?

According to my interpretation the definitions in art. 2  c) and d) say
that it has to be used for TX to be under this directive.

What do you think ?

Best regards,

Kim Boll Jensen
Bolls Raadgivning
Denmark


*


RE: ventilation holes

2002-02-27 Thread Bill Ellingford

Hi Gregg
I had a look at the safety test and beleive there are some incorrect Q A's
regarding European mains voltages.  One Q asks if the Euro mains is 220v.
Another later question asks is the Euro mains 240v.  Both of these are
incorrect, a directive on harmonisation of mains supplies calls for most EU
countries to adjust their mains volatge by increasing from 220 to 230 whilst
UK and Eire are to adjust downward from 240 to 230.

Have any of my UK colleagues stuck a DMM across their mains recently, both
my Home and works supplies have been set at 230v now.  Not sure how up to
date the rest of EU are with these plans?

Also, the question re: does UL listing for a product at 240v ensure Euro
safety compliance?  Yes, it can do now since the adoption of the latest IEC
60950 as UL 60950, providing you ask for EU deviations.

Maybe the test needs updating or have I missed something by not requesting
the answers???

Bill Ellingford

-Original Message-
From: Gregg Kervill [mailto:gkerv...@pgtv.net]
Sent: 27 February 2002 02:06
To: 'George Stults'; emc-p...@majordomo.ieee.org
Subject: RE: ventilation holes



Please have a look at   http://www.test4safety.com/html/elearning.htm for
some of the free downloadable training aids.


The one that you need is ES/2001/PHYSMECH/D 005 The Understanding Product
Safety - series - Physical and Mechanical Considerations


There is also a test on the home page for anyone brave enough!

Best reagrds

Gregg






PLEASE NOTE:

We are currently experiencing serious problems with our service provider
PLEASE reply only to gr...@test4safety.com mailto:gr...@test4safety.com
and ignore any reference to pgtv.net, Thank you.



--Original Message-
-From: owner-emc-p...@majordomo.ieee.org
-[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of George Stults
-Sent: Tuesday, February 26, 2002 1:24 PM
-To: 'emc-p...@majordomo.ieee.org'
-Subject: ventilation holes
-
-
-
-Hi Folks,
-
-I have a safety question for the group.   I  have a small
-(about 8 x 10 x 2
-inch)  piece of ITE equipment, SELV, enclosed in a plastic
-case,  powered by
-an external 12 volt brick from AC mains.
-
-The problem is, the device tends to run a little hotter than
-desired.   One
-proposed solution is to cut some vent holes in the top.
-These would be
-roughly (1/2) inch long by  (1/6) inch wide, spaced (1/4) inch apart,
-running across the top near the front of the device.
-
-I haven't seen many (any?) devices with vent holes in the top, so I'm
-wondering if there is a basic reason why not, such as the
-cover must shed
-water, etc.
-My questions are,  what considerations arise and what sections
-of EN 60950
-apply to this, either to allow it or to exclude it.
-
-Thanks in advance
-
-George S.
-
-

-This message is from the IEEE EMC Society Product Safety
-Technical Committee emc-pstc discussion list.
-
-Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
-
-To cancel your subscription, send mail to:
- majord...@ieee.org
-with the single line:
- unsubscribe emc-pstc
-
-For help, send mail to the list administrators:
- Ron Pickard:  emc-p...@hypercom.com
- Dave Heald:   davehe...@mediaone.net
-
-For policy questions, send mail to:
- Richard Nute:   ri...@ieee.org
- Jim Bacher: j.bac...@ieee.org
-
-All emc-pstc postings are archived and searchable on the web at:
-http://ieeepstc.mindcruiser.com/
-Click on browse and then emc-pstc mailing list


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


*

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http

RE: Different shades of UL

2002-02-22 Thread Bill Ellingford

A very quick and basic summary:

Very roughly speaking, the UL marks can be interpretted as follows.  (OK
there are pages and pages of jargon attached to each but the quick messy
answers are):

the UL, UL listed and CUL listed products are those that have been tested at
a UL test facility and passed the relevant applicable product tests (safety)
for such a device.  The CUL denotes listing is acceptable to UL and
harmonised Canadian standards. The list info and file will outline the
standard applied (maybe UL1950 / UL60950) and models of the equipment
covered.  Such listed devices are manufactured at UL inspected factory
facilities.

