Re: [PSES] [EXTERNAL] RE: Clearances >30 kHz

2023-07-26 Thread Boštjan Glavič
Ryan

Table 10 is fof frequencies < 30kHz. Temporary overvoltage is at mains 
frequency. Therefore in most cases your input for table 10 is TOV.

Best regards
Boštjan

Poslano iz Outlook za Android


Od: Ryan Jazz 
Poslano: sreda, julij 26, 2023 10:43:29 pop.
Za: Boštjan Glavič 
Kp: EMC-PSTC@LISTSERV.IEEE.ORG 
Zadeva: RE: [EXTERNAL] RE: Clearances >30 kHz

Hello Boštjan,
Appreciate your reply.
I have since learned that Table 10 and Table 11 are for the Working Voltages.
Table 14 is what you mentioned,  Withstand Voltage (Transient)
Scott, Thank you for your reply also.
Sincerely,
Ryan Jazz

Ryan Jayasinghe
Regulatory Compliance Engineer
rjayasin...@line6.com

"After silence, that which best expresses the inexpressible, is music" - Aldous 
Huxley

LINE6
26580 Agoura Road
Calabasas CA 91302
818.575.3711
line6.com
ampeg.com

From: Boštjan Glavič 
Sent: Tuesday, July 25, 2023 10:13 PM
To: Ryan Jazz ; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [EXTERNAL] RE: Clearances >30 kHz

Dear Ryan,

Table 10 – input is your temporary overvoltage. Normally 2000Vpk for mains 
voltages up to 250Vac
Table 11 – input is your working voltage
Table 14 – input is your transient voltage – defined by OVC (for OVC II 
2500Vpk).
So table 11 brings you very low value and normally table 10 and 15 are 
dominating.

I hope this helps.

Best regards,
Boštjan



From: Ryan Jazz 
mailto:rjayasin...@yamahaguitargroup.com>>
Sent: Wednesday, July 26, 2023 12:39 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Clearances >30 kHz

CAUTION: This email originated from outside of our organisation. Do not click 
links or open attachments unless you recognise the sender and know the content 
is safe.

Dear Members,
Hope you can help me understand the requirement for the clearance needed 
between the bottom PCB of power supply to metal chassis.
Looking up UL 62368-1 Third Edition, and using the ‘Voltage up to an including 
peak’ of 2000 V for overvoltage category II Table 10 for <30 kHz.
I see the clearance is 1,27 mm.
Going over to Table 11 >30 kHz this clearance value jumps to 13,2 mm.
Am I doing this correctly? Or should I be using the ‘working voltage’ of the 
power supply, Primary to Earthed Dead Metal 392 Vpk, Primary to Secondary 520 
Vpk.
100-240 Vac, 100 W, 90 kHz switching frequency, AC power supply with a 2x3 inch 
footprint.
End product is, overvoltage category II, pollution degree 2, material group III.
Indoor audio music processor, Class 1.
All guidance would be appreciated.
If this 13,2 mm value is indeed correct, I may need to use an insulator under 
the power supply.
Any recommendations for a UL rated insulator type?
Thank you,
Ryan Jazz
Ryan Jayasinghe
Regulatory Compliance Engineer
rjayasin...@line6.com

"After silence, that which best expresses the inexpressible, is music" - Aldous 
Huxley

LINE6
26580 Agoura Road
Calabasas CA 91302
818.575.3711
line6.com
ampeg.com



This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to All 
emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website: https://ewh.ieee.org/soc/pses/
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org



To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1


-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  
_
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1


Re: [PSES] [EXTERNAL] RE: Clearances >30 kHz

2023-07-26 Thread Ryan Jazz
Hello Boštjan,
Appreciate your reply.
I have since learned that Table 10 and Table 11 are for the Working Voltages.
Table 14 is what you mentioned,  Withstand Voltage (Transient)
Scott, Thank you for your reply also.
Sincerely,
Ryan Jazz

Ryan Jayasinghe
Regulatory Compliance Engineer
rjayasin...@line6.com

"After silence, that which best expresses the inexpressible, is music" - Aldous 
Huxley

LINE6
26580 Agoura Road
Calabasas CA 91302
818.575.3711
line6.com
ampeg.com

From: Boštjan Glavič 
Sent: Tuesday, July 25, 2023 10:13 PM
To: Ryan Jazz ; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [EXTERNAL] RE: Clearances >30 kHz

Dear Ryan,

Table 10 - input is your temporary overvoltage. Normally 2000Vpk for mains 
voltages up to 250Vac
Table 11 - input is your working voltage
Table 14 - input is your transient voltage - defined by OVC (for OVC II 
2500Vpk).
So table 11 brings you very low value and normally table 10 and 15 are 
dominating.

I hope this helps.

Best regards,
Boštjan



From: Ryan Jazz 
mailto:rjayasin...@yamahaguitargroup.com>>
Sent: Wednesday, July 26, 2023 12:39 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Clearances >30 kHz

CAUTION: This email originated from outside of our organisation. Do not click 
links or open attachments unless you recognise the sender and know the content 
is safe.

Dear Members,
Hope you can help me understand the requirement for the clearance needed 
between the bottom PCB of power supply to metal chassis.
Looking up UL 62368-1 Third Edition, and using the 'Voltage up to an including 
peak' of 2000 V for overvoltage category II Table 10 for <30 kHz.
I see the clearance is 1,27 mm.
Going over to Table 11 >30 kHz this clearance value jumps to 13,2 mm.
Am I doing this correctly? Or should I be using the 'working voltage' of the 
power supply, Primary to Earthed Dead Metal 392 Vpk, Primary to Secondary 520 
Vpk.
100-240 Vac, 100 W, 90 kHz switching frequency, AC power supply with a 2x3 inch 
footprint.
End product is, overvoltage category II, pollution degree 2, material group III.
Indoor audio music processor, Class 1.
All guidance would be appreciated.
If this 13,2 mm value is indeed correct, I may need to use an insulator under 
the power supply.
Any recommendations for a UL rated insulator type?
Thank you,
Ryan Jazz
Ryan Jayasinghe
Regulatory Compliance Engineer
rjayasin...@line6.com

"After silence, that which best expresses the inexpressible, is music" - Aldous 
Huxley

LINE6
26580 Agoura Road
Calabasas CA 91302
818.575.3711
line6.com
ampeg.com



This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to All 
emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website: https://ewh.ieee.org/soc/pses/
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org



To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 


All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  
_
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1