RE: surges on 24VAC

2001-12-22 Thread Enci

At 15:16 21/12/01 -0500, John Juhasz wrote:
>
>If the 24V AC is generated via a Class II Direct Plug-In power
>pack, wouldn't the test be run 'through' the power pack - the power
>pack plugged into the outlet on the surge tester?

I see your point, but as I understand it, only if the power pack is made
available with the apparatus to the end user, i.e. a system. This is up to
the manufacturer to define.


Enci


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: surges on 24VAC

2001-12-22 Thread John Woodgate

I read in !emc-pstc that John Juhasz  wrote
(in <2a1845f4cde8d511b4400090279c703b14e...@bctexc10.na.ilxi.net>) about
'surges on 24VAC', on Fri, 21 Dec 2001:

>The functional circuit operates off of 24V AC,
>but the primary power is AC Mains  - whether it's
>supplied through a line cord/power entry module combo
>or a direct plug-in transformer.

We aren't told what supplies the 24 V a.c. . It may be a supply that is
highly unlikely to experience a surge of any sort. Whatever the supply
system is, the surge test intended for mains voltage ports is not
appropriate to be applied to the 24 V a.c. port. 
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
After swimming across the Hellespont, I felt like a Hero. 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: surges on 24VAC

2001-12-21 Thread John Woodgate

I read in !emc-pstc that Mavis, Robert  wrote (in
) about
'surges on 24VAC', on Fri, 21 Dec 2001:

>The AC Mains test is just that AC Mains. The Definition of AC mains is
>basically what comes out of the wall. Since the product is 24VAC it falls
>under low voltage/signal lines. Test is as a signal line.

No, the standard uses the term 'a.c. power port' in Table 4. It says
noting about 'mains'.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
After swimming across the Hellespont, I felt like a Hero. 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: surges on 24VAC

2001-12-21 Thread John Juhasz

If the 24V AC is generated via a Class II Direct Plug-In power
pack, wouldn't the test be run 'through' the power pack - the power
pack plugged into the outlet on the surge tester?
The power pack runs off of AC Mains. 
For argument sake, what's the difference of that scenario
as compared to having to test a product which is
configured with an IEC 320 power entry module through which
a 24V AC transformer inside the product receives it's 
AC Mains? 
The functional circuit operates off of 24V AC,
but the primary power is AC Mains  - whether it's
supplied through a line cord/power entry module combo
or a direct plug-in transformer.

My opinion only . . . 

John Juhasz
Fiber Options
Bohemia, NY


-Original Message-
From: Mavis, Robert [mailto:rma...@pelco.com]
Sent: Friday, December 21, 2001 1:46 PM
To: Jennifer Banh; emc-p...@majordomo.ieee.org
Subject: RE: surges on 24VAC




The AC Mains test is just that AC Mains. The Definition of AC mains is
basically what comes out of the wall. Since the product is 24VAC it falls
under low voltage/signal lines. Test is as a signal line.

-Original Message-
From: Jennifer Banh [mailto:jb...@bb-elec.com]
Sent: Monday, December 17, 2001 11:44 AM
To: emc-p...@majordomo.ieee.org
Subject: surges on 24VAC



Hello everyone,
I am currently trying to test a product of ours that falls under
50082-1
generic standard for light industrial equipment.  Our problem is that we
have a 24VAC power input port.  The generic standard calls out for EN
61000-4-5 on AC power input ports.  After looking at EN 61000-4-5 it seems
that it is intended for AC mains voltages, but I couldn't find anything that
says a 24VAC input is exempt from this test.  I am looking for outside
opinions on whether this test is truly applicable.

Thanks,
Jennifer Banh

BTW, we already tried just testing to the spec, and failed.  Any suggestions
on how to protect against this test would also be appreciated.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server..

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: surges on 24VAC

2001-12-21 Thread Mavis, Robert


The AC Mains test is just that AC Mains. The Definition of AC mains is
basically what comes out of the wall. Since the product is 24VAC it falls
under low voltage/signal lines. Test is as a signal line.

