RE: Surge Suppressors on a UPS

2003-06-03 Thread Price, Ed

From: Price, Ed 
Sent: Monday, June 02, 2003 8:19 AM
To: 'EMC-PSTC List'
Subject: Surge Suppressors on a UPS



Hi Group! 


Last Friday, I got ambushed in a meeting. I hate it when that happens! 

A question was asked about whether it's OK to put a surge suppressor on the
output of a UPS that is supplying power to some expensive equipment. I opined
that I didn't think it should be necessary, but that it also shouldn't hurt
anything either. So then somebody asks me why all the UPS manufacturer's sites
say not to use a surge suppressor. I expertly reply that gosh, I don't know,
but I'll take a look.

The next question nails me again. Are there any standards for UPS output
power quality? Uh, well, I'll look into that too.

Now, the market is light industrial, USA, but are there any applicable EN
standards also? 

Just for some background, here's a typical entry from Tripp-Lite's FAQ list
for UPS's (not to pick on Tripp-Lite; they just said it most succinctly of
several sites I looked at):

http://www.tripplite.com/support/faq/tech_ups.cfm 
Can I plug a surge suppressor or extension cord into my UPS?
No. Using an extension cord will void your equipment coverage warranty, as all
equipment must be plugged directly into the UPS. Tripp Lite does not recommend
plugging a surge protector into a battery backup outlet of a UPS either as
this can overload it. Also, when some UPS systems switch to battery power they
will output a waveform that a surge suppressor may see as a surge and
short-circuit the UPS. Again, this setup will void the equipment coverage
warranty.

Now this is getting to be a big can of worms! What do they mean by some UPS?
Is there one kind that does, and another kind that doesn't; and how do you
know which is which? And if some UPS will create a voltage transient (is that
what they mean?) sufficient to trigger a surge suppressor, then why is it OK
to let the UPS apply that transient to my protected equipment? All this talk
about uninterrupted power isn't worth anything if the UPS kills my equipment
when it switches to battery power mode.

And who's fault is this? I mean, a surge suppressor is pretty dumb; it just
sits there waiting for the voltage to go over a certain level and then it
conducts. What's this about the surge suppressor may see something as a
surge? That's saying the surge suppressor could mis-interpret the waveform it
sees. If the surge suppressor is conducting, then I think the UPS has just
done something very naughty.

I also don't understand the prohibition of an extension cord. Maybe this is a
legal issue, as I can't see any valid safety or regulation issues here. We
regularly put a UPS in the bottom of a rack system, and then wire a stripline
outlet set for the height of the rack. Isn't that the electrical equivalent of
an extension cord? What am I missing?

Thanks in advance! 

Ed  

 

I'm replying to my own post because, so far, my question has not really been
answered.
 
It HAS generated a really large volume of private emails expressing concern
about things like what happens when you use a UPS to power equipment with
built-in surge suppression. Or questions about just what are these switching
event waveforms that a surge suppressor might want to suppress, and why
should they be allowed to be applied to equipment without surge suppressors
(equipment designed with the assumption that the UPS is protecting it from the
public mains).
 
It looks like racking and stacking a UPS, with a power distribution strip (the
moral equivalent of an extension cord?) feeding a group of discrete
electronics boxes (most of which have built-in filters and suppressors) is
quite common. Yet UPS manufacturers seem to be saying that this bad practice
and will even void the UPS warranty. 
 
So far, all comments have been from USERS of a UPS. I would like to hear from
the other side, the UPS designers. (Privately if you must, but I would like to
be able to later post unattributed answers.)
 
Thanks again!
 
Ed

Ed Price 
ed.pr...@cubic.com WB6WSN 
NARTE Certified EMC Engineer  Technician 
Electromagnetic Compatibility Lab 
Cubic Defense Systems 
San Diego, CA  USA 
858-505-2780  (Voice) 
858-505-1583  (Fax) 
Military  Avionics EMC Is Our Specialty 

 




Re: Surge Suppressors on a UPS

2003-06-02 Thread don_borow...@selinc.com








David Heald hea...@symbol.com wrote on 06/02/2003 11:51:50 AM:

 Most UPS's use a stepped approximation of a sine wave when in battery
 mode.  While most switching supplies don't care (and are the intended
 loads for these UPS's), surge suppressors can cause real issues - It has
 something to do with capacitive overload of the output circuits.

