Re: [PSES] OSM decision
Mr P - Correct about the change of scoped voltage. UL62109-1 scopes 1500Vdc (not listed by ANSI or SCC yet), and NEC article 690 will be also updated. FWIW, took customer's box back to the ranch and did several fault conditions and some surge stuff(C62.41 and 4-5). What a mess. They never listen. What a maroon. Brian -Original Message- From: Pete Perkins [mailto:0061f3f32d0c-dmarc-requ...@ieee.org] Sent: Monday, January 26, 2015 7:28 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] FW: [PSES] OSM decision Rich, et al, I wouldn't be so quick to claim that dc systems will not have transient voltages on them. I recently worked on a certification project that included solar panels feeding power back into the line to make the overall project 'greener'. In commercial systems solar panels are ganged together to get the overall voltage up to 600Vdc with 10's of Amps per ganged collexion. 10 or more of these are combined to drive a SMPS inverter which outputs AC fed into the power system. Atmospherics can disrupt either the dc or the AC side so protection of the SMPS inverter on each side should be considered. More nightmares for the designers and field folks who need a clean design that is robust and long-lived giving continued protection. Some new work is being done with SPDs. See IEEE Xactions on EMC v56n6 Dec 2014: HE Dy, SPD Protection Distance to Household Appliances Connected in Parallel. There might be other info that could be pulled from the bibliography for this paper. Finally, for your fun and enjoyment, the US NEC is being updated to allow the Low Voltage DC limits to go to 1000V soon and 1500Vdc later to accommodate larger solar panel installations. :) br, Pete Peter E Perkins, PE Principal Product Safety Engineer PO Box 23427 Tigard, ORe 97281-3427 503/452-1201 fone/fax p.perk...@ieee.org -Original Message- From: Richard Nute [mailto:ri...@ieee.org] Sent: Monday, January 26, 2015 1:52 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] OSM decision What is the purpose of the MOV in this situation? What is the MOV Joule dissipation rating (can it dissipate the expected overvoltage)? Is the MOV protected by a fuse? (An equipment d.c. bus is not likely to have high-voltage transients.) -Original Message- From: Brian Oconnell [mailto:oconne...@tamuracorp.com] Sent: Monday, January 26, 2015 11:56 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] OSM decision Was reviewing customer's construction where a 475V MOV was across the (floated) 420Vdc bus. Said this was bad idea, and they referred me to OSM/EE decision sheet 09/01 for EN60950-1:2006; which says ok to do whatever you want with a VDR on primary side that is not connected to mains. Can think of more than one SFC that would result in this combination of circuit configuration and component ratings making a mess. Any record of TC108 having affirmed this? Thanks, Brian - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
[PSES] OSM decision
Was reviewing customer's construction where a 475V MOV was across the (floated) 420Vdc bus. Said this was bad idea, and they referred me to OSM/EE decision sheet 09/01 for EN60950-1:2006; which says ok to do whatever you want with a VDR on primary side that is not connected to mains. Can think of more than one SFC that would result in this combination of circuit configuration and component ratings making a mess. Any record of TC108 having affirmed this? Thanks, Brian - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] OSM decision
Hi Brian: (An equipment d.c. bus is not likely to have high-voltage transients.) AC mains input to this equipment, so must assume the box will see at least 2500V The transient overvoltage is not likely to appear on the d.c. Conduct a test by applying the 1.2x50 2500-volts peak pulse to the a.c. mains. If you don't have the pulse generator, use a 2500 volts peak hi-pot tester. This will prove whether you need the MOV. I'll bet you can take the MOV out. Best regards, Rich - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
[PSES] FW: [PSES] OSM decision