-Original Message-
From: Jennifer Banh [mailto:jb...@bb-elec.com]
Sent: Monday, December 17, 2001 11:44 AM
To: emc-p...@majordomo.ieee.org
Subject: surges on 24VAC



Hello everyone,
I am currently trying to test a product of ours that falls under
50082-1
generic standard for light industrial equipment.  Our problem is that we
have a 24VAC power input port.  The generic standard calls out for EN
61000-4-5 on AC power input ports.  After looking at EN 61000-4-5 it seems
that it is intended for AC mains voltages, but I couldn't find anything that
says a 24VAC input is exempt from this test.  I am looking for outside
opinions on whether this test is truly applicable.

Thanks,
Jennifer Banh

BTW, we already tried just testing to the spec, and failed.  Any suggestions
on how to protect against this test would also be appreciated.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: surges on 24VAC

2001-12-18 Thread Gary McInturff

Blush you appear correct. Availability error I guess. The most available 
situation to my mind was my own recent DC situation. Actually, it makes this a 
even more intersting question. I apologize if I confused anyone
Gary

-Original Message-
From: Yow, Steve (IndSys, GEFanuc, NA) [mailto:steve@gefanuc.com]
Sent: Tuesday, December 18, 2001 8:19 AM
To: emc-p...@majordomo.ieee.org
Subject: RE: surges on 24VAC



It seems all the answers are for DC power. I thought the question was for
24V AC.  At least that is how it read in the subject..
 
Any changes to the comments.

-Original Message-
From: Michael Taylor [mailto:mtay...@hach.com]
Sent: Tuesday, December 18, 2001 9:34 AM
To: 'KC CHAN [PDD]'; jb...@bb-elec.com; emc-p...@majordomo.ieee.org
Subject: RE: surges on 24VAC



As a matter of policy my company tests DC ports to the appropriate levels on
all products where we do not supply the external DC Power Supply. As we
cannot guarantee the quality of the DC power supply the customer will use or
the installation, we assume the worst.  In this instance you would be
relying on a DC supply you know nothing about to protect your product from
transients. It's simply a matter of "Do you want to be known as a supplier
of products that work ALL THE TIME - or SOME of the time.

Occasionally you have to remind the marketing department of the cost of poor
quality.  While it may cost a dollar or two to add appropriate protection,
the cost of no protection is much higher in the long run.  Warranty costs
can eat a company alive not to mention the reputation one could acquire for
quality problems.  In my opinion, it's not worth the risk to not test & fix,
where appropriate.  

Just one guy's opinion. 
Regards, 
Michael Taylor 
Colorado 


-Original Message- 
From: KC CHAN [PDD] [ mailto:kcc...@hkpc.org <mailto:kcc...@hkpc.org> ] 
Sent: Monday, December 17, 2001 6:49 PM 
To: jb...@bb-elec.com; emc-p...@majordomo.ieee.org 
Subject: Re: surges on 24VAC 



I am thinking if it is possible to connect the source input to the surge
tester to a DC source, instead of the AC source, then you can apply the
surge tests to the DC input of your product.


>>> "Jennifer Banh"  12/18/01 03:43am >>> 

Hello everyone, 
I am currently trying to test a product of ours that falls under
50082-1 
generic standard for light industrial equipment.  Our problem is that we 
have a 24VAC power input port.  The generic standard calls out for EN 
61000-4-5 on AC power input ports.  After looking at EN 61000-4-5 it seems 
that it is intended for AC mains voltages, but I couldn't find anything that

says a 24VAC input is exempt from this test.  I am looking for outside 
opinions on whether this test is truly applicable. 

Thanks, 
Jennifer Banh 

BTW, we already tried just testing to the spec, and failed.  Any suggestions

on how to protect against this test would also be appreciated. 



--- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
<http://www.ewh.ieee.org/soc/emcs/pstc/>  

To cancel your subscription, send mail to: 
 majord...@ieee.org 
with the single line: 
 unsubscribe emc-pstc 

For help, send mail to the list administrators: 
 Michael Garretson:pstc_ad...@garretson.org 
 Dave Healddavehe...@mediaone.net 

For policy questions, send mail to: 
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at: 
No longer online until our new server is brought online and the old
messages are imported into the new server. 


--- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
<http://www.ewh.ieee.org/soc/emcs/pstc/>  

To cancel your subscription, send mail to: 
 majord...@ieee.org 
with the single line: 
 unsubscribe emc-pstc 

For help, send mail to the list administrators: 
 Michael Garretson:pstc_ad...@garretson.org 
 Dave Healddavehe...@mediaone.net 

For policy questions, send mail to: 
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at: 
No longer online until our new server is brought online and the old
messages are imported into the new server. 


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 ma

RE: surges on 24VAC

2001-12-18 Thread Gary McInturff

I couldn't find a requirement either when I looked under various 
standards that I have to comply with 55024 which calls out the 82-1 
requirements, NEBS and some ETSI standards. I was a little more concerned 
because the equipment I am looking at is actually outdoors so there will be 
copper lines that don't have any primary protection and are as exposed to 
lightning strikes and power cross as are AC supply lines. The lines will be 
feet rather than kilometers for the AC power grid and that is beneficial but 
doesn't solve it all, IMHO. However, I did decide to put transient protection 
on the product regardless of a known requirement to test, but again I am in 
somewhat of an unusual position. Powered by DC but up on a power pole or power 
strand line. If you run across anything that requires the test from any 
direct e-mail please let me know also.
Thanks
Gary

-Original Message-
From: Mike Hopkins [mailto:mhopk...@thermokeytek.com]
Sent: Tuesday, December 18, 2001 6:40 AM
To: 'KC CHAN [PDD]'; jb...@bb-elec.com; emc-p...@majordomo.ieee.org
Subject: RE: surges on 24VAC



Most Surge testers having ac mains couplers will also work with DC power
(some require minor options to work), so actually doing the test is pretty
easy Question as I read it was if it is in fact reasonable

Mike Hopkins
Thermo KeyTek

-Original Message-
From: KC CHAN [PDD] [mailto:kcc...@hkpc.org]
Sent: Monday, December 17, 2001 8:49 PM
To: jb...@bb-elec.com; emc-p...@majordomo.ieee.org
Subject: Re: surges on 24VAC



I am thinking if it is possible to connect the source input to the surge
tester to a DC source, instead of the AC source, then you can apply the
surge tests to the DC input of your product.


>>> "Jennifer Banh"  12/18/01 03:43am >>>

Hello everyone,
I am currently trying to test a product of ours that falls under
50082-1
generic standard for light industrial equipment.  Our problem is that we
have a 24VAC power input port.  The generic standard calls out for EN
61000-4-5 on AC power input ports.  After looking at EN 61000-4-5 it seems
that it is intended for AC mains voltages, but I couldn't find anything that
says a 24VAC input is exempt from this test.  I am looking for outside
opinions on whether this test is truly applicable.

Thanks,
Jennifer Banh

BTW, we already tried just testing to the spec, and failed.  Any suggestions
on how to protect against this test would also be appreciated.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org 
 Dave Healddavehe...@mediaone.net 

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.

---
This mes

Re: surges on 24VAC

2001-12-18 Thread John Woodgate

I read in !emc-pstc that Michael Taylor  wrote (in
) about
'surges on 24VAC', on Tue, 18 Dec 2001:
>As a matter of policy my company tests DC ports to the appropriate levels on
>all products where we do not supply the external DC Power Supply. As we
>cannot guarantee the quality of the DC power supply the customer will use or
>the installation, we assume the worst.  In this instance you would be
>relying on a DC supply you know nothing about to protect your product from
>transients. 

He quite clearly says it's a 24 V AC, not DC, power port.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
After swimming across the Hellespont, I felt like a Hero. 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: surges on 24VAC

2001-12-18 Thread Yow, Steve (IndSys, GEFanuc, NA)

It seems all the answers are for DC power. I thought the question was for
24V AC.  At least that is how it read in the subject..
 
Any changes to the comments.

