RE: What's the deal with Wire Nuts?

2008-11-20 Thread Haynes, Tim (SELEX GALILEO, UK)
Don, Hi.
 
In your response to Brian you said...
 
  However, written into the body of the IEC 60950-1 and EN 60950-1 (and other
national derivative standards) is a wiring method for permanent connection to
the mains not acceptable in the US and Canada – the use of a non-detachable
power supply cord for permanent connection. 
 
Can you please supply to me the reference that prohibits that wiring method in
US and Canada? 

 

Regards

Tim

 



Tim Haynes A1N10

Electromagnetic Engineering Specialist

SELEX Sensors and Airborne Systems 

300 Capability Green

Luton LU1 3PG

( Tel  : +44 (0)1582 886239

7 Fax : +44 (0)1582 795863 

) Mob: +44 (0)7703 559 310 

* E-mail : tim.hay...@selexgalileo.com

P Please consider the environment before printing this email. 

 

There are 10 types of people in the world-those who understand binary and
those who don't. J. Paxman

 

SELEX Sensors and Airborne Systems Limited
Registered Office: Sigma House, Christopher Martin Road, Basildon, Essex SS14
3EL
A company registered in England  Wales. Company no. 02426132

This email and any attachments are confidential to the intended
recipient and may also be privileged. If you are not the intended
recipient please delete it from your system and notify the sender.
You should not copy it or use it for any purpose nor disclose or
distribute its contents to any other person.



-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org
David Heald dhe...@gmail.com 




RE: What's the deal with Wire Nuts?(Non-Detachable Power Supply Cords)

2008-11-20 Thread Don Gies
Tim,

 

Sure.  In clause 3.2.3, “Permanently connected equipment”, it says:

 

“PERMANENTLY CONNECTED EQUIPMENT shall be provided with either
(strikethrough):

 

*  a set of terminals as specified in 3.3; or (strikethrough)

*  a NON-DETACHABLE POWER SUPPLY CORD (strikethrough)

 

PERMANENTLY CONNECTED EQUIPMENT having a set of terminals shall:”

 

This has been there since UL 1950 and CSA C22.2 No. 950 of old times.

 

The source of this omission is in the following US National Electrical Code
and Canadian Electrical Code, Part I sections:

 

NEC (2008), Article 400 – FLEXIBLE CORDS AND CABLES

 

“400.7 Uses Permitted.”

“(B)  Attachment Plugs.  Where used as permitted in 400.7(A)(3), (A)(6), and
(A)(8), each flexible cord shall be equipped with an attachment plug and shall
be energized from a receptacle outlet.”

 

“400.8 Uses Not Permitted.  Unless specifically permitted in 400.7, flexible
cords shall not be used for the following:”

 

(1) As a substitute for the fixed wiring of a structure

(4) Where attached to building surfaces

(6)  Where installed in raceways, except as otherwise permitted in this Code.

 

CSA C22.1, Canadian Electrical Code, Part I (2006), 

 

4-010, Uses of flexible cords

(3)  Flexible cords shall not be used 

(a)  as a substitute for the fixed wiring of structures and shall
not be 

(i)  permanently secured to any structural member;

 

Best Regards,

 

Don Gies, N.C.E

Senior Product Compliance Engineer

Alcatel-Lucent

Murray Hill, NJ  07974-0636 USA

 



From: Haynes, Tim (SELEX GALILEO, UK) [mailto:tim.hay...@selexgalileo.com] 
Sent: Thursday, November 20, 2008 4:03 AM
To: Don Gies; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: What's the deal with Wire Nuts?

 

 

Don, Hi.

 

In your response to Brian you said...

 

  However, written into the body of the IEC 60950-1 and EN 60950-1 (and other
national derivative standards) is a wiring method for permanent connection to
the mains not acceptable in the US and Canada – the use of a non-detachable
power supply cord for permanent connection. 

 

Can you please supply to me the reference that prohibits that wiring method in
US and Canada? 

 

Regards

Tim

 



Tim Haynes A1N10

Electromagnetic Engineering Specialist

SELEX Sensors and Airborne Systems 

300 Capability Green

Luton LU1 3PG

* Tel  : +44 (0)1582 886239

* Fax : +44 (0)1582 795863 

* Mob: +44 (0)7703 559 310 

* E-mail : tim.hay...@selexgalileo.com

P Please consider the environment before printing this email. 

 

There are 10 types of people in the world-those who understand binary and
those who don't. J. Paxman

 

SELEX Sensors and Airborne Systems Limited
Registered Office: Sigma House, Christopher Martin Road, Basildon, Essex SS14
3EL
A company registered in England  Wales. Company no. 02426132

This email and any attachments are confidential to the intended
recipient and may also be privileged. If you are not the intended
recipient please delete it from your system and notify the sender.
You should not copy it or use it for any purpose nor disclose or
distribute its contents to any other person.



-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org
David Heald dhe...@gmail.com 




RE: What's the deal with Wire Nuts?

2008-11-20 Thread Jim Eichner
Flexible cord is not to be used where a permanent wiring system is required,
except under certain exceptions.  The concern is that flexible cord is not as
robust as wiring in conduit or wiring in walls, and over the long-term
exposure that permanent installation implies, a flexible cord could become
damaged and hazardous.

