Thanks to all who replied publicly and privately to my question on ESD to metal 
surfaces with non-paint coatings.  It seems everyone agrees to treat them the 
same as paint.

As Brian points out, the Standard I'm looking at (BS EN 61000-4-2:2009) is a 
bit fuzzy using the term "paint" then switching to "coating".

So now I'm just left with a rhetorical question.  Has anyone heard such a 
declaration from a manufacturer?  In my decades of EMC work, I have not.

Thanks again,
Bob


From: Brian Kunde <bkundew...@gmail.com>
Sent: Tuesday, September 19, 2023 9:45 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [EXTERNAL] Re: [PSES] ESD testing - Contact Mode to plated metal 
surfaces?

The standard I have says this in section 8. 3. 2: "In the case of painted 
surfaces covering a conducting substrate, the following procedure shall be 
adopted: If the coating is not declared to be an insulating coating by the 
equipment manufacturer,

The standard I have says this in section 8.3.2:

"In the case of painted surfaces covering a conducting substrate, the following 
procedure shall be adopted:

If the coating is not declared to be an insulating coating by the equipment 
manufacturer, then the pointed tip of the generator shall penetrate the coating 
so as to make contact with the conducting substrate. Coating declared as 
insulating by the manufacturer shall only be submitted to the air discharge. 
The contact discharge test shall not be applied to such surfaces.

In the case of air discharges, the ESD generator shall approach the EUT as fast 
as possible until contact between the electrode and the EUT is made (without 
causing mechanical damage). After each discharge, the ESD generator (discharge 
electrode) shall be removed from the EUT. The generator is then retriggered for 
a new single discharge. This procedure shall be repeated until the discharges 
are completed. In the case of an air discharge test, the discharge switch, 
which is used for contact discharge, shall be closed."

The standard probably should not call out "painted" but worded in a way that 
would include all types of coatings.  Maybe the newer versions of the standard 
clarifies this.

The Other Brian

On Mon, Sep 18, 2023 at 9:13 PM Brent DeWitt 
<bdew...@ix.netcom.com<mailto:bdew...@ix.netcom.com>> wrote:
I believe the language said something like: "the contact discharge tip shall be 
applied to any coating not expressly declared as insulative"

Could be wrong though.

Brent DeWitt
Milford, MA
On 9/18/2023 7:39 PM, Ken Wyatt wrote:
Always had the impression the sharp end of the CD tip was designed to punch 
through any coated metal.
Kenneth Wyatt
Woodland Park, CO
Sent from my iPhone.


On Sep 18, 2023, at 09:48, Sykes, Bob 
<bob.sy...@gilbarco.com><mailto:bob.sy...@gilbarco.com> wrote:

Worldly Experts,

I have a question regarding the suitability of contact mode ESD testing to 
plated metal surfaces.  I understand the wording in IEC 61000-4-2 regarding 
painted and bare metal.  Does the same logic used for painted metal surfaces 
also apply to other coatings (anodized, plated, passivated etc.)?  These are 
not addressed in the Standard.

adTHANKSvance,
Bob Sykes


________________________________

Please be advised that this email may contain confidential information. If you 
are not the intended recipient, please notify us by email by replying to the 
sender and delete this message.

________________________________

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to All 
emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/<https://urldefense.com/v3/__https:/www.mail-archive.com/emc-pstc@listserv.ieee.org/__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteSeZaPBdA$>

Website: https://ewh.ieee.org/soc/pses/ 
<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteQZOpwujw$>
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/list.html__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteTp34Drcw$>
List rules: 
https://ewh.ieee.org/soc/pses/listrules.html<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/listrules.html__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteRCGbpUvA$>

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net<mailto:msherma...@comcast.net>
Rick Linford at: linf...@ieee.org<mailto:linf...@ieee.org>

For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org<mailto:j.bac...@ieee.org>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://urldefense.com/v3/__https:/listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteSyjErcwA$>

________________________________

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to All 
emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/<https://urldefense.com/v3/__https:/www.mail-archive.com/emc-pstc@listserv.ieee.org/__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteSeZaPBdA$>

Website: https://ewh.ieee.org/soc/pses/ 
<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteQZOpwujw$>
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/list.html__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteTp34Drcw$>
List rules: 
https://ewh.ieee.org/soc/pses/listrules.html<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/listrules.html__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteRCGbpUvA$>

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net<mailto:msherma...@comcast.net>
Rick Linford at: linf...@ieee.org<mailto:linf...@ieee.org>

For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org<mailto:j.bac...@ieee.org>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://urldefense.com/v3/__https:/listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteSyjErcwA$>

________________________________

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to All 
emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/<https://urldefense.com/v3/__https:/www.mail-archive.com/emc-pstc@listserv.ieee.org/__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteSeZaPBdA$>

Website: https://ewh.ieee.org/soc/pses/ 
<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteQZOpwujw$>
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/list.html__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteTp34Drcw$>
List rules: 
https://ewh.ieee.org/soc/pses/listrules.html<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/listrules.html__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteRCGbpUvA$>

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net<mailto:msherma...@comcast.net>
Rick Linford at: linf...@ieee.org<mailto:linf...@ieee.org>

For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org<mailto:j.bac...@ieee.org>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://urldefense.com/v3/__https:/listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteSyjErcwA$>

________________________________

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to All 
emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/<https://urldefense.com/v3/__https:/www.mail-archive.com/emc-pstc@listserv.ieee.org/__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteSeZaPBdA$>

Website: https://ewh.ieee.org/soc/pses/ 
<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteQZOpwujw$>
Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/list.html__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteTp34Drcw$>
List rules: 
https://ewh.ieee.org/soc/pses/listrules.html<https://urldefense.com/v3/__https:/ewh.ieee.org/soc/pses/listrules.html__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteRCGbpUvA$>

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net<mailto:msherma...@comcast.net>
Rick Linford at: linf...@ieee.org<mailto:linf...@ieee.org>

For policy questions, send mail to:
Jim Bacher at: j.bac...@ieee.org<mailto:j.bac...@ieee.org>

________________________________

To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://urldefense.com/v3/__https:/listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1__;!!IJTm5Pv7pnzb!O0RzmI-5FnBA4YlbU-yYDqxEB35OLspWv9sJcph2dGRZ8vpUVCY3HTWF5F_hoeBnNO0Z-Xgml8IuteSyjErcwA$>

________________________________

Please be advised that this email may contain confidential information. If you 
are not the intended recipient, please notify us by email by replying to the 
sender and delete this message.

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/emc-pstc@listserv.ieee.org/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: msherma...@comcast.net
Rick Linford at: linf...@ieee.org

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1