-Original Message-
From: Michael Taylor [mailto:mtay...@hach.com]
Sent: Tuesday, December 18, 2001 9:34 AM
To: 'KC CHAN [PDD]'; jb...@bb-elec.com; emc-p...@majordomo.ieee.org
Subject: RE: surges on 24VAC



As a matter of policy my company tests DC ports to the appropriate levels on
all products where we do not supply the external DC Power Supply. As we
cannot guarantee the quality of the DC power supply the customer will use or
the installation, we assume the worst.  In this instance you would be
relying on a DC supply you know nothing about to protect your product from
transients. It's simply a matter of "Do you want to be known as a supplier
of products that work ALL THE TIME - or SOME of the time.

Occasionally you have to remind the marketing department of the cost of poor
quality.  While it may cost a dollar or two to add appropriate protection,
the cost of no protection is much higher in the long run.  Warranty costs
can eat a company alive not to mention the reputation one could acquire for
quality problems.  In my opinion, it's not worth the risk to not test & fix,
where appropriate.  

Just one guy's opinion. 
Regards, 
Michael Taylor 
Colorado 


-Original Message- 
From: KC CHAN [PDD] [ mailto:kcc...@hkpc.org <mailto:kcc...@hkpc.org> ] 
Sent: Monday, December 17, 2001 6:49 PM 
To: jb...@bb-elec.com; emc-p...@majordomo.ieee.org 
Subject: Re: surges on 24VAC 



I am thinking if it is possible to connect the source input to the surge
tester to a DC source, instead of the AC source, then you can apply the
surge tests to the DC input of your product.


>>> "Jennifer Banh"  12/18/01 03:43am >>> 

Hello everyone, 
I am currently trying to test a product of ours that falls under
50082-1 
generic standard for light industrial equipment.  Our problem is that we 
have a 24VAC power input port.  The generic standard calls out for EN 
61000-4-5 on AC power input ports.  After looking at EN 61000-4-5 it seems 
that it is intended for AC mains voltages, but I couldn't find anything that

says a 24VAC input is exempt from this test.  I am looking for outside 
opinions on whether this test is truly applicable. 

Thanks, 
Jennifer Banh 

BTW, we already tried just testing to the spec, and failed.  Any suggestions

on how to protect against this test would also be appreciated. 



--- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
<http://www.ewh.ieee.org/soc/emcs/pstc/>  

To cancel your subscription, send mail to: 
 majord...@ieee.org 
with the single line: 
 unsubscribe emc-pstc 

For help, send mail to the list administrators: 
 Michael Garretson:pstc_ad...@garretson.org 
 Dave Healddavehe...@mediaone.net 

For policy questions, send mail to: 
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at: 
No longer online until our new server is brought online and the old
messages are imported into the new server. 


--- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
<http://www.ewh.ieee.org/soc/emcs/pstc/>  

To cancel your subscription, send mail to: 
 majord...@ieee.org 
with the single line: 
 unsubscribe emc-pstc 

For help, send mail to the list administrators: 
 Michael Garretson:pstc_ad...@garretson.org 
 Dave Healddavehe...@mediaone.net 

For policy questions, send mail to: 
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at: 
No longer online until our new server is brought online and the old
messages are imported into the new server. 


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer 

RE: surges on 24VAC

2001-12-18 Thread Mike Hopkins

Most Surge testers having ac mains couplers will also work with DC power
(some require minor options to work), so actually doing the test is pretty
easy Question as I read it was if it is in fact reasonable

Mike Hopkins
Thermo KeyTek

-Original Message-
From: KC CHAN [PDD] [mailto:kcc...@hkpc.org]
Sent: Monday, December 17, 2001 8:49 PM
To: jb...@bb-elec.com; emc-p...@majordomo.ieee.org
Subject: Re: surges on 24VAC



I am thinking if it is possible to connect the source input to the surge
tester to a DC source, instead of the AC source, then you can apply the
surge tests to the DC input of your product.