 

Canada: CEC part 1 2006 rule 4-010

 

US: NEC 2008 rule 400.7

 

 

Jim Eichner, P.Eng.
Compliance Engineering Manager
Xantrex Technology Inc.
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com http://www.xantrex.com/   

Confidentiality Notice: This email message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Haynes, Tim
(SELEX GALILEO, UK)
Sent: Thursday, November 20, 2008 1:03 AM
To: Don Gies; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: What's the deal with Wire Nuts?

 

 

Don, Hi.

 

In your response to Brian you said...

 

  However, written into the body of the IEC 60950-1 and EN 60950-1 (and other
national derivative standards) is a wiring method for permanent connection to
the mains not acceptable in the US and Canada – the use of a non-detachable
power supply cord for permanent connection. 

 

Can you please supply to me the reference that prohibits that wiring method in
US and Canada? 

 

Regards

Tim

 



Tim Haynes A1N10

Electromagnetic Engineering Specialist

SELEX Sensors and Airborne Systems 

300 Capability Green

Luton LU1 3PG

( Tel  : +44 (0)1582 886239

7 Fax : +44 (0)1582 795863 

) Mob: +44 (0)7703 559 310 

* E-mail : tim.hay...@selexgalileo.com

P Please consider the environment before printing this email. 

 

There are 10 types of people in the world-those who understand binary and
those who don't. J. Paxman

 

SELEX Sensors and Airborne Systems Limited
Registered Office: Sigma House, Christopher Martin Road, Basildon, Essex SS14
3EL
A company registered in England  Wales. Company no. 02426132

This email and any attachments are confidential to the intended
recipient and may also be privileged. If you are not the intended
recipient please delete it from your system and notify the sender.
You should not copy it or use it for any purpose nor disclose or
distribute its contents to any other person.


-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org
David Heald dhe...@gmail.com 

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:
Jim Bacher j.bac...@ieee.org
David Heald dhe...@gmail.com 




RE: What's the deal with Wire Nuts?

2008-11-18 Thread Don Gies
Brian,

 

The use of wire nuts on short wire pigtails in a wiring box for connection to
the building wiring is primarily a North American wiring method.  You can
deduce this by looking at the marks on the box that they came in.  They most
likely have listing marks for the US, Canada, and/or Mexico, and wire sizes
are in “AWG”.  If, on the other hand, you saw the CE Mark or wire sizes
posted in “mm2”, or some other international certification markings, you
would have evidence that the use of those wire nuts is an acceptable wiring
method elsewhere.

 

More evidence of this can be seen in national deviations found in Annex NAE of
UL 60950-1/CSA C22.2 No. 60950-1 vs.the group deviations of EN 60950-1. 
UL/CSA 69050-1, Annex NAE 3.2.3 describes leads for field wiring connections
to be not smaller than 150 mm (6 inches) in length, making reference to
sections of the National Electrical Code and Canadian Electrical Code, Part I.
 Annex NAE 3.2.9 further describes box volume calculations required by the NEC
and Canadian Electrical Code for the number of conductors being connected in a
wiring box, normally by wire nuts.On the other hand, EN 60950-1 has no
such deviations or notations. However, written into the body of the IEC
60950-1 and EN 60950-1 (and other national derivative standards) is a wiring
method for permanent connection to the mains not acceptable in the US and
Canada – the use of a non-detachable power supply cord for permanent
connection.

 

The most universally accepted means for permanent connection to the mains is
to use a field wiring terminal block with a current rating 125 % of the
current rating of the product it is installed in, certified for the country of
deployment.   In conjunction, holes should be supplied nearby for
accommodation of a conduit system or cable-securing glands. 

 

Best Regards,

 

Don Gies, N.C.E

Senior Product Compliance Engineer

Alcatel-Lucent

Murray Hill, NJ  07974-0636 USA

 



From: Kunde, Brian [mailto:brian_ku...@lecotc.com] 
Sent: Monday, November 17, 2008 3:53 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: What's the deal with Wire Nuts?

 

Scott,

 

Does the 60950 standard give examples of what would satisfy the “two
independent fixings” requirement?  How would a terminal block satisfy this?  

 

I have heard that a wire nut can be used for the electrical connection, but
you have to also mechanically hold the wires together which can be done with a
cable tie.  No where have I found this documented, though.

 

The Other Brian

 



From: scott barrows [mailto:sbarro...@yahoo.com] 
Sent: Monday, November 17, 2008 2:50 PM
To: sbarro...@yahoo.com; Ted Eckert; EMC-PSTC@LISTSERV.IEEE.ORG; Aldous,
Scott; Kunde, Brian
Subject: RE: What's the deal with Wire Nuts?

 

Hello Other Brian, 

That is a term I have heard from years gone by. 

 

A standard does not specifically prohibit them however if you look at IEC
60950 para 3.1.9 it would be difficult to use wire nut that met the
requirements of two independent fixings. Most EU standards have a similar
discription as well.

 

Best Regards,

Scott

 



--- On Mon, 11/17/08, Kunde, Brian brian_ku...@lecotc.com wrote:

From: Kunde, Brian brian_ku...@lecotc.com
Subject: RE: What's the deal with Wire Nuts?
To: sbarro...@yahoo.com, Ted Eckert ted.eck...@microsoft.com,
EMC-PSTC@LISTSERV.IEEE.ORG, Aldous, Scott scott.ald...@aei.com
Date: Monday, November 17, 2008, 2:31 PM

Where does the term, “Redundant Captive Device” come from?