If the capacitance of MOVs is a problem, then the capacitance of the X caps
and Y caps found in most power supplies would be an even bigger problem.

Don Borowski
Schweitzer Engineering Labs
Pullman, WA



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Surge Suppressors on a UPS

2003-06-02 Thread Robert Johnson
This is a multi-part message in MIME format.
So much for extension cords. I assume the UPS manufacturer claims his
product is unsuitable for use with all computer products containing surge
suppressors.

Bob Johnson
ITE Safety
 


Title: RE: Surge Suppressors on a UPS






So much for extension cords. I assume the UPS manufacturer claims his

product is unsuitable for use with all computer products containing surge

suppressors.


Bob Johnson

ITE Safety






attachment: Robert_Johnson.vcf


Re: Surge Suppressors on a UPS

2003-06-02 Thread Barry Rowland

Dear EMC-PSTC colleagues;

I mentioned off-list to Ed Price that almost all of the UPS from Tripplite 
are in fact back up rather than uninterruptible; they perform a switch 
from conditioned line power to inverter power in the event of an AC main 
failure. This means that they may produce unknown phase/voltage 
transitions at the switch point, and could cause some big trouble if they 
are driving inductive loads or inductive/capacitive suppressors.

If the inverters have a sufficiently non-sine output waveform, they could 
experience significant load effects from suppressors or line conditioners.
  I think they would be OK with passive MOV suppressors, but harmonics 
and spike voltages from inductive loads may cause more current flow than 
normal in the MOV's.

They may also not be FCC EMC approved when the load is plugged in to an 
extension cord, which might be considered a rather large antenna!

Barry Rowland
Vancouver BC



On Monday, June 2, 2003, at 01:45 PM, Cortland Richmond wrote:


 I don't believe there are any power quality requirements imposed on
 inverters except those specified by buyers (in the USA, anyway). You can
 still buy square-wave inverters, after all, and the modified sine wave
 could be called Chock Fulla Harmonic power. Harmful interference is a
 limitation, but not one I'd expect manufacturers to be eager to fix,
 except, perhaps, to refund the purchase price. (Who's fixing the zillion
 SP's plugged into our toys?)

 And that warranty opens a whole _barrel_ of worms. Does user equipment 
 with
 an integral surge suppressor void the warranty? The consumer doesn't know
 it's there, either. I'd imagine state attorneys general would have things
 to say about implied warranty of serviceability, if this came to their
 attention in a sufficiently egregious way. Passengers would sure hesitate
 to get on a liner whose lifeboats were described so unconfidently.

 As for plugging all equipment directly onto the inverter, that's
 unrealistic. I install an inverter in or on the battery compartment, in
 accordance with manufacturer recommendations, to minimize DC voltage drop.
 The inverter is connected to an AC distribution panel (which includes 
 surge
 suppressors and filters). Then equipment I want to run, analyzer,
 receivers, signal generators, whatever., plugs into that. An IEC line cord
 won't even _reach_ the battery compartment where the inverter is 
 installed.


 And a UPS that generates transients enough to fire suppressors, transients
 from which users ARE FORBIDDEN TO PROTECT EQUIPMENT, seems to me one to
 avoid. Could be, such warranties will end up costing vendors more than
 they'd expected.

 Then too, a good corporate counsel would point to the hundreds of
 warranties honored in spite of extension cords and surge suppressors, and
 convince a trial judge that state implied warranty, and vendor's existing
 warranty performance, had voided those restrictions historically, and
 presently.

 Cortland

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   emc_p...@symbol.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 Archive is being moved, we will announce when it is back on-line.
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Surge Suppressors on a UPS

2003-06-02 Thread Fred Townsend



Chris Maxwell wrote:

 Fred,

 Maybe you're right.  Do UPSs protect against lightning surge?

Your question resolves into two issues: 1) Marketing Hype  2) Reality

1) I have seen some marketing hype that says their UPS will do everything to
protect your system and wash the windows while it is at it.  I think we know
BS when we read it.

2) The reality is lightning is called an Act of God for good reason.  Many
of the things that determine whether you are protected from a lightning strike
depend on circumstances beyond your control like how far are you from the
strike, how far are you from the mains, and how conductive is the
ground you walk on.

I think one of the better UPSs out there recognizes no one can guarantee
protection from Act of God but they do offer a free insurance policy to
replace your equipment if it fails due to a lightning strike when connected to
their UPS.  Now that's putting your money where your mouth is.

