The worst case of ground potential difference that I have heard of is a case
where guy got a shock from the grounded metal reflector of his trouble light
while working outside on his car.



Turns out the pump in his neighbor's well (fed from the same transformer) had a
  short from from line to ground. The potential difference between the
  ground tied to line at the neighbor's and the ground tied to neutral at
  this guy's house caused a voltage gradient along ground between the
  properties high enough to cause a shock when enough distance was covered
  (by the cord of the trouble light).



Don Borowski

Schweitzer Engineering Labs

Pullman, WA
This e-mail may contain SEL confidential information.  The opinions expressed
are not necessarily those of SEL.  Any unauthorized disclosure, distribution or
other use is prohibited.  If you received this e-mail in error, please notify
the sender, permanently delete it, and destroy any printout.  Thank you.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Ground potential differences

2002-10-14 Thread Doug McKean

I've no publications, but I did have personal experience with the
more destructive results with ground potential differences. At another
company, I witnessed  the insulation of a coax cable melting after
being connected between equipment in a lab where I worked.  The
problem being a difference in ground potential of 15vac.  That in and
of itself wasn't the problem. The amperage capacity through ground
of the mains system was the culprit.  Circa 1983 or so.

Turned out that the building was supplied by two electrical substations
at opposite ends of the building.  And for some strange reason, the
substations each shared about half the outlets in the lab. And the potential
difference was caused by the electricians connecting to slightly different
points on the transformers for ground.

The electricians were told and were able to fix the problem.

And as far as anything in the field showing a similar problem, I have
only dealt with one such instance.  And relating the substation
transformer ground tap story fixed it for them.

Regards, Doug McKean



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


RE: Ground potential differences

2002-10-14 Thread Robert Johnson
Most earth potential differences come from load currents. Leakage
currents don't usually add up to very much. Electrical installations
should have one neutral to earth connection at the source of the system
(at the transformer or service entry). However many electrical
installations have branch panels with earth and neutral incorrectly
connected together at the panel. This means the neutral and earth paths
are parallel returns to the source. The IR drop generates potential
differences between different building areas. These stray currents can
amount to tens or hundreds of amps in big installations. Occasionally
these same currents come from miswired plugs or receptacles with neutral
and earth switched.  
To look for stray currents, put a clamp on ammeter around all mains
conductors together (phases and neutral). Often they will show up even
with the meter around the conduit. The resulting voltage differences in
grounds typically amount to 2 to 5 volts. It depends on load currents,
neutral resistance, ground resistance, current paths, etc. Transients
and noise of course include all those present on the load currents.
In residential applications where several services, each with their own
ground, are fed from a single transformer (also with its neutral
grounded). Several amps typically flow in the parallel earth connections
between houses, but this is irrelevant. The important thing to achieve
is an equipotential earth environment around the particular house
involved.

Bob Johnson
ITE Safety
 

-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org] On Behalf Of John Woodgate
Sent: Saturday, October 12, 2002 12:53 PM
To: emc-p...@majordomo.ieee.org
Subject: Re: Ground potential differences


I read in !emc-pstc that Bailey, Jeff jbai...@mysst.com wrote (in
B115DFA26896D511BAB600105AA3493275EA3F@SSTMAIL) about 'Ground
potential differences' on Fri, 11 Oct 2002:

 I am interested
to know what the actual magnitude of ground differences may be from one
end
of a plant to another as well as where the numbers come from.  

It depends on what sort of equipment is present. Some things have very
high leakage current, putting a lot of amps in total into ground
conductors. Then, in old plants, there may be bad ground wiring that
doesn't show up as a fault.

Have they
been calculated or actually measured? 

Both. Usually after the problem has been discovered by chance. I've
measured 9 V over a distance of 20 m, but there are reports of much
higher voltages.

If shields are connected directly to
chassis at each node of a network will there be an effect of equalizing
the
ground levels through the network or will enough current flow to melt
the
shield of the cable?

Both are possible.
-- 
Regards, John Woodgate, OOO - Own Opinions Only.
http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go
to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list
attachment: Robert Johnson.vcf

Re: Ground potential differences

2002-10-13 Thread John Barnes

Jeff,
I used to develop network interfaces for printers at IBM and Lexmark. 
As I recall, the Ethernet 10BASE2, 10BASE-T, and 100BASE-Tx standards
required 1500V isolation between the network cabling and the product.
This was no problem for 10BASE-T and 100BASE-Tx, because the
transformers easily gave us this much isolation.  But we had to put
TransGuards on several 10BASE2 products because the circuitry required
both a capacitive and a weak resistive connection between shield ground
and chassis ground to work.

As part of our product qualification tests, we would hit 10BASE-T and
100BASE-Tx ports with +/-400V surges, and 10BASE2 ports with +/-800V
surges.  These could be rather noisy when the 40 joules of available
energy blasted weak components right off a prototype card...  (This was
not a test to run if you were tired or careless-- it could kill you with
one zap.)