>>> "Jennifer Banh"  12/18/01 03:43am >>>

Hello everyone,
I am currently trying to test a product of ours that falls under
50082-1
generic standard for light industrial equipment.  Our problem is that we
have a 24VAC power input port.  The generic standard calls out for EN
61000-4-5 on AC power input ports.  After looking at EN 61000-4-5 it seems
that it is intended for AC mains voltages, but I couldn't find anything that
says a 24VAC input is exempt from this test.  I am looking for outside
opinions on whether this test is truly applicable.

Thanks,
Jennifer Banh

BTW, we already tried just testing to the spec, and failed.  Any suggestions
on how to protect against this test would also be appreciated.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org 
 Dave Healddavehe...@mediaone.net 

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: surges on 24VAC

2001-12-18 Thread Michael Taylor
As a matter of policy my company tests DC ports to the appropriate levels on
all products where we do not supply the external DC Power Supply. As we
cannot guarantee the quality of the DC power supply the customer will use or
the installation, we assume the worst.  In this instance you would be
relying on a DC supply you know nothing about to protect your product from
transients. It's simply a matter of "Do you want to be known as a supplier
of products that work ALL THE TIME - or SOME of the time.

Occasionally you have to remind the marketing department of the cost of poor
quality.  While it may cost a dollar or two to add appropriate protection,
the cost of no protection is much higher in the long run.  Warranty costs
can eat a company alive not to mention the reputation one could acquire for
quality problems.  In my opinion, it's not worth the risk to not test & fix,
where appropriate.  

Just one guy's opinion.
Regards, 
Michael Taylor
Colorado


-Original Message-
From: KC CHAN [PDD] [mailto:kcc...@hkpc.org]
Sent: Monday, December 17, 2001 6:49 PM
To: jb...@bb-elec.com; emc-p...@majordomo.ieee.org
Subject: Re: surges on 24VAC



I am thinking if it is possible to connect the source input to the surge
tester to a DC source, instead of the AC source, then you can apply the
surge tests to the DC input of your product.


>>> "Jennifer Banh"  12/18/01 03:43am >>>

Hello everyone,
I am currently trying to test a product of ours that falls under
50082-1
generic standard for light industrial equipment.  Our problem is that we
have a 24VAC power input port.  The generic standard calls out for EN
61000-4-5 on AC power input ports.  After looking at EN 61000-4-5 it seems
that it is intended for AC mains voltages, but I couldn't find anything that
says a 24VAC input is exempt from this test.  I am looking for outside
opinions on whether this test is truly applicable.

Thanks,
Jennifer Banh

BTW, we already tried just testing to the spec, and failed.  Any suggestions
on how to protect against this test would also be appreciated.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org 
 Dave Healddavehe...@mediaone.net 

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.


Re: surges on 24VAC

2001-12-18 Thread Enci

Hi Jennifer, 

I would argue that the test should not be applied that port, simply because
that port is fed from a 24V supply upstream. It is perfectly reasonable to
specify in the product documentation that the supply upstream must meet the
requirements. Why make the compliance process more onerous?

Furthermore, Annex A, and  Annex B of EN61000-4-5, recognises a product
such as yours by allowing you to specify the installation classification,
e.g. Class 0, look at Table A.1 and all the tests are not applicable.

Regards, 
Enci



At 13:43 17/12/01 -0600, you wrote:
>
>Hello everyone,
>   I am currently trying to test a product of ours that falls under 50082-1
>generic standard for light industrial equipment.  Our problem is that we
>have a 24VAC power input port.  The generic standard calls out for EN
>61000-4-5 on AC power input ports.  After looking at EN 61000-4-5 it seems
>that it is intended for AC mains voltages, but I couldn't find anything that
>says a 24VAC input is exempt from this test.  I am looking for outside
>opinions on whether this test is truly applicable.
>
>Thanks,
>Jennifer Banh
>
>BTW, we already tried just testing to the spec, and failed.  Any suggestions
>on how to protect against this test would also be appreciated.
>
>
>
>---
>This message is from the IEEE EMC Society Product Safety
>Technical Committee emc-pstc discussion list.
>
>Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
>
>To cancel your subscription, send mail to:
> majord...@ieee.org
>with the single line:
> unsubscribe emc-pstc
>
>For help, send mail to the list administrators:
> Michael Garretson:pstc_ad...@garretson.org
> Dave Healddavehe...@mediaone.net
>
>For policy questions, send mail to:
> Richard Nute:   ri...@ieee.org
> Jim Bacher: j.bac...@ieee.org
>
>All emc-pstc postings are archived and searchable on the web at:
>No longer online until our new server is brought online and the old
messages are imported into the new server.
>
>