Fred Townsend

 I know that they protect against low frequency, low magnitude voltage dips
and surges.  However, I'm unsure of their ability to protect against lightning
surge.

 If the UPS is specified by its manufacturer to protect against lightning
surge; then my question is moot.  Even so, I would still wonder, does the UPS
guarantee that the UPS and the equipment attached to it would survive the
surge?  Or does the UPS sacrifice itself in order to protect its load?

 If there is any question, I would seriously consider putting the surge
protector in front of the UPS and protect the whole system.

 We must also consider the power availability angle.

 If the surge protector is in front of the UPS; then even if the surge
protector sacrifices itself; or blows a fuse to protect the UPS from the
surge; the UPS will still power all of the equipment attached to it from its
battery.

 If the surge suppressor were after the UPS; then blowing a fuse or tripping
the surge suppressor would prevent the UPS from powering its outputs.

 Chris Maxwell | Design Engineer - Optical Division
 email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

 NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
 web www.nettest.com | tel +1 315 797 4449 |




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Surge Suppressors on a UPS

2003-06-02 Thread Cortland Richmond

Chris Maxwell wrote:

 To me, this whole thread begs the question:  Why not put the surge
supressor in front of the UPS? 

A lot of us have relied on full-time UPS's to stop transients. But the bit
about a UPS itself producing large enough ones to trigger suppressors, that
is worrisome. 

Cortland


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Surge Suppressors on a UPS

2003-06-02 Thread Chris Maxwell

Fred,

Maybe you're right.  Do UPSs protect against lightning surge?  I know that
they protect against low frequency, low magnitude voltage dips and surges. 
However, I'm unsure of their ability to protect against lightning surge.

If the UPS is specified by its manufacturer to protect against lightning
surge; then my question is moot.  Even so, I would still wonder, does the UPS
guarantee that the UPS and the equipment attached to it would survive the
surge?  Or does the UPS sacrifice itself in order to protect its load?

If there is any question, I would seriously consider putting the surge
protector in front of the UPS and protect the whole system.  

We must also consider the power availability angle.

If the surge protector is in front of the UPS; then even if the surge
protector sacrifices itself; or blows a fuse to protect the UPS from the
surge; the UPS will still power all of the equipment attached to it from its
battery.

If the surge suppressor were after the UPS; then blowing a fuse or tripping
the surge suppressor would prevent the UPS from powering its outputs.


Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 












This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Surge Suppressors on a UPS

2003-06-02 Thread Jim Eichner

Ed - You were asking about output power quality standards for UPS, and while
I don't know the current correct answer (maybe someone from a UPS company
can help us), here are 3 standards that all cover UPS performance:

1. EN50091-3
2. IEC62040-3
3. IEC 146-4

I suspect all 3 are the same document in different stages of life, or at
least have the same basis.

Hope this helps,

Jim Eichner, P.Eng. 
Compliance Engineering Manager
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.




From: David Heald [mailto:hea...@symbol.com]
Sent: Monday, June 02, 2003 11:52 AM
To: ed.pr...@cubic.com; emc-p...@majordomo.ieee.org
Subject: Re: Surge Suppressors on a UPS



Most UPS's use a stepped approximation of a sine wave when in battery
mode.  While most switching supplies don't care (and are the intended
loads for these UPS's), surge suppressors can cause real issues - It has
something to do with capacitive overload of the output circuits.  

And for the second question - there are huge variances in the output
wave quality.  The brand I am familiar with has both stepped
approximation and true sine wave output models - the sine models being
the expensive ones.  The stepped approximation models are ideal for
switching supplies, while the sine output models can handle all kinds of
loads including motors (but a quick check says that they still can't use
surge supressors - this one has me puzzled!)

The UPS EMC standard is 50091-2 (or was it 92-1?), but I'm not sure how
much help it may offer.

Best Regards,
Dave Heald

 Price, Ed ed.pr...@cubic.com 06/02/03 11:18AM 
Hi Group!


Last Friday, I got ambushed in a meeting. I hate it when that happens!

A question was asked about whether it's OK to put a surge suppressor on
the
output of a UPS that is supplying power to some expensive equipment. I
opined that I didn't think it should be necessary, but that it also
shouldn't hurt anything either. So then somebody asks me why all the
UPS
manufacturer's sites say not to use a surge suppressor. I expertly
reply
that gosh, I don't know, but I'll take a look.