 

The device which has the wire nuts (twist-on wire connectors) is a water
chiller used as a peripheral for a piece of laboratory equipment to be sold
internationally.  The manufacturer is not used to making laboratory equipment,
but industrial cooling devices in the US where it maybe acceptable to use wire
nuts. 

 

Looking at the IEC/EN 61010-1 standard I cannot see any specific requirement
for redundant captive device or redundant connection.  I do see a statement in
10.5.3b regarding “insulation which supports the TERMINALS shall be made of
material that will not soften” due to dissipated heat from current through
the connection.  I assume that if the plastic cap of a wire nut gets hot from
current passing through the connection and softens then the connection will
become loose.  Some wire nuts are all plastic and the larger ones have a
copper spring inside. In either case, it is the plastic that secures the
connection.

 

On a crimp type connection (such as a spade lug or crimp splice), even though
they have a plastic case, the electrical connection is made from a metal part
which is not likely to soften. 

 

It would be nice if there was a clear statement (chapter and verse)
documenting if wire nuts can be used in Europe or not or some kind of
interpretation letter.

 

The Other Brian

 



From: scott barrows

RE: What's the deal with Wire Nuts?

2008-11-17 Thread Ted Eckert
Hello Brian,

 

Off hand, I am unaware of anything preventing the use of a twist-on wire
connector in portable equipment, but that doesn’t mean that the prohibition
doesn’t exist.  Other list members may know of specific cases where the
connectors are prohibited.  However, the description of the connector covered
in electrical tape indicates that the connector is likely used outside of its
UL Listing (if it is even a Listed connector.)

 

First, let me state that “Wire-Nut” is a registered trademark of Ideal
Industries.  If you are looking for information in standards, the term
“twist-on wire connector” will be used.

 

Vibration during use is probably not the main issue.  There are many types of
fixed equipment, such as an air conditioner or other motor driven appliance,
where twist-on connectors are used and they are subject to regular vibration. 
The connectors may see more vibration in these applications than they might
see in some portable appliances.

 

However, your description gives me cause to be concerned.  UL does List
twist-on connectors under category code ZMVV and they have been around for
quite a while.  (Ideal’s UL file number is E5238 and that should give you an
idea as to the age of the product.)  The connectors’ Listing does have some
very specific requirements.  Specific size connectors are Listed only for use
with specific wire sizes and types.  The installation instructions must be
followed closely.  Some of the wire connectors specify that you should not
twist the wires first.  The twisting of the wire connector will twist the
wires to make the proper connection.  If you see a connector covered with
black tape, there is likely a problem.  The tape is typically used when there
is a concern that the connector will come loose.  This is done based on the
installer’s experience.  If they have had connectors come loose, it is
because they are likely using them incorrectly.  The tape does not fix
anything.  Electrical tape will not likely withstand the test of time and the
adhesive will degrade.  Cheap electrical tape rarely lasts long at all.

 

There are numerous crimp connectors suitable for connecting wires.  There are
but splices and crimp connectors designed to perform the same purpose as a
twist-on connector.  The crimp connectors make a good, permanent splice.  The
twist-on connector is intended for use where connections are made in the
field, particularly where they may need to be undone for servicing.  Crimp
connections and terminal blocks are better options for factory connections.

 

Ted Eckert

Compliance Engineer

Microsoft Corporation

ted.eck...@microsoft.com

 

The opinions expressed are my own and do not necessarily reflect those of my
employer.

 

 

 

From: Kunde, Brian [mailto:brian_ku...@lecotc.com] 
Sent: Monday, November 17, 2008 6:18 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: What's the deal with Wire Nuts?

 

Greetings Experts.

 

This should be an easy one for those who know the answer.

 

What is the deal with Wire Nuts?  Where can be they be used, where can’t
they be used?  Are there different rules for permanently mounted equipment
verse portable equipment? Do you have to also use a mechanical device such are
a tie wrap? How about black tape?

 

Our company does not use wire nuts but we always had the impression that
safety inspectors do not like to see wire nuts in portable equipment.  We are
evaluating a product made by another company that uses wire nuts on primary
wiring with black tape wrapped around it.  Is this technique acceptable
internationally on portable equipment?

 

Thanks to all in advance for the education.  

 

The Other Brian

_ 

LECO Corporation Notice: This communication may contain confidential
information intended for the named recipient(s) only. If you received this by
mistake, please destroy it and notify us of the error. Thank you. 

-


This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc 

-


This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 


RE: What's the deal with Wire Nuts?

2008-11-17 Thread Aldous, Scott
Hi Brian,

 

When I worked for UL, I had heard that the use of wire nuts was not acceptable
for the EU (CE Marking), but I don’t recall ever seeing the source of this
alleged requirement. I have a vague recollection about them not having any
type of international certifications, but I’m not sure about that.

 

There is a book, CE Marking Handbook: A Practical Approach to Global Safety
Certification, by David Lohbeck, published in 1998, which covers this, but not
in depth. You can preview the book on Google.

 

On page 119, that book indicates that “U.S. wire-nuts are not permitted for
wire connections.” I don’t believe the source of this statement is
provided, and it well may just be the opinion of the author.