Rich, et al, I wouldn't be so quick to claim that dc systems will not have transient voltages on them. I recently worked on a certification project that included solar panels feeding power back into the line to make the overall project 'greener'. In commercial systems solar panels are ganged together to get the overall voltage up to 600Vdc with 10's of Amps per ganged collexion. 10 or more of these are combined to drive a SMPS inverter which outputs AC fed into the power system. Atmospherics can disrupt either the dc or the AC side so protection of the SMPS inverter on each side should be considered. More nightmares for the designers and field folks who need a clean design that is robust and long-lived giving continued protection. Some new work is being done with SPDs. See IEEE Xactions on EMC v56n6 Dec 2014: HE Dy, SPD Protection Distance to Household Appliances Connected in Parallel. There might be other info that could be pulled from the bibliography for this paper. Finally, for your fun and enjoyment, the US NEC is being updated to allow the Low Voltage DC limits to go to 1000V soon and 1500Vdc later to accommodate larger solar panel installations. :) br, Pete Peter E Perkins, PE Principal Product Safety Engineer PO Box 23427 Tigard, ORe 97281-3427 503/452-1201 fone/fax p.perk...@ieee.org -Original Message- From: Richard Nute [mailto:ri...@ieee.org] Sent: Monday, January 26, 2015 1:52 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] OSM decision What is the purpose of the MOV in this situation? What is the MOV Joule dissipation rating (can it dissipate the expected overvoltage)? Is the MOV protected by a fuse? (An equipment d.c. bus is not likely to have high-voltage transients.) -Original Message- From: Brian Oconnell [mailto:oconne...@tamuracorp.com] Sent: Monday, January 26, 2015 11:56 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] OSM decision Was reviewing customer's construction where a 475V MOV was across the (floated) 420Vdc bus. Said this was bad idea, and they referred me to OSM/EE decision sheet 09/01 for EN60950-1:2006; which says ok to do whatever you want with a VDR on primary side that is not connected to mains. Can think of more than one SFC that would result in this combination of circuit configuration and component ratings making a mess. Any record of TC108 having affirmed this? Thanks, Brian - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] OSM decision
Dear Brian, I am afraid they are right. There are no requirements for VDR located after bridge rectifier - same as for X capacitors. Best regards, Bostjan -Original Message- From: Brian Oconnell [mailto:oconne...@tamuracorp.com] Sent: Monday, January 26, 2015 8:56 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] OSM decision Was reviewing customer's construction where a 475V MOV was across the (floated) 420Vdc bus. Said this was bad idea, and they referred me to OSM/EE decision sheet 09/01 for EN60950-1:2006; which says ok to do whatever you want with a VDR on primary side that is not connected to mains. Can think of more than one SFC that would result in this combination of circuit configuration and component ratings making a mess. Any record of TC108 having affirmed this? Thanks, Brian - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] OSM decision
Hi Rich and the group, Even DC power internal busses in equipment are likely to have 1000 Volt transients if hot plug of power supplies and/or loads are allowed. Outside transients are not necessary to have this happen. I have personally observed these EFT events. The effect on the power supply control circuits (sources and loads) is a lot like ESD causing over voltage/over current shutdowns and potentially other problems. The protection circuits should have limited frequency response to ward off problems of false trips. Their response time should be as long as can be tolerated but no faster than one microsecond. Doug University of Oxford Tutor Department for Continuing Education Oxford, Oxfordshire, United Kingdom -- ___ _Doug Smith \ / ) P.O. Box 60941 = Boulder City, NV 89006-0941 _ / \ / \ _TEL/FAX: 702-570-6108/570-6013 / /\ \ ] / /\ \ Mobile: 408-858-4528 | q-( ) | o | Email: d...@dsmith.org \ _ /]\ _ / Web: http://www.dsmith.org -- On 1/26/15 6:11 PM, Richard Nute wrote: Hi Brian: (An equipment d.c. bus is not likely to have high-voltage transients.) AC mains input to this equipment, so must assume the box will see at least 2500V The transient overvoltage is not likely to appear on the d.c. Conduct a test by applying the 1.2x50 2500-volts peak pulse to the a.c. mains. If you dont have the pulse generator, use a 2500 volts peak hi-pot tester. This will prove whether you need the MOV. Ill bet you can take the MOV out. Best regards, Rich - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher j.bac...@ieee.org David Heald dhe...@gmail.com - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher j.bac...@ieee.org David Heald dhe...@gmail.com
Re: [PSES] OSM decision
Greetings Mr. Nute, See below. Brian -Original Message- From: Richard Nute [mailto:ri...@ieee.org] Sent: Monday, January 26, 2015 1:52 PM To: Brian Oconnell; EMC-PSTC@LISTSERV.IEEE.ORG Subject: RE: [PSES] OSM decision What is the purpose of the MOV in this situation? As SPD, and to push me one step closer to madness What is the MOV Joule dissipation rating (can it dissipate the expected overvoltage)? NO - at least not by my calculations - and the MOV will, during some line/load conditions, probably start conducting a few mA during 'normal' operations Is the MOV protected by a fuse? Fuse on line input. And doubt that it would pass the G.8 stuff in 63268-1(but submittal is 60950-1) (An equipment d.c. bus is not likely to have high-voltage transients.) AC mains input to this equipment, so must assume the box will see at least 2500V -Original Message- From: Brian Oconnell [mailto:oconne...@tamuracorp.com] Sent: Monday, January 26, 2015 11:56 AM To: EMC-PSTC@LISTSERV.IEEE.ORGmailto:EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] OSM decision Was reviewing customer's construction where a 475V MOV was across the (floated) 420Vdc bus. Said this was bad idea, and they referred me to OSM/EE decision sheet 09/01 for EN60950-1:2006; which says ok to do whatever you want with a VDR on primary side that is not connected to mains. Can think of more than one SFC that would result in this combination of circuit configuration and component ratings making a mess. Any record of TC108 having affirmed this? Thanks, Brian - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] OSM decision
In message blupr02mb116efadd6d2fad04953cffcc1...@blupr02mb116.namprd02.prod.outlook .com, dated Mon, 26 Jan 2015, Brian Oconnell oconne...@tamuracorp.com writes: Was reviewing customer's construction where a 475V MOV was across the (floated) 420Vdc bus. Said this was bad idea, and they referred me to OSM/EE decision sheet 09/01 for EN60950-1:2006; which says ok to do whatever you want with a VDR on primary side that is not connected to mains. Can think of more than one SFC that would result in this combination of circuit configuration and component ratings making a mess. Any record of TC108 having affirmed this? I think so. This MOV subject is very difficult. Putting a VDR on a primary side that is not connected to mains is not inherently unsafe if the VDR goes open-circuit. If it explodes, *provided the product remains safe (even if badly damaged)*, the safety standard is not violated. -- OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk When I turn my back on the sun, it's to look for a rainbow John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com
Re: [PSES] OSM decision
What is the purpose of the MOV in this situation? What is the MOV Joule dissipation rating (can it dissipate the expected overvoltage)? Is the MOV protected by a fuse? (An equipment d.c. bus is not likely to have high-voltage transients.) -Original Message- From: Brian Oconnell [mailto:oconne...@tamuracorp.com] Sent: Monday, January 26, 2015 11:56 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] OSM decision Was reviewing customer's construction where a 475V MOV was across the (floated) 420Vdc bus. Said this was bad idea, and they referred me to OSM/EE decision sheet 09/01 for EN60950-1:2006; which says ok to do whatever you want with a VDR on primary side that is not connected to mains. Can think of more than one SFC that would result in this combination of circuit configuration and component ratings making a mess. Any record of TC108 having affirmed this? Thanks, Brian - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to emc-p...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas sdoug...@ieee.org Mike Cantwell mcantw...@ieee.org For policy questions, send mail to: Jim Bacher: j.bac...@ieee.org David Heald: dhe...@gmail.com