The next question nails me again. Are there any standards for UPS
output
power quality? Uh, well, I'll look into that too.

Now, the market is light industrial, USA, but are there any applicable
EN
standards also?

Just for some background, here's a typical entry from Tripp-Lite's FAQ
list
for UPS's (not to pick on Tripp-Lite; they just said it most succinctly
of
several sites I looked at):

http://www.tripplite.com/support/faq/tech_ups.cfm 
Can I plug a surge suppressor or extension cord into my UPS?
No. Using an extension cord will void your equipment coverage warranty,
as
all equipment must be plugged directly into the UPS. Tripp Lite does
not
recommend plugging a surge protector into a battery backup outlet of a
UPS
either as this can overload it. Also, when some UPS systems switch to
battery power they will output a waveform that a surge suppressor may
see as
a surge and short-circuit the UPS. Again, this setup will void the
equipment
coverage warranty.

Now this is getting to be a big can of worms! What do they mean by
some
UPS? Is there one kind that does, and another kind that doesn't; and
how do
you know which is which? And if some UPS will create a voltage
transient (is
that what they mean?) sufficient to trigger a surge suppressor, then
why is
it OK to let the UPS apply that transient to my protected equipment?
All
this talk about uninterrupted power isn't worth anything if the UPS
kills my
equipment when it switches to battery power mode.

And who's fault is this? I mean, a surge suppressor is pretty dumb; it
just
sits there waiting for the voltage to go over a certain level and then
it
conducts. What's this about the surge suppressor may see something as
a
surge? That's saying the surge suppressor could mis-interpret the
waveform
it sees. If the surge suppressor is conducting, then I think the UPS
has
just done something very naughty.

I also don't understand the prohibition of an extension cord. Maybe
this is
a legal issue, as I can't see any valid safety or regulation issues
here. We
regularly put a UPS in the bottom of a rack system, and then wire a
stripline outlet set for the height of the rack. Isn't that the
electrical
equivalent of an extension cord? What am I missing?

Thanks in advance!

Ed


Ed Price
ed.pr...@cubic.com 
NARTE Certified EMC Engineer  Technician
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA  USA
858-505-2780  (Voice)
858-505-1583  (Fax)
Military  Avionics EMC Is Our

Re: Surge Suppressors on a UPS

2003-06-02 Thread Cortland Richmond

I don't believe there are any power quality requirements imposed on
inverters except those specified by buyers (in the USA, anyway). You can
still buy square-wave inverters, after all, and the modified sine wave
could be called Chock Fulla Harmonic power. Harmful interference is a
limitation, but not one I'd expect manufacturers to be eager to fix,
except, perhaps, to refund the purchase price. (Who's fixing the zillion
SP's plugged into our toys?)

And that warranty opens a whole _barrel_ of worms. Does user equipment with
an integral surge suppressor void the warranty? The consumer doesn't know
it's there, either. I'd imagine state attorneys general would have things
to say about implied warranty of serviceability, if this came to their
attention in a sufficiently egregious way. Passengers would sure hesitate
to get on a liner whose lifeboats were described so unconfidently. 

As for plugging all equipment directly onto the inverter, that's
unrealistic. I install an inverter in or on the battery compartment, in
accordance with manufacturer recommendations, to minimize DC voltage drop.
The inverter is connected to an AC distribution panel (which includes surge
suppressors and filters). Then equipment I want to run, analyzer,
receivers, signal generators, whatever., plugs into that. An IEC line cord
won't even _reach_ the battery compartment where the inverter is installed.


And a UPS that generates transients enough to fire suppressors, transients
from which users ARE FORBIDDEN TO PROTECT EQUIPMENT, seems to me one to
avoid. Could be, such warranties will end up costing vendors more than
they'd expected.

Then too, a good corporate counsel would point to the hundreds of
warranties honored in spite of extension cords and surge suppressors, and
convince a trial judge that state implied warranty, and vendor's existing
warranty performance, had voided those restrictions historically, and
presently. 

Cortland


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Surge Suppressors on a UPS

2003-06-02 Thread Fred Townsend

I disagree.  One assumes some degree of surge suppression since suppression is
touted as a UPS
feature.  Therefore your question is moot.