 

Scott Aldous

Compliance Engineer

Advanced Energy

Tel: 970-407-6872

Fax: 970-407-5872



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Ted Eckert
Sent: Monday, November 17, 2008 9:39 AM
To: Kunde, Brian; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: What's the deal with Wire Nuts?

 

Hello Brian,

 

Off hand, I am unaware of anything preventing the use of a twist-on wire
connector in portable equipment, but that doesn’t mean that the prohibition
doesn’t exist.  Other list members may know of specific cases where the
connectors are prohibited.  However, the description of the connector covered
in electrical tape indicates that the connector is likely used outside of its
UL Listing (if it is even a Listed connector.)

 

First, let me state that “Wire-Nut” is a registered trademark of Ideal
Industries.  If you are looking for information in standards, the term
“twist-on wire connector” will be used.

 

Vibration during use is probably not the main issue.  There are many types of
fixed equipment, such as an air conditioner or other motor driven appliance,
where twist-on connectors are used and they are subject to regular vibration. 
The connectors may see more vibration in these applications than they might
see in some portable appliances.

 

However, your description gives me cause to be concerned.  UL does List
twist-on connectors under category code ZMVV and they have been around for
quite a while.  (Ideal’s UL file number is E5238 and that should give you an
idea as to the age of the product.)  The connectors’ Listing does have some
very specific requirements.  Specific size connectors are Listed only for use
with specific wire sizes and types.  The installation instructions must be
followed closely.  Some of the wire connectors specify that you should not
twist the wires first.  The twisting of the wire connector will twist the
wires to make the proper connection.  If you see a connector covered with
black tape, there is likely a problem.  The tape is typically used when there
is a concern that the connector will come loose.  This is done based on the
installer’s experience.  If they have had connectors come loose, it is
because they are likely using them incorrectly.  The tape does not fix
anything.  Electrical tape will not likely withstand the test of time and the
adhesive will degrade.  Cheap electrical tape rarely lasts long at all.

 

There are numerous crimp connectors suitable for connecting wires.  There are
but splices and crimp connectors designed to perform the same purpose as a
twist-on connector.  The crimp connectors make a good, permanent splice.  The
twist-on connector is intended for use where connections are made in the
field, particularly where they may need to be undone for servicing.  Crimp
connections and terminal blocks are better options for factory connections.

 

Ted Eckert

Compliance Engineer

Microsoft Corporation

ted.eck...@microsoft.com

 

The opinions expressed are my own and do not necessarily reflect those of my
employer.

 

 

 

From: Kunde, Brian [mailto:brian_ku...@lecotc.com] 
Sent: Monday, November 17, 2008 6:18 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: What's the deal with Wire Nuts?

 

Greetings Experts.

 

This should be an easy one for those who know the answer.

 

What is the deal with Wire Nuts?  Where can be they be used, where can’t
they be used?  Are there different rules for permanently mounted equipment
verse portable equipment? Do you have to also use a mechanical device such are
a tie wrap? How about black tape?

 

Our company does not use wire nuts but we always had the impression that
safety inspectors do not like to see wire nuts in portable equipment.  We are
evaluating a product made by another company that uses wire nuts on primary
wiring with black tape wrapped around it.  Is this technique acceptable
internationally on portable equipment?

 

Thanks to all in advance for the education.  

 

The Other Brian

_ 

LECO Corporation Notice: This communication may contain confidential
information intended for the named recipient(s) only. If you received this by
mistake, please destroy it and notify us of the error. Thank you. 

-


This message

RE: What's the deal with Wire Nuts?

2008-11-17 Thread scott barrows
It is not a redundant captive device.
 
Scott

--- On Mon, 11/17/08, Aldous, Scott scott.ald...@aei.com wrote:


From: Aldous, Scott scott.ald...@aei.com
Subject: RE: What's the deal with Wire Nuts?
To: Ted Eckert ted.eck...@microsoft.com, Kunde, Brian
brian_ku...@lecotc.com, EMC-PSTC@LISTSERV.IEEE.ORG
Date: Monday, November 17, 2008, 12:08 PM



Hi Brian,

 

When I worked for UL, I had heard that the use of wire nuts was not
acceptable for the EU (CE Marking), but I don’t recall ever seeing the
source of this alleged requirement. I have a vague recollection about them not
having any type of international certifications, but I’m not sure about that.

 

There is a book, CE Marking Handbook: A Practical Approach to Global 
Safety
Certification, by David Lohbeck, published in 1998, which covers this, but not
in depth. You can preview the book on Google.

 

On page 119, that book indicates that “U.S. wire-nuts are not permitted 
for
wire connections.” I don’t believe the source of this statement is
provided, and it well may just be the opinion of the author.

 

Scott Aldous

Compliance Engineer

Advanced Energy

Tel: 970-407-6872

Fax: 970-407-5872




From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Ted 
Eckert
Sent: Monday, November 17, 2008 9:39 AM
To: Kunde, Brian; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: What's the deal with Wire Nuts?

 

Hello Brian,

 

Off hand, I am unaware of anything preventing the use of a twist-on wire
connector in portable equipment, but that doesn’t mean that the prohibition
doesn’t exist.  Other list members may know of specific cases where the
connectors are prohibited.  However, the description of the connector covered
in electrical tape indicates that the connector is likely used outside of its
UL Listing (if it is even a Listed connector.)

