SV: Synchronizing TOD between mainframe and other platforms
There's one very good reason to get file 501: it comes with ets1, a pc program that will connect with your 9037 via RS232, and act as an ETS. This will let you syncronize your mainframe time with anything the pc can be synced with. Regards Frank Brüchmann Scott Rowe wrote: z/OS has had it's own time server for quite some time now, no need to use the CBT version. Angel-Luis Dominguez angel_luis_dominguez_mar...@yahoo.es 8/20/2009 1:06 AM Have a look at FILE 501 from CBT. It is a very simple and effective way to sync every machine, even PC's obtaining directly time from mainframe. -- For IBM-MAIN subscribe / signoff / archive access instructions, send email to lists...@bama.ua.edu with the message: GET IBM-MAIN INFO Search the archives at http://bama.ua.edu/archives/ibm-main.html
Re: Synchronizing TOD between mainframe and other platforms
On Thu, 20 Aug 2009 00:06:39 -0500, Angel-Luis Dominguez wrote: Have a look at FILE 501 from CBT. It is a very simple and effective way to sync every machine, even PC's obtaining directly time from mainframe. There's a struggle here that's as much political as technical. If your IT czar is a partisan of non-mainframe systems, and those systems are now synched to a high-stratum NTP server, you must prove that the mainframe with SNTP is a more accurate reference, else why should they switch? And the README in CBT 501 says: 4) Verify your sysplex timer: - it must be set to UCT (GMT) time with your local offset - be sure it has the correct time and syncs to a good time source regularly. There's no point to having the wrong time. - warning! in case you don't know, NEVER set the 9037, always adjust it. Max adjustment is +/- 5.00 seconds per day. 5) Start the server (S SNTP) - be sure both TCPIP and SNTP have a high enough dispatching priority to provide a consistent response There are obvious hazards here. And the argument that the mainframe must be the reference is self-defeating: If the mainframe won't sync to anything else, what keeps it accurate? -- gil -- For IBM-MAIN subscribe / signoff / archive access instructions, send email to lists...@bama.ua.edu with the message: GET IBM-MAIN INFO Search the archives at http://bama.ua.edu/archives/ibm-main.html
Re: Synchronizing TOD between mainframe and other platforms
It is not possible to have the Sysplex Timer (9037) attach to non-S/390 or zSeries servers. However, there is a way that customers can get the same time across both zSeries and non-zSeries servers in their data center. The 9037 can attach to an External Time Source (ETS), the options are described in the 9037 Model 2 planning manual as well as the Redbook SG24-2070. The 9037 attachment to an ETS supports 3 possible RS-232 protocols. To get the same time across zSeries and non-zSeries, a potential solution is: The customer uses an NTP server that also has the RS-232 protocols supported by the 9037. These NTP servers are available from multiple vendors - one example is the Symmetricom SyncServ S250. http://www.symmetricom.com/products/ntp-servers/ntp-network-appliances/SyncServer-S250/ Input options for these devices includes GPS, IRIG-B and the USA NIST ACTS telephone service. Outputs for this device includes an Ethernet NTP (Network Time Protocol) Time Server as well as the necessary EIA-232 serial time code for the 9037, the former could connect to their non-S390 or non-zSeries servers and the latter to the 9037. This would allow a customer to have the same external time source for both a S/390 or zSeries server and a non-System z server. Note that this does not provide the kind of synchronization that is required in a zSeries or S/390 Parallel Sysplex. However, it will allow the customer to have the enterprise running on the same time standard and therefore coordinate time stamps, etc. The above product is not necessarily the only one that provides this capability. Other Symmetricom models also provide this function, and if you want a second source for your External Time Source that provides similar function please do your own research to find another vendor. Other vendors I am aware of that provide this capability are Meinberg, Spectracom. Noshir Dhondy (dho...@us.ibm.com) -- For IBM-MAIN subscribe / signoff / archive access instructions, send email to lists...@bama.ua.edu with the message: GET IBM-MAIN INFO Search the archives at http://bama.ua.edu/archives/ibm-main.html
Re: Synchronizing TOD between mainframe and other platforms