I've never seen a document that mentioned/specified the maximum AC or DC
voltage that you could expect between the network cabling and the
product under normal conditions.  But I don't think that it is very
high, because the BNC connectors and BNC T's used for 10BASE2 have
exposed bare metal connected to the shield of the cable.  So when you
are connecting/disconnecting a 10BASE2 cable from a product, you can
have one hand on network voltage and the other hand on chassis ground,
with any leakage current going through your heart.  IEC 950 specifies a
maximum of 30 Vrms for alternating current, or 42.4 Vdc (60 Vdc for a
telecom port), for exposed metal in Safety Extra-Low Voltage (SELV)
circuits.  So I expect that normal network-to-product voltage are well
under these limits.

John Barnes KS4GL SM
dBi Corporation
http://www.dbicorporation.com/

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Ground potential differences

2002-10-12 Thread John Woodgate

I read in !emc-pstc that Bailey, Jeff jbai...@mysst.com wrote (in
B115DFA26896D511BAB600105AA3493275EA3F@SSTMAIL) about 'Ground
potential differences' on Fri, 11 Oct 2002:

 I am interested
to know what the actual magnitude of ground differences may be from one end
of a plant to another as well as where the numbers come from.  

It depends on what sort of equipment is present. Some things have very
high leakage current, putting a lot of amps in total into ground
conductors. Then, in old plants, there may be bad ground wiring that
doesn't show up as a fault.

Have they
been calculated or actually measured? 

Both. Usually after the problem has been discovered by chance. I've
measured 9 V over a distance of 20 m, but there are reports of much
higher voltages.

If shields are connected directly to
chassis at each node of a network will there be an effect of equalizing the
ground levels through the network or will enough current flow to melt the
shield of the cable?

Both are possible.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Ground potential differences

2002-10-11 Thread Bailey, Jeff

Greetings all,

I have become involved in a discussion regarding potential ground voltage
differences between opposite ends of long network lines in industrial
locations.  As I understand it these differences are the reason for some
network types floating cable shields or connecting them through snubbing
networks to chassis instead  of connecting directly.

In the past I have simply accepted this explanation however I am becoming
less comfortable with just accepting it.  Can someone provide me with or
point me to where I can obtain information on this subject?  I am interested
to know what the actual magnitude of ground differences may be from one end
of a plant to another as well as where the numbers come from.  Have they
been calculated or actually measured? If shields are connected directly to
chassis at each node of a network will there be an effect of equalizing the
ground levels through the network or will enough current flow to melt the
shield of the cable?

Thanks in advance for any replies. 

Jeff Bailey
Compliance Engineering
SST - A Division of Woodhead Canada
Phone: (519) 725 5136 ext. 363
Fax: (519) 725 1515
email: jbai...@mysst.com
Web: www.mysst.com 



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


Re: Ground potential differences....

2000-05-07 Thread Rich Nute




Hi Doug:


   Without knowing the issue, we connected two different machines 
   with a coax.  Each machine eventually connected to different 
   substations by way of differently sourced outlets.  And we 
   watched with amazement as the rubber jacket of the coax melted.  
   All with a 15V difference.  The electricians were notified 

I'll bet it wasn't the voltage, but the current through the
resistance of the coax that caused the voltage difference.

I'll bet the coax was carrying part of the neutral current.
If the neutral is grounded at more than one point, then the
protective ground conductors are in parallel with the 
neutral and will carry some of the neutral current.


Best regards,
Rich




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: Ground potential differences....

2000-05-07 Thread Ralph Cameron

Doug:

Just to enhance your observation, at RF ( i.e. broadcast frequencies
520-1800 Khz)  there is a pseudo resonant effect that places RF ground at
different places in a building , home etc. The RF ground is dependant on the
intereception of direct radiation and is related to how much wiring is
exposed and the angle of exposure.   It would make an interesting problem to
model.

In one case, a CD system on a second floor was completely disabled by RF
 common mode) and the only way to re establish a ground reference was tying
the ground lead from the CD player to the bedprings.  It may sound far
fetched, but it worked.

Sometimes plugging into a different AC outlet in the same room , cleared the
problem.

Ground potential difference can also occur when transformer insulation
becomes leaky , mainly due to age.

Cheers.

Ralph Cameron
EMC Consultant for Suppression of Consuemr Electronic Equipment
(After Sale)

- Original Message -
From: Doug dmck...@gte.net
To: emc-p...@majordomo.ieee.org
Sent: Saturday, May 06, 2000 1:18 PM
Subject: Re: Ground potential differences



 I'm going to stick my neck out here and say from two
 experiences with this topic, there's a couple of things
 to consider ...