 

First, let me state that “Wire-Nut” is a registered trademark of Ideal
Industries.  If you are looking for information in standards, the term
“twist-on wire connector” will be used.

 

Vibration during use is probably not the main issue.  There are many 
types of
fixed equipment, such as an air conditioner or other motor driven appliance,
where twist-on connectors are used and they are subject to regular vibration. 
The connectors may see more vibration in these applications than they might
see in some portable appliances.

 

However, your description gives me cause to be concerned.  UL does List
twist-on connectors under category code ZMVV and they have been around for
quite a while.  (Ideal’s UL file number is E5238 and that should give you an
idea as to the age of the product.)  The connectors’ Listing does have some
very specific requirements.  Specific size connectors are Listed only for use
with specific wire sizes and types.  The installation instructions must be
followed closely.  Some of the wire connectors specify that you should not
twist the wires first.  The twisting of the wire connector will twist the
wires to make the proper connection.  If you see a connector covered with
black tape, there is likely a problem.  The tape is typically used when there
is a concern that the connector will come loose.  This is done based on the
installer’s experience.  If they have had connectors come loose, it is
because they are likely using them incorrectly.  The tape does not fix
anything.  Electrical tape will not likely withstand the test of time and the
adhesive will degrade.  Cheap electrical tape rarely lasts long at all.

 

There are numerous crimp connectors suitable for connecting wires.  
There are
but splices and crimp connectors designed to perform the same purpose as a
twist-on connector.  The crimp connectors make a good, permanent splice.  The
twist-on connector is intended for use where connections are made in the
field, particularly where they may need to be undone for servicing.  Crimp
connections and terminal blocks are better options for factory connections.

 

Ted Eckert

Compliance Engineer

Microsoft Corporation

ted.eck...@microsoft.com

 

The opinions expressed are my own and do not necessarily reflect those 
of my
employer.

 

 

 

From: Kunde, Brian [mailto:brian_ku...@lecotc.com] 
Sent: Monday, November 17, 2008 6:18 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: What's the deal with Wire Nuts?

 

Greetings Experts.

 

This should be an easy one for those who know the answer.

 

What is the deal with Wire Nuts?  Where can be they be used, where can’t
they be used?  Are there different rules for permanently

RE: What's the deal with Wire Nuts?

2008-11-17 Thread James, Chris
What approvals does this other equipment purport to have? 

 

Chris

 

 



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Kunde, Brian
Sent: 17 November 2008 14:18
To: emc-p...@ieee.org
Subject: What's the deal with Wire Nuts?

 

Greetings Experts.

 

This should be an easy one for those who know the answer.

 

What is the deal with Wire Nuts?  Where can be they be used, where can’t
they be used?  Are there different rules for permanently mounted equipment
verse portable equipment? Do you have to also use a mechanical device such are
a tie wrap? How about black tape?

 

Our company does not use wire nuts but we always had the impression that
safety inspectors do not like to see wire nuts in portable equipment.  We are
evaluating a product made by another company that uses wire nuts on primary
wiring with black tape wrapped around it.  Is this technique acceptable
internationally on portable equipment?

 

Thanks to all in advance for the education.  

 

The Other Brian

_ 

LECO Corporation Notice: This communication may contain confidential
information intended for the named recipient(s) only. If you received this by
mistake, please destroy it and notify us of the error. Thank you. 

-



This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc 

-



This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc 

-



This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc 



This message (including any attachments) may contain confidential information
intended for a specific individual and purpose. If you are not the intended
recipient, delete this message. If you are not the intended recipient,
disclosing, copying, distributing, or taking any action based on this message
is strictly prohibited. 

-



This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 

Instructions: http://listserv.ieee.org/request/user-guide.html 

List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org 

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com 

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc 




Re: What's the deal with Wire Nuts?

2008-11-17 Thread Doug Nix
Brian,

In my experience, electrical inspectors do not like to see twist-on wire
connectors used in equipment due to the perceived potential for them to
vibrate loose, usually because they were incorrectly installed in the first
place. Some inspectors will insist that they be over-wrapped with approved
electrical tape with enough layers to match the insulation thickness of the
connected wires. Some just won't accept them at all.

For equipment applications, it is up to the reviewing engineers looking at the
product during the certification evaluations to determine if the connector is
a) suitable for the application and b) approved for the application. This is
why they are frequently found inside equipment, but why they are not generally
accepted on field-installed equipment (control panels and the like).

I believe that Scott Barrows is correct in his comment that they are not
redundant, captive devices and thus not acceptable in the EU.

As far as I know, these connectors were originally intended for use in
building wiring applications on fixed wiring installations, not for
applications subject too vibration and shock in normal use.  

-- 
Doug Nix, A.Sc.T.
IEEE PSES 
Toronto Section, Ontario, Canada

d...@ieee.org 
mobile (519) 729-5704
fax (519) 653-1318

Find me LinkedIn at http://www.linkedin.com/in/dougnix


On Nov 17, 2008, at 9:17, Kunde, Brian wrote:



Greetings Experts.
 
This should be an easy one for those who know the answer.
 