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: surges on 24VAC

2001-12-18 Thread Lfresearch

Jennifer,
I have instructed those clients I deal with to test the input as follows:

Get a transformer thats typical for your unit, and apply the surge to the 
input of it. Keep the leads short.

By doing this you have made an attempt to met the standard. And, yes I know 
it's not perfect, but it beats doing nothing

Derek.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: surges on 24VAC

2001-12-18 Thread KC CHAN [PDD]

I am thinking if it is possible to connect the source input to the surge tester 
to a DC source, instead of the AC source, then you can apply the surge tests to 
the DC input of your product.


>>> "Jennifer Banh"  12/18/01 03:43am >>>

Hello everyone,
I am currently trying to test a product of ours that falls under 50082-1
generic standard for light industrial equipment.  Our problem is that we
have a 24VAC power input port.  The generic standard calls out for EN
61000-4-5 on AC power input ports.  After looking at EN 61000-4-5 it seems
that it is intended for AC mains voltages, but I couldn't find anything that
says a 24VAC input is exempt from this test.  I am looking for outside
opinions on whether this test is truly applicable.

Thanks,
Jennifer Banh

BTW, we already tried just testing to the spec, and failed.  Any suggestions
on how to protect against this test would also be appreciated.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org 
 Dave Healddavehe...@mediaone.net 

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: surges on 24VAC

2001-12-17 Thread John Woodgate

I read in !emc-pstc that Jennifer Banh  wrote (in
) about 'surges on
24VAC', on Mon, 17 Dec 2001:
>I am currently trying to test a product of ours that falls under 50082-1
>generic standard for light industrial equipment.  

If this is a new product, you should be using EN61000-6-1. Look at
clause 8. It is indeed not reasonable to apply the mains surge test to a
24 V power port. 

Make sure you explain this fully in your technical file.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
After swimming across the Hellespont, I felt like a Hero. 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: surges on 24VAC

2001-12-17 Thread Mike Hopkins

The surge test in 61000-4-5 is for testing for the effects of a lightning
remnants getting into the mains or an I-O/Telecom line. Some product
committees require surge tests to any power port, regardless of the source
of that power, but it seems to me that unless the 24V power is from a
distributed DC system coming from outside a structure where a lightning
remnant could get in, lightning testing doesn't make much sense. We it WOULD
make sense is to unit that converts the AC into 24V!.

It seems there are such things as distributed DC systems (i.e. the telephone
system in the US is a 48V DC system bring DC into homes and buildings from
wires strung on telephone poles) and for these systems, lightning testing
might make sense -- hence no provision in the standard that makes DC systems
exempt from testing.

Hope this is helpful...

Mike Hopkins
Thermo KeyTek

-Original Message-
From: Jennifer Banh [mailto:jb...@bb-elec.com]
Sent: Monday, December 17, 2001 2:44 PM
To: emc-p...@majordomo.ieee.org
Subject: surges on 24VAC



Hello everyone,
I am currently trying to test a product of ours that falls under
50082-1
generic standard for light industrial equipment.  Our problem is that we
have a 24VAC power input port.  The generic standard calls out for EN
61000-4-5 on AC power input ports.  After looking at EN 61000-4-5 it seems
that it is intended for AC mains voltages, but I couldn't find anything that
says a 24VAC input is exempt from this test.  I am looking for outside
opinions on whether this test is truly applicable.

Thanks,
Jennifer Banh

BTW, we already tried just testing to the spec, and failed.  Any suggestions
on how to protect against this test would also be appreciated.



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.