Fred Townsend

Chris Maxwell wrote:

 To me, this whole thread begs the question:  Why not put the surge supressor
in front of the UPS?

 Chris Maxwell | Design Engineer - Optical Division
 email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

 NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
 web www.nettest.com | tel +1 315 797 4449 |

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   emc_p...@symbol.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 Archive is being moved, we will announce when it is back on-line.
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Surge Suppressors on a UPS

2003-06-02 Thread Chris Maxwell

To me, this whole thread begs the question:  Why not put the surge supressor
in front of the UPS?

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 






This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Surge Suppressors on a UPS

2003-06-02 Thread David Heald

Most UPS's use a stepped approximation of a sine wave when in battery
mode.  While most switching supplies don't care (and are the intended
loads for these UPS's), surge suppressors can cause real issues - It has
something to do with capacitive overload of the output circuits.  

And for the second question - there are huge variances in the output
wave quality.  The brand I am familiar with has both stepped
approximation and true sine wave output models - the sine models being
the expensive ones.  The stepped approximation models are ideal for
switching supplies, while the sine output models can handle all kinds of
loads including motors (but a quick check says that they still can't use
surge supressors - this one has me puzzled!)

The UPS EMC standard is 50091-2 (or was it 92-1?), but I'm not sure how
much help it may offer.

Best Regards,
Dave Heald

 Price, Ed ed.pr...@cubic.com 06/02/03 11:18AM 
Hi Group!


Last Friday, I got ambushed in a meeting. I hate it when that happens!

A question was asked about whether it's OK to put a surge suppressor on
the
output of a UPS that is supplying power to some expensive equipment. I
opined that I didn't think it should be necessary, but that it also
shouldn't hurt anything either. So then somebody asks me why all the
UPS
manufacturer's sites say not to use a surge suppressor. I expertly
reply
that gosh, I don't know, but I'll take a look.

The next question nails me again. Are there any standards for UPS
output
power quality? Uh, well, I'll look into that too.

Now, the market is light industrial, USA, but are there any applicable
EN
standards also?

Just for some background, here's a typical entry from Tripp-Lite's FAQ
list
for UPS's (not to pick on Tripp-Lite; they just said it most succinctly
of
several sites I looked at):

http://www.tripplite.com/support/faq/tech_ups.cfm 
Can I plug a surge suppressor or extension cord into my UPS?
No. Using an extension cord will void your equipment coverage warranty,
as
all equipment must be plugged directly into the UPS. Tripp Lite does
not
recommend plugging a surge protector into a battery backup outlet of a
UPS
either as this can overload it. Also, when some UPS systems switch to
battery power they will output a waveform that a surge suppressor may
see as
a surge and short-circuit the UPS. Again, this setup will void the
equipment
coverage warranty.

Now this is getting to be a big can of worms! What do they mean by
some
UPS? Is there one kind that does, and another kind that doesn't; and
how do
you know which is which? And if some UPS will create a voltage
transient (is
that what they mean?) sufficient to trigger a surge suppressor, then
why is
it OK to let the UPS apply that transient to my protected equipment?
All
this talk about uninterrupted power isn't worth anything if the UPS
kills my
equipment when it switches to battery power mode.

And who's fault is this? I mean, a surge suppressor is pretty dumb; it
just
sits there waiting for the voltage to go over a certain level and then
it
conducts. What's this about the surge suppressor may see something as
a
surge? That's saying the surge suppressor could mis-interpret the
waveform
it sees. If the surge suppressor is conducting, then I think the UPS
has
just done something very naughty.

I also don't understand the prohibition of an extension cord. Maybe
this is
a legal issue, as I can't see any valid safety or regulation issues
here. We
regularly put a UPS in the bottom of a rack system, and then wire a
stripline outlet set for the height of the rack. Isn't that the
electrical
equivalent of an extension cord? What am I missing?

Thanks in advance!

Ed


Ed Price
ed.pr...@cubic.com 
NARTE Certified EMC Engineer  Technician
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA  USA
858-505-2780  (Voice)
858-505-1583  (Fax)
Military  Avionics EMC Is Our Specialty




This email has been scanned for computer viruses.


This email has been scanned for computer viruses.