What is the deal with Wire Nuts?  Where can be they be used, where can’t
they be used?  Are there different rules for permanently mounted equipment
verse portable equipment? Do you have to also use a mechanical device such are
a tie wrap? How about black tape?
 
Our company does not use wire nuts but we always had the impression that
safety inspectors do not like to see wire nuts in portable equipment.  We are
evaluating a product made by another company that uses wire nuts on primary
wiring with black tape wrapped around it.   Is this technique acceptable
internationally on portable equipment?
 
Thanks to all in advance for the education. 
  
The Other Brian
_ 

LECO Corporation Notice: This communication may contain confidential
information intended for the named recipient(s) only. If you received this by
mistake, please destroy it and notify us of the error. Thank you.

-



This message is from the IEEE Product Safety Engineering Society 
emc-pstc
discussion list. Website: http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions: http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html
http://www.ieee-pses.org/li strules.html 

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

-



This message is from the IEEE Product Safety Engineering Society 
emc-pstc
discussion list. Website: http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions: http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc

-



This message is from the IEEE Product Safety Engineering Society 
emc-pstc
discussion list. Website: http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions: http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:

Jim Bacher: j.bac...@ieee.org
David Heald: dhe...@gmail.com

All emc-pstc postings are archived and 

Re: What's the deal with Wire Nuts?

2008-11-17 Thread John Woodgate

In message 
7995b996909d2a40b3cb7d0db4cceaa90273d...@aedcexcvs1.aei.com, dated 
Mon, 17 Nov 2008, Aldous, Scott scott.ald...@aei.com writes:


On page 119, that book indicates that ?U.S. wire-nuts are not permitted 
for wire connections.? I don?t believe the source of this statement is 
provided, and it well may just be the opinion of the author.

I think it may be a ruling requested by European test-houses, with 
supporting evidence of problems, before the formal 'interpretation 
sheet' procedure was in place.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
Either we are causing global warming, in which case we may be able to stop it,
or natural variation is causing it, and we probably can't stop it. You choose!
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com





RE: What's the deal with Wire Nuts?

2008-11-17 Thread Kunde, Brian
Where does the term, “Redundant Captive Device” come from?

 

The device which has the wire nuts (twist-on wire connectors) is a water
chiller used as a peripheral for a piece of laboratory equipment to be sold
internationally.  The manufacturer is not used to making laboratory equipment,
but industrial cooling devices in the US where it maybe acceptable to use wire
nuts. 

 

Looking at the IEC/EN 61010-1 standard I cannot see any specific requirement
for redundant captive device or redundant connection.  I do see a statement in
10.5.3b regarding “insulation which supports the TERMINALS shall be made of
material that will not soften” due to dissipated heat from current through
the connection.  I assume that if the plastic cap of a wire nut gets hot from
current passing through the connection and softens then the connection will
become loose.  Some wire nuts are all plastic and the larger ones have a
copper spring inside. In either case, it is the plastic that secures the
connection.

 

On a crimp type connection (such as a spade lug or crimp splice), even though
they have a plastic case, the electrical connection is made from a metal part
which is not likely to soften. 

 

It would be nice if there was a clear statement (chapter and verse)
documenting if wire nuts can be used in Europe or not or some kind of
interpretation letter.

 

The Other Brian

 



From: scott barrows [mailto:sbarro...@yahoo.com] 
Sent: Monday, November 17, 2008 12:26 PM
To: Ted Eckert; Kunde, Brian; EMC-PSTC@LISTSERV.IEEE.ORG; Aldous, Scott
Subject: RE: What's the deal with Wire Nuts?

 

It is not a redundant captive device.

 

Scott

--- On Mon, 11/17/08, Aldous, Scott scott.ald...@aei.com wrote:

From: Aldous, Scott scott.ald...@aei.com
Subject: RE: What's the deal with Wire Nuts?
To: Ted Eckert ted.eck...@microsoft.com, Kunde, Brian
brian_ku...@lecotc.com, EMC-PSTC@LISTSERV.IEEE.ORG
Date: Monday, November 17, 2008, 12:08 PM

Hi Brian,

 

When I worked for UL, I had heard that the use of wire nuts was not
acceptable for the EU (CE Marking), but I don’t recall ever seeing the
source of this alleged requirement. I have a vague recollection about them not
having any type of international certifications, but I’m not sure about that.

 

There is a book, CE Marking Handbook: A Practical Approach to Global Safety
Certification, by David Lohbeck, published in 1998, which covers this, but not
in depth. You can preview the book on Google.

 

On page 119, that book indicates that “U.S. wire-nuts are not permitted for
wire connections.” I don’t believe the source of this statement is
provided, and it well may just be the opinion of the author.

 

Scott Aldous

Compliance Engineer

Advanced Energy

Tel: 970-407-6872

Fax: 970-407-5872



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Ted Eckert
Sent: Monday, November 17, 2008 9:39 AM
To: Kunde, Brian; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: What's the deal with Wire Nuts?

 

Hello Brian,

 

Off hand, I am unaware of anything preventing the use of a twist-on wire
connector in portable equipment, but that doesn’t mean that the prohibition
doesn’t exist.  Other list members may know of specific cases where the
connectors are prohibited.  However, the description of the connector covered
in electrical tape indicates that the connector is likely used outside of its
UL Listing (if it is even a Listed connector.)

