On Wednesday 24 February 2021 17:41:25 Alan Condit wrote:

> > From: "Peter C. Wallace" 
> > Subject: Re: [Emc-users] 7i76 spindle speed control with Cyclotrol
> > C150 Controller Date: February 23, 2021 at 11:01:44 AM CST
> > To: Alan Condit 
> > Cc: "Emc-users@lists.sourceforge.net"
> > 
> >
> > On Tue, 23 Feb 2021, Alan Condit wrote:
> >> Date: Tue, 23 Feb 2021 10:53:26 -0600
> >> From: Alan Condit 
> >> To: "Emc-users@lists.sourceforge.net"
> >> , Wallace Peter C.
> >> 
> >> Subject: 7i76 spindle speed control with Cyclotrol C150 Controller
> >>
> >> PCW,
> >>
> >> I am trying to use my 7i76 Mesa card�s spindle control to control
> >> the speed on my DanFoss Cyclotrol C150 controller. The manual says,
> >>
> >>> "PROCESS CONTROL SIGNALS
> >>> A 0-10v dc control signal input may be used by connecting process
> >>> signal(+) to SP2 and process(-) to SP3. With tachometer feedback,
> >>> the motor speed will track the process voltage to better than 1 %
> >>> linearity. The input impedance is approx. 50K ohms. Current
> >>> process signals may be used with an additional resistor. A 1-5 mA
> >>> signal can be accommodated by shunting SP2 and SP3 with a 2.0K
> >>> ohms, 1 /2 watt resistor; for 4-20 mA, use a 500 ohms , 1 /2 watt.
> >>> Set the "P" switch in the closed (up) position, to allow the
> >>> Cycletrol 150 to operate with current process signals.�
> >>>
> >>> OPEN SWITCHES (DOWN)
> >>> "A�, �B�, �C�, �D"
> >>> BASIC SPEED CONTROL
> >>> Control RUNS/STOPS from a single input command.
> >>> Closure on JOG puts Cycletrol into a RUN mode.
> >>> Opening the JOG produces a STOP command.
> >>
> >> I am not sure if SP1 should connect to Spindle+ or Spindle-. I am
> >> pretty sure SP2 should be SpindleOut. SP3 should connect to either
> >> Spindle- or Spindle+ which ever is left open after connecting SP1.
> >> Can anyone tell from the info I have furnished what the correct
> >> wiring should be. I am leaning towards Spindle- to SP3, SpindleOut
> >> to SP2 and Spindle+ to SP1. If I guess wrong will it damage the
> >> 7i76 board?
> >>
> >> The full manual is at
> >> <https://www.grahammotorandcontrols.com/pdf/Cycletrol%20C150%20DC%2
> >>0Instruction%20Manual.pdf
> >> <https://www.grahammotorandcontrols.com/pdf/Cycletrol%20C150%20DC%2
> >>0Instruction%20Manual.pdf>>
> >>
> >>
> >> Thanks,
> >> Alan
> >
> > As long as the voltage at SP1 is less than 15V, (relative to SP3)
> > you should be OK with
> >
> > SP1 --> SPIN+
> > SP2 --> SPINOUT
> > SP3 --> SPIN-
> >
> > Peter Wallace
> > Mesa Electronics
>
> Peter,
>
>
>
> I don’t know what was going on yesterday with the spindle brake. This
> morning  I disconnected the SPINDLE ENA from the JOG and COM and
> reconnected the external switch in the original configuration and the
> spindle brake was working again. Then I reconnected the external
> switch in the same configuration as I had with the Mesa SPINDLE ENA
> pair and the spindle brake still worked. So I reconnected the SPINDLE
> ENA+ to JOG and the SPINDLE ENA- to COM(-) and the spindle brake
> continues to work. MYSTERY!
>
> It seems to bring the spindle to a stop from 500rpm in about a quarter
> rotation of the spindle (the specs say a maximum of ¼ second delay).
>
> So now I need to see if I can get a sample config from someone that
> monitors the spindle  rotation coming to 0 rpm before changing the
> spindle direction, before I install the relay to reverse the spindle
> direction.
>
> Thanks,
> Alan
>
That shouldn't be too difficult. Here I am blocking the dir change, but 
us its detection to switch a mux2 in series with the spindle speed to 
ground the speed signal to a limit3, the outout of which is driving the 
pid. The xor that detected the dir change also starts a timer which is 
watching the encoder a or b leg and when 10 millisecs has expired with 
no new encoder edge, the timer resets with restores the input to the 
limit3 and also allows the dir change to get to the pwmgen, the limit3 
then ramps the motor back tp the requested speed, turning the other 
direction. The pico pwm-servo is a full 4 quadrant controller recovering 
the motor energy as it stops it, running the supply up to an overvoltage 
state for the filter caps stopping the motor but uses that to accell the 
motor 