z/OS has had it's own time server for quite some time now, no need to use the CBT version. Angel-Luis Dominguez angel_luis_dominguez_mar...@yahoo.es 8/20/2009 1:06 AM Have a look at FILE 501 from CBT. It is a very simple and effective way to sync every machine, even PC's obtaining directly time from mainframe. -- For IBM-MAIN subscribe / signoff / archive access instructions, send email to lists...@bama.ua.edu with the message: GET IBM-MAIN INFO Search the archives at http://bama.ua.edu/archives/ibm-main.html CONFIDENTIALITY/EMAIL NOTICE: The material in this transmission contains confidential and privileged information intended only for the addressee. If you are not the intended recipient, please be advised that you have received this material in error and that any forwarding, copying, printing, distribution, use or disclosure of the material is strictly prohibited. If you have received this material in error, please (i) do not read it, (ii) reply to the sender that you received the message in error, and (iii) erase or destroy the material. Emails are not secure and can be intercepted, amended, lost or destroyed, or contain viruses. You are deemed to have accepted these risks if you communicate with us by email. Thank you. -- For IBM-MAIN subscribe / signoff / archive access instructions, send email to lists...@bama.ua.edu with the message: GET IBM-MAIN INFO Search the archives at http://bama.ua.edu/archives/ibm-main.html
Re: Synchronizing TOD between mainframe and other platforms
Hello : I want to unsuscribe for IBM Mainframe Discussion list. Thanks in advance. Regards T-Systems Iberia IT/TC Operations / SL MSY Storage Support Francesc Xavier Martínez Escudero Autovia A2, km.585, 08760 Martorell +34 93 7733351 (Tel.) +34 93 7733176 (Fax) +34 690886041 (Telèfon mòbil) Correu electrònic: franciscojavier.marti...@t-systems.es Internet: http://www.t-systems.es -Mensaje original- De: IBM Mainframe Discussion List [mailto:ibm-m...@bama.ua.edu] En nombre de Noshir Dhondy Enviado el: jueves, 20 de agosto de 2009 14:48 Para: IBM-MAIN@bama.ua.edu Asunto: Re: Synchronizing TOD between mainframe and other platforms It is not possible to have the Sysplex Timer (9037) attach to non-S/390 or zSeries servers. However, there is a way that customers can get the same time across both zSeries and non-zSeries servers in their data center. The 9037 can attach to an External Time Source (ETS), the options are described in the 9037 Model 2 planning manual as well as the Redbook SG24-2070. The 9037 attachment to an ETS supports 3 possible RS-232 protocols. To get the same time across zSeries and non-zSeries, a potential solution is: The customer uses an NTP server that also has the RS-232 protocols supported by the 9037. These NTP servers are available from multiple vendors - one example is the Symmetricom SyncServ S250. http://www.symmetricom.com/products/ntp-servers/ntp-network-appliances/SyncServer-S250/ Input options for these devices includes GPS, IRIG-B and the USA NIST ACTS telephone service. Outputs for this device includes an Ethernet NTP (Network Time Protocol) Time Server as well as the necessary EIA-232 serial time code for the 9037, the former could connect to their non-S390 or non-zSeries servers and the latter to the 9037. This would allow a customer to have the same external time source for both a S/390 or zSeries server and a non-System z server. Note that this does not provide the kind of synchronization that is required in a zSeries or S/390 Parallel Sysplex. However, it will allow the customer to have the enterprise running on the same time standard and therefore coordinate time stamps, etc. The above product is not necessarily the only one that provides this capability. Other Symmetricom models also provide this function, and if you want a second source for your External Time Source that provides similar function please do your own research to find another vendor. Other vendors I am aware of that provide this capability are Meinberg, Spectracom. Noshir Dhondy (dho...@us.ibm.com) -- For IBM-MAIN subscribe / signoff / archive access instructions, send email to lists...@bama.ua.edu with the message: GET IBM-MAIN INFO Search the archives at http://bama.ua.edu/archives/ibm-main.html This e-mail and any attachments may contain confidential or privileged information. Any unauthorized copying, use or distribution of this information is strictly prohibited. -- For IBM-MAIN subscribe / signoff / archive access instructions, send email to lists...@bama.ua.edu with the message: GET IBM-MAIN INFO Search the archives at http://bama.ua.edu/archives/ibm-main.html