 

First, let me state that “Wire-Nut” is a registered trademark of Ideal
Industries.  If you are looking for information in standards, the term
“twist-on wire connector” will be used.

 

Vibration during use is probably not the main issue.  There are many types of
fixed equipment, such as an air conditioner or other motor driven appliance,
where twist-on connectors are used and they are subject to regular vibration. 
The connectors may see more vibration in these applications than they might
see in some portable appliances.

 

However, your description gives me cause to be concerned.  UL does List
twist-on connectors under category code ZMVV and they have been around for
quite a while.  (Ideal’s UL file number is E5238 and that should give you an
idea as to the age of the product.)  The connectors’ Listing does have some
very specific requirements.  Specific size connectors are Listed only for use
with specific wire sizes and types.  The installation instructions must be
followed closely.  Some of the wire connectors specify that you should not
twist the wires first.  The twisting of the wire connector will twist the
wires to make the proper connection.  If you see a connector covered with
black tape, there is likely a problem.  The tape is typically used when there
is a concern that the connector will come loose.  This is done based on the
installer’s experience.  If they have had connectors come loose, it is
because they are likely

RE: What's the deal with Wire Nuts?

2008-11-17 Thread scott barrows
Hello Other Brian, 
That is a term I have heard from years gone by. 
 
A standard does not specifically prohibit them however if you look at IEC
60950 para 3.1.9 it would be difficult to use wire nut that met the
requirements of two independent fixings. Most EU standards have a similar
discription as well.
 
Best Regards,
Scott
 


--- On Mon, 11/17/08, Kunde, Brian brian_ku...@lecotc.com wrote:


From: Kunde, Brian brian_ku...@lecotc.com
Subject: RE: What's the deal with Wire Nuts?
To: sbarro...@yahoo.com, Ted Eckert ted.eck...@microsoft.com,
EMC-PSTC@LISTSERV.IEEE.ORG, Aldous, Scott scott.ald...@aei.com
Date: Monday, November 17, 2008, 2:31 PM



Where does the term, “Redundant Captive Device” come from?

 

The device which has the wire nuts (twist-on wire connectors) is a water
chiller used as a peripheral for a piece of laboratory equipment to be sold
internationally.  The manufacturer is not used to making laboratory equipment,
but industrial cooling devices in the US where it maybe acceptable to use wire
nuts. 

 

Looking at the IEC/EN 61010-1 standard I cannot see any specific 
requirement
for redundant captive device or redundant connection.  I do see a statement in
10.5.3b regarding “insulation which supports the TERMINALS shall be made of
material that will not soften” due to dissipated heat from current through
the connection.  I assume that if the plastic cap of a wire nut gets hot from
current passing through the connection and softens then the connection will
become loose.  Some wire nuts are all plastic and the larger ones have a
copper spring inside. In either case, it is the plastic that secures the
connection.

 

On a crimp type connection (such as a spade lug or crimp splice), even 
though
they have a plastic case, the electrical connection is made from a metal part
which is not likely to soften. 

 

It would be nice if there was a clear statement (chapter and verse)
documenting if wire nuts can be used in Europe or not or some kind of
interpretation letter.

 

The Other Brian

 




From: scott barrows [mailto:sbarro...@yahoo.com] 
Sent: Monday, November 17, 2008 12:26 PM
To: Ted Eckert; Kunde, Brian ; EMC-PSTC@LISTSERV.IEEE.ORG; Aldous, Scott
Subject: RE: What's the deal with Wire Nuts?

 

It is not a redundant captive device.

 

Scott

--- On Mon, 11/17/08, Aldous, Scott scott.ald...@aei.com wrote:

From: Aldous, Scott scott.ald...@aei.com
Subject: RE: What's the deal with Wire Nuts?
To: Ted Eckert ted.eck...@microsoft.com,  Kunde, Brian 
brian_ku...@lecotc.com, EMC-PSTC@LISTSERV.IEEE.ORG
Date: Monday, November 17, 2008, 12:08 PM

Hi Brian,

 

When I worked for UL, I had heard that the use of wire nuts was not
acceptable for the EU (CE Marking), but I don’t recall ever seeing the
source of this alleged requirement. I have a vague recollection about them not
having any type of international certifications, but I’m not sure about that.

 

There is a book, CE Marking Handbook: A Practical Approach to Global Safety
Certification, by David Lohbeck, published in 1998, which covers this, but not
in depth. You can preview the book on Google.

 

On page 119, that book indicates that “ U.S. wire-nuts are not permitted for
wire connections.” I don’t believe the source of this statement is
provided, and it well may just be the opinion of the author.

 

Scott Aldous

Compliance Engineer

Advanced Energy

Tel: 970-407-6872

Fax: 970-407-5872



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Ted Eckert
Sent: Monday, November 17, 2008 9:39 AM
To: Kunde, Brian ; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: What's the deal with Wire Nuts?

 

Hello Brian,

 

Off hand, I am unaware of anything preventing the use of a twist-on wire
connector in portable equipment, but that doesn’t mean that the prohibition
doesn’t exist.  Other list members may know of specific cases where the
connectors are prohibited.  However, the description of the connector covered
in electrical tape indicates that the connector is likely used outside of its
UL Listing (if it is even a Listed connector.)