The mirror image logo is applied to components and parts for which UL have a
manufacturing scheme.  This means parts marked with the logo have been
tested using UL inspected methods and under a UL checked quality system.
This could be on a cable such a a VW-1 rated cord or a PCB with V0 Rating
etc.  Adopting logo marked parts for use in a UL listed product makes for
easier tracability of critical components.

There is also a UL listed Accessory which is for devices intended to be
installed in a host (like a card for a PC).  This is like the UL, CUL mark
but requires installation instructions as part of the assessment.

Hope this helps:  Bill Ellingford
Approvals and Compliance manager
Motion Media Technology

-Original Message-
From: Chris Maxwell [mailto:chris.maxw...@nettest.com]
Sent: 22 February 2002 14:40
To: EMC-PSTC Internet Forum
Subject: Different shades of UL



Hi all,

I know that this has been covered before.  But please indulge my
ignorance.

There are many different forms of UL marks, each with subtle
differences.  

There is the UL in a circle.  There is also the mirror lettered RU.
There are also some subscripts denoting approval for Canada as well.
There may be some other variations that I can't remember.  Anyone care
to blow a few minutes on a Friday afternoon to explain which symbol
means what?  

Thanks,

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797
8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


*

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Packaging vs. Shipping Container

1999-06-23 Thread Bill Ellingford
Hi Treg world
Re CE mark, 
The mark allows the free movement of goods within the EU and EFTA nations.  
This is because it is indicating conformity against certain directives, which 
apply throughout the union.  Therefore, if a product falls within the category 
of a directive, it requires the mark even if only sold in one member state.  
This legislation will become even more important under the new RTTE directive 
99/5/EC.

When CE marking a product, you are also declaring conformity against the 
applicable directives (interested parties may request a copy of this 
declaration).  A product that does not meet any directives would not be CE 
marked.  This could occurr for items that do not fall within the scope of 
current directives otherwise for products that do, the product would be 
non-conformant.

Most things electrical will fall under either the EMC directive or the Low 
Voltage Directive and thus require CE marking to show conformity.  SES and TTE 
fall under the SESTTE directive which is also linked to the harmonised use of 
the CE mark.

Note also that when the RTTE comes into force, the LVD is to be changed such 
that electrical safety requirements apply to any RTTE product.

The mark may be prominently displayed on packaging to assist European customs.  
It does not need to be placed on shipping containers as these are allowed to be 
opened and inspected under customs legislation.

This is a slightly rushed response so I appologise if it is not well worded.  
The scope I believe to be accurate but I welcome others to join in on this one.

Bill Ellingford.  Approvals Manager
Motion Media Technology Ltd 

--
From:   
colin_mcgeec...@hp-unitedkingdom-om4.om.hp.com[SMTP:colin_mcgeec...@hp-unitedkingdom-om4.om.hp.com]
Sent:   23 June 1999 15:16
To: mschm...@xrite.com
Cc: t...@world.std.com
Subject:RE: Packaging vs. Shipping Container

 Richard, Mark,
 
 I have to disagree, the intention of the CE mark is to show 
 compliance with European Directives (those applicable), it allows 
 free movement of goods across the EU borders. It's intention is 
 not to provide the consumer with information so that they can 
 make an informed purchasing decision.
 
 I would suggest that a product can be designed, manufactured and 
 sold within one European Country without having the CE mark 
 applied. It may well be within the scope of some European 
 Directive, but as long as it does not cross any National Border 
 then the CE mark is not required, so long as it meets the local 
 regulations.
 