Re: [Emc-users] 7i76 spindle speed control with Cyclotrol C150 Controller

2021-02-24 Thread Alan Condit
> From: "Peter C. Wallace" 
> Subject: Re: [Emc-users] 7i76 spindle speed control with Cyclotrol C150 
> Controller
> Date: February 23, 2021 at 11:01:44 AM CST
> To: Alan Condit 
> Cc: "Emc-users@lists.sourceforge.net" 
> 
> 
> On Tue, 23 Feb 2021, Alan Condit wrote:
> 
>> Date: Tue, 23 Feb 2021 10:53:26 -0600
>> From: Alan Condit 
>> To: "Emc-users@lists.sourceforge.net" ,
>>Wallace Peter C. 
>> Subject: 7i76 spindle speed control with Cyclotrol C150 Controller
>> 
>> PCW,
>> 
>> I am trying to use my 7i76 Mesa card�s spindle control to control the speed 
>> on my DanFoss Cyclotrol C150 controller. The manual says,
>> 
>>> "PROCESS CONTROL SIGNALS
>>> A 0-10v dc control signal input may be used by connecting process signal(+) 
>>> to SP2 and process(-) to SP3. With tachometer feedback, the motor speed 
>>> will track the process voltage to better than 1 % linearity. The input 
>>> impedance is approx. 50K ohms.
>>> Current process signals may be used with an additional resistor. A 1-5 mA 
>>> signal can be accommodated by shunting SP2 and SP3 with a 2.0K ohms, 1 /2 
>>> watt resistor; for 4-20 mA, use a 500 ohms , 1 /2 watt. Set the "P" switch 
>>> in the closed (up) position, to allow the Cycletrol 150 to operate with 
>>> current process signals.�
>> 
>>> OPEN SWITCHES (DOWN)
>>> "A�, �B�, �C�, �D"
>>> BASIC SPEED CONTROL
>>> Control RUNS/STOPS from a single input command.
>>> Closure on JOG puts Cycletrol into a RUN mode.
>>> Opening the JOG produces a STOP command.
>> 
>> 
>> 
>> 
>> I am not sure if SP1 should connect to Spindle+ or Spindle-. I am pretty 
>> sure SP2 should be SpindleOut. SP3 should connect to either Spindle- or 
>> Spindle+ which ever is left open after connecting SP1. Can anyone tell from 
>> the info I have furnished what the correct wiring should be. I am leaning 
>> towards Spindle- to SP3, SpindleOut to SP2 and Spindle+ to SP1. If I guess 
>> wrong will it damage the 7i76 board?
>> 
>> The full manual is at 
>> <https://www.grahammotorandcontrols.com/pdf/Cycletrol%20C150%20DC%20Instruction%20Manual.pdf
>>  
>> <https://www.grahammotorandcontrols.com/pdf/Cycletrol%20C150%20DC%20Instruction%20Manual.pdf>>
>> 
>> 
>> Thanks,
>> Alan
> 
> As long as the voltage at SP1 is less than 15V, (relative to SP3) you should 
> be OK with
> 
> SP1 --> SPIN+
> SP2 --> SPINOUT
> SP3 --> SPIN-
> 
> Peter Wallace
> Mesa Electronics
> 
> 
Peter,



I don’t know what was going on yesterday with the spindle brake. This morning  
I disconnected the SPINDLE ENA from the JOG and COM and reconnected the 
external switch in the original configuration and the spindle brake was working 
again. Then I reconnected the external switch in the same configuration as I 
had with the Mesa SPINDLE ENA pair and the spindle brake still worked. So I 
reconnected the SPINDLE ENA+ to JOG and the SPINDLE ENA- to COM(-) and the 
spindle brake continues to work. MYSTERY!

It seems to bring the spindle to a stop from 500rpm in about a quarter rotation 
of the spindle (the specs say a maximum of ¼ second delay).

