Re: voltage on Neutral line, Measurements From Chile

1999-06-30 Thread Patrick Lawler

Wow!  What kind of three-phase power is this - delta or wye?
Is this an example of the neutral conductor not being grounded, and just being
a tap on a transformer? 


On Mon, 28 Jun 1999 17:10:42 -0700, Donald Kimball dkimb...@qualcomm.com
wrote:
At 12:08 AM 6/29/99 -0700, mvald...@netvision.net.il wrote:
What voltages can I expect on the Neutral (referenced to ground) line in 
various countries 
and connection systems? Is there a limit on how high the voltage may be, 
both in normal and 
fault conditions?

Some of our Cellular base stations are located in regions of Chile where power 
is being intentionally turned off due to low water conditions at 
hydro-electric plants. We have been montoring the voltage at these sites due 
to concerns about the battery backup system. The cell sites use 380V Line to 
Line, 220V Line to Neutral, 3-Phase power. During restoration of power, the 
voltage on neutral sometimes rises to 220V Line to Ground for several cycles. 
The voltage on the phases has been measured as great as 440V Line to Line for 
several cycles, with Line to Neutral voltages as high as 380V.  There does not 
seem to be much power available during this transition time with the wild 
voltages. 

Preliminary measurements in Brazil are showing some of the same results. The 
load regulation at remote sites seems to be a problem. 

Don Kimball



thanks in advance,
Moshe

Name: moshe valdman
E-mail: mvald...@netvision.net.il
Phone: 972-54-881334
Telefax: 972-3-5496369
Date: 29/6/99
Time: 0:08:41

--
Patrick Lawler
plaw...@west.net

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: voltage on Neutral line

1999-06-29 Thread Rich Nute




Hi Moshe:


The voltage of the neutral with respect to the ground wire
is a function of its resistance and its current:

E  =  I * R

Maximum normal current is the rating of the fuse or circuit-
breaker protecting that particular circuit.  For a 120-volt
circuit in the USA and Canada, the current would be either
15 or 20 amperes.

The resistance is a function of the wire cross-sectional 
area and its length.

According to a licensed electrical engineer colleague, circuits 
in the USA are designed for a maximum 6% voltage drop, preferably 
3% voltage drop at the load.  This means that the voltage drop
across the neutral from the load to the distribution transformer
is 3% maximum, 1.5% preferable.

So, the resistance is selected according to maximum voltage 
drop at the circuit rating.

The answer to your question is that the neutral voltage varies
from zero to 1.5% nominal, 3% maximum, of the supply voltage 
depending on load.  

It further varies with the distance of the point of interest
from the point where the neutral is grounded.  If the point of
interest is within a few feet of the point where the neutral is
grounded, then the neutral voltage will be a fraction of a 
percent.  If the point of interest is near the maximum distance
from the grounding point, and if the load is also at that point,
then the neutral voltage will approach 1.5% nominal to 3% 
maximum.

Fault current is a function of time.  Overcurrent devices will 
operate according to their time-current curves.  So, if you 
know the fault current, then you can calculate the voltage at
any point along the neutral according to where the fault 
current is introduced and where the neutral is grounded.  
Fault current exists only for the period of time it takes to
operate the overcurrent device (I-T curve).

For a 120-volt system, you can expect about 1.8 volts drop 
nominal, 3.6 volts maximum, assuming a single, maximum load 
furthest from the point of grounding, and your measurement is
also at that point.


Best regards,
Rich



-
 Richard Nute  Product Safety Engineer
 Hewlett-Packard Company   Product Regulations Group 
 AiO Division  Tel   :   +1 858 655 3329 
 16399 West Bernardo Drive FAX   :   +1 858 655 4979 
 San Diego, California 92127   e-mail:  ri...@sdd.hp.com 
-






-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: voltage on Neutral line, Measurements From Chile

1999-06-29 Thread Donald Kimball

At 12:08 AM 6/29/99 -0700, mvald...@netvision.net.il wrote:

Hello everyone,

What voltages can I expect on the Neutral (referenced to ground) line in 
various countries 
and connection systems? Is there a limit on how high the voltage may be, 
both in normal and 
fault conditions?

Some of our Cellular base stations are located in regions of Chile where power 
is being intentionally turned off due to low water conditions at hydro-electric 
plants. We have been montoring the voltage at these sites due to concerns about 
the battery backup system. The cell sites use 380V Line to Line, 220V Line to 
Neutral, 3-Phase power. During restoration of power, the voltage on neutral 
sometimes rises to 220V Line to Ground for several cycles. The voltage on the 
phases has been measured as great as 440V Line to Line for several cycles, with 
Line to Neutral voltages as high as 380V.  There does not seem to be much power 
available during this transition time with the wild voltages. 

Preliminary measurements in Brazil are showing some of the same results. The 
load regulation at remote sites seems to be a problem. 

Don Kimball



thanks in advance,
Moshe

Name: moshe valdman
E-mail: mvald...@netvision.net.il
Phone: 972-54-881334
Telefax: 972-3-5496369
Date: 29/6/99
Time: 0:08:41



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).





-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: voltage on Neutral line

1999-06-29 Thread jrbarnes

What voltages can I expect on the Neutral (referenced to ground) line in
various countries
and connection systems? Is there a limit on how high the voltage may be, both
in normal and
fault conditions?

Moshe,
THE's booklet, World Electricity Supplies, lists the supply voltage,
frequency, and power distribution systems used in over 200 countries.  You can
order it through Technical Standards Services, Ltd. webpage at
http://www.techstandards.co.uk/thsguide.html

TN and TT power systems (IEC 950  1.2.12.1 and 1.2.12.2) are the ones
usually encountered.  Neutral-to-ground voltages should be less than a few (5 or
so) volts even under a line-to-ground fault.  Hospitals and other
high-reliability installations sometimes use IT power systems (IEC 950
1.2.12.3) permitting continued operation even if a line-to-ground fault occurs--
at the cost of:
*  Neutral-to-ground voltage approaching the single-phase line voltage.
*  In a three-phase system, the other phase-to-ground voltages approaching
sqrt(3) times the single-phase line voltage.

This can double the required creepage and clearance distances for (to us) a tiny
additional market.  So we specify that our products are not to be installed on
IT power systems, but may be powered by an isolation transformer that gets its
power from an IT power system  to create a local TN-S power system.
John Barnes   Advisory
Engineer
Lexmark International



-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



voltage on Neutral line

1999-06-28 Thread mvaldman

Hello everyone,

What voltages can I expect on the Neutral (referenced to ground) line in 
various countries 
and connection systems? Is there a limit on how high the voltage may be, both 
in normal and 
fault conditions?

thanks in advance,
Moshe

Name: moshe valdman
E-mail: mvald...@netvision.net.il
Phone: 972-54-881334
Telefax: 972-3-5496369
List-Post: emc-pstc@listserv.ieee.org
Date: 29/6/99
Time: 0:08:41



-