 

First, let me state that “Wire-Nut” is a registered trademark of Ideal
Industries.  If you are looking for information in standards, the term
“twist-on wire connector” will be used.

 

Vibration during use is probably not the main issue.  There are many types of
fixed equipment, such as an air conditioner or other motor driven appliance,
where twist-on connectors are used and they are subject to regular vibration. 
The connectors may see more vibration in these applications than they might
see in some portable appliances.

 

However, your description gives me cause to be concerned.  UL does List

RE: What's the deal with Wire Nuts?

2008-11-17 Thread Kunde, Brian
Scott,

 

Does the 60950 standard give examples of what would satisfy the “two
independent fixings” requirement?  How would a terminal block satisfy this?  

 

I have heard that a wire nut can be used for the electrical connection, but
you have to also mechanically hold the wires together which can be done with a
cable tie.  No where have I found this documented, though.

 

The Other Brian

 



From: scott barrows [mailto:sbarro...@yahoo.com] 
Sent: Monday, November 17, 2008 2:50 PM
To: sbarro...@yahoo.com; Ted Eckert; EMC-PSTC@LISTSERV.IEEE.ORG; Aldous,
Scott; Kunde, Brian
Subject: RE: What's the deal with Wire Nuts?

 

Hello Other Brian, 

That is a term I have heard from years gone by. 

 

A standard does not specifically prohibit them however if you look at IEC
60950 para 3.1.9 it would be difficult to use wire nut that met the
requirements of two independent fixings. Most EU standards have a similar
discription as well.

 

Best Regards,

Scott

 



--- On Mon, 11/17/08, Kunde, Brian brian_ku...@lecotc.com wrote:

From: Kunde, Brian brian_ku...@lecotc.com
Subject: RE: What's the deal with Wire Nuts?
To: sbarro...@yahoo.com, Ted Eckert ted.eck...@microsoft.com,
EMC-PSTC@LISTSERV.IEEE.ORG, Aldous, Scott scott.ald...@aei.com
Date: Monday, November 17, 2008, 2:31 PM

Where does the term, “Redundant Captive Device” come from?

 

The device which has the wire nuts (twist-on wire connectors) is a water
chiller used as a peripheral for a piece of laboratory equipment to be sold
internationally.  The manufacturer is not used to making laboratory equipment,
but industrial cooling devices in the US where it maybe acceptable to use wire
nuts. 

 

Looking at the IEC/EN 61010-1 standard I cannot see any specific requirement
for redundant captive device or redundant connection.  I do see a statement in
10.5.3b regarding “insulation which supports the TERMINALS shall be made of
material that will not soften” due to dissipated heat from current through
the connection.  I assume that if the plastic cap of a wire nut gets hot from
current passing through the connection and softens then the connection will
become loose.  Some wire nuts are all plastic and the larger ones have a
copper spring inside. In either case, it is the plastic that secures the
connection.

 

On a crimp type connection (such as a spade lug or crimp splice), even though
they have a plastic case, the electrical connection is made from a metal part
which is not likely to soften. 

 

It would be nice if there was a clear statement (chapter and verse)
documenting if wire nuts can be used in Europe or not or some kind of
interpretation letter.

 

The Other Brian

 



From: scott barrows [mailto:sbarro...@yahoo.com] 
Sent: Monday, November 17, 2008 12:26 PM
To: Ted Eckert; Kunde, Brian ; EMC-PSTC@LISTSERV.IEEE.ORG; Aldous, Scott
Subject: RE: What's the deal with Wire Nuts?

 

It is not a redundant captive device.

 

Scott

--- On Mon, 11/17/08, Aldous, Scott scott.ald...@aei.com wrote:

From: Aldous, Scott scott.ald...@aei.com
Subject: RE: What's the deal with Wire Nuts?
To: Ted Eckert ted.eck...@microsoft.com,  Kunde, Brian 
brian_ku...@lecotc.com, EMC-PSTC@LISTSERV.IEEE.ORG
Date: Monday, November 17, 2008, 12:08 PM

Hi Brian,

 

When I worked for UL, I had heard that the use of wire nuts was not acceptable
for the EU (CE Marking), but I don’t recall ever seeing the source of this
alleged requirement. I have a vague recollection about them not having any
type of international certifications, but I’m not sure about that.

 

There is a book, CE Marking Handbook: A Practical Approach to Global Safety
Certification, by David Lohbeck, published in 1998, which covers this, but not
in depth. You can preview the book on Google.

 

On page 119, that book indicates that “ U.S. wire-nuts are not permitted for
wire connections.” I don’t believe the source of this statement is
provided, and it well may just be the opinion of the author.

 

Scott Aldous

Compliance Engineer

Advanced Energy

Tel: 970-407-6872

Fax: 970-407-5872



From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Ted Eckert
Sent: Monday, November 17, 2008 9:39 AM
To: Kunde, Brian ; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: What's the deal with Wire Nuts?

 

Hello Brian,

 

Off hand, I am unaware of anything preventing the use of a twist-on wire
connector in portable equipment, but that doesn’t mean that the prohibition
doesn’t exist.  Other list members may know of specific cases where the
connectors are prohibited.  However, the description of the connector covered
in electrical tape indicates that the connector is likely used outside of its
UL Listing (if it is even a Listed connector.)

 

First, let me state that “Wire-Nut” is a registered trademark of Ideal