So now I need to see if I can get a sample config from someone that monitors 
the spindle  rotation coming to 0 rpm before changing the spindle direction, 
before I install the relay to reverse the spindle direction.

Thanks,
Alan

> 
> ___
> Emc-users mailing list
> Emc-users@lists.sourceforge.net
> https://lists.sourceforge.net/lists/listinfo/emc-users


___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] 7i76 spindle speed control with Cyclotrol C150 Controller

2021-02-23 Thread Peter C. Wallace

On Tue, 23 Feb 2021, Alan Condit wrote:


Date: Tue, 23 Feb 2021 10:53:26 -0600
From: Alan Condit 
To: "Emc-users@lists.sourceforge.net" ,
Wallace Peter C. 
Subject: 7i76 spindle speed control with Cyclotrol C150 Controller


PCW,

I am trying to use my 7i76 Mesa card??s spindle control to control the speed on 
my DanFoss Cyclotrol C150 controller. The manual says,


"PROCESS CONTROL SIGNALS
A 0-10v dc control signal input may be used by connecting process signal(+) to 
SP2 and process(-) to SP3. With tachometer feedback, the motor speed will track 
the process voltage to better than 1 % linearity. The input impedance is 
approx. 50K ohms.
Current process signals may be used with an additional resistor. A 1-5 mA signal can be 
accommodated by shunting SP2 and SP3 with a 2.0K ohms, 1 /2 watt resistor; for 4-20 mA, 
use a 500 ohms , 1 /2 watt. Set the "P" switch in the closed (up) position, to 
allow the Cycletrol 150 to operate with current process signals.??



OPEN SWITCHES (DOWN)
"A??, ??B??, ??C??, ??D"
BASIC SPEED CONTROL
Control RUNS/STOPS from a single input command.
Closure on JOG puts Cycletrol into a RUN mode.
Opening the JOG produces a STOP command.





I am not sure if SP1 should connect to Spindle+ or Spindle-. I am pretty sure 
SP2 should be SpindleOut. SP3 should connect to either Spindle- or Spindle+ 
which ever is left open after connecting SP1. Can anyone tell from the info I 
have furnished what the correct wiring should be. I am leaning towards Spindle- 
to SP3, SpindleOut to SP2 and Spindle+ to SP1. If I guess wrong will it damage 
the 7i76 board?

The full manual is at 
>


Thanks,
Alan


As long as the voltage at SP1 is less than 15V, (relative to SP3) you should be 
OK with


SP1 --> SPIN+
SP2 --> SPINOUT
SP3 --> SPIN-

Peter Wallace
Mesa Electronics
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


[Emc-users] 7i76 spindle speed control with Cyclotrol C150 Controller

2021-02-23 Thread Alan Condit

PCW,

I am trying to use my 7i76 Mesa card’s spindle control to control the speed on 
my DanFoss Cyclotrol C150 controller. The manual says, 

> "PROCESS CONTROL SIGNALS
> A 0-10v dc control signal input may be used by connecting process signal(+) 
> to SP2 and process(-) to SP3. With tachometer feedback, the motor speed will 
> track the process voltage to better than 1 % linearity. The input impedance 
> is approx. 50K ohms.
> Current process signals may be used with an additional resistor. A 1-5 mA 
> signal can be accommodated by shunting SP2 and SP3 with a 2.0K ohms, 1 /2 
> watt resistor; for 4-20 mA, use a 500 ohms , 1 /2 watt. Set the "P" switch in 
> the closed (up) position, to allow the Cycletrol 150 to operate with current 
> process signals.” 

> OPEN SWITCHES (DOWN) 
> "A”, “B”, “C”, “D" 
> BASIC SPEED CONTROL 
> Control RUNS/STOPS from a single input command. 
> Closure on JOG puts Cycletrol into a RUN mode. 
> Opening the JOG produces a STOP command. 




I am not sure if SP1 should connect to Spindle+ or Spindle-. I am pretty sure 
SP2 should be SpindleOut. SP3 should connect to either Spindle- or Spindle+ 
which ever is left open after connecting SP1. Can anyone tell from the info I 
have furnished what the correct wiring should be. I am leaning towards Spindle- 
to SP3, SpindleOut to SP2 and Spindle+ to SP1. If I guess wrong will it damage 
the 7i76 board?

The full manual is at 
>


Thanks,
Alan