Re: Synchronizing TOD between mainframe and other platforms
Then you need to follow the instructions at the bottom of every email! Martinez Escudero, Francisco Javier franciscojavier.marti...@t-systems.es 8/20/2009 9:48 AM Hello : I want to unsuscribe for IBM Mainframe Discussion list. Thanks in advance. Regards T-Systems Iberia IT/TC Operations / SL MSY Storage Support Francesc Xavier Martínez Escudero Autovia A2, km.585, 08760 Martorell +34 93 7733351 (Tel.) +34 93 7733176 (Fax) +34 690886041 (Telèfon mòbil) Correu electrònic: franciscojavier.marti...@t-systems.es Internet: http://www.t-systems.es CONFIDENTIALITY/EMAIL NOTICE: The material in this transmission contains confidential and privileged information intended only for the addressee. If you are not the intended recipient, please be advised that you have received this material in error and that any forwarding, copying, printing, distribution, use or disclosure of the material is strictly prohibited. If you have received this material in error, please (i) do not read it, (ii) reply to the sender that you received the message in error, and (iii) erase or destroy the material. Emails are not secure and can be intercepted, amended, lost or destroyed, or contain viruses. You are deemed to have accepted these risks if you communicate with us by email. Thank you. -- For IBM-MAIN subscribe / signoff / archive access instructions, send email to lists...@bama.ua.edu with the message: GET IBM-MAIN INFO Search the archives at http://bama.ua.edu/archives/ibm-main.html
Re: Synchronizing TOD between mainframe and other platforms
In a message dated 8/20/2009 9:03:59 A.M. Central Daylight Time, franciscojavier.marti...@t-systems.es writes: I want to unsuscribe for IBM Mainframe Discussion list. Read the bottom three lines of any post. -- For IBM-MAIN subscribe / signoff / archive access instructions, send email to lists...@bama.ua.edu with the message: GET IBM-MAIN INFO Search the archives at http://bama.ua.edu/archives/ibm-main.html
Synchronizing TOD between mainframe and other platforms
We currently have 2 z900 that is running in a Sysplex. We do have 2 9037-002 connected. We need to synchronise the TOD of our Z900 with the other platforms. All the other platforms currently obtain their time from a SUN Server that receives it's time from a ETS on the WWW. We are investigating using the Z900 as the time source, but it will still have to be connected to a ETS. The other option will be to obtain the time from the SUN Server. I have been reading on the forums and through the 9037 Redbooks, but it appears to me that I can't connect my 9037 in any way to the SUN server, even using a PC as a intermediatry source. Am I correct ? Is anyone connecting their 9037 to a AIX or Sun Server to obtain the TOD? We can't exploit STP because of the limitations of our hardware. We are currently running z/OS 1.9 Any feedback will be much appreciated Regards Jaco -- For IBM-MAIN subscribe / signoff / archive access instructions, send email to lists...@bama.ua.edu with the message: GET IBM-MAIN INFO Search the archives at http://bama.ua.edu/archives/ibm-main.html
Re: Synchronizing TOD between mainframe and other platforms
On Wed, 19 Aug 2009 05:23:54 -0500, Jaco Kruger wrote: I have been reading on the forums and through the 9037 Redbooks, but it appears to me that I can't connect my 9037 in any way to the SUN server, even using a PC as a intermediatry source. Am I correct ? I believe in one of mode its modes of operation, the 9037 will dial out to a time server such as NIST. If the 9037 is connected via a null modem to the intermediary PC, the PC should be able to intercept the dial out command and simulate the responses of time server. SMOP. -- gil -- For IBM-MAIN subscribe / signoff / archive access instructions, send email to lists...@bama.ua.edu with the message: GET IBM-MAIN INFO Search the archives at http://bama.ua.edu/archives/ibm-main.html
Re: Synchronizing TOD between mainframe and other platforms
Have a look at FILE 501 from CBT. It is a very simple and effective way to sync every machine, even PC's obtaining directly time from mainframe. -- For IBM-MAIN subscribe / signoff / archive access instructions, send email to lists...@bama.ua.edu with the message: GET IBM-MAIN INFO Search the archives at http://bama.ua.edu/archives/ibm-main.html