 Why would Joe Public care if his pc printer had a CE mark as long 
 as it gives good quality prints and doesn't interfere with his TV 
 set. You're mixing customer needs with regulatory requirements.
 
 I'd say put the mark on any of the packaging you see fit, as long 
 as you can back this up with some rational. If a customs 
 inspector isn't satisfied with the markings on the shipping 
 container, they'll keep peeling the layers until they find what 
 they are after.
 
 Cheers,
 
 Colin.


__ Reply Separator _
Subject: RE: Packaging vs. Shipping Container
Author:  Non-HP-MSchmidt (mschm...@xrite.com) at HP-UnitedKingdom,mimegw6
List-Post: emc-pstc@listserv.ieee.org
Date:06/23/99 2:29 PM


Richard,
 
I agree.
Your definitions are very rational. 
 
Regards,
 
Mark Schmidt
mschm...@xrite.com mailto:mschm...@xrite.com 
Phone:  (616) 257-2469
X-Rite Incorporated
3100 44th Street, S. W. 
Grandville, Michigan 49418
USA
Website -  www.x-rite.com http://www.x-rite.com  
 
 
-Original Message-
From:   WOODS, RICHARD [SMTP:wo...@sensormatic.com] 
Sent:   Wednesday, June 23, 1999 8:49 AM
To: 'emc-pstc'; 'treg'
Subject:Packaging vs. Shipping Container
 
Various EU Directives require certain information to be placed on the 
packaging of a product. However, packaging is not defined. The intent of 
the requirements appears to be to provide the consumer with information so 
that they can make an informed purchasing decision. Please put on your 
lawyer's hat and tell me if the following definitions are reasonable to 
distinguish packaging from a shipping container for compliance marking 
purposes.
 
Shipping Container: A protective container in which a product is placed for 
shipping purposes. The container is not intended for public display of the 
product such as in a retail store, nor is it intended to convey product 
information to the consumer; therefore, displayed product information may be 
limited. The product in the shipping container may or may not be enclosed in 
packaging.
Products intended to be shipped direct to the end user may not include 
packaging.
 
Packaging: A container in which the product is placed for public display 
purposes in retail shops and similar stores

RE: E M terminology . . . .

1999-06-17 Thread Bill Ellingford
Hi Treg 
Barry!  good to see you in text coming through the Ether.  You said sorry, I 
was wrong but you have a definition Earth and Magneto.  This is the same as my 
Earth and Make to Battery!
I rest my case m'lord.

I do believe Ear and Mouth are the most commonly used words but maybe not the 
correct ones.

Bill Ellingford

--
From:   Barry C. Quinlan[SMTP:bsi_little...@csi.com]
Sent:   16 June 1999 19:23
To: t...@world.std.com
Subject:Re: E  M terminology . . . . 

The definition in the 15th Edition of Newton's Telecom Dictionary is:

Ear  Mouth
Earth and Magneto
rEceive and transMit

So it appears everyone is right except Bill. Sorry Bill.


Best Regards

Barry C. Quinlan
Manager
BSI Product Services (USA)
Tel: 978 486 4666 x270
Fax: 978 486 8600
- Original Message -
From: Bill Ellingford bill.ellingf...@motionmedia.co.uk
To: t...@world.std.com
Sent: Wednesday, June 16, 1999 1:32 PM
Subject: RE: E  M terminology . . . .


Hi Treg

In the back of my mind (probably where it should remain) something tells me
that E  M referred to the function i.e Earth Lead and Make Lead.  Make
being pulsed battery (positive or negative) and earth being the detector
circuit to ground.

I can confirm that it is used for PW CCT pulse signalling against
international signalling sytems SSDC5 and SSDC10.

Feasible?  Bill Ellingford
Motion Media Technology

--
From: kkee...@host.igs.net[SMTP:kkee...@host.igs.net]
Sent: 16 June 1999 11:57
To: t...@world.std.com
Subject: RE: E  M terminology . . . .


Your Wrong!

application/ms-tnef