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Surge Suppressors on a UPS

2003-06-02 Thread John Woodgate

I read in !emc-pstc that michael.sundst...@nokia.com wrote (in
57a26d272f67a743952f6b4371b8f81101e42...@daebe007.americas.nokia.com)
about 'Surge Suppressors on a UPS' on Mon, 2 Jun 2003:
I also don't understand the prohibition of an extension cord. Maybe 
this is a legal issue, as I can't see any valid safety or 
regulation issues here. We regularly put a UPS in the bottom of a 
rack system, and then wire a stripline outlet set for the height of 
the rack. Isn't that the electrical equivalent of an extension 
cord? What am I missing?

I think you are right. The advice is a cop-out. A surge suppressor on
the output of a UPS should, in theory, never be activated. But something
outside the spec of the UPS, such as a close lighting strike, might
activate it and perhaps damage the UPS. 

Banning extension cords (without surge suppressors) is bizarre and
inexplicable. I see the leaden hand of the corporate attorney there.


-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   emc_p...@symbol.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Surge Suppressors on a UPS

2003-06-02 Thread michael.sundst...@nokia.com
Ed, I also hate it when I get ambushed.
 
In the matter of the extension cord: I guess to lessen their liability they
don't want any extra voltage drop from a cord?
 
I also agree, why would I hook up a UPS that could fry my equipment with a
switching event?
 
When you find out let me know, as this sounds like something I need to know!

Michael Sundstrom 
 NOKIA 
  TCC Dallas / EMC 
   of: (972) 374-1462 
cell: (817) 917-5021 
 amateur call: KB5UKT 



From: ext Price, Ed [mailto:ed.pr...@cubic.com]
Sent: Monday, June 02, 2003 10:19 AM
To: 'EMC-PSTC List'
Subject: Surge Suppressors on a UPS



Hi Group! 


Last Friday, I got ambushed in a meeting. I hate it when that happens! 

A question was asked about whether it's OK to put a surge suppressor on the
output of a UPS that is supplying power to some expensive equipment. I opined
that I didn't think it should be necessary, but that it also shouldn't hurt
anything either. So then somebody asks me why all the UPS manufacturer's sites
say not to use a surge suppressor. I expertly reply that gosh, I don't know,
but I'll take a look.

The next question nails me again. Are there any standards for UPS output
power quality? Uh, well, I'll look into that too.

Now, the market is light industrial, USA, but are there any applicable EN
standards also? 

Just for some background, here's a typical entry from Tripp-Lite's FAQ list
for UPS's (not to pick on Tripp-Lite; they just said it most succinctly of
several sites I looked at):

http://www.tripplite.com/support/faq/tech_ups.cfm 
Can I plug a surge suppressor or extension cord into my UPS?
No. Using an extension cord will void your equipment coverage warranty, as all
equipment must be plugged directly into the UPS. Tripp Lite does not recommend
plugging a surge protector into a battery backup outlet of a UPS either as
this can overload it. Also, when some UPS systems switch to battery power they
will output a waveform that a surge suppressor may see as a surge and
short-circuit the UPS. Again, this setup will void the equipment coverage
warranty.

Now this is getting to be a big can of worms! What do they mean by some UPS?
Is there one kind that does, and another kind that doesn't; and how do you
know which is which? And if some UPS will create a voltage transient (is that
what they mean?) sufficient to trigger a surge suppressor, then why is it OK
to let the UPS apply that transient to my protected equipment? All this talk
about uninterrupted power isn't worth anything if the UPS kills my equipment
when it switches to battery power mode.

And who's fault is this? I mean, a surge suppressor is pretty dumb; it just
sits there waiting for the voltage to go over a certain level and then it
conducts. What's this about the surge suppressor may see something as a
surge? That's saying the surge suppressor could mis-interpret the waveform it
sees. If the surge suppressor is conducting, then I think the UPS has just
done something very naughty.

I also don't understand the prohibition of an extension cord. Maybe this is a
legal issue, as I can't see any valid safety or regulation issues here. We
regularly put a UPS in the bottom of a rack system, and then wire a stripline
outlet set for the height of the rack. Isn't that the electrical equivalent of
an extension cord? What am I missing?

Thanks in advance! 

Ed 


Ed Price 
ed.pr...@cubic.com 
NARTE Certified EMC Engineer  Technician 
Electromagnetic Compatibility Lab 
Cubic Defense Systems 
San Diego, CA  USA 
858-505-2780  (Voice) 
858-505-1583  (Fax) 
Military  Avionics EMC Is Our Specialty