 First, ideally, any potential difference between GROUNDS
 should be zero.  If you had asked about NEUTRALS, I'd have
 to say - unknown.  The physical connection is a function
 of the connection to the transformer by the electricians
 and imperfections in the transformer.

 Second, it's a function of what's sourcing the difference.
 I worked at a place where the outlets in one half of the
 lab were supplied by a different substation than the outlets
 at the other end of the lab.

 Without knowing the issue, we connected two different machines
 with a coax.  Each machine eventually connected to different
 substations by way of differently sourced outlets.  And we
 watched with amazement as the rubber jacket of the coax melted.
 All with a 15V difference.  The electricians were notified
 and the problem was solved but a potential difference of
 some sort was still there.  I don't think you'll ever get
 away from it.

 So, I guess what I'm saying is that you should not only
 consider the voltage difference, but the power involved.
 And that would be have to tested some other way.

  - Doug McKean

 Kelly Tsudama wrote:
 
  Hi gang!
 
  I have been asked to look into ground potential differences by one of
the teams that I support.  Can any of you provide any insight on how I can
determine the maximum potential difference between different ground circuits
within a building???  I've heard numbers ranging from 2V to 50V!!!  Even
with all the bonding requirements in the NEC, there must be some voltage
differential between grounding points???
 
  Thanks for any help you can provide.
 
  Kelly

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Jim Bacher:  jim_bac...@mail.monarch.com
  Michael Garretson:pstc_ad...@garretson.org

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: Ground potential differences....

2000-05-06 Thread Doug

I'm going to stick my neck out here and say from two 
experiences with this topic, there's a couple of things 
to consider ... 

First, ideally, any potential difference between GROUNDS 
should be zero.  If you had asked about NEUTRALS, I'd have 
to say - unknown.  The physical connection is a function 
of the connection to the transformer by the electricians 
and imperfections in the transformer. 

Second, it's a function of what's sourcing the difference. 
I worked at a place where the outlets in one half of the 
lab were supplied by a different substation than the outlets 
at the other end of the lab.  

Without knowing the issue, we connected two different machines 
with a coax.  Each machine eventually connected to different 
substations by way of differently sourced outlets.  And we 
watched with amazement as the rubber jacket of the coax melted.  
All with a 15V difference.  The electricians were notified 
and the problem was solved but a potential difference of 
some sort was still there.  I don't think you'll ever get 
away from it. 

So, I guess what I'm saying is that you should not only 
consider the voltage difference, but the power involved. 
And that would be have to tested some other way. 

 - Doug McKean 

Kelly Tsudama wrote:
 
 Hi gang!
 
 I have been asked to look into ground potential differences by one of the 
 teams that I support.  Can any of you provide any insight on how I can 
 determine the maximum potential difference between different ground circuits 
 within a building???  I've heard numbers ranging from 2V to 50V!!!  Even with 
 all the bonding requirements in the NEC, there must be some voltage 
 differential between grounding points???
 
 Thanks for any help you can provide.
 
 Kelly

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org



Re: Ground potential differences....

2000-05-04 Thread Rich Nute




Hi Kelly:


First, I presume you are considering the TN power
distribution system.  The answers to your question
are dependent upon the type of power distribution
system, whether TN, TT, or IT.  My response does
not apply to the TT and IT systems.

The first question that must be asked in dealing 
with ground potential differences is:  What is 
the reference?  I will assume it is the body of
the earth, a non-current-carrying earth rod.

The second question that must be asked is:  What 
is the source of current that causes the voltage 
drop across the resistance (due to the resistance 
of the wire in question)?

The potential difference between different PE 
conductors arises when the neutral has two or more
earth connections.  This occurs when the same 
service has two or more service entrances, 
where each service entrance is required by the NEC
to have the neutral connected to earth.  These 
multiple earth connections allow the earth to 
conduct part of the neutral current (because the 
two or more connections make the earth a parallel 
path to the neutral).  Kirchoff's Laws.  (I'm too 
lazy to draw an ASCII schematic diagram to show 
the circuit.)

The potential difference between two PE conductors 
cannot be pre-determined because it is a function 
of the neutral current, the earth resistance 
between the two or more ground rods, and the 
number of ground rods.  

The problem of connecting equipment signal grounds
of two different service entrances means that some
of the neutral current will flow in the ground of
the signal leads.  Often, this current will 
corrupt the signal or, worse, cause an open in the
ground side of the signal lead.

When the neutral has two or more grounding points,
then there will ALWAYS be a potential difference
between PE wires (grounds) of the two service 
entrances.

The PE wire (ground) is at earth potential only 
when the neutral is grounded at a single point.


Good luck, and best regards,
Rich




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Jim Bacher:  jim_bac...@mail.monarch.com
 Michael Garretson:pstc_ad...